How To Tie Two 200 amp Panels Together


this thread has 20 replies and has been viewed 5388 times

Reply
 
Thread Tools Display Modes
  #1  
Old 05-07-2012, 08:50 AM
Slick 50 Slick 50 is offline
Registered-II
 
Join Date: Aug 2010
Location: Texas
Posts: 217
Thanks: 55
Thanked 47 Times in 41 Posts
Default How To Tie Two 200 amp Panels Together

I am wanting to tie two 200 amp single phase panels together on the load side. Both panels are fed from a single meter. My thoughts are to use number 2 wire to each panel with a breaker at each end in the panel.
Is there any problem with doing this to tie the panels together?
Thanks for any help.
Rick
Reply With Quote
Sponsored Links
  #2  
Old 05-07-2012, 09:27 AM
Gary Bahre Gary Bahre is offline
Subscriber
 
Join Date: Oct 2004
Location: Sparta, Illinois, USA
Posts: 336
Thanks: 2,287
Thanked 1,704 Times in 193 Posts
Default Re: How To Tie Two Panels Together

Slick; In the area that I live in the power co. uses a 320 amp service, this feeds 2, 200 amp box's from one meter. Check with your power supplier to see what box's and other things you need to do this. Gary
Reply With Quote
The Following User Says Thank You to Gary Bahre:
  #3  
Old 05-07-2012, 10:57 AM
Slick 50 Slick 50 is offline
Registered-II
 
Join Date: Aug 2010
Location: Texas
Posts: 217
Thanks: 55
Thanked 47 Times in 41 Posts
Default Re: How To Tie Two Panels Together

Thanks Gary,
The panels are already in and wired. They are Square D QO panels. Hoping to prove or disprove my thoughts about phasing. Does it matter what leg is tied to a particular bus bar? I'm thinking it does but not sure.
Thanks,
Rick
Reply With Quote
  #4  
Old 05-07-2012, 12:24 PM
Power Power is offline
Registered-III
 
Join Date: Aug 2011
Location: New Jersey
Posts: 2,788
Thanks: 673
Thanked 1,446 Times in 912 Posts
Default Re: How To Tie Two Panels Together

Why do you want to do this?
Violates national electric code.
Will not be approved by AHJ.
You would have 2 feeds into a panel @200 amps each - in excess of manufacturer's ratings for panel
You would have 2 disconnects- one top, one bottom
When something goes wrong, insurer will not cover it.
Reply With Quote
  #5  
Old 05-07-2012, 03:06 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,084
Thanks: 42
Thanked 1,106 Times in 882 Posts
Default Re: How To Tie Two 200 amp Panels Together

If all you want to do is experiment that when you connect one "phase" to the other "phase", you do indeed have a short circuit, go ahead.

You can do the same thing from any 2 pole breaker in each box, no need to do it with expensive 200 amp breakers. Take a volt meter, test the two breakers respective terminals and when you find the ones that test 0 volts between them, those are in phase, If you test two poles and get 240 volts, those are out of phase. Confirm that each breaker is indeed turned ON by testing voltage to neutral after you test voltage between the two breakers.

With single phase panels, no it doesn't matter which line is connected to which bus bar. If it was a 3 phase panel, then I could see that it might be nice to have phaser rotation be A, B, C in both panels. However, this would not necessarily be the same phases to the same bus bars. Could be, but not necessarily the same. A,B,C is the same as C,A,B or B,C,A but is opposite of C,B,A etc...
Reply With Quote
The Following User Says Thank You to Jim Rankin:
  #6  
Old 05-07-2012, 03:33 PM
Slick 50 Slick 50 is offline
Registered-II
 
Join Date: Aug 2010
Location: Texas
Posts: 217
Thanks: 55
Thanked 47 Times in 41 Posts
Default Re: How To Tie Two 200 amp Panels Together

Jim,
Thank you so much for the response. The tie wire between panels is actually number 4, memory not always so good. As mentioned, on each end of that wire will be breakers, in this case, 90 amp. I had planned on checking continuity from the meter to each leg on the tie for proper line up before energizing. We are still about a month away from powering up the house.
Thanks again,
Rick
Reply With Quote
  #7  
Old 05-07-2012, 05:03 PM
grif grif is offline
Registered-III
 
Join Date: Oct 2011
Location: Yakima, Washington
Posts: 640
Thanks: 141
Thanked 139 Times in 108 Posts
Default Re: How To Tie Two 200 amp Panels Together

Was your phasing question whether or not you had three phase available? Or if you really just had two panels of center tapped 240 single phase?
Reply With Quote
  #8  
Old 05-07-2012, 05:22 PM
Slick 50 Slick 50 is offline
Registered-II
 
Join Date: Aug 2010
Location: Texas
Posts: 217
Thanks: 55
Thanked 47 Times in 41 Posts
Default Re: How To Tie Two 200 amp Panels Together

The question was about single phase 240 volt only. The limit with 42 spaces per panel is what got me, needed a few more spaces. It's all about powering the panels with a generator and the main feed opened with a disconnect.

Thanks for the quick help, very much appreciated.
Rick
Reply With Quote
  #9  
Old 05-07-2012, 05:58 PM
davidradio davidradio is offline
Registered-I
 
Join Date: Jan 2009
Location: sycamore ill usa
Posts: 53
Thanks: 1
Thanked 24 Times in 15 Posts
Default Re: How To Tie Two 200 amp Panels Together

i would not do this both mains have to be off to prevent feed back to line

i would only use two 200 amp tranfer switches only that way
there can be no feed back if mains are left on

one other option would be to put an inter lock in both panels
from interlock.com that way there will be no feed back to power line

and if power is restored
with main on you will have a mess burnt up generator and possible
fire in house and insurance will not cover this as voliation of nec
big time
Reply With Quote
  #10  
Old 05-07-2012, 05:59 PM
grif grif is offline
Registered-III
 
Join Date: Oct 2011
Location: Yakima, Washington
Posts: 640
Thanks: 141
Thanked 139 Times in 108 Posts
Default Re: How To Tie Two 200 amp Panels Together

Sounds like the same configuration I've got, except I've got lots of slots left, my issue is the two panels are 100 feet apart. I've about decided to put the jolly green giant transfer switch right at my side of the meter, and I've got critical load on each panel. (poor planning on my part).
Reply With Quote
  #11  
Old 05-07-2012, 06:09 PM
jht1057 jht1057 is offline
Registered-III
 
Join Date: Oct 2007
Location: Millerstown, PA
Posts: 684
Thanks: 1,374
Thanked 513 Times in 203 Posts
Default Re: How To Tie Two 200 amp Panels Together

Slick,

You can tie panels together and it is approved by code.
The panel that the meter feeds would be the "main" panel, the second panel would be the "sub" panel.

When wiring mains to the bus bars, I always kept the white on the right.

Jim
Reply With Quote
The Following User Says Thank You to jht1057:
  #12  
Old 05-07-2012, 07:13 PM
Power Power is offline
Registered-III
 
Join Date: Aug 2011
Location: New Jersey
Posts: 2,788
Thanks: 673
Thanked 1,446 Times in 912 Posts
Default Re: How To Tie Two 200 amp Panels Together

You can tie panels together and it is approved by code.
The panel that the meter feeds would be the "main" panel, the second panel would be the "sub" panel.

That's ok, but then the most amperage available is the rating of the main panel breaker - 200 amps. Also, there are restrictions on the size of sub panel breaker. It cannot equal main.
Reply With Quote
  #13  
Old 05-07-2012, 07:21 PM
Tencubed Tencubed is offline
Registered-II
 
Join Date: Jan 2012
Location: Centerville, Washington
Posts: 107
Thanks: 211
Thanked 94 Times in 44 Posts
Default Re: How To Tie Two 200 amp Panels Together

Sounds to me like it's Jerry Rig time on this project.

Your home owners insurance and a lot of other problems can get involved really quick.

I'd sure suggest you get a licensed electrician to take a look at your project and give you the advice you are seeking.

Just my opinion of course but what any of us say about your project is worth every dime you're paying for it.

Mike
Reply With Quote
  #14  
Old 05-07-2012, 07:34 PM
Graycenphil Graycenphil is offline
Subscriber
 
Join Date: Sep 2011
Location: Eastford, Connecticut
Posts: 544
Thanks: 419
Thanked 101 Times in 79 Posts
Default Re: How To Tie Two 200 amp Panels Together

Quote:
Originally Posted by Slick 50 View Post
The question was about single phase 240 volt only. The limit with 42 spaces per panel is what got me, needed a few more spaces. It's all about powering the panels with a generator and the main feed opened with a disconnect.

Thanks for the quick help, very much appreciated.
Rick
If all you need are a few more spaces for circuit breakers, can't you just use a few piggyback breakers? Or as someone suggested, add a subpanel for a few extra circuits.
Reply With Quote
  #15  
Old 05-07-2012, 08:09 PM
Craig Mattson Craig Mattson is offline
Registered-I
 
Join Date: May 2009
Location: Lake Park, MN, USA
Posts: 34
Thanks: 14
Thanked 11 Times in 6 Posts
Default Re: How To Tie Two 200 amp Panels Together

I would suggest the piggyback sub panel method. I have done it both ways much easier to get the inspector to ok it that way. Good luck
Reply With Quote
  #16  
Old 05-07-2012, 08:59 PM
Daverepair Daverepair is offline
Registered-III
 
Join Date: Dec 2009
Location: Plymouth, Massachusetts
Posts: 787
Thanks: 36
Thanked 356 Times in 232 Posts
Default Re: How To Tie Two 200 amp Panels Together

Are you talking about connecting a generator to 2 200 amp panels that are fed in parallel from one meeter. See drawing attached. If so, BAD IDEA
Attached Thumbnails
backfeed.jpg  
Reply With Quote
  #17  
Old 05-07-2012, 09:03 PM
Daverepair Daverepair is offline
Registered-III
 
Join Date: Dec 2009
Location: Plymouth, Massachusetts
Posts: 787
Thanks: 36
Thanked 356 Times in 232 Posts
Default Re: How To Tie Two 200 amp Panels Together

Lots of room for problems. How about two transfer switches, one before each panel or one big switch right after the meter. That would requirer a big generator.!00kw I believe.
Reply With Quote
  #18  
Old 05-08-2012, 10:36 AM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 1,927
Thanks: 35
Thanked 328 Times in 294 Posts
Default Re: How To Tie Two 200 amp Panels Together

MY HOUSE:

the entry panel with bonding point and where the mains disconnect
is interlocked with the generator feed breaker.
there is also a 125 amp breaker feeding a sub panel
all sub panels must have an isolated neutral

the feed from the portable generator is 4 wire
with the neutral isolated from the generator frame.

if you have a permanent generator installed
then a transfer system [or manual switch] is required

code now requires a disconnect between the meter and transfer

if the permanently installed generator feeds more than one transfer
it must have overload protection correct for each line and be bonded, thus
requiring all transfers to be 3 pole and following panels have isolated neutrals

Last edited by armandh; 05-08-2012 at 04:14 PM.
Reply With Quote
The Following User Says Thank You to armandh:
  #19  
Old 05-08-2012, 01:08 PM
Power Power is offline
Registered-III
 
Join Date: Aug 2011
Location: New Jersey
Posts: 2,788
Thanks: 673
Thanked 1,446 Times in 912 Posts
Default Re: How To Tie Two 200 amp Panels Together

Armandth - sounds like a safe system. What is amperage on your main?
Reply With Quote
  #20  
Old 05-08-2012, 03:45 PM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 1,927
Thanks: 35
Thanked 328 Times in 294 Posts
Default Re: How To Tie Two 200 amp Panels Together

225 amp
http://www.smokstak.com/forum/attach...9&d=1158413795

turn off main breaker causing the
breaker lever alignment with notch in plate
slide plate right to lock mains breaker off and that
clears an area for gen breaker to be moved right to on
attempts to disengage the lock flip the gen breaker off

I only load the generator to a 12.5Kw max [50 Amp]
well below generac's alleged 17.5 continuous and 26 surge KW
and as these screamers are not likely to out live us, for a back up,
I have an 1800 rpm '64 vintage k582 powered 7.2 [real] Kw homelite [1.0 pf]
one can load it until the breakers open, and at about 3 hp/kw it is not even working hard
http://www.smokstak.com/forum/attach...1&d=1188565666

Last edited by armandh; 05-08-2012 at 04:13 PM.
Reply With Quote
The Following User Says Thank You to armandh:
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
MEP Control Panels MadMachinist Military MEP and Aircraft Gen-Sets 5 10-07-2011 12:54 AM
Where to get rocker panels for willys vern0n Antique Autos and Trucks 1 04-24-2011 05:17 PM
Encloser Panels Cruiser Onan Generators 1 02-21-2010 09:20 PM
electric panels bob botsford Generators & Motors General Discussion 2 01-18-2003 09:01 PM


All times are GMT -4. The time now is 05:35 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark
A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2014 by Harry Matthews
P.O. Box 5612 - Sarasota, FL 34277