Generac under voltage shutdown


this thread has 29 replies and has been viewed 12012 times

Reply
 
Thread Tools Display Modes
  #1  
Old 12-07-2011, 06:16 PM
Bawb Bawb is offline
Registered-I
 
Join Date: Nov 2011
Location: Prudhoe Bay, Alaska
Posts: 25
Likes: 1
Liked 3 Times in 2 Posts
Default Generac under voltage shutdown

I have two generacs (model 59180, 700 hours) (model 60541, 8 hours). Both will run for 5 seconds and shut down with an under voltage message. The 700 hour one I felt I may have overloaded it operating a 2 hp motor although it was not operating that motor when it quit. The 8 hour model ran fine with about a 3000 watt load and then shut down. I'm operating them through the panel/transfer switch that came with the 59180. There is no utility power here. I know it is not intended as a prime power generator. The plan was to use it a few hours a day for charging a battery bank and running a couple block heaters.

Any ideas would be appreciated. I have a good meter with frequency, amp clamp, etc but the machines won't run long enough to test much. I'm 500 miles from the nearest dealer. Also, I bought them at Costco so the dealers don't feel obligated.
Reply With Quote
Sponsored Links
  #2  
Old 12-07-2011, 09:23 PM
DPeterik DPeterik is offline
Registered-I
 
Join Date: Mar 2011
Location: Two Rivers, Wisconsin
Posts: 74
Likes: 9
Liked 25 Times in 24 Posts
Default Re: Generac under voltage shutdown

I need the serial numbers of these units. Also pull off the covers to the controllers. Need the part number and revision number. The boards should be OH6680B Rev F. Will also need to check software. If it is a 8kw it should be 0J1467 Rev F. 10-20kw should be Rev C.
Can you take pics. There was an issue with some controllers having the under voltage issue. If the controllers meet the criteria this may be a warrantable issue. Let me know I may be able to help you out. These are Honeywell branded but use Nexus controllers.
Reply With Quote
  #3  
Old 12-07-2011, 10:32 PM
Bawb Bawb is offline
Registered-I
 
Join Date: Nov 2011
Location: Prudhoe Bay, Alaska
Posts: 25
Likes: 1
Liked 3 Times in 2 Posts
Default Re: Generac under voltage shutdown

The serial numbers are 6139038 and 6139038. I've attached pictures of the board and software tags.

The smaller unit had an issue early on where the choke plate was sticking but I managed to figure that out on my own. Both choke plates operate freely now.
Attached Thumbnails
010 (1024x768).jpg   011 (1024x768).jpg   012 (1024x768).jpg   013 (1024x768).jpg  
Reply With Quote
  #4  
Old 12-08-2011, 08:14 AM
DPeterik DPeterik is offline
Registered-I
 
Join Date: Mar 2011
Location: Two Rivers, Wisconsin
Posts: 74
Likes: 9
Liked 25 Times in 24 Posts
Default Re: Generac under voltage shutdown

You gave me the same serial number for both. 6139038 is a 10 kw Guardian with a GT530 V-twin engine. Purchased on 6-24-2011, warranty expires on 6-24-2014.
Recheck the other serial number. The first two pics, that board is the bad one. needs to be replaced with a OH6680B. Will need to check on the Honeywell board, those are programmed specific to Honeywell.
Reply With Quote
  #5  
Old 12-08-2011, 03:34 PM
Bawb Bawb is offline
Registered-I
 
Join Date: Nov 2011
Location: Prudhoe Bay, Alaska
Posts: 25
Likes: 1
Liked 3 Times in 2 Posts
Default Re: Generac under voltage shutdown

Whoops. Second serial number is 6659492.
Reply With Quote
  #6  
Old 12-08-2011, 05:55 PM
DPeterik DPeterik is offline
Registered-I
 
Join Date: Mar 2011
Location: Two Rivers, Wisconsin
Posts: 74
Likes: 9
Liked 25 Times in 24 Posts
Default Re: Generac under voltage shutdown

Email, me at dpxholdings@msn.com. I will send you a diagnostic manual for these units. On the Honeywell you will need to perform a Fixed Excitation/Rotor Amp Draw test. The manual will take you step by step.
The other unit may be a controller replacement due to the Rev # and serial number.
I will give you more info on this when you email me.
P.S. I may not be able to reply until later tonight or tomorrow.
Thanks
Dave
Reply With Quote
  #7  
Old 12-09-2011, 01:21 AM
Bawb Bawb is offline
Registered-I
 
Join Date: Nov 2011
Location: Prudhoe Bay, Alaska
Posts: 25
Likes: 1
Liked 3 Times in 2 Posts
Default Re: Generac under voltage shutdown

It should be in your mailbox. Thanks.
Reply With Quote
  #8  
Old 12-15-2011, 07:10 PM
Bawb Bawb is offline
Registered-I
 
Join Date: Nov 2011
Location: Prudhoe Bay, Alaska
Posts: 25
Likes: 1
Liked 3 Times in 2 Posts
Default Re: Generac under voltage shutdown

Dave:

I emailed you, but am getting no reply. Maybe it got caught in your spam filter.

Bob
Reply With Quote
  #9  
Old 12-19-2011, 03:49 AM
Bawb Bawb is offline
Registered-I
 
Join Date: Nov 2011
Location: Prudhoe Bay, Alaska
Posts: 25
Likes: 1
Liked 3 Times in 2 Posts
Default Re: Generac under voltage shutdown

This diagnostic manual, (OH9172 Rev D) does not list the 12kw model. Should I slide the 10kw back into firing position or use this manual on the 12kw that is already hooked to gas and the panel?
Reply With Quote
  #10  
Old 12-19-2011, 06:29 PM
DPeterik DPeterik is offline
Registered-I
 
Join Date: Mar 2011
Location: Two Rivers, Wisconsin
Posts: 74
Likes: 9
Liked 25 Times in 24 Posts
Default Re: Generac under voltage shutdown

The 12 kw and the 14 kw are the same unit. If it lists a 14 use that.
Reply With Quote
The Following User Likes This Post:
  #11  
Old 12-28-2011, 06:46 AM
Bawb Bawb is offline
Registered-I
 
Join Date: Nov 2011
Location: Prudhoe Bay, Alaska
Posts: 25
Likes: 1
Liked 3 Times in 2 Posts
Default Re: Generac under voltage shutdown

This report is about the results of tests done on a 12 Kw with about 7 hours total run time with a 3 Kw load.

The results of Test 4, the fixed excitation/ rotor amp draw test, were zero or residual voltage and zero current draw. This leads to test eight, resistance check of rotor circuit, all of which were open. This leads to test nine, check brushes and slip rings, the first step of which is commence major disassembly.

Looking into the prospect of major disassembly, I find that some of the wires, like the 8 ga ones coming from the gen head look and feel to be glued or melted together for about 3 inches after exiting the gen head and before entering the wire loom. It is difficult to get a good look and feel of them in their installed position.
Reply With Quote
  #12  
Old 12-28-2011, 10:44 AM
Bassplayer1985 Bassplayer1985 is online now
Subscriber
 
Join Date: Sep 2011
Location: Southwestern Connecticut
Posts: 1,005
Likes: 144
Liked 321 Times in 252 Posts
Default Re: Generac under voltage shutdown

Quote:
Originally Posted by Bawb View Post
Looking into the prospect of major disassembly, I find that some of the wires, like the 8 ga ones coming from the gen head look and feel to be glued or melted together for about 3 inches after exiting the gen head and before entering the wire loom. It is difficult to get a good look and feel of them in their installed position.
I would suspect the machine was overloaded and unbalanced between the neutral. I ran into the same issue with my 7k, and the hottest wire was the neutral. Once that melted the other wires began to thermally fail. Once I got inside the panel just about every single wire had melted together.
Reply With Quote
  #13  
Old 12-29-2011, 10:20 AM
Bawb Bawb is offline
Registered-I
 
Join Date: Nov 2011
Location: Prudhoe Bay, Alaska
Posts: 25
Likes: 1
Liked 3 Times in 2 Posts
Default Findings

[ATTACH]Click image for larger version

Name:	038 (1024x768).jpg
Views:	50
Size:	61.2 KB
ID:	124206[/ATTACH]

So, after 7 hours of operation with a 3K load, one of the brushes was burned, twisted and mutilated. The other one is perfect.

Once I got it flipped over and in the light, there was nothing wrong with the wires exiting the alternator.
Attached Thumbnails
034 (1024x768).jpg  
Reply With Quote
  #14  
Old 12-29-2011, 03:12 PM
Bassplayer1985 Bassplayer1985 is online now
Subscriber
 
Join Date: Sep 2011
Location: Southwestern Connecticut
Posts: 1,005
Likes: 144
Liked 321 Times in 252 Posts
Default Re: Generac under voltage shutdown

Wow thats a crispy bush assembly. Its def arcing.

1. My first guess is there is a short in the rotor windings.
2. Insulation near the slip rings has broken down and the brush is arcing to ground

Not sure where to go from here, a tech can troubleshoot more if the problem lies in the voltage regulator, but for it to be arcing like that suggests to me a bad connection or insulation failure.
Reply With Quote
  #15  
Old 12-29-2011, 07:39 PM
Power Power is online now
Registered-III
 
Join Date: Aug 2011
Location: New Jersey
Posts: 2,793
Likes: 674
Liked 1,454 Times in 914 Posts
Default Re: Generac under voltage shutdown

Purchased on 6-24-2011, warranty expires on 6-24-2014.
If it is under warranty, I would not fool with it. That amount of heat probably damaged slip ring assembly. It may no longer be concentric, and replacing brush & holder may not fix the issue.
Reply With Quote
  #16  
Old 12-29-2011, 08:35 PM
Bawb Bawb is offline
Registered-I
 
Join Date: Nov 2011
Location: Prudhoe Bay, Alaska
Posts: 25
Likes: 1
Liked 3 Times in 2 Posts
Default Re: Generac under voltage shutdown

Due to the remote location, a warranty claim would involve shipping costs equal to about half the value of the gen set.
Reply With Quote
  #17  
Old 12-29-2011, 08:46 PM
Ed Sparks Ed Sparks is offline
Subscriber
 
Join Date: Sep 2011
Location: Bailey Island, Maine
Posts: 4,162
Likes: 2,501
Liked 3,154 Times in 1,801 Posts
Default Re: Generac under voltage shutdown

you mean generac doesn't have an authorized service center up there on the north pole???
Reply With Quote
  #18  
Old 12-30-2011, 05:27 PM
Bawb Bawb is offline
Registered-I
 
Join Date: Nov 2011
Location: Prudhoe Bay, Alaska
Posts: 25
Likes: 1
Liked 3 Times in 2 Posts
Default Re: Generac under voltage shutdown

>>you mean generac doesn't have an authorized service center up there on the north pole??

Clearly an oversight on their part.
Reply With Quote
  #19  
Old 12-31-2011, 12:55 PM
Bassplayer1985 Bassplayer1985 is online now
Subscriber
 
Join Date: Sep 2011
Location: Southwestern Connecticut
Posts: 1,005
Likes: 144
Liked 321 Times in 252 Posts
Default Re: Generac under voltage shutdown

Looking for the pics again Bawb, I noticed that it is the inner brush thats getting cooked. When the brush holder is mounted, is there any exposure to the metal frame at all? Also is the spring firmly up against the slip rings?
Could you post the picture of the rotor end/slip ring assembly?

A shorted winding in the rotor will definitley cause this and you mentioned the rotor was open circuit. The one part that is escaping me with this conclusion is why just that one brush and not both of them being cooked?

Funny, I actually have a spare rotor here in Connecticut but its only good up to 7k watts for a Generac 7000EXL. Part# B1342G. measures 15 ohms on the rings.
Reply With Quote
  #20  
Old 01-01-2012, 09:36 PM
Bawb Bawb is offline
Registered-I
 
Join Date: Nov 2011
Location: Prudhoe Bay, Alaska
Posts: 25
Likes: 1
Liked 3 Times in 2 Posts
Default Re: Generac under voltage shutdown

Picture of slip rings attached.
Attached Thumbnails
035 (1024x768).jpg  
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Generac, low AC voltage on ouput peterbell Generac Generators (SEARS, etc.) 7 09-11-2011 09:57 AM
Voltage Regulator for MC-40 Generac golddredger Generac Generators (SEARS, etc.) 10 01-21-2011 12:50 AM
Generac 5.5 (RV) voltage surges jerseyjim Generac Generators (SEARS, etc.) 4 08-28-2009 01:29 AM
Generac voltage problems kphee Generac Generators (SEARS, etc.) 6 12-09-2008 12:57 AM
Generac 7000EXL Voltage Problem David G. Generac Generators (SEARS, etc.) 5 11-10-2008 02:41 PM