Plug Wiring Question


Okay, I know this is dumb, but better safe than sorry. One of my generators has two 20 amp, 115...

this thread has 12 replies and has been viewed 8670 times

Reply
 
Thread Tools Display Modes
  #1  
Old 02-07-2005, 10:02 PM
Zira Zira is offline
Subscriber
 
Join Date: Nov 2004
Location: Apex, North Carolina USA
Posts: 1,378
Thanks: 274
Thanked 355 Times in 272 Posts
Default Plug Wiring Question

Okay, I know this is dumb, but better safe than sorry.

One of my generators has two 20 amp, 115 volt 3-prong twist-lock outlets. The mating plugs have the 3 connections labled G, X, & Y. G is obviously ground by shape & color (green). My question is, which does the black wire go to & which does the white wire go to (or, which is hot & which is neutral)? I am used to the plugs where the terminals are color coded (green, silver, and brass/gold). BTW, these are Hubbell plugs, if that matters.

Thanks for keeping me from electricuting myself or frying all my electrical stuff.

David
Reply With Quote
Sponsored Links
  #2  
Old 02-07-2005, 10:53 PM
Jim Tremble Jim Tremble is offline
Subscriber
 
Join Date: Nov 2004
Location: Washington
Posts: 1,757
Thanks: 2,100
Thanked 572 Times in 299 Posts
Default Re: Plug Wiring Question

David

White goes to the Silver and Black goes to the Gold or Brass terminal. Green is ground.

Jim
Reply With Quote
  #3  
Old 02-07-2005, 11:49 PM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is offline
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 1,693
Thanks: 195
Thanked 657 Times in 389 Posts
Default Re: Plug Wiring Question

Right. But this plug doesn't have silver and gold screws.

Is this a L5-20P plug? According to the picture in my Graingers catalog, the neutral is the prong nearest the bent tang end of the ground prong.

I suspect you may not have a L5-20P. If it's labeled X, Y, and G, it could very well be a 240V plug. (like maybe a L6-20P?) All the 120V plugs I see here are shown with a W - indicating white, or neutral.
Reply With Quote
  #4  
Old 02-08-2005, 08:07 AM
Mark Abby Mark Abby is offline
Registered-II
 
Join Date: Jan 2005
Location: Rochester, New York USA
Posts: 34
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Plug Wiring Question

here is a web site that may help you identify what you have. (you need adobe reader..it's a pdf file)

http://www.hubbell-canada.com/wiring...t/pdf/h/h3.pdf
Reply With Quote
  #5  
Old 02-08-2005, 05:43 PM
Zira Zira is offline
Subscriber
 
Join Date: Nov 2004
Location: Apex, North Carolina USA
Posts: 1,378
Thanks: 274
Thanked 355 Times in 272 Posts
Default Re: Plug Wiring Question

Thanks for that link, it is clearer than the picture in the McMaster-Carr catalog. It is an L9-20. Does that help?
Reply With Quote
  #6  
Old 02-08-2005, 07:29 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,039
Thanks: 41
Thanked 1,084 Times in 867 Posts
Default Re: Plug Wiring Question

since you are certain which is the ground, plug only the body of the plug into the outlet and start the generator. Then check with a voltmeter between the three plug connecting screws and the frame of the generator. The ground should show no reading, the neutral might show some small voltage, probably not, and the hot should show 115 to the frame, the ground and the neutral. This way you can be sure you are wiring the plug correctly for your generator.

Jim
Reply With Quote
  #7  
Old 02-08-2005, 08:24 PM
Mark Abby Mark Abby is offline
Registered-II
 
Join Date: Jan 2005
Location: Rochester, New York USA
Posts: 34
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Plug Wiring Question

why not open up the panel box on the generator and see which is wired to where?
Reply With Quote
  #8  
Old 02-08-2005, 11:15 PM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is offline
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 1,693
Thanks: 195
Thanked 657 Times in 389 Posts
Default Re: Plug Wiring Question

Is this a home-built set? It's odd that there's a L9-20 outlet - that's a 600V connector. It does not have a designated neutral prong. It has a ground and two hots.

Let us know the results of the test that Jim R. suggested.

Also, there may not be a neutral. Some gensets don't bond either output line to ground, so neutral is whichever one you bond to ground.

Is there also a regular 120V outlet on the set? That'll tell us which line is neutral...
Reply With Quote
  #9  
Old 02-09-2005, 09:23 PM
Zira Zira is offline
Subscriber
 
Join Date: Nov 2004
Location: Apex, North Carolina USA
Posts: 1,378
Thanks: 274
Thanked 355 Times in 272 Posts
Default Re: Plug Wiring Question - some answers

Thanks for all the help. Here are the answers to some questions people asked, and some things I found:
- It is not a homebuilt set, and these are the original outlets. I bought 2 of these from a guy who bought 4 at an auction from a county auction, and they were all the same.
- I said the outlet was a L9-20, that is not correct. It is the same pattern as an L9-20, but a different diameter. I went to the Hubbell web site, and I could not find it there at all. It is still available (at least within the last few years), as I found another male plug of this pattern on a fairly new piece of equipment headed to the scrap yard from a local plant that was closing.
- Instead of trying the test Jim Rankin suggested, I wired a pigtail to a normal 15-amp outlet & used one of those $4 testers with the LED's. This allowed me to sort it out.
- At least on my genset, X is the black (hot) wire, and Y is the white (neutral) wire. This is consistent on both outlets, on both generators.
- Interestingly, the plug I found this week was wire the other way (Y was hot).

I would still like to know what the correct name for these plugs/outlets is (like L5-20). Maybe it is not a NEMA-standard configuration?

David
Reply With Quote
  #10  
Old 09-24-2009, 04:07 PM
Short43158 Short43158 is offline
Registered
 
Join Date: Sep 2009
Location: Union Furnace, Ohio USA
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Plug Wiring Question

I'm sure it has a NEMA number can you post a pic for me I am very visual telling me it looks like a L9-20 really don't work for me.
Reply With Quote
  #11  
Old 09-24-2009, 04:20 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 3,779
Thanks: 229
Thanked 3,129 Times in 1,446 Posts
Default Re: Plug Wiring Question - some answers

Quote:
Originally Posted by Zira View Post
...I would still like to know what the correct name for these plugs/outlets is (like L5-20). Maybe it is not a NEMA-standard configuration?...
Not all locking plugs have a NEMA nomenclature. This http://www.lexproducts.com/cs/indust...oductLineId=23 may be what you have.
Reply With Quote
  #12  
Old 09-24-2009, 04:38 PM
Short43158 Short43158 is offline
Registered
 
Join Date: Sep 2009
Location: Union Furnace, Ohio USA
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Plug Wiring Question

I take it all back maybe your plug is a non NEMA look at the chart in the lower left (you may need to zoom I did)
http://www.passandseymour.com/litera...mat_101107.pdf
There is a plug and receptical set that looks like L9-20. Really it looks more like L8-20, but I think it might be your plug.
Reply With Quote
  #13  
Old 09-24-2009, 09:58 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,039
Thanks: 41
Thanked 1,084 Times in 867 Posts
Default Re: Plug Wiring Question

I wouldn't waste too much effort on this one, it's over 4 years old!
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Wiring Question Jim Davis Generators & Motors General Discussion 15 11-25-2008 08:13 AM
Model T electical wiring question Preston Wells Antique Autos and Trucks 5 08-09-2007 07:50 AM
Spark plug question Mark K Antique Gas Engine Discussion 4 05-24-2005 05:05 PM
Wiring Diagram Question Howard Yoshida Generators & Motors General Discussion 6 11-21-2004 08:42 PM
Generator Wiring Question Howard Yoshida Generators & Motors General Discussion 17 09-07-2003 06:00 AM


All times are GMT -4. The time now is 02:31 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark
A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2014 by Harry Matthews
P.O. Box 5612 - Sarasota, FL 34277