MEP-018a tripping breaker


hello, i loaned this set out during resent hurricane. the fellow said when he tryed to start his 3...

this thread has 8 replies and has been viewed 1171 times

Reply
 
Thread Tools Display Modes
  #1  
Old 09-27-2008, 05:10 PM
Jim Kinler Jim Kinler is offline
Registered-II
 
Join Date: Sep 2005
Location: Livingston. Louisiana USA
Posts: 241
Thanks: 0
Thanked 26 Times in 25 Posts
Default MEP-018a tripping breaker

hello, i loaned this set out during resent hurricane. the fellow said when he tryed to start his 3 1/2 ton certral air it would through the breaker. he was only trying the central unit when this happened. it did the rest of the house ok. i know this set should handle this. ive had to change diodes and voltage regulators on these before but they didnt trip the breaker anyone have any ideas? thanks
Reply With Quote
Sponsored Links
  #2  
Old 09-27-2008, 05:57 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 2,922
Thanks: 189
Thanked 2,120 Times in 1,023 Posts
Default Re: mep-018a tripping breaker

I would expect that 3.5 ton AC to draw around 100 amps when starting. There is probably nothing wrong with your set, it just "doesn't like" the 20+kw load.
Reply With Quote
  #3  
Old 09-27-2008, 09:04 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 3,489
Thanks: 27
Thanked 801 Times in 661 Posts
Default Re: mep-018a tripping breaker

lots of modern AC condensing units have PSC type compressors which do not have a starting switch and capacitor. The older types had 'em and drew less of a starting surge.

So there's a difference between 3.5 Ton units in the starting surge.

He could also have a weak capacitor on either type compressor that he hasn't noticed, yet. It may show up sooner rather than later.
Reply With Quote
  #4  
Old 09-28-2008, 08:46 AM
Jim Kinler Jim Kinler is offline
Registered-II
 
Join Date: Sep 2005
Location: Livingston. Louisiana USA
Posts: 241
Thanks: 0
Thanked 26 Times in 25 Posts
Default Re: MEP-018a tripping breaker

thanks for replys, i dont know what type ac he has. my ac unit 4 ton says 26 amps running 46 start i think, so i thought it should have handled his. i had put put about 25 amps on unit and it did fine before he got it. got it back yesterday and havnt ran it yet. he put about 80 hrs. on it after the storm said it ran fine and ran everything else in the house. but with his ac unit the blower and possible hidden loads it may have been to much.
Reply With Quote
  #5  
Old 09-30-2008, 11:17 PM
panzerwillie panzerwillie is offline
Registered-II
 
Join Date: Jan 2008
Location: miami fl
Posts: 79
Thanks: 0
Thanked 4 Times in 4 Posts
Default Re: MEP-018a tripping breaker

I got one of those units in my house runing in natural gas and i have a old 3 ton unit that pulls about 45-50 amps on start up, and about 22 amps runing, i install hot start capacitors in the ac unit and it help plus i ran thick gauge wire between the gen set and my house which help, but most important i crank the AC firts and once is running the rest of the house follows and it does well, hope this info helps
Reply With Quote
  #6  
Old 10-01-2008, 09:07 AM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 3,489
Thanks: 27
Thanked 801 Times in 661 Posts
Default Re: MEP-018a tripping breaker

The "boost" or hot start capacitor units are a packaged start capacitor and relay that is connected across the run capacitor terminals of a single phase motor. It can help the Permanent Splitphase Capacitor (PSC) type compressor or other motor the most, because these motors do not have a start capacitor and relay. A motor which already has a start capacitor and relay shouldn't get much boost from one, though I know refrigeration guys that will try them on any compressor they see that has ever had capacitor failure or problems starting.

They are primarily intended for situations where voltage is low at the compressor, but should help out when running on a backup generator as you describe.
Reply With Quote
  #7  
Old 10-01-2008, 12:59 PM
Jim Kinler Jim Kinler is offline
Registered-II
 
Join Date: Sep 2005
Location: Livingston. Louisiana USA
Posts: 241
Thanks: 0
Thanked 26 Times in 25 Posts
Default Re: MEP-018a tripping breaker

i started gen. up yesterday voltage was 113. i had to turn the voltage adjust knob to the bottom quarter of the range to get 126. when it left i got 126 at about 1 or 2 oclock position. the unit has one of the older style voltage regulators, so i changed it out with a nos i had. i attached the 3 jumper wires as per instuctions on the reg. and attached the large plug. started up and got 103 no matter how i turned the adjust knob. after 3 min. lost everything. put the old reg. back in got 126 at about 5 oclock postion on the vol. adj. knob. the fuse was blown on the 120 volt receptical on the front control panel i know it was fine when it left. i have another new style nos reg. i would like to put in. do i have to also change out the voltage adust knob. iam just wondering if i had a bad regulator although it did look to be new. i dont wont to damage another regulator.
Reply With Quote
  #8  
Old 10-01-2008, 02:19 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 3,489
Thanks: 27
Thanked 801 Times in 661 Posts
Default Re: MEP-018a tripping breaker

problem could be in the voltage adjust knob, not the regulators? Sounds suspicious to me.
Reply With Quote
  #9  
Old 10-01-2008, 06:51 PM
Rich Mc Rich Mc is offline
Registered-II
 
Join Date: Nov 2004
Location: Near Boston
Posts: 270
Thanks: 12
Thanked 41 Times in 38 Posts
Default Re: MEP-018a tripping breaker

While inquiring about a missing regulator on one of my military units(5KW) at one of the big surplus houses the first question ask of me was; what is the ohmic value of the voltage control pot on your unit? then it was stated "If it is not the correct pot for the regulator you install you will have problems". I don't recall the details but I do recall the warning. I guess the regulators are not 100% interchangeable between different models.
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
MEP-018a firemedic Military MEP and Aircraft Gen-Sets 2 07-28-2008 08:34 AM
MEP 018A questions sdwest Military MEP and Aircraft Gen-Sets 15 07-26-2008 12:20 PM
Breaker, breaker! (circuit breakers) Nubian Onan Generators 5 02-12-2008 07:34 AM
Exciter Breaker Tripping in4ni Onan Generators 9 07-03-2007 05:36 PM
mep-018a questions Jim Kinler Generators & Motors General Discussion 3 05-28-2007 01:51 PM


All times are GMT -4. The time now is 04:28 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark
A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2012 by Harry Matthews
P.O. Box 5612 - Sarasota, FL 34277