Default Generac with an attitude

97 model with 7.4L GM

Started with a problem with the fan drive, one of those odd ones with the shaft running through the radiator, gear box on the other end so the engine can run in the power band. Lovejoy coupling came apart and trashed everything in front of the radiator. Fixed all of that and now no start.

I'm a diesel person but thought I had these things figured out. No fire from any of the plugs. Getting 12VDC to the coil. Pulled the cap and we have rotation. Removed the HEI module and off to Advance. Checked bad, installed a new one. Still no fire. Ohmed the trigger, 840 ohms. Makes a little over .5 VAC when cranking (auto parts store man says that is good, suggested a bad coil) Bad coils are few and far in between but since they are $17.00, hung a new one on. Same song, no fire. Can't buy the trigger (cam position sensor/device that signals the HEI when to fire) alone, got to buy a whole distributor.

Thoughts/comments/recommendations from the experts?
Reply With Quote
Sponsored Links
  #2  
Old 06-20-2008, 09:46 PM
Douglas Douglas is offline
Registered-III
 
Join Date: Feb 2007
Location: Northern Ontario
Posts: 203
Thanks: 3
Thanked 3 Times in 2 Posts
Default Re: Generac with an attitude

Not sure if this is the same part but I see no harm in taking a trip to the local recylcer or repair shop and seeing if they have some HEI distributors around you can have. Odds are you can strip out the parts you need.

I had a 305 in a 1984 GMC 1/2 ton that developed a problem like you discribe and it turned out to be the pick up coil was failing making it hard to start untill one day it didn't. I just swapped out the entire distibutor from another used small block and never looked back
Reply With Quote
  #3  
Old 06-20-2008, 09:52 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 1,955
Thanks: 6
Thanked 154 Times in 149 Posts
Default Re: Generac with an attitude

Don't they have a crank position sensor? Possibly damaged by the failure? One reason for a sudden death if so equipped.
Reply With Quote
  #4  
Old 06-21-2008, 08:36 AM
PFT's Avatar
PFT PFT is offline
Subscriber
 
Join Date: Apr 2006
Location: Marietta, NY USA
Posts: 369
Images: 31
Thanks: 222
Thanked 81 Times in 52 Posts
Default Re: Generac with an attitude

Gunny, I remember in the early days of HEI they would burn thru the rotor under the center tab that contacted the coil output. The spark then went to the shaft under the rotor.
Just a thought, and has no relation to your original problem.
Good luck, PT
Reply With Quote
  #5  
Old 06-21-2008, 09:18 AM
Gunny Gunny is offline
Registered-III
 
Join Date: Feb 2005
Location: United States
Posts: 1,580
Thanks: 31
Thanked 180 Times in 171 Posts
Default Re: Generac with an attitude

Paul:

Thought about that too. Pulled the wire from the coil off of the distributor cap and plugged in a spark plug, laid it on the intake manifold and no spark.
Reply With Quote
  #6  
Old 06-21-2008, 09:37 AM
BDMelon BDMelon is offline
Subscriber
 
Join Date: Oct 2005
Location: USA
Posts: 1,426
Images: 11
Thanks: 161
Thanked 136 Times in 48 Posts
Default Re: Generac with an attitude

just a question does this HEI system, is this the older one with vacuum advance on dist. ? if so
the wire on the pick -up may be broken under the pick up coil, wire get rub through , or the flex of the advance
unit after some time, break wire off the soldering point.. just my to cents worth
__________________


Bdmelon
Reply With Quote
  #7  
Old 06-21-2008, 10:23 AM
K D Redd K D Redd is offline
Registered-III
 
Join Date: Nov 2004
Location: Southwest Missouri
Posts: 2,414
Thanks: 1
Thanked 312 Times in 297 Posts
Default Re: Generac with an attitude

I would have to check a HEI pick-up coil at the shop BUT I think 840 ohms is way to high. Go to you local part store with YOUR ohm meter and have them pull one of the shelf and OHM it. I think it should be closer to 150 ohms. The HEI chip can be triggered with other pick-up coil as I am using a HEI chip with a standard NON-resistor coil and a Chrysler electronic distributor in my old 1967 Dodge 400 truck. The reason I did the ignition system that way was the wireing was much simpler than the Chrysler system.

Kent
Reply With Quote
  #8  
Old 06-21-2008, 11:40 AM
Gunny Gunny is offline
Registered-III
 
Join Date: Feb 2005
Location: United States
Posts: 1,580
Thanks: 31
Thanked 180 Times in 171 Posts
Default Re: Generac with an attitude

Kent:

You are correct. Did some more research this morning. Monday going to dig up a new pickup coil or another distributor. I'll post the results.

BDMelon:
This is on a genset. They run at a fixed RPM, no vacum advance. The only moving part in the distributor is the shaft and anything afixed to it.

Sort of suspicious as a few other things on this machine have been seriously jury rigged and it shows other evidence of someone's work that tells me they didn't know what they were doing.
Reply With Quote
  #9  
Old 06-21-2008, 01:39 PM
pegasuspinto pegasuspinto is offline
Registered-III
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 347
Thanks: 2
Thanked 75 Times in 52 Posts
Default Re: Generac with an attitude

is this one of the self-contained HEI distributors, with the coil in the cap, or a seperate coil and distributor? You can get ANY component part for the coil-in cap GM HEI units. I kept a complete set of spare bits in my motorhome. I wouldn't of thought anyone would bother putting the later Fuel Injection HEI units on a genset.

Robert
Reply With Quote
  #10  
Old 06-21-2008, 02:51 PM
Tom Kilgore Tom Kilgore is offline
Subscriber
 
Join Date: Dec 2007
Location: Adamsville Alabama USA
Posts: 357
Thanks: 253
Thanked 83 Times in 59 Posts
Arrow Re: Generac with an attitude

cam pos sensor lx756 standard ign brand, crankshaft position sensor pc123t I think,I know these are correct for gm trucks
Reply With Quote
  #11  
Old 06-22-2008, 03:47 PM
K D Redd K D Redd is offline
Registered-III
 
Join Date: Nov 2004
Location: Southwest Missouri
Posts: 2,414
Thanks: 1
Thanked 312 Times in 297 Posts
Default Re: Generac with an attitude

Gunny,
I do not know if I was correct or not. Yesterday aftenoon after I got back with my combind header, I measured a HEI pick-up coil from a computor controlled, NO Mechanical/Vacuum Advance HEI. It read 850 ohms. This unit was a junker and the pick-up is of unknown quaility.

Kent
Quote:
Originally Posted by Gunny View Post
Kent:

You are correct. Did some more research this morning. Monday going to dig up a new pickup coil or another distributor. I'll post the results.

BDMelon:
This is on a genset. They run at a fixed RPM, no vacum advance. The only moving part in the distributor is the shaft and anything afixed to it.

Sort of suspicious as a few other things on this machine have been seriously jury rigged and it shows other evidence of someone's work that tells me they didn't know what they were doing.
Reply With Quote
  #12  
Old 06-22-2008, 10:29 PM
Gunny Gunny is offline
Registered-III
 
Join Date: Feb 2005
Location: United States
Posts: 1,580
Thanks: 31
Thanked 180 Times in 171 Posts
Default Re: Generac with an attitude

New one at NAPA ohms at 790 ohms.

Also retested the HEI, the one that Advance tested as bad, it tested good this time.

Now I'm gonna have to scratch my head and think.
Reply With Quote
  #13  
Old 06-22-2008, 11:24 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: KY
Posts: 580
Thanks: 12
Thanked 65 Times in 64 Posts
Default Re: Generac with an attitude

I have nothing meaningful to add, just wanted to express condolences. Now others know why there are so many gen-set stories that start with "It was about 3 pm on Friday afternoon, and we had this #%$@* Generac that..."
Reply With Quote
  #14  
Old 06-23-2008, 12:53 AM
rrfxxxr rrfxxxr is offline
Registered-II
 
Join Date: Jan 2008
Location: Clinton, MS USA
Posts: 134
Thanks: 7
Thanked 17 Times in 16 Posts
Default Re: Generac with an attitude

Quote:
Originally Posted by Wayne 440 View Post
I have nothing meaningful to add, just wanted to express condolences. Now others know why there are so many gen-set stories that start with "It was about 3 pm on Friday afternoon, and we had this #%$@* Generac that..."
Heh heh I heard that. We had a few, didn't hold up too well. The 3.5kW Honda units we had were better. (if you let the carb run dry when you shut them down.)
Sbw
Reply With Quote
  #15  
Old 06-26-2008, 09:43 AM
Billy J Shafer Billy J Shafer is offline
Registered-III
 
Join Date: Nov 2004
Location: Centerville TEXAS
Posts: 3,059
Thanks: 235
Thanked 742 Times in 522 Posts
Default Re: Generac with an attitude

Gunny. Why are you waisting your time on junk. Saw one of those units down here last week. Shaft came off and took out the whole front end. Told the coustomer to go buy a kohler. Engine is trashed anyway. They have a pit on site and I think that is going to be its new home.
Reply With Quote
  #16  
Old 07-01-2008, 10:24 AM
K D Redd K D Redd is offline
Registered-III
 
Join Date: Nov 2004
Location: Southwest Missouri
Posts: 2,414
Thanks: 1
Thanked 312 Times in 297 Posts
Default Re: Generac with an attitude

Gunny,

Did you ever get the HEI figured out?

Kent
Reply With Quote
  #17  
Old 07-03-2008, 08:53 PM
Gunny Gunny is offline
Registered-III
 
Join Date: Feb 2005
Location: United States
Posts: 1,580
Thanks: 31
Thanked 180 Times in 171 Posts
Default Re: Generac with an attitude

Well.........yes.

I wanted to go with an old style distributor, one wire with the coil in the cap. Ran into a snag with that, service manager vetoed that idea, the genset is at a nursing home, life safety and liability issues so had to be OEM replacement.

Got a new one from GM and got pulled off the job. New distributor was installed by someone else and still no fire. Back on the job. Seems there is a resistor in the wiring harness that ohms OK but when there is a load on it, goes open. Generac claimed its a GM resistor and GM denies any knowledge of its existance. 8 ohm resistor. Found a 5 ohm 20 watt resistor in my "bag" of spare parts, extra washers, screws, relays, fuses, good used parts and smoke restorer. Up and running just fine now.

Remembered something passed on to me many years ago by a real wise gas engine man. Best way to time a fixed speed dry fuel engine is with a vacum gage. Let it run and warm up with a vacum gage on the intake, adjust the timing to get the highest vacum reading, bolt it down and call it done.
Reply With Quote
  #18  
Old 07-04-2008, 11:46 AM
K D Redd K D Redd is offline
Registered-III
 
Join Date: Nov 2004
Location: Southwest Missouri
Posts: 2,414
Thanks: 1
Thanked 312 Times in 297 Posts
Default Re: Generac with an attitude

Gunny,

Ate you saying this resistor is in the 12 volt feed wire for the HEI? In GM cars and the one half GM, one half Chrysler system I have on my old Dodge 400 Fescue seed truck you DO NOT use a resistor in the feed line between the ignition switch and the HEI 12 volt input. That is the beauty of the system, No resitor to burn out.

Kent
Reply
Reply


Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Old RV Generac Arthur Generac Generators (SEARS, etc.) 9 09-11-2009 09:37 PM
Generac ChrisMar Generac Generators (SEARS, etc.) 1 02-10-2008 05:49 PM
Generac regulator Andre Blanchard Generac Generators (SEARS, etc.) 2 02-06-2006 12:34 PM
Generac rotation ?? Stans Generac Generators (SEARS, etc.) 20 11-23-2005 11:05 PM
generac pwest Generac Generators (SEARS, etc.) 1 09-14-2004 11:51 AM


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
F o r u m Jump


All times are GMT -4. The time now is 04:51 AM.


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark
A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2009 by Harry Matthews
P.O. Box 5612 - Sarasota, FL 34277