MEP105A Generator Injector Pump


I have a 1976 Libby built with a White Engines Ind, Hercules Engine Division engine model...

this thread has 12 replies and has been viewed 5155 times

Reply
 
Thread Tools Display Modes
  #1  
Old 07-02-2007, 04:49 PM
fdilley fdilley is offline
Registered-I
 
Join Date: May 2007
Location: Renton, WA USA
Posts: 17
Thanks: 1
Thanked 0 Times in 0 Posts
Question MEP105A Generator Injector Pump

I have a 1976 Libby built with a White Engines Ind, Hercules Engine Division engine model D-298-ERX37. I have all the electrical problems worked out of it and the engine turns over, but will not start. I have fuel to the injector pump but nothing comes out of the pump to the injectors. I measured the resistance of the shut of solenoid to be 14 ohms and I have 24 volts on it when cranking. I was told I could put 20psi of air on the last strainer to try and force fuel into the pump. But I don't want to damage the pump. Has anyone have a suggestions? Without removing it?

Thanks much
Reply With Quote
Sponsored Links
  #2  
Old 07-02-2007, 08:56 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is online now
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 8,589
Thanks: 3,447
Thanked 5,635 Times in 2,794 Posts
Default Re: MEP105A Generator Injector Pump

Look for a screw on the side of the pump. It takes a 1/2 inch wrench to open it. It is the bleed off screw open it and if the engine has a primer pump,pump it until you have fuel coming out of the pump. Also you will need to open the injector lines on top of the engine. Turn the engine over untill you have fuel at the lines.Do not put air pressure into the pump. You could blow out all the seals and pumps are not cheap to repair.
Reply With Quote
  #3  
Old 07-03-2007, 02:33 AM
Raymond Raymond is offline
Subscriber
 
Join Date: Nov 2004
Location: Zebulon, North Carolina USA
Posts: 461
Thanks: 0
Thanked 16 Times in 16 Posts
Default Re: MEP105A Generator Injector Pump

I have a Hercules D198 on a 1969 15 KW military (model slipped) but it has a day tank with a float in it. The shutdown system will stop it if the fuel gets low, I don't remember without looking at the diagram but make sure one side of the run coil is hot and the other is grounded. You should be able to hear a click as it pulls in. The pump is a Roosa-Master (Hartford screw co.) just like on the GM diesels and many (most) others that don't use Bosch, or CAV.
Reply With Quote
  #4  
Old 07-03-2007, 02:37 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 3,488
Thanks: 27
Thanked 801 Times in 661 Posts
Default Re: MEP105A Generator Injector Pump

The return line to the tank could be stopped up. There is usually a fitting out the top of the injection pump that has a line from it up to a tee into the return line from the injectors that goes back to the tank.

The fitting in the top of the injection pump can be totally clogged with debris from the pump and not allow the pump to pump fuel.

If you have 24volts to the solenoid coil, make sure there isn't some safety system that interrupts the ground of the coil. The grounds can also be corroded.
Reply With Quote
  #5  
Old 07-03-2007, 03:00 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is online now
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 8,589
Thanks: 3,447
Thanked 5,635 Times in 2,794 Posts
Default Re: MEP105A Generator Injector Pump

What Jim is talking about is a common problem. I forgot about the fitting on top of the pump. Most of the time it will let the engine start and then it will slow down and stop. If you remove it and find parts of rubber seals in it you will need to have the pump rebuilt.
Reply With Quote
  #6  
Old 07-03-2007, 03:51 PM
BTPost's Avatar
BTPost BTPost is offline
Moderator
 
Join Date: Jan 2005
Location: Excursion Inlet, Alaska USA 99850-0090
Posts: 4,487
Images: 1
Thanks: 451
Thanked 1,553 Times in 1,054 Posts
Talking Re: MEP105A Generator Injector Pump

All the preceeding Posts are very good advice. If it were "Me", I would
rebleed the complete Injection System. First at the Input to the Injector Pump.
Second, at the Return Line out of the Injector Pump. Then Check the Shutdown
Solenoid to "MAKE SURE" it is actually pulling in to "Run" position,
while I cranked the engine. With that "Confirmed", then crack each of the
Injector lines, at the pump, and make sure that the Pump itself, is outputting
Fuel Pulses. Be careful NOT to get your appendiges anywhere near the
cracked High Pressure Injector lines, as fuel injected under your skin, is
a really BAD thing. Once you have confirmed that the Injector pump is
pulsing fuel to the Injecter Lines, retighten them at the Injection Pump,
and crack them at the Injectors, and crank the engine untill you have the
Fuel, pulsing out on each Injector. When this is confirmed, retighten the
individual Injector Lines at the Injectors, and you should get White Smoke
starting to come from the Exhaust. Hit the GlowPlug Switch, if you have one,
or blow some Hot Air down the Intake Manifold, (Politico's are really handy
for this step) and if the timing is correct, your engiine should start.

Bruce in alaska____ Diesel Engine Injection System Bleeding 101
............................
Reply With Quote
  #7  
Old 07-03-2007, 09:22 PM
fdilley fdilley is offline
Registered-I
 
Join Date: May 2007
Location: Renton, WA USA
Posts: 17
Thanks: 1
Thanked 0 Times in 0 Posts
Default Re: MEP105A Generator Injector Pump

I want to say thanks to all who answered my question. This injector pump has no primer pump on it. The only bleed screw that I could find is on the top near the shut off solenoid and it takes a larger screwdriver than I have (note: buy more tools!) I took all the injector caps off and found rust in all of them. I will check all injector lines and make sure the solenoid is working. Again Thanks much

Lee in Seattle
Reply With Quote
  #8  
Old 07-03-2007, 10:08 PM
oldtool53 oldtool53 is offline
Registered-III
 
Join Date: Jan 2006
Location: New Bern North Carolina USA
Posts: 218
Thanks: 3
Thanked 23 Times in 14 Posts
Default Re: MEP105A Generator Injector Pump

Quote:
Originally Posted by fdilley View Post
I have a 1976 Libby built with a White Engines Ind, Hercules Engine Division engine model D-298-ERX37. I have all the electrical problems worked out of it and the engine turns over, but will not start. I have fuel to the injector pump but nothing comes out of the pump to the injectors. I measured the resistance of the shut of solenoid to be 14 ohms and I have 24 volts on it when cranking. I was told I could put 20psi of air on the last strainer to try and force fuel into the pump. But I don't want to damage the pump. Has anyone have a suggestions? Without removing it?

Thanks much
Hi,
A Hercules (white) D298 is probably a Roosa Master (Stanadyne) model DB pump. It has no bleed screw. The bolt on the side (1/2") is a head locking srew. There is no internal passage to this screw hole for bleeding. Often confused with tho old C.A.V. (Lucas) DPA pump which does have a bleed screw in this same location.
You may have a stuck metering valve. This happens often to pumps that sit unused for long periods. If you are lucky you can get it freed up. Remove the top cover to access the metering valve.
You may also have stuck pumping plungers, which would require complete disassembly of the pump to correct. At the worst the head and rotor assembly may be seized. This is where it can get very expensive.
As for feeding the pump you will do no harm to the pump by pushing fuel with compressed air at 20 psi but you could burst the filter. Just use an electric fuel pump.

Mark
Reply With Quote
  #9  
Old 07-04-2007, 10:20 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is online now
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 8,589
Thanks: 3,447
Thanked 5,635 Times in 2,794 Posts
Default Re: MEP105A Generator Injector Pump

Can you post a picture of the pump.
Reply With Quote
  #10  
Old 07-04-2007, 04:56 PM
fdilley fdilley is offline
Registered-I
 
Join Date: May 2007
Location: Renton, WA USA
Posts: 17
Thanks: 1
Thanked 0 Times in 0 Posts
Red face Re: MEP105A Generator Injector Pump

Yes it is a Stanadyne type pump. I pulled off the timing line cover and some gunk came out. It seemed like pices of seals? I guess its time to pull the pump. I turned the crankshaft clockwise a couple of times, but never saw another timeing mark on what was rotating. So if you have any other suggestions, please let me know. It's real hard to see the timing marks on the drive gear and the idler. I don't want to have to pull the drive pulley and the timing cover if I don't have to. Thanks much.

Lee from Seattle

PS. My camera broke today just befor I could yake a photo.
Reply With Quote
  #11  
Old 07-04-2007, 05:38 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is online now
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 8,589
Thanks: 3,447
Thanked 5,635 Times in 2,794 Posts
Default Re: MEP105A Generator Injector Pump

The timing mark is there just real hard to see. It will be better to line the marks up than to pull everything apart.
Reply With Quote
  #12  
Old 07-04-2007, 05:54 PM
John Schwiebert John Schwiebert is offline
Registered-III
 
Join Date: Jan 2006
Location: Hamler Ohio USA
Posts: 1,027
Thanks: 0
Thanked 213 Times in 192 Posts
Default Re: MEP105A Generator Injector Pump

Is this a vertical or a horizonal mounted pump? Do get the lines in the pump to align before you remove it. Can not speek for the 4 cylinder Hercules but the 6 cylinder version of that same engine has some versions that are timed to number 6 cylinder instead of number one. Worse case, remove the valve cover and watch the push rods to see if you are on #1 or number 4 cylinder,compression stroke when the lines in the pump timing window align. If you have rust in the injector caps remove all four injectors and have those checked as well. Moisture is a diesel fuel system killer.
Reply With Quote
  #13  
Old 07-05-2007, 09:46 AM
fdilley fdilley is offline
Registered-I
 
Join Date: May 2007
Location: Renton, WA USA
Posts: 17
Thanks: 1
Thanked 0 Times in 0 Posts
Red face Re: MEP105A Generator Injector Pump

Well guys I pulled the pump yesterday and I'm droping it off to Seattle Injector for repair. It had more wrong with it than I want to try to repair. So thanks for all the help and now I will wait for the repair.

Thanks Again

Lee from Seattle
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Steam Pump vs Injector Gary K Stationary Steam & Traction Engines 17 12-07-2008 10:47 PM
looking for injector pump MDJA Tommy Tsimogianis Onan Generators 3 11-17-2005 07:20 PM
MDJE injector pump problems on 7.5/3cr ntjock Onan Generators 5 10-01-2005 08:35 AM
Hercules Fuel Injector Pump David Orgain Generators & Motors General Discussion 0 02-27-2004 12:10 PM
Lister-Blackstone fuel injector pump JODY Vintage Diesel Engines 1 02-28-2002 01:30 AM