MEP-803A Start And Load Test
this thread has 0 replies and has been viewed 1496 times
Old 11-19-2015, 10:50:18 AM
CT-Mike CT-Mike is offline
Default MEP-803A Start And Load Test
Picked up an -803A from Ft Drum back in February with 16 hours showing on the clock. Unit had just been rebuilt at Letterkenny and still had the refurbished tags and final inspection report in the documents box.
It also has the diesel fired hydronic block, nice little bonus. Only visible issue was that someone had bashed some of the sheet metal on the fuel tank end, but otherwise this thing is basically brand new following reset.
Ended up having to tear a lot of it apart to replace the leaky fuel tank drain well nut. Got everything put back together, and had a friend from work come over to help check things out prior to starting. He is the system engineer at responsible for our 5MW emergency diesel generators - just cost me a little pizza and beer for his expertise.
After checking everything out, it fired up after a couple of failures - we're thinking a relay in the starting circuit was sticky and has since freed up.
http://youtu.be/D7dAFxnkOA4
Yesterday I built a redneck load bank using 10KW worth of water heater elements in a barrel full of water. The generator worked flawlessly and didn't even flinch when I threw all 10KW on it simultaneously. Let it run for a little over an hour to drive any condensation out of the windings.
http://youtu.be/tEl45PpaIMo
Overall I couldn't be happier.
Thanks for looking,
Mike
The Following User Says Thank You to CT-Mike For This Post:
Second Load Test For My 15.0JC JohnnyC Onan Generators 5 07-16-2015 12:58:16 PM
best way to do a load test? rodymartin Onan Generators 8 08-27-2013 09:38:00 PM
What are you using to test load your generator? Motorhead Onan Generators 16 12-31-2011 08:27:31 AM
Startup, load test, 120% overload test of MEP-006A sewerzuk Military MEP and Aircraft Gen-Sets 0 10-12-2011 09:19:29 PM
Getting Ready to load Test Cruiser Onan Generators 1 03-05-2010 11:07:55 PM