17kw generac starts and shuts down after 2 sec


this thread has 11 replies and has been viewed 8315 times

Reply
 
Thread Tools Display Modes
  #1  
Old 11-16-2012, 10:34:14 PM
wstang254 wstang254 is offline
Registered
 
Join Date: Nov 2012
Location: Shelton, Connecticut, USA
Posts: 8
Thanks: 0
Thanked 0 Times in 0 Posts
Default 17kw generac starts and shuts down after 2 sec

hi hopefully someone on here can help , i had a customers 17 kw ran for 5 days straight and on the 6th day shut down, checked the gas pressure its good, the unit cranks on manual starts up and shuts down after 2 seconds , red light is on , on the side , can't seem to find someone with same issue on the net .
unit has oil


Thanks to you guys i was able to fix my older dayton which had governor issue , the weights were stuck in the motor and got them to free up , thanks
Reply With Quote
Sponsored Links
  #2  
Old 11-17-2012, 12:01:16 AM
DriverR DriverR is offline
Registered
 
Join Date: Aug 2012
Location: Glastonbury, Connecticut USA
Posts: 282
Thanks: 57
Thanked 91 Times in 67 Posts
Default Re: 17kw generac starts and shuts down after 2 sec

You have come to the right place. The guys will ask for a model #.

I thought we were on the Onan forum, sorry.
Reply With Quote
  #3  
Old 11-17-2012, 12:10:41 AM
wstang254 wstang254 is offline
Registered
 
Join Date: Nov 2012
Location: Shelton, Connecticut, USA
Posts: 8
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: 17kw generac starts and shuts down after 2 sec

unit is 10 months old , bought at apelectric dot com , with 200 se switch , i would have to stop by owners house to get model or serial.
Reply With Quote
  #4  
Old 11-17-2012, 01:05:21 AM
DriverR DriverR is offline
Registered
 
Join Date: Aug 2012
Location: Glastonbury, Connecticut USA
Posts: 282
Thanks: 57
Thanked 91 Times in 67 Posts
Default Re: 17kw generac starts and shuts down after 2 sec

The unit should be covered under warranty, if you want to fix yourself thats fine. It will shut down if certain parameters are not met i.e. oil pressure or not generating. Have you done any type of checking to confirm essential operating conditions. Does it generate within the two seconds prior to shutdown.
Reply With Quote
  #5  
Old 11-17-2012, 09:15:41 AM
Joe Romas Joe Romas is offline
Subscriber
 
Join Date: Jan 2005
Location: Columbus, Ohio
Posts: 405
Thanks: 24
Thanked 93 Times in 85 Posts
Default Re: 17kw generac starts and shuts down after 2 sec

Like driverR says
You could try bypassing the oil pressure switch to rule out low pressure or a bad switch
BUT if there's no or low oil pressure things could get nasty fast
Reply With Quote
  #6  
Old 11-18-2012, 03:23:22 AM
wstang254 wstang254 is offline
Registered
 
Join Date: Nov 2012
Location: Shelton, Connecticut, USA
Posts: 8
Thanks: 0
Thanked 0 Times in 0 Posts
Smile Re: 17kw generac starts and shuts down after 2 sec

thanks alot for the help, unit is covered under warranty , but i wanted to know in time of crisis, you know how hard it is to get a tech out during power outtage, if i get a chance will try to get over to the unit to check a few more of the things everyone suggested.It makes me frustrated and mad when you can't solve something lol. i went to motorcycle mechanic school years ago and after fixing my own generator i find them interesting , like a complecated puzzle , can never learn too much , plus if you find it is something minor during a black out and you can fix it makes one very happy customer

Reply With Quote
  #7  
Old 11-19-2012, 11:27:37 PM
byrone byrone is offline
Registered
 
Join Date: Nov 2012
Location: WS, North Carolina
Posts: 16
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: 17kw generac starts and shuts down after 2 sec

If it shuts down after 4 seconds then it is likely the low oil pressure switch. If it shuts down after 2 seconds, then likely it is the rpm sensor on the flywheel. It can go bad or go out of adjustment. Check the sensor output while running , even if only 2 secs, you should get 0.4-0.6 v AC and the sensor should have 1000 ohms +- 10 % resistance. You can adjust the sensor to flywheel gap down to "one half turn" in Generac speak if the voltage output is not there. Also listen if the starter disengages or not after the 2 sec runtime. I it does disengage like normal, then you likely have an engine problem. But don't know your exact model, so these are only generic Generac troubleshooting guidelines I have learned.
Reply With Quote
  #8  
Old 11-20-2012, 11:29:44 AM
Bassplayer1985 Bassplayer1985 is offline
Subscriber
 
Join Date: Sep 2011
Location: Oakville, Connecticut
Posts: 1,514
Thanks: 194
Thanked 413 Times in 336 Posts
Default Re: 17kw generac starts and shuts down after 2 sec

Wstang,

Did you remove the oil pressure sensor temporarily? Is the customer in Shelton? Shelton is super close, right down Route 8 for me.
Reply With Quote
  #9  
Old 11-20-2012, 08:29:30 PM
byrone byrone is offline
Registered
 
Join Date: Nov 2012
Location: WS, North Carolina
Posts: 16
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: 17kw generac starts and shuts down after 2 sec

Most modern generacs won't start at all unless they see a zero voltage from the oil pressure switch, verifying that it is there, it's a fail safe. So if you remove the oil press switch wire, you should get a no start at all. Unless the logic changed on this model. But worth a try.
Reply With Quote
  #10  
Old 11-21-2012, 09:34:00 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Moderator
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 18,919
Thanks: 9,997
Thanked 16,797 Times in 7,772 Posts
Default Re: 17kw generac starts and shuts down after 2 sec

If it is under warranty. Don't touch it. Generac finds out and you can kiss warranty goodby. I have seen it happen many times.
Reply With Quote
  #11  
Old 11-21-2012, 10:26:23 AM
Bassplayer1985 Bassplayer1985 is offline
Subscriber
 
Join Date: Sep 2011
Location: Oakville, Connecticut
Posts: 1,514
Thanks: 194
Thanked 413 Times in 336 Posts
Default Re: 17kw generac starts and shuts down after 2 sec

Billy is right Wstang, see if the warranty will kick in, it sounds like a simple issue to correct, and why spend money when warranty will cover it.
Reply With Quote
  #12  
Old 11-21-2012, 11:50:30 AM
pegasuspinto pegasuspinto is offline
Registered
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 2,981
Thanks: 319
Thanked 1,442 Times in 934 Posts
Default Re: 17kw generac starts and shuts down after 2 sec

Did anyone check the oil level? I sure wouldn't let generac see it unless it was full of oil! and after several days runtime, maybe it ran out....more common then you might think!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Generac starts but won't stay running RoyW Generac Generators (SEARS, etc.) 13 05-07-2019 07:32:04 AM
Generac 17kw starts n shuts down wstang254 Generac Generators (SEARS, etc.) 13 11-17-2012 04:00:59 AM
Onan 6.5MCCK-3CR/1H Starts runs for 45 seconds and shuts off truk911 Onan Generators 4 10-16-2011 03:47:58 PM
Generac xp 6247-8 starts but will not stay running Kevin Henshaw Generac Generators (SEARS, etc.) 3 05-19-2010 05:31:38 PM
Onan generator/ starts then shuts down Styners4x4 Onan Generators 3 06-22-2009 06:04:42 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 12:24:09 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277