Hello, I have a 10kw Onan HDKAG generator powered by a 4 cylinder kubota diesel engine with...

this thread has 10 replies and has been viewed 4802 times

Reply
 
Thread Tools Display Modes
  #1  
Old 06-25-2006, 10:51 PM
coolya coolya is offline
Registered
 
Join Date: Jun 2006
Location: Caymans
Posts: 2
Thanks: 0
Thanked 0 Times in 0 Posts
Default Onan diesel generator

Hello,
I have a 10kw Onan HDKAG generator powered by a 4 cylinder kubota diesel engine with approximately 3400 hrs.

The unit starts fine and runs strong, but there’s a very noticeable black haze when at or over 80% load. The exhaust temperature also seems to get very hot and the paint on the exhaust is starting to burn.

Not sure if it's a big issue, but I did research online and everything seems to be pointing to over-fueling. I've tried adjusting the fuel delivery underload and the unit stops hazing but then loses power.

Can anyone think of anything else?

Thanks!
Reply With Quote
Sponsored Links
  #2  
Old 06-25-2006, 11:06 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,031
Thanks: 41
Thanked 1,081 Times in 864 Posts
Default Re: Onan diesel generator

air filter restriction or if turbocharged, you could have an exhaust leak dropping the boost a little, turbocharger failing, but they usually loose a lot of oil down the exhaust. Any of these would increase EGT and increase soot in the exhaust due to less "excess air" . It could be perfectly normal also, diesels get very hot exhaust and usually paint will not stay on the manifolds at least on the ones I see most often.
Reply With Quote
  #3  
Old 06-25-2006, 11:19 PM
coolya coolya is offline
Registered
 
Join Date: Jun 2006
Location: Caymans
Posts: 2
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Onan diesel generator

The unit is naturally aspirated. I've changed the air and fuel filter with no positive results.

I wish I knew how much exhaust soot is acceptable in a kubota.

Thanks!
Reply With Quote
  #4  
Old 06-26-2006, 02:40 AM
BTPost's Avatar
BTPost BTPost is offline
Moderator
 
Join Date: Jan 2005
Location: Excursion Inlet, Alaska USA 99850-0090
Posts: 4,625
Images: 1
Thanks: 502
Thanked 1,684 Times in 1,121 Posts
Talking Re: Onan diesel generator

Just what did you adjust on the diesel to try and fix the problem? Usually
this type of problem is only resolved by Flow Benching the Injector Pump,
and the Injectors, as they are what regulates the fuel flow in a diesel engine.
If it is NA, then I suspect Injectors or Injection Pump problems.......Black
Smoke on a diesel at 80% load, is not normal for Kabota engines.

Bruce in alaska
Reply With Quote
  #5  
Old 06-26-2006, 07:34 AM
J. McNugget's Avatar
J. McNugget J. McNugget is offline
Registered-III
 
Join Date: Jan 2005
Location: North Bay, Ontario, Canada
Posts: 529
Thanks: 451
Thanked 213 Times in 121 Posts
Default Re: Onan diesel generator

We have an HDKAG with over 10,000 hours on it - a pusher fan model. Ours does not smoke black - a little white on startup, but a pittance compared to my DJC.

If you have 3,400 hours on it and the paint is still on the exhaust, I think the engine probably needs a good, 90% load for 4-6 hours to clean it out. It doesn't seem like it has worked hard enough yet, and your 80% load is moving it into the "working hard" threshold.

We frequently trip the breaker in ours with the loads we subject it to. Load it up and let it run. Make sure you are using a quality brand of 15 W-40 oil too.
John
Reply With Quote
  #6  
Old 06-26-2006, 08:54 AM
pnora pnora is offline
Registered-II
 
Join Date: Jan 2006
Location: Ishpeming, Michigan USA
Posts: 379
Thanks: 1
Thanked 89 Times in 62 Posts
Default Re: Onan diesel generator

Before you waste any money you should read the actual exhaust temperature. This can be done with a hand held pyrometer gun. You can read the manifold at each port to determine if one or all are getting to hot. As said if the paint is not burned off it most likely has never been run under a load for a length of time. A diesel may seem to smoke because it is burning up all the soot and carbon. You also could install a pyrometer like an autometer in the manifold collectorhere all the cylinders meet and then you will be able to constantly monitor it.
Reply With Quote
  #7  
Old 06-26-2006, 07:03 PM
Elden DuRand's Avatar
Elden DuRand Elden DuRand is offline
Subscriber
 
Join Date: Nov 2004
Location: Port St. Joe, Florida USA
Posts: 5,647
Images: 6
Thanks: 7,120
Thanked 3,885 Times in 1,723 Posts
Exclamation Re: Onan diesel generator

Quote:
Originally Posted by coolya
Hello,
I have a 10kw Onan HDKAG generator powered by a 4 cylinder kubota diesel engine with approximately 3400 hrs.

The unit starts fine and runs strong, but there’s a very noticeable black haze when at or over 80% load. The exhaust temperature also seems to get very hot and the paint on the exhaust is starting to burn.
I had an '82 Isuzu Diesel pickup that I converted to a Class C camper. Initially, it smoked A LOT!

I tapped the exhaust manifold and installed a pyrometer and boy, was I surprised at what I found out! At heavy load (not firewalled), the gauge would peg at 1,500 degrees F! By that point, it was smoking like crazy.

My solution was to design a Rajay turbocharger setup, including making both manifolds. With the turbo setup, it would just touch 1,500 degrees after a really long hill. Most pulls would see it peak around 1,200 to 1300 degrees. Peak manifold pressure was close to 18 PSI.

I got much less smoke and a little more power. I did NOT modify the injection pump. It was interesting to note that after I put the turbo on, the oil temperature ran higher. I suppose that was because since more of the fuel was burning in the combustion chamber, not going past the exhaust valves, the pistons got hotter, heating the oil.

It had almost 120,000 miles on it when we traded it and was still running fine. I always wonder if it would have lasted without the turbo. Lots of smoke and red-hot valves doesn't strike me as a good way to make an engine last.

Take care - Elden
Reply With Quote
  #8  
Old 06-27-2006, 07:53 AM
J. McNugget's Avatar
J. McNugget J. McNugget is offline
Registered-III
 
Join Date: Jan 2005
Location: North Bay, Ontario, Canada
Posts: 529
Thanks: 451
Thanked 213 Times in 121 Posts
Default Re: Onan diesel generator

Sounds like a good result Elden. The oil would run hotter because you would have had an oil line running to the turbo to lubricate the turbine bearings. Lots of heat in those little things.

Any word on loading it up or pyro testing the exhaust, coolya?
Reply With Quote
  #9  
Old 06-27-2006, 10:03 PM
Steve Dawkins Steve Dawkins is offline
Registered-III
 
Join Date: Feb 2005
Location: Virginia Beach, VA USA
Posts: 319
Thanks: 28
Thanked 14 Times in 10 Posts
Default Re: Onan diesel generator

Hi Guys, please pardon the interruption. I'm curious what model Kubota engine is on the HDKAG genset? I have a Kubota V1505 4 cylinder diesel engine on a 12.5 kW genset, and was wondering if Cummins/Onan used that same engine on their 10 kW unit. Thanks.
Reply With Quote
  #10  
Old 06-28-2006, 07:45 AM
J. McNugget's Avatar
J. McNugget J. McNugget is offline
Registered-III
 
Join Date: Jan 2005
Location: North Bay, Ontario, Canada
Posts: 529
Thanks: 451
Thanked 213 Times in 121 Posts
Default Re: Onan diesel generator

Hi Steve - the .pdf spec sheet I have for our unit lists the engine as the 1.339 litre size of the 05 family: D1305.

It was used in the 8 and 10 kW HDKAG series machines apparently.

I think the new Lincoln Vantage 300 welder uses the V 1505. I was looking at one of those, but it is not in the cards right now.

John
Reply With Quote
  #11  
Old 06-29-2006, 05:30 PM
Steve Dawkins Steve Dawkins is offline
Registered-III
 
Join Date: Feb 2005
Location: Virginia Beach, VA USA
Posts: 319
Thanks: 28
Thanked 14 Times in 10 Posts
Default Re: Onan diesel generator

John, thanks for the reply.

Steve
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan 2 cyl upright diesel Generator Jim Leighton Onan Generators 8 03-17-2011 10:13 PM
Onan DRP diesel generator Jeff Conner Onan Generators 14 02-15-2009 04:25 AM
Onan DJC Diesel Generator jd318 Onan Generators 0 02-02-2006 11:22 PM
Onan Diesel Generator Jeff Conner Onan Generators 4 02-04-2003 04:59 PM
Onan diesel generator Max Koone Onan Generators 1 09-21-2002 06:32 PM