Default Protection of Downstream Loads

I have a Onan 20.ES and it runs well, I'm curious as to what other members do to protect the loads in the event of over/under current, engine failure, fuel loss, etc. With all of the sensitive electronics in todays stoves, flat screens, A/C, etc. I'm somewhat concerned. Thanks
Reply With Quote
Sponsored Links
  #2  
Old 01-11-2018, 02:07:02 PM
Augie1 Augie1 is offline
Registered-I
 
Join Date: Nov 2016
Location: Montevideo, Minnesota, USA
Posts: 79
Thanks: 42
Thanked 27 Times in 17 Posts
Default Re: Protection of Downstream Loads

Most will just let the branch circuit breakers protect the circuit from shorts and overloads. In this area I have never seen over/under voltage protection. I suppose it could be done if you wanted to spend the money. Plug a voltmeter in both lines and monitor it seems to work good. I have volt and amp meters connected ahead of the transfer switch so I know what the generator is putting out before I transfer power to the gen.
Reply With Quote
  #3  
Old 01-11-2018, 02:16:57 PM
Ifix71 Ifix71 is offline
Subscriber
 
Join Date: Mar 2014
Location: Lake Wales, Florida, USA
Posts: 10
Thanks: 24
Thanked 4 Times in 2 Posts
Default Re: Protection of Downstream Loads

I use a computer UPS on my DVR and flat screen , that way it don't
Reboot every Time the lights flicker or you switch power sources.
I did notice during Irma that it don't like a frequency above 61 hertz!
John
Reply With Quote
  #4  
Old 01-11-2018, 03:06:51 PM
motion motion is offline
Registered-I
 
Join Date: Jul 2015
Location: Mandeville, Louisiana
Posts: 57
Thanks: 0
Thanked 9 Times in 6 Posts
Default Re: Protection of Downstream Loads

Quote:
Originally Posted by Augie1 View Post
Most will just let the branch circuit breakers protect the circuit from shorts and overloads. In this area I have never seen over/under voltage protection. I suppose it could be done if you wanted to spend the money. Plug a voltmeter in both lines and monitor it seems to work good. I have volt and amp meters connected ahead of the transfer switch so I know what the generator is putting out before I transfer power to the gen.
I was thinking about the times you may not be standing near the generator i.e. sleeping or away and something goes wrong. I thought about a shunt trip breaker in conjunction with a over/under voltage, phase loss module. but I'd still need power to trip the breaker.
Reply With Quote
  #5  
Old 01-11-2018, 03:21:43 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,645
Thanks: 656
Thanked 2,096 Times in 1,254 Posts
Default Re: Protection of Downstream Loads

Good question! I think if you have a quality product, that is, a generator which is properly maintained you should have little to worry about.

In my situation, I employ a 1960's designed Onan 7500 watt magneciter JB generator. I was concerned like you about under voltage and more importantly under frequency operation and how this would affect not only connected appliances but the generator itself during under frequency operation as would occur should the generator wind down under load.

So without modifying the genuine Onan designed JB, I designed a separate shunt trip circuit which monitors the generator frequency and automatically disconnect the down stream loads should the frequency go low or high.

I never got around to modifying the shunt trip to not only disconnect the downstream loads but also shut down the plant seeing the generator voltage regulator is susceptible to damage should prolong operation occur at a reduced frequency/RPM.

Today, after some 45+ years of reliable JB operation, I have great confidence in the reliability of my unit that I am not in a hurry to modify my shunt trip to not only disconnect the downstream load but also shut down the plant.

If interested I can send you some information on my simple but reliable black box shunt trip design.
Reply With Quote
  #6  
Old 01-11-2018, 04:57:31 PM
Steve Dawkins Steve Dawkins is online now
Sponsor
 
Join Date: Feb 2005
Location: Virginia Beach, Virginia, USA
Posts: 720
Thanks: 428
Thanked 260 Times in 143 Posts
Default Re: Protection of Downstream Loads

Quote:
Originally Posted by motion View Post
I was thinking about the times you may not be standing near the generator i.e. sleeping or away and something goes wrong. I thought about a shunt trip breaker in conjunction with a over/under voltage, phase loss module. but I'd still need power to trip the breaker.
I don't think you need to go to that extent of protection, unless you've got a lot of expensive equipment to protect. Since you mentioned phase loss, is your genset configured for 3 phase output?

If your generator is supplying whole house power for 120/240V, single phase operation, a good surge protector on your distribution panel should adequately protect the loads from severe overvoltage and spikes. Should you decide to incorporate a shunt trip system, you can get shunt trip breakers that have 12 VDC coils. Thus, you can use battery voltage to operate the shunt trip mechanism. There are other options available for circuit breakers, such as auxiliary contacts. You could wire this into the generator run circuit to stop the engine if the shunt trip activates.
Reply With Quote
  #7  
Old 01-11-2018, 06:31:07 PM
Wayne 440 Wayne 440 is online now
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 5,355
Thanks: 324
Thanked 4,470 Times in 2,124 Posts
Default Re: Protection of Downstream Loads

I have a UPS on my DSL modem, but that is merely for convenience - so I don't have to wait for DSL to resync after a power failure. Other than that, I figure that if some device I have is too "sensitive" to accept power from the RDJC, I should be getting rid of said device anyway.
Reply With Quote
The Following 4 Users Say Thank You to Wayne 440 For This Post:
  #8  
Old 01-11-2018, 08:38:07 PM
dracer dracer is offline
Registered
 
Join Date: Apr 2017
Location: Klamath River, California
Posts: 47
Thanks: 0
Thanked 9 Times in 7 Posts
Default Re: Protection of Downstream Loads

Quote:
Originally Posted by Wayne 440 View Post
I have a UPS on my DSL modem, but that is merely for convenience - so I don't have to wait for DSL to resync after a power failure. Other than that, I figure that if some device I have is too "sensitive" to accept power from the RDJC, I should be getting rid of said device anyway.
I have a ups on my computer and modem and the wif , I think the wireless phone is on it also , we used to have a lot of power outs that where on and offs but when the ranger changed and the new one let the power company trim the the trees that was cured
Reply With Quote
  #9  
Old 01-11-2018, 08:50:24 PM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is online now
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 3,923
Thanks: 644
Thanked 2,123 Times in 1,235 Posts
Default Re: Protection of Downstream Loads

Quote:
Originally Posted by motion View Post
I was thinking about the times you may not be standing near the generator i.e. sleeping or away and something goes wrong. I thought about a shunt trip breaker in conjunction with a over/under voltage, phase loss module. but I'd still need power to trip the breaker.
I think that what you describe, possibly with the addition of an under/over frequency trip could be of some use in preventing damage to some loads under unusual generator operation. Whether it's actually worth the cost, bother, lower system reliability, and inevitable nuisance trips is a question only you can answer. For me, the answer is 'no'.
Reply With Quote
  #10  
Old 01-11-2018, 10:26:37 PM
I like oldstuff I like oldstuff is offline
Subscriber
 
Join Date: Jan 2012
Location: Milwaukee, Wisconsin, USA
Posts: 4,739
Thanks: 1,003
Thanked 4,409 Times in 1,874 Posts
Default Re: Protection of Downstream Loads

Keep in mind that a lot of the new electronics (computers, tv's, cable boxes and so on) use a switching power supply that rectifies ac to dc. These will work fine from around 80 volts @~40hZ and up to 250V @100+ hZ. If the power drops off or goes low from your gen these things will just stop making enough dc to power the device. I don't know however if they have any over voltage protection.
Reply With Quote
  #11  
Old 01-11-2018, 10:46:27 PM
rmchambers rmchambers is offline
Subscriber
 
Join Date: Dec 2011
Location: Stratford, Connecticut, USA
Posts: 603
Thanks: 105
Thanked 380 Times in 196 Posts
Default Re: Protection of Downstream Loads

I have a 3600W Trace/Xantrex inverter and 8 golf cart batteries. I run the loads I want to run from this. (at night it's quiet) the entire output from the generator goes into this device when I fire it up. The inverter will send power through to the loads and charge the batteries up, if the generator stops or gets wiggy, the inverter will drop off the power and work like a UPS and feed the loads.
Reply With Quote
The Following User Says Thank You to rmchambers For This Post:
  #12  
Old 01-12-2018, 06:46:01 AM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 2,734
Thanks: 178
Thanked 662 Times in 532 Posts
Default Re: Protection of Downstream Loads

Yes you can blow stuff up with a generator

my late friend Tom had one that did this until I fixed it.
Mr "drier outlet back-feed" gave me his old "problem" generator when
he went to a 200A transfer switch and twice as big in generator size.
gave = I paid the $75 late fees on the trailer title transfer and for the new plates.

the problem; it was running out of governor spring under heavy load.
rather than move the working end closer to the pivot
he tightened the adjustment end, but when the load came off,
HZ and V went through the roof, and fritzed goodies. [induction regulated]

I went to a longer softer spring that, after some trial and error, held 60 HZ
from a light load through breaker opening overload without hunting.
and learned a lot about mechanical inverse feed back!

positive feed back [over center spring] or
inverse feed back [above the tangent spring]
__________________
.
by using this free advise, you, your heirs, etc
absolve, save, and hold harmless the advisor.
CAVEAT EMPTOR
YMMV

Last edited by armandh; 01-12-2018 at 07:19:10 AM.
Reply With Quote
  #13  
Old 01-12-2018, 07:23:42 AM
motion motion is offline
Registered-I
 
Join Date: Jul 2015
Location: Mandeville, Louisiana
Posts: 57
Thanks: 0
Thanked 9 Times in 6 Posts
Default Re: Protection of Downstream Loads

Thanks for all of the replies. Mine is set up for 208v, three phase, 4wire. As other have said it's not super important but would be nice (belts and suspenders). It's something that I'll think about.
Reply With Quote
  #14  
Old 01-12-2018, 10:17:36 AM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,645
Thanks: 656
Thanked 2,096 Times in 1,254 Posts
Default Re: Protection of Downstream Loads

With all due respect did you really say this? "the problem; it was running out of governor spring under heavy load."!

What kind of a machine was that? And to try and correct the problem the way mentioned. Wow! Not a good idea. Sounds like it was not set up properly to begin with.
Reply With Quote
  #15  
Old 01-12-2018, 01:32:54 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 3,451
Thanks: 4,401
Thanked 1,450 Times in 962 Posts
Default Re: Protection of Downstream Loads

My 6-1/2 kw Kohler came with what looked like a piece of wire twisted around to make a "spring" for the governor. It would go from over 63 cycles to less than 58 when a 5 kw lamp was thrown on the line.

I did pretty much the same thing. Found a suitable spring and adjusted it until it would just not hunt. Problem solved.
Reply With Quote
  #16  
Old 01-12-2018, 03:17:19 PM
Newoldstock Newoldstock is offline
Registered-I
 
Join Date: Dec 2013
Location: Toronto Canada
Posts: 489
Thanks: 151
Thanked 270 Times in 123 Posts
Default Re: Protection of Downstream Loads

Quote:
Originally Posted by Vanman View Post
My 6-1/2 kw Kohler came with what looked like a piece of wire twisted around to make a "spring" for the governor. It would go from over 63 cycles to less than 58 when a 5 kw lamp was thrown on the line.

I did pretty much the same thing. Found a suitable spring and adjusted it until it would just not hunt. Problem solved.
Moving the spring closer to the fulcrum of the governor arm will increase sensitivity.
If the engine starts to hunt it is too sensitive and a different choice of spring might help.

Long springs have a more constant tension rate short ones are more progressive ( the shorter less likely to hunt the longer ones more )

A dash pot from a different carb might also help with hunting., but this will slow load responds time.

Reply With Quote
  #17  
Old 01-12-2018, 07:04:59 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 3,451
Thanks: 4,401
Thanked 1,450 Times in 962 Posts
Default Re: Protection of Downstream Loads

Yes, indeed not having access to factory parts I selected a fairly long spring to ensure that I would be able to adjust the sensitivity to be as sensitive as possible, ie just less than continuous hunting. It works great.
Reply With Quote
  #18  
Old 01-13-2018, 08:05:09 AM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 2,734
Thanks: 178
Thanked 662 Times in 532 Posts
Default Re: Protection of Downstream Loads

same thing

a 7.2 KW K-582 powered 1800 rpm generator
1964 vintage and no knowing how many amateur repairs.

when the load went on the spring pulled the throttle open until it fully collapsed
way short of full open throttle, it was probably NOT OEM

finding the right spring at the right angle to give quick response with out hunting
through out the load range took a bit of experimentation.

Quote
Moving the spring closer to the fulcrum of the governor arm will increase sensitivity. if you don't move the other end to the original tangent
If the engine starts to hunt it is too sensitive and a different choice of spring might help.
but if the spring is within the governors ability to pull the throttle closed changing the angle of the fixed end changes sensitivity as well

less inverse feed back = more sensitivity and likely-hood to hunt

as you move the fixed end of the spring above the arc the first part of the governor pull has greater mechanical advantage
photo less/more sensitivity
Attached Thumbnails
Click image for larger version

Name:	img445.jpg
Views:	32
Size:	51.3 KB
ID:	300322  
__________________
.
by using this free advise, you, your heirs, etc
absolve, save, and hold harmless the advisor.
CAVEAT EMPTOR
YMMV

Last edited by armandh; 01-13-2018 at 12:58:24 PM.
Reply With Quote
The Following User Says Thank You to armandh For This Post:
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Low PF loads on Onan CCK and NHD Magnetite Onan Generators 3 06-15-2012 05:48:00 AM
RUSSELL Horsepowers at various loads Gary K Steam Stationary Engines, Traction Engines, Steam Boats 0 01-05-2012 12:56:29 PM
Loads & Loads of Engines Doug Waggonner Oil Field Engines 26 12-14-2011 10:13:46 PM
Wisconsin TJD Loads up budro Wisconsin Engines 2 10-20-2010 04:39:39 PM
balancing loads John T Generators & Electric Motors General Discussion 10 09-13-2004 08:14:51 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 10:42:13 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277