Genset 100kw ENBA NG to Propane Questions


this thread has 65 replies and has been viewed 2279 times

Reply
 
Thread Tools Display Modes
  #21  
Old 12-11-2017, 12:50:11 PM
EricWood's Avatar
EricWood EricWood is online now
Registered-III
 
Join Date: Oct 2005
Location: West Concord, Minnesota USA
Posts: 1,900
Thanks: 239
Thanked 1,365 Times in 745 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions

Natural gas set up is going to run a little too rich on propane, at the same settings.
Reply With Quote
Sponsored Links
  #22  
Old 12-11-2017, 12:53:30 PM
reid070 reid070 is offline
Registered-I
 
Join Date: Dec 2015
Location: Wentworth, Nova Scotia, Canada
Posts: 76
Thanks: 98
Thanked 22 Times in 14 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions

If it was running on NG previously you will be richer running on propane . Be careful as richer with dry fuels can burn valves . Opposite of gasoline

Steve
Reply With Quote
The Following User Says Thank You to reid070 For This Post:
  #23  
Old 12-11-2017, 03:11:22 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 15,308
Thanks: 404
Thanked 5,516 Times in 4,008 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

Generally engines consume fuel proportional to kw rating, ei doubling the rating doubles the fuel consumption ( both no-load and full load).

So with a 100kw gen and only needing a 25 kw gen your about 4X oversized on the gen, that will cost you BIG TIME in extra fuel use. So much that you might save money by giving the 100kw gen away for free and buying a used gen of correct size. ( do need to be oversized a little to start big motors if you have any).

For comparison if had a 30kw gen and only needed 15kw gen then after ~ 2 weeks of cumulative run time the extra gasoline consumption of larger gen would be about the cost of a buying a used 15kw Onan gen. Run your fuel cost numbers, over sized gens only make cost sense if you hardly ever use them, but then again you will have to run them periodically to exercise them .
Reply With Quote
  #24  
Old 12-12-2017, 12:06:03 AM
Jonny Hotnuts Jonny Hotnuts is offline
Registered
 
Join Date: Dec 2017
Location: Corbett, Oregon, USA
Posts: 16
Thanks: 0
Thanked 10 Times in 6 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

Quote:
Originally Posted by len k View Post
Generally engines consume fuel proportional to kw rating, ei doubling the rating doubles the fuel consumption ( both no-load and full load).

So with a 100kw gen and only needing a 25 kw gen your about 4X oversized on the gen, that will cost you BIG TIME in extra fuel use. So much that you might save money by giving the 100kw gen away for free and buying a used gen of correct size. ( do need to be oversized a little to start big motors if you have any).

For comparison if had a 30kw gen and only needed 15kw gen then after ~ 2 weeks of cumulative run time the extra gasoline consumption of larger gen would be about the cost of a buying a used 15kw Onan gen. Run your fuel cost numbers, over sized gens only make cost sense if you hardly ever use them, but then again you will have to run them periodically to exercise them .
Let me clarify, its REALLY only just a mere 66kw at single so it will hardly use ANY fuel right?!!

-I guess this would be a bad time to suggest I was considering a turbo upgrade? I have a spare FP Billet GT3582r that would look AWESOME on this Onan!


Truth is I get that it is more generator than I need....however....the kid in me likes the fact that its ridiculous. If it was just a little to big it would be meh. The fact that it is a mountain makes me laugh. Now, I NEVER said I made good decisions.



Yeah, it will use lots of gas but IMO one can not put a price on awesomeness. LOL

~JH
Reply With Quote
  #25  
Old 12-12-2017, 01:09:52 AM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is offline
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 3,919
Thanks: 644
Thanked 2,120 Times in 1,233 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

Quote:
Originally Posted by Jonny Hotnuts View Post
...Let me clarify, its REALLY only just a mere 66kw at single so it will hardly use ANY fuel right?...
I think you're being facetious, but no. Lightly loaded, it'll still inhale gas as if it were a 100 kW set, even though you'll see only 66kW of capacity.
Reply With Quote
  #26  
Old 12-12-2017, 02:28:41 AM
AngrySailor AngrySailor is offline
Subscriber
 
Join Date: Apr 2017
Location: West Prince, Prince Edward Isand, Canada
Posts: 455
Thanks: 119
Thanked 283 Times in 155 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions

Johnny, you and I have the same "issues" I would say
Attached Thumbnails
Click image for larger version

Name:	IMG_0665.JPG
Views:	50
Size:	113.5 KB
ID:	298164   Click image for larger version

Name:	IMG_1335.JPG
Views:	51
Size:	34.1 KB
ID:	298165   Click image for larger version

Name:	IMG_1326.PNG
Views:	50
Size:	326.4 KB
ID:	298166  
Reply With Quote
  #27  
Old 12-12-2017, 10:55:05 AM
grif grif is offline
Registered-III
 
Join Date: Oct 2011
Location: Yakima, Washington
Posts: 1,254
Thanks: 443
Thanked 320 Times in 236 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions

Seems like you'll keep enough tank pressure for liquid delivery way below zero,,, in my mind something like -30F.
Reply With Quote
  #28  
Old 12-12-2017, 11:10:37 AM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 15,308
Thanks: 404
Thanked 5,516 Times in 4,008 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

Quote:
Originally Posted by Jonny Hotnuts View Post
Yeah, it will use lots of gas but IMO one can not put a price on awesomeness. LOL
Maybe one can't , but the gas company can.....

Bit like driving cross country at 8 mpg in a 1969 Camaro Z-28 with 327 , high lift cams, Holley duel pumpers, headers, chambered exhaust, class winner at the dragway, ( only got to drive it 1 weekend, car sold in 4 days). Dad was a car dealer, we keep couple 55 gal barrels of gas just to make sure we could stay in business, demo and sell the regular cars during Arab Oil Embargo of ~ 1972

Quote:
Originally Posted by Jonny Hotnuts View Post
Let me clarify, its REALLY only just a mere 66kw at single so it will hardly use ANY fuel right?!!
Using post #7 numbers of ~ 6 GPH no-load Propane, 14 GPH full load, which sound reasonable,
I estimate your 100kw gen at 8kw load is 6.6 GPH, at 25kw load 8.
Whereas a 25kw gen at 8kw load is 2.1 , 25 kw load 3.5, big difference!!

Problem is 100kw gen no-load will use ~ 4X fuel of a 25kw gen at no-load.......no-load consumption of oversized engines is wallet killer on long runs (a day or so) . And as you apply a load fuel consumption only goes up from there. Run fuel numbers for a day or week run, costs will surprise you.

Unless your Bill Gates after some run time cost gets so bad you'll want to shut it off and sit in dark. Even with a small 7kw gen cost/KWH of electricity will be ~ 4X that of utility at BEST ( full load), maybe 8X at 1/2 load, don't want to even think what it is at 1/4 load. Your MINIMUM fuel cost will be no-load times hours you run it. For 100kw gen, a one week run 24/7 your minimum cost (no-load) would be ~ 1000 gal, if gasoline that would be ~ $2400 That's why it's awesome if someone can afford to run it.

Fuel tank $$..... ignoring vaporization ability , a given tank will only last ~ 44% as long with a 100kw vs 25 kw gen (assumes 25kw load), this 44% drops to 32 % if load is 8kw. This can become a problem during blizzards or emergencies if a truck can't get in to bring more fuel.

.

Last edited by len k; 12-12-2017 at 05:33:16 PM. Reason: Add info, clarify
Reply With Quote
  #29  
Old 12-12-2017, 03:12:42 PM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 2,734
Thanks: 178
Thanked 662 Times in 532 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions

propane is a way richer fuel than NG

and YES you must adjust for it.

a generator that is 17.5 KW on gasoline
is 16 on propane 15 on NG

the different BTU density is substantial about 7% greater in your case
Reply With Quote
  #30  
Old 12-12-2017, 04:59:21 PM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,797
Thanks: 5,039
Thanked 5,438 Times in 2,931 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

Quote:
Originally Posted by Jonny Hotnuts View Post
Let me clarify, its REALLY only just a mere 66kw at single
Looking at the rating tag, it is rated at 300 amps 120/240 3 phase. It is rated 347 amps 120/240 single phase (last box, lower right of tag). It looks like a little more than 66 KW in single phase. What am I misinterpreting here?
Reply With Quote
The Following User Says Thank You to Max Thompson For This Post:
  #31  
Old 12-12-2017, 05:16:51 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 5,345
Thanks: 324
Thanked 4,460 Times in 2,119 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

Quote:
Originally Posted by Max Thompson View Post
Looking at the rating tag, it is rated at 300 amps 120/240 3 phase. It is rated 347 amps 120/240 single phase (last box, lower right of tag). It looks like a little more than 66 KW in single phase. What am I misinterpreting here?
Onan often derates the single phase kW capability of their 3 phase sets considerably more than the laws of physics dictate. I don't know why - but I do know that a generator end that is capable of 240v/347A driven by a turbocharged 460 Ford will typically carry considerably more than 66kW of load at unity power factor.
Reply With Quote
  #32  
Old 12-12-2017, 05:30:08 PM
Jonny Hotnuts Jonny Hotnuts is offline
Registered
 
Join Date: Dec 2017
Location: Corbett, Oregon, USA
Posts: 16
Thanks: 0
Thanked 10 Times in 6 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions

Quote:
Originally Posted by armandh View Post
propane is a way richer fuel than NG

and YES you must adjust for it.

a generator that is 17.5 KW on gasoline
is 16 on propane 15 on NG

the different BTU density is substantial about 7% greater in your case


I read through the ENBA manual and its recommendations for adjusting mix is under full load.

Ok, guys here is a BS question, I know I shouldnt ask but Im gonna:

-I have no prob in installing an O2 bung/sensor in the exhaust however this will be a little ways down the road; there is no real way I can do a 'sniffer' O2 setup as the muffler has no pipe distance and back pulses will contaminate the reading. When I install a bung it will be within 8" of the turbine outlet and pre muffler.
We can say the generator will be running fat on propane with the NG setup; this I get. IN THE MEANTIME is there a 'ball park' adjustment I can do to the mix to get it running 'safer'? (*take note that I do not know if unscrewing the jet at the base of the mixer translates into leaner or richer). Is it possible to say "loosen the jam, and unscrew (or screw in) the mix adjustment a full turn (or whatever) and re-secure the jam. I understand all these engines are different (and how identical engines can have different settings between them just because of no real explainable reason). I am not looking for perfection, only to get it to a place where there isnt a concern that I will burn a valve.


Thanks!

~JH

Also, I am including a garage shot of a couple old trucks of mine for no reason:



---------- Post added at 04:30:08 PM ---------- Previous post was at 04:27:13 PM ----------



(*pic didnt show in previous post)
Reply With Quote
The Following 2 Users Say Thank You to Jonny Hotnuts For This Post:
  #33  
Old 12-12-2017, 06:09:22 PM
Sprbob99 Sprbob99 is offline
Registered
 
Join Date: Dec 2017
Location: Oregon City, Oregon
Posts: 5
Thanks: 7
Thanked 0 Times in 0 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions

I have a 20 kw with a 4 cylandar ford.
I got it with the same by setup. The Marlow was pointed up. I turned it over and ran lp.
You have twice the consumption as I do.
Off a 500 gal tank I am using a first stage reg to reduce to 10lb. Then through a second stage reg to reduce to a 9-13 water column. It ran rich so I adjusted the air fuel mixture to lean it out and it runs great..
Reply With Quote
  #34  
Old 12-12-2017, 06:31:55 PM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is offline
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 3,919
Thanks: 644
Thanked 2,120 Times in 1,233 Posts
Default Re: Genset 100kw ENBA NG to propane questions.

Quote:
Originally Posted by Max Thompson View Post
Looking at the rating tag, it is rated at 300 amps 120/240 3 phase. It is rated 347 amps 120/240 single phase (last box, lower right of tag). It looks like a little more than 66 KW in single phase. What am I misinterpreting here?
The power factor. It's rated at 0.8 PF (even in single phase) so that works out to 347A at 240V, which is 83 kVA.
Reply With Quote
The Following User Says Thank You to Jim McIntyre For This Post:
  #35  
Old 12-12-2017, 08:03:20 PM
Jonny Hotnuts Jonny Hotnuts is offline
Registered
 
Join Date: Dec 2017
Location: Corbett, Oregon, USA
Posts: 16
Thanks: 0
Thanked 10 Times in 6 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions



I took a closer look at the mixer. It appears the only adjustable element is this screw on the backside of the mixer. Can someone confirm if this is in fact the mix control.



This on the front side does not appear to be adjustable.

.

OT III



Pic of the ATS

Also....

I know its going to use a lot of gas, I am not worried about it in the least.

Quote:
Originally Posted by EricWood View Post

Make sure the plugs are set at 0.035", and timing is at 32 BTDC @ 1800 rpms.
Thoughts on going a number colder on the plugs?

~JH
Reply With Quote
  #36  
Old 12-12-2017, 08:08:40 PM
EricWood's Avatar
EricWood EricWood is online now
Registered-III
 
Join Date: Oct 2005
Location: West Concord, Minnesota USA
Posts: 1,900
Thanks: 239
Thanked 1,365 Times in 745 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions

In your second picture in post 35 above, that one that you thought might not be adjustable, is in fact, the power valve. See the embossed "R" next to it? There is a corresponding "L" on the other side. This is a less than 1/2-turn adjusting valve. It don't take much movement to make a change when at full load.

Posting a photo of the style of exhaust adapter I use withe LM2 meter's wideband O2 sensor; it gets in the pipe about 5-6 inches, and at full load, you are not going to have the diluted reading you think you might.
Attached Thumbnails
Click image for larger version

Name:	LM2_exhaust adapter.png
Views:	28
Size:	38.6 KB
ID:	298212  
Reply With Quote
The Following User Says Thank You to EricWood For This Post:
  #37  
Old 12-12-2017, 08:18:43 PM
EricWood's Avatar
EricWood EricWood is online now
Registered-III
 
Join Date: Oct 2005
Location: West Concord, Minnesota USA
Posts: 1,900
Thanks: 239
Thanked 1,365 Times in 745 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions

As for the spark plugs, I'd recommend just staying with the original heat range. I've seen many stand-by gassers with 30 year old plugs in them still purr like a kitten. Pull the plugs for inspection. Are the fairly clean/lightly tanned, or a dull gray? Are the back cylinders partially oil-carbon fouled? If so, may need new valve seals. Treat it to a new set of plugs if they're still original, then recheck them after about 20 hours or so, to see how they look. Should still be pretty white at that point yet.
Reply With Quote
  #38  
Old 12-12-2017, 09:22:36 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 15,308
Thanks: 404
Thanked 5,516 Times in 4,008 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions

On chevys with fouled plugs in rear we just put couple numbers hotter plug in cylinders that had fouled plugs., tends to burn it off. Never had problems, took one car out to ~ 280k before frame got rusty, 5.0L V8 engine was tired but still good.

Last edited by len k; 12-13-2017 at 08:47:51 PM.
Reply With Quote
  #39  
Old 12-13-2017, 12:44:14 AM
AngrySailor AngrySailor is offline
Subscriber
 
Join Date: Apr 2017
Location: West Prince, Prince Edward Isand, Canada
Posts: 455
Thanks: 119
Thanked 283 Times in 155 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions

Love the trucks! Yours looks a like '69-71 c-10... attached is my '68 910 which is now my fathers summer ride. It was my daily until it was rear ended by a drunk and needed a box and frame The '67 biscayne is now my summer car. It sat since '81 when the original owner stopped driving it at about 47,000 miles. He logged every fill up, last was 119th tank of gas is '81 then it sat till this spring when I finally plated it again. It's first trip was 1200 miles to my new place. Made it with no issues
Attached Thumbnails
Click image for larger version

Name:	IMG_0109.jpg
Views:	42
Size:	282.7 KB
ID:	298223  
Reply With Quote
  #40  
Old 12-13-2017, 09:57:43 AM
PopsGarage PopsGarage is offline
Subscriber
 
Join Date: Dec 2013
Location: Barnegat, New Jersey
Posts: 560
Thanks: 176
Thanked 275 Times in 208 Posts
Default Re: Genset 100kw ENBA NG to Propane Questions

Quote:
Originally Posted by Jonny Hotnuts View Post


I read through the ENBA manual and its recommendations for adjusting mix is under full load.

Ok, guys here is a BS question, I know I shouldnt ask but Im gonna:

-I have no prob in installing an O2 bung/sensor in the exhaust however this will be a little ways down the road; there is no real way I can do a 'sniffer' O2 setup as the muffler has no pipe distance and back pulses will contaminate the reading. When I install a bung it will be within 8" of the turbine outlet and pre muffler.
We can say the generator will be running fat on propane with the NG setup; this I get. IN THE MEANTIME is there a 'ball park' adjustment I can do to the mix to get it running 'safer'? (*take note that I do not know if unscrewing the jet at the base of the mixer translates into leaner or richer). Is it possible to say "loosen the jam, and unscrew (or screw in) the mix adjustment a full turn (or whatever) and re-secure the jam. I understand all these engines are different (and how identical engines can have different settings between them just because of no real explainable reason). I am not looking for perfection, only to get it to a place where there isnt a concern that I will burn a valve.


Thanks!

~JH

Also, I am including a garage shot of a couple old trucks of mine for no reason:



---------- Post added at 04:30:08 PM ---------- Previous post was at 04:27:13 PM ----------



(*pic didnt show in previous post)
Jim, nice trucks, the adjustment in the photo is a butterfly valve 1/4 turn from wide open to shut off there might be a R and L on the casting for rich and lean settings..
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan Microlite 2.5 Genset Propane Generator RMoe Onan Generators 2 01-19-2016 05:04:38 PM
A 1983 1 KW Onan genset on Propane analog man Onan Generators 3 11-15-2010 01:45:19 AM
30RZGB Gas Propane Genset Trouble Joe Batts Kohler Generators 3 09-07-2010 03:05:53 PM
Kurz & Root 100kw genset Fatboy Generators & Electric Motors General Discussion 18 12-18-2007 11:32:18 PM
HELP, Propane genset delemma Gary Koleno Onan Generators 14 11-22-2004 01:58:57 AM