Pe-95-f Signal Corp GeneratorI have a 1952 4 cylinder Willie engine on a Ohan Generator. It produces electricity at idel, but...this thread has 1 replies and has been viewed 948 times
|
![]() |
|
|
Thread Tools | Display Modes |
|
#1
|
|||
|
|||
|
I have a 1952 4 cylinder Willie engine on a Ohan Generator. It produces electricity at idel, but when you put a load on it the engine dies down and the voltage drops then the engine will not recover..... Any suggestions?????
Also looking for a manual. |
| Sponsored Links |
|
#2
|
|||
|
|||
|
Sounds like the governor is not working. Disconnected, rusted, linkage bound up?
Engine should be turning at 1850 or so with no load and not drop below 1750 with a load. |
![]() |