Hello all,

I was given an Onan 100kw ENBA and 1K amp switcher (nice gift right! especially considering it has about 300hrs run time) but its factory natural gas. I purchased the Impco Model E gassifier/reg and Impco VFF30 (flow back stop) to convert to propane as we have no NG availability in my area.

NOTE- THis is the ENBA with the turbocharged Ford 460 and NOT the V10. The V10 lists fuel as NG/Propane, the 460 is NG.




Here is a pic of the components pre turbo. There is a 'Maxitrol' reg and what I am assuming is the mixer going into the turbo inlet on the compressor.

Questions:

-Do I remove the Maxitrol reg and connect the Model E gas output into the mixer or should leave (or would it matter) if I left this reg and connected the Impco into this reg? I almost like the idea of leaving it IF it doesnt hurt anything as it would be cool to have a 'NG/Propane ready' generator.


-Is there anything else I need to do to be able to safely run this engine with propane (jetting, ignition timing or other)?

-Do I need a post regulator pressure gauge or secondary regulation?

Thanks for any help on this matter!

~JH
Reply With Quote
Sponsored Links
  #2  
Old 12-10-2017, 12:18:15 AM
ulgydog56 ulgydog56 is offline
Registered
 
Join Date: Dec 2017
Location: Smithcreek, Michigan
Posts: 47
Thanks: 10
Thanked 11 Times in 7 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

maxietrol is a pressure regulater,nat gas runs at 3.3 to3.8 in equip normally in usa,check equipment,ratings,lp gas normally runs at 10 to 12 ins of water collium, regs are adjustable,but from 1 gas to another u normally change regulators or springs and possably jet or orface size,should be a kit for it,make sure its got to be right......
Reply With Quote
  #3  
Old 12-10-2017, 03:59:43 AM
armandh armandh is online now
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 2,960
Thanks: 234
Thanked 774 Times in 605 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

this is a total guess but
once the pressure is reduced to the inlet of the demand regulator
with a typical tank regulator of sufficient size

if the arrow in the picture is pointing to an adjustment screw with jam nut
it is likely the mixture to be adjusted less for the higher BTU fuel
Attached Thumbnails
Click image for larger version

Name:	adjustment.JPG
Views:	217
Size:	34.2 KB
ID:	298047  
Reply With Quote
  #4  
Old 12-10-2017, 04:13:20 AM
AngrySailor AngrySailor is online now
Subscriber
 
Join Date: Apr 2017
Location: West Prince, Prince Edward Isand, Canada
Posts: 1,346
Thanks: 563
Thanked 877 Times in 492 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

I wonder how long this would run on a BBQ tank

What a gift! Do you have a use for all that power?
Reply With Quote
The Following User Says Thank You to AngrySailor For This Post:
  #5  
Old 12-10-2017, 04:30:42 AM
armandh armandh is online now
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 2,960
Thanks: 234
Thanked 774 Times in 605 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

depends on the load

had a 71 Lincoln with that 460 motor
it had a GM style starter & solenoid
Reply With Quote
  #6  
Old 12-10-2017, 10:23:31 AM
pegasuspinto pegasuspinto is offline
Registered-III
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 2,718
Thanks: 332
Thanked 1,282 Times in 836 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

The device labeled "maxtrol" in the picture is the demand regulator and that is the component that will need changed.

On dual fuel units, there will be a T between the demand regulator and the mixer and there will be a second demand regulator, one for each fuel, and the inlet solenoids select between the two.

Natural gas gensets, especially this big, use pressures more in the 11-14 inches range.

I am a little puzzled because the demand regulator is normally installed with the 'snout' straight up or straight down, because it's calibrated with a weight inside. Sometimes all you need to do to convert them is to flip it over and remove the spring.
Reply With Quote
  #7  
Old 12-10-2017, 11:26:00 AM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is offline
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 4,221
Thanks: 738
Thanked 2,373 Times in 1,377 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

Quote:
Originally Posted by AngrySailor View Post
I wonder how long this would run on a BBQ tank
Somewhere around 14 GPH Propane at full load and (guessing) 6 GPH at no load. With 3 gallons in your BBQ tank, that's 30 minutes at no load and 13 minutes at full load. Of course the BBQ tank wouldn't support this draw rate...
Reply With Quote
  #8  
Old 12-10-2017, 11:51:14 AM
JT240Z JT240Z is offline
Subscriber
 
Join Date: Dec 2011
Location: Grayson, Georgia
Posts: 259
Thanks: 0
Thanked 81 Times in 50 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

That "gift" is going to cost you a ton to operate.
Reply With Quote
The Following User Says Thank You to JT240Z For This Post:
  #9  
Old 12-10-2017, 06:35:33 PM
Jonny Hotnuts Jonny Hotnuts is offline
Registered
 
Join Date: Dec 2017
Location: Corbett, Oregon, USA
Posts: 16
Thanks: 0
Thanked 10 Times in 6 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

Yes 'Big Pig' will use a fair clip of fuel. My calcs are a little better than the above estimation of GPH burn but do understand this is a big piece. My demand range for my house would realistically be in the 8K (lowest without heat and the water heaters cycled off) to 25-35K (highest). As can be heard in the video the sound is the WIND in our area (Columbia River Gorge). Its not uncommon for us to loose power for a few hours (often) or days (rare but it happens) a few times each winter. Ironically our power was out during the video and the second time in the last few days. I estimate the generator will be running at 10-20% load and we will only use it during awake-occupied times.

-My plan is to use 4x 100# tanks (ganged) and have 6x or so 30# 'forklift LP' tanks as backup.



Quote:
Originally Posted by pegasuspinto View Post
The device labeled "maxtrol" in the picture is the demand regulator and that is the component that will need changed.



Natural gas gensets, especially this big, use pressures more in the 11-14 inches range.

I am a little puzzled because the demand regulator is normally installed with the 'snout' straight up or straight down, because it's calibrated with a weight inside. Sometimes all you need to do to convert them is to flip it over and remove the spring.
I found this from Maxitrol for this 'LMP 53' regarding using this with propane:

Remove the cap on the end of the cone & notice the white plastic threaded adjuster that compresses the spring.
Remove the adjuster with a screwdriver & take out the spring.
Turn in the adjuster approx 2/3 - 3/4 of the way down the threaded cone so there is room to store the spring above the adjuster.
Replace the threaded cap at the end of the cone.
The spring is now just in storage and NOT used to regulate pressure, so now instead the regulator controls volume or flow, based on engine demand created by vacuum from the engine.
The device must now be positioned with the cone pointed DOWN, so that the internal "valve" will drop down and shut off the fuel until engine demand / vacuum calls for it.



Got the big pig to run!

I didnt point the Maxitrol down during test but it is now. I also have not connected the coolant passage lines to the gasifier or connect the back purge device. I just wanted to see if it fired and ran ok.

https://www.facebook.com/jonny.hotnu...3624522303418/


I was actually shocked how fast it started after not being run since 2003.
It fired in a split second and was running very smoothly.

Now the big question:

Now that shes running, how can I tell if its running healthy? Meaning if this was a gas engine I could check AFR/EGT or read plugs or listen to any knock to get an idea of engine health.
Some have mentioned that I may need to adjust mixture/jetting but how can you tell if any changes made are beneficial/detrimental?

Sorry if this is a bone headed question; this propane stuff is WAY out of my wheelhouse.

Oh....AND BIG PIG LIVES! LOL

~JH
Reply With Quote
The Following User Says Thank You to Jonny Hotnuts For This Post:
  #10  
Old 12-10-2017, 06:48:47 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 6,266
Thanks: 370
Thanked 5,282 Times in 2,549 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

I claim no expertise, but FYI- years ago my employer installed a 30kW Kohler and used 4 x 100 lb tanks as a fuel supply. The actual load was about 10kW, and the tanks would not vaporize an adequate volume below about 40 degrees.

My advice- consider liquid feed and a much larger tank arrangement.
Reply With Quote
The Following User Says Thank You to Wayne 440 For This Post:
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan Microlite 2.5 Genset Propane Generator RMoe Onan Generators 2 01-19-2016 05:04:38 PM
A 1983 1 KW Onan genset on Propane analog man Onan Generators 3 11-15-2010 01:45:19 AM
30RZGB Gas Propane Genset Trouble Joe Batts Kohler Generators 3 09-07-2010 03:05:53 PM
Kurz & Root 100kw genset Fatboy Generators & Electric Motors General Discussion 18 12-18-2007 11:32:18 PM
HELP, Propane genset delemma Gary Koleno Onan Generators 14 11-22-2004 01:58:57 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 03:36:12 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277