Cummins 100 KW DGDB Diesel genset


All, I was hopefull to tap into the knowledge here. At one of my jobs they just got this used...

this thread has 26 replies and has been viewed 2338 times

Reply
 
Thread Tools Display Modes
  #1  
Old 10-06-2012, 01:09 AM
richard.bessey richard.bessey is offline
Registered-III
 
Join Date: Jan 2008
Location: Walla Walla, WA
Posts: 473
Thanks: 54
Thanked 103 Times in 89 Posts
Default Cummins 100 KW DGDB Diesel genset

All,
I was hopefull to tap into the knowledge here.

At one of my jobs they just got this used Cummins/Onan 100 KW DJDB diesel genset. It has the Cummins inline 6 (6bt engine) in it. I had to install new batteries (24 volt) and a new fuel line, otherwise its running great.

One problem, with the switch in the "Off" position, you can clear a clicking in the control box. Sounds like a relay click on and off, about every 2 seconds. If you put the switch in the remote position, the clicking stops.

Any idea what that cause of the clicking could be?
I am fairly familiar with the older Onan wiring, but these new ones, are similar but different
Reply With Quote
Sponsored Links
  #2  
Old 10-06-2012, 05:26 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 10,820
Thanks: 4,759
Thanked 7,939 Times in 3,797 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

I should have the service manual. Being in off should clear the control system. Can you put your hand on anything while it clicks. You might find what is causing the problem.
Reply With Quote
  #3  
Old 10-06-2012, 05:52 AM
Tony Rye Tony Rye is offline
Subscriber
 
Join Date: Aug 2008
Location: Mobile, Alabama
Posts: 267
Thanks: 11
Thanked 49 Times in 47 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

the sw is in the wrong setting move it up are down one setting i will have to go down to ares to find out for sure. but when you do it will stop clicking.the clicking if i remember is the sw being set for remote start and no remote sys. in place
Reply With Quote
  #4  
Old 10-06-2012, 06:25 AM
Gunny Gunny is offline
Subscriber
 
Join Date: Feb 2005
Location: North Carolina
Posts: 3,110
Thanks: 737
Thanked 1,167 Times in 769 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

Tony:

The controller on that genset is referred to as a 12 light control.

In the "Off" position the "Not in Auto" light should be flashing.

The click you hear is the flasher relay. If you don't see the light flashing, bulb is burned out. Hit the "Lamp Test" switch and see how many more of the are out.

Cummins is real proud of those bulbs.
Reply With Quote
The Following 2 Users Say Thank You to Gunny:
  #5  
Old 10-06-2012, 07:43 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 10,820
Thanks: 4,759
Thanked 7,939 Times in 3,797 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

Thanks Gunny. Guess I have been out of the trade to long. Completely forgot about that. If I remember correctly They went to a higher voltage bulb to make them last longer. I know I got tired of changing the things every time I checked one.
Reply With Quote
  #6  
Old 10-06-2012, 08:18 AM
Gunny Gunny is offline
Subscriber
 
Join Date: Feb 2005
Location: North Carolina
Posts: 3,110
Thanks: 737
Thanked 1,167 Times in 769 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

Billy: They made those bulb in 12, 14 24, 28 and 56 volt. Some, like the ones in the ATSs (normal available and connected) seemed to burn out once a week or so, emergency available and connected would last forever. I modified a bunch with a LED, they appeared to have a long and happy life.

The 12 volt ones get real bright if you apply 24 volts but not as bright as what 56 did to them. Don't run long either. Make your eye blink and see blue dots everywhere for an hour or so.

All the different variations of the 12 Light Control, some had as many as 18 lights, plenty of spares for a few years. Use the unused ones to replace the ones that burn out, or the ones an engineer spec'd but never used.

Really liked that 12 Light, in my opinion, for what its worth, the best controller Onan ever built. Easy to work on until they put that relay board over top of it.
Reply With Quote
  #7  
Old 10-07-2012, 07:45 PM
richard.bessey richard.bessey is offline
Registered-III
 
Join Date: Jan 2008
Location: Walla Walla, WA
Posts: 473
Thanks: 54
Thanked 103 Times in 89 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

I will go back and check to see if I can figure out which relay is clicking.

I did a quick Lamp check, and I thought all of the lamps lit up, but I will double check.
I will also look and see if there is a "not in auto" lamp on the control panel.
Reply With Quote
  #8  
Old 10-07-2012, 08:13 PM
pegasuspinto pegasuspinto is offline
Registered-III
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 1,611
Thanks: 221
Thanked 770 Times in 482 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

The light really is burned out

The easy solution, is to keep it in 'remote' when it's not needed. These sets were made for standby service, so it's as important to make sure there is a warning/alarm when the set is disabled as it is to have warnings for overtemp or low oil pressure-they both have the same effect, the lights stay out and your phone rings at 2am!!

Robert
Reply With Quote
  #9  
Old 10-07-2012, 09:08 PM
Gunny Gunny is offline
Subscriber
 
Join Date: Feb 2005
Location: North Carolina
Posts: 3,110
Thanks: 737
Thanked 1,167 Times in 769 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

Its supposed to click if not in auto. The important light on a 7 or 12 light is the green run light. If it comes on in test, the bulb is good, if the bulb is good and it does not come on when the genset is running, either you have no AC output or the alternator is not charging. Then you don't have one of the start disconnects.
Reply With Quote
  #10  
Old 10-07-2012, 09:17 PM
EricWood's Avatar
EricWood EricWood is online now
Registered-III
 
Join Date: Oct 2005
Location: West Concord, Minnesota USA
Posts: 1,493
Thanks: 170
Thanked 929 Times in 516 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

If, by chance, this genset is a Detector 7-Light, and the A11 control board has been replaced, you will hear the clicking when not in auto, but, with the 7-light there is no Not In Auto lamp. All Detector boards are replaced by the current production 12-light board. So, with 7 lights, clicking, but no lamp.

eric
Reply With Quote
The Following 3 Users Say Thank You to EricWood:
  #11  
Old 10-09-2012, 11:02 PM
richard.bessey richard.bessey is offline
Registered-III
 
Join Date: Jan 2008
Location: Walla Walla, WA
Posts: 473
Thanks: 54
Thanked 103 Times in 89 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

OK, you were all correct. I checked the bulbs again, the bulb labeled "SWITCH OFF" is burned out.

Now, does anyone know of a replacement? (other then Cummins???)

---------- Post added at 10:02 PM ---------- Previous post was at 09:34 PM ----------

Found the cummins part number - 322-0369-02
Reply With Quote
  #12  
Old 10-09-2012, 11:10 PM
Kpack Kpack is offline
Subscriber
 
Join Date: Feb 2012
Location: Bryan, Texas
Posts: 2,679
Thanks: 3,660
Thanked 1,449 Times in 954 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

There are a lot of numbers close on this bulbs but you would have to talk with them tomorrow to see if any would work http://www.srsales.com/ it didn't pull up my inventory check but I copied it to my email if you give me your email i will send it to you pm or post it
Reply With Quote
  #13  
Old 10-10-2012, 12:33 AM
richard.bessey richard.bessey is offline
Registered-III
 
Join Date: Jan 2008
Location: Walla Walla, WA
Posts: 473
Thanks: 54
Thanked 103 Times in 89 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

I think I may have found the replacement bulb here
http://www.bulbtown.com/2176_MINIATU...ASE_p/2176.htm
or here
http://www.bulbtown.com/6838_MINIATU...ASE_p/6838.htm
I would have to wire the bulb into the socket, but that is easily doable with a solder gun.
Also, I found them Ebay, $8 each + $5 shipping.
Still looking for an LED replacement though
Reply With Quote
  #14  
Old 10-10-2012, 01:12 AM
PnishrPW PnishrPW is offline
Registered-II
 
Join Date: May 2012
Location: Western Washington
Posts: 368
Thanks: 171
Thanked 121 Times in 81 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

Leds are easy, Led + Resistor. Depending on color (red/amber/green etc, and current desired) your resistor will vary. Super- bright/HO units only pull 20-30 mA (.02-.03Amp). Start w/ the basics: what size hole does it need to fit into? 1/4 - 5/16 - 3/8 - 1/2" sealed snap in assm`s are common. How bright do you want? If you want, PM me a # and a time to call and I`ll help you out. I do complete custom led dashs and tailights, at any given time I have 2-3000 led`s in stock, and handfulls of resistors... Toss on some heatshrink and you re good to go! Upside: 5000 hr+ life expectancy and no filament/vibration issues!
Reply With Quote
  #15  
Old 10-10-2012, 08:18 AM
pegasuspinto pegasuspinto is offline
Registered-III
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 1,611
Thanks: 221
Thanked 770 Times in 482 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

Yall know Onan did not invent the electric light? Don't even have a factory that makes them

http://www.mouser.com/ProductDetail/...2OFch1TJQTo%3d

These come with the lenses. The white lens was cheapest, you can just snap the lens off. If you need another voltage and/or color this link will get you close.

There is tons of room in this housing for a resistor and a LED as well, but at that price it's not so painfull to replace the burned out ones immediately and then convert the dead ones to LED for future use.
Reply With Quote
  #16  
Old 10-10-2012, 08:42 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 10,820
Thanks: 4,759
Thanked 7,939 Times in 3,797 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

They did burn fast. I replaced one did my inspection and replaced the same one again before I left.
Reply With Quote
  #17  
Old 10-10-2012, 11:41 AM
Kpack Kpack is offline
Subscriber
 
Join Date: Feb 2012
Location: Bryan, Texas
Posts: 2,679
Thanks: 3,660
Thanked 1,449 Times in 954 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

I would go with pnishrpw sounds pretty good and got the stuff on hand can't go wrong
Reply With Quote
The Following User Says Thank You to Kpack:
  #18  
Old 10-10-2012, 05:33 PM
PnishrPW PnishrPW is offline
Registered-II
 
Join Date: May 2012
Location: Western Washington
Posts: 368
Thanks: 171
Thanked 121 Times in 81 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

Quote:
Originally Posted by Billy J Shafer View Post
They did burn fast. I replaced one did my inspection and replaced the same one again before I left.
Wow... That`s got to be annoying.
Reply With Quote
  #19  
Old 10-10-2012, 06:02 PM
Gunny Gunny is offline
Subscriber
 
Join Date: Feb 2005
Location: North Carolina
Posts: 3,110
Thanks: 737
Thanked 1,167 Times in 769 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

Put a lot of funds in someones pocket. If I remember they were something like $14.00 or so each. Think you could also buy the bulb, no lens for a little less.

If you solder in a LED, remember they are polarity sensitive.

Think the ones in the ATS went out faster, AC kills them faster than DC does. Keep that in mind if you go to make up some LED bulbs for your ATS. Those are 24VAC, except for the real old ones that are 56VAC.
Reply With Quote
  #20  
Old 10-10-2012, 07:34 PM
len k len k is online now
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 5,066
Thanks: 74
Thanked 1,750 Times in 1,328 Posts
Default Re: Cummins 100 KW DGDB Diesel genset

I don't know but I suspect the bulbs that burn out faster, are being run at higher voltages than they are rated for.
Also the filaments in some light bulds have more mechanical supports than others, vibration issues. In cars some bulbs have none others have 5 supports. Just like rough service bulbs in trouble lights (120V 75Watt types)

---------- Post added at 07:34 PM ---------- Previous post was at 07:32 PM ----------

IF you look at bulb with magnifing glass you can see them.
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Cummins Diesel engine 6hpMarty Antique Gas Engine Discussion 18 11-03-2012 11:54 AM
onan cummins genset 30 model L634d-1 ls1561 Onan Generators 12 09-20-2012 12:59 PM
'89 Onan DKD genset, 7.5kw Cummins 3 cyl pianodan Onan Generators 53 05-29-2012 09:20 PM
16hp Cummins Diesel bobgill2009 Vintage Diesel Engines 8 05-09-2012 12:23 AM
GE Genset 1954 - Cummins John Radovich Generators & Motors General Discussion 1 08-25-2008 10:58 PM


All times are GMT -4. The time now is 11:54 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark
A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2014 by Harry Matthews
P.O. Box 5612 - Sarasota, FL 34277