Onan OT 225 Transfer switch
this thread has 15 replies and has been viewed 2110 times
Old 06-05-2013, 04:10:19 PM
Longbranch Longbranch is offline
Default Onan OT 225 Transfer switch
Hello,
This is my first post on this board. I installed a onan genset and transfer switch for a lady and I am having trouble with the transfer switch it is a J series. The source lights on the mother board will not light up, as well as the timming card. I am getting 27 volts out of the two transformers. Does anyone have any suggestions?
Thanks,
Old 06-05-2013, 04:34:13 PM
Default Re: Onan OT 225 Transfer switch
My first suggestion is that you post the full model and spec number of the generator and switch.
The Following 2 Users Say Thank You to Wayne 440 For This Post:
Old 06-05-2013, 06:15:20 PM
Ok,
The genset is a 45EM-V and the transfer switch is OT/ON-CT/CN OTIII 225, spec no. is 4935J, the serial no. is G930514846. The genset was originaly 120/208 three phase and I changed it to 120/240 single phase. I changed the selector switches on the mother board to single phase and rewired the two transformers and rewired the transformers connected to the mother board.
Old 06-05-2013, 07:08:34 PM
Were the set and switch used together previously? If so, were you able to verify proper operation of the switch before the reconfiguration?
Old 06-05-2013, 07:29:24 PM
Billy J Shafer's Avatar
Have you reset the cards for the new voltage.
Old 06-05-2013, 07:33:10 PM
I think so, it was taken out of a grocery store that had been damaged by a storm. It has been exposed to the weather for a couple of years, the genset runs fine. I sent the mother board and cards to be checked and they repaired the undervoltage cards and I still cann't get the lights to work on the cards.
Old 06-05-2013, 07:37:29 PM
Do you have the manual for it.
Old 06-05-2013, 08:38:38 PM
Gunny Gunny is offline
Anyone got a copy of the service manual for an OTIII in PDF they can send him?
If it was 120/208 you should be good to go on the linear motor.
The Following User Says Thank You to Gunny For This Post:
Old 06-05-2013, 09:16:47 PM
I have a installation manual, I have done the calibration, etc. It doesn't have a troubleshooting guide.
Old 06-05-2013, 10:07:45 PM
The OP's e-m-a-i-l is clhowell01(at)windstreamDOTnet help appreciated.
Old 06-05-2013, 10:34:18 PM
EricWood's Avatar
EricWood EricWood is offline
Just sent needed manual to address in Wayne's post above.
Eric
The Following 4 Users Say Thank You to EricWood For This Post:
Old 06-05-2013, 10:46:37 PM
farokh farokh is offline
Just in case, I put a copy of the Service manual up on my web server and sent an email to clhowell01 with the URL to grab it. My copy runs 39 megabytes...
The Following 3 Users Say Thank You to farokh For This Post:
Old 06-06-2013, 09:05:56 PM
Got it set for single phase sensing?
Old 06-06-2013, 10:24:09 PM
I have both selector switches set to single phase.
The Following User Says Thank You to Longbranch For This Post:
Old 06-06-2013, 11:24:26 PM
EricWood's Avatar
Do you have your AC connections going through contactor terminals A and B?
Have you recalibrated the cards?
Do you recall if you had to make a jumper (or possibly two) on the sensing transformers when rewiring? When going from three phase (factory built) to single phase (field modification), there aren't enough jumpers, unless there was an extra, unused one wire-tied to the bundle at the transformers.
eric
The Following User Says Thank You to EricWood For This Post:
Old 06-07-2013, 06:37:50 AM
[QUOTE=EricWood;920965]Do you have your AC connections going through contactor terminals A and B?
eric
This problem has me stumped. I am self-employed and I get to work on it here and there. I haven't had the time to go back there with the service manual in hand yet. I believe that its something simple that I am just overlooking.
onan transfer switch bswalsh55 Onan Generators 5 02-07-2013 10:00:53 AM
Transfer Switch for my Onan BigBlockChev Onan Generators 6 03-08-2012 04:19:38 PM
Help on Onan OT Transfer Switch hoghunter69 Onan Generators 11 12-07-2011 08:25:19 PM
Value of 60 amp Onan Transfer Switch Danile Onan Generators 2 03-05-2011 05:32:04 PM
Onan Transfer Switch don-mar Onan Generators 1 07-16-2009 11:42:06 PM