Generac Generators (SEARS, etc.)

Generac 7000EXL Voltage Problem


Well this is all new to me, let me see if I can make this understandable:) I'm not an electrician,...

this thread has 5 replies and has been viewed 1872 times

Reply
 
Thread Tools Display Modes
  #1  
Old 11-08-2008, 07:44 PM
David G. David G. is offline
Registered
 
Join Date: Nov 2008
Location: Starks, La. USA
Posts: 4
Thanks: 2
Thanked 0 Times in 0 Posts
Default Generac 7000EXL Voltage Problem

Well this is all new to me, let me see if I can make this understandable I'm not an electrician, but I do have some knowledge of it. If I unplug leads coming off stator I measure 170+ volts to ground @60 hertz. Between leads 44 & 22 I see 340+volts. Between lead 11&22 or 11&44 it's 170 volts. Lead 11 is the neutral. If I plug these back in I have little or no voltage at the outlets. 8+volts on the 120's and 16+ on the 240. Question 1. Is this the normal output voltage at the stator, to be regulated by the System Control Board, or am I losing the neutral causing the high voltage? Question 2. If so why do I lose the voltage when I reattach the wires? I have followed the neutral through the part of the circuit I can test and it's good. Could it be apart inside somewhere? This generator has only a couple hours of run time on it. Thank you very much in advance for your help! I'm pretty sure I'll never buy another generac.
Reply With Quote
Sponsored Links
  #2  
Old 11-10-2008, 01:19 AM
EricWood's Avatar
EricWood EricWood is offline
Registered-III
 
Join Date: Oct 2005
Location: West Concord, Minnesota USA
Posts: 484
Thanks: 16
Thanked 73 Times in 67 Posts
Default Re: Generac 7000EXL Voltage Problem

David, I don't know for sure, that's kind of a tough one to diagnose without the hands-on.

The 8/16 volts sounds like proper residual voltages, such as your voltage regulation is defective/shutdown.

The fact that you unplugged the 11/22/44 plug, and saw high voltages is puzzling.

Looking at the schematic and diagram, I would suggest trying to disconnect the 155 and 156 wires from the idle control transformer to the system control board and isolate them, then try running it verrrrry briefly, to see if you get the elevated voltage with the 11/22/44 plug connected. Also, just to get it out of the picture, disconnect the plug to the idle control solenoid before checking, too.

If the high voltage is valid that you are measuring, then it sounds like your regulator is going to full-field (max DC to the field via the 1 & 4 wires on the 1/2/6/4 plug). If you had isolated originally at the 11/22/44 plug, that eliminates any burden and/or malfunction of the idle control circuit and eliminates the system control board from operating.

Just a hunch until you test again, but if voltage checks out high with 155/156 isolated and all else connected, then possibly the system control board is not sensing loaded/non loaded conditions, and is shutting the voltage regulation down when 155/156 are supplying input into it.

I'm guessing you have the manual, but just in case, here's a link to where it can be viewed on line:

http://www.generac-portables.com/ser...nuals.cfm?rd=1

eric
Reply With Quote
The Following User Says Thank You to EricWood:
  #3  
Old 11-10-2008, 09:44 AM
David G. David G. is offline
Registered
 
Join Date: Nov 2008
Location: Starks, La. USA
Posts: 4
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: Generac 7000EXL Voltage Problem

Eric, Thank you very much for the quick reply.I will try these tests as soon as I have time and get back with you. One thing I forgot to mention. If I disconnect lead 11 and leave the other two connected I then have voltage at the outlets, but its 240 on the 120 receps. As soon as I plug 11 back in it goes back to the residual voltage. I am testing with a fluke 87 vom. The reason I was suspecting the neutral was past experience with my home. I lost the neutral on the service coming to the house and my voltages spiked and ruined a lot of appliances, cordless phones and other things. My expertise is dwindling swiftly.

Thanks again Eric, I really appreciate the help.
Reply With Quote
  #4  
Old 11-10-2008, 10:07 AM
Elden DuRand's Avatar
Elden DuRand Elden DuRand is offline
Subscriber
 
Join Date: Nov 2004
Location: Port St. Joe, Florida USA
Posts: 2,595
Images: 6
Thanks: 976
Thanked 703 Times in 370 Posts
Default Re: Generac 7000EXL Voltage Problem

David:

A suggestion: Try measuring the voltages using an analog meter (remember......they're the kind with the glass front and the little pointy thing that moves when you hook it to a hot circuit)

If the analog meter shows near normal, you've got spikes that the digital meter is misinterpreting. You can try filtering the meter input with a 1K resistor in series with the testing point and a shunt .01 microfarad capacitor across the meter and see if this tames the spikes.

Anyhoo - prolly won't work but worth a shot.

Take care - Elden
Reply With Quote
The Following User Says Thank You to Elden DuRand:
  #5  
Old 11-10-2008, 02:25 PM
David G. David G. is offline
Registered
 
Join Date: Nov 2008
Location: Starks, La. USA
Posts: 4
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: Generac 7000EXL Voltage Problem

Elden,
Thanks very much, I don't have an analog meter, but I checked it with wiggies and it seems to be a little above 240 across the leads. I guess the fluke was giving a bad reading.
Thank again for your response.
David
Reply With Quote
  #6  
Old 11-10-2008, 02:41 PM
David G. David G. is offline
Registered
 
Join Date: Nov 2008
Location: Starks, La. USA
Posts: 4
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: Generac 7000EXL Voltage Problem

Quote:
Originally Posted by EricWood View Post
David, I don't know for sure, that's kind of a tough one to diagnose without the hands-on.

The 8/16 volts sounds like proper residual voltages, such as your voltage regulation is defective/shutdown.

The fact that you unplugged the 11/22/44 plug, and saw high voltages is puzzling.

Looking at the schematic and diagram, I would suggest trying to disconnect the 155 and 156 wires from the idle control transformer to the system control board and isolate them, then try running it verrrrry briefly, to see if you get the elevated voltage with the 11/22/44 plug connected. Also, just to get it out of the picture, disconnect the plug to the idle control solenoid before checking, too.

If the high voltage is valid that you are measuring, then it sounds like your regulator is going to full-field (max DC to the field via the 1 & 4 wires on the 1/2/6/4 plug). If you had isolated originally at the 11/22/44 plug, that eliminates any burden and/or malfunction of the idle control circuit and eliminates the system control board from operating.

Just a hunch until you test again, but if voltage checks out high with 155/156 isolated and all else connected, then possibly the system control board is not sensing loaded/non loaded conditions, and is shutting the voltage regulation down when 155/156 are supplying input into it.

I'm guessing you have the manual, but just in case, here's a link to where it can be viewed on line:

http://www.generac-portables.com/ser...nuals.cfm?rd=1

eric
Eric,
I did those tests with the 155/156 and idle control solenoid disconnected, still just residual voltage. I gave some false information in the first post. 22 is the neutral. When I did those same test with 22 disconnected I got 212 volts at the 120 receps and a little above 240 @ the 220 recep. As soon as I reconnect 22 all the voltage leaves except residual. You were right on with the fluke, I think it was showing spikes. I didn't have an analog meter but I checked it with wiggies and it was a little above 240 across the leads.Thanks again.
Reply
Reply


Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Coleman Generator problem, low voltage goatchay Generators & Motors General Discussion 12 10-03-2008 12:43 PM
Onan voltage problem pward99 Onan Generators 1 10-01-2008 12:27 AM
Generac 3500XL problem Charlie Herrmann Generac Generators (SEARS, etc.) 4 06-12-2007 02:22 PM
Witte Generator voltage problem? Need help please. bushm0nkey Generators & Motors General Discussion 7 07-14-2005 01:59 PM
Onan 12.0DJC 3CR voltage problem schlosserj Onan Generators 4 11-10-2004 09:44 PM


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On