Onan genset model #5.0 CCK stops running ater 10 or 20 min


this thread has 15 replies and has been viewed 3106 times

Reply
 
Thread Tools Display Modes
  #1  
Old 04-22-2011, 06:44:49 PM
M.Linskens M.Linskens is offline
Registered-I
 
Join Date: Apr 2011
Location: Daytona Beach, Florida
Posts: 7
Thanks: 9
Thanked 0 Times in 0 Posts
Question Onan genset model #5.0 CCK stops running ater 10 or 20 min

first time to post , look at alot of other post but havn't fond this one. it seems the more power i need from it ,it starts to spudder and die thanks.
Reply With Quote
Sponsored Links
  #2  
Old 04-22-2011, 07:02:07 PM
kg5388 kg5388 is offline
Registered-I
 
Join Date: Apr 2011
Location: tenneessee
Posts: 86
Thanks: 18
Thanked 56 Times in 36 Posts
Default Re: onan gen set model #5.0cck stops running ater 10 or 20 min

when it stops will it start right back up and run for 10 to 20 min?

Do you have to wait a certain amount of time before it will start and run again?

When you restart it does the run time stay constant 10 to 20 min or does it get shorter and shorter each time you restart it?

does it run ok without any load or does this problem just occurs when you add load to the genset ?

have you unpluged one plug wire and run the genset then plug it in and unplug the other and try to run it to see if you have a dead cylinder?
Reply With Quote
The Following User Says Thank You to kg5388 For This Post:
  #3  
Old 04-22-2011, 07:17:20 PM
BTPost's Avatar
BTPost BTPost is offline
Moderator
 
Join Date: Jan 2005
Location: Excursion Inlet, Alaska USA 99850-0090
Posts: 4,840
Thanks: 556
Thanked 1,868 Times in 1,207 Posts
Images: 1
Talking Re: onan gen set model #5.0cck stops running ater 10 or 20 min

Quote:
Originally Posted by kg5388 View Post
have you unpluged one plug wire and run the genset then plug it in and unplug the other and try to run it to see if you have a dead cylinder?
This is NOT Possible to do on a Standard Onan CCK Factory wired Ignition System. Simply because, the Spark Plugs are wired in series. So if you unplug a Spark Plug, and do NOT Ground that Spark Plug Wire, the remaining Spark Plug can't fire, because it no longer has a Path to Ground, thru the Coil, as the Coil Secondary is NOT Grounded, internally like a Car Coil. Onan CCK coils are more like Harley Davidson Twin Tower Coils, which are sometimes used to replace Onan coils on the CCK Gensets.

http://www.smokstak.com/forum/showthread.php?t=56022
__________________
Bruce in alaska
Reply With Quote
The Following 3 Users Say Thank You to BTPost For This Post:
  #4  
Old 04-22-2011, 07:28:35 PM
M.Linskens M.Linskens is offline
Registered-I
 
Join Date: Apr 2011
Location: Daytona Beach, Florida
Posts: 7
Thanks: 9
Thanked 0 Times in 0 Posts
Default Re: onan gen set model #5.0cck stops running ater 10 or 20 min

seems that if i don't put a load it runs longer . i took the low oil wire of the coil but still happens thanks for any info
Reply With Quote
  #5  
Old 04-22-2011, 07:44:39 PM
kg5388 kg5388 is offline
Registered-I
 
Join Date: Apr 2011
Location: tenneessee
Posts: 86
Thanks: 18
Thanked 56 Times in 36 Posts
Default Re: onan gen set model #5.0cck stops running ater 10 or 20 min

Quote:
Originally Posted by BTPost View Post
This is NOT Possible to do on a Standard Onan CCK Factory wired Ignition System.
DOH!! my mistake it's been long day and tried to ask the basic questions quickly without thinking CCK
Reply With Quote
The Following User Says Thank You to kg5388 For This Post:
  #6  
Old 04-22-2011, 07:49:51 PM
M.Linskens M.Linskens is offline
Registered-I
 
Join Date: Apr 2011
Location: Daytona Beach, Florida
Posts: 7
Thanks: 9
Thanked 0 Times in 0 Posts
Default Re: onan gen set model #5.0cck stops running ater 10 or 20 min

hey thats ok, time for a beer !
Reply With Quote
  #7  
Old 04-22-2011, 08:14:58 PM
kg5388 kg5388 is offline
Registered-I
 
Join Date: Apr 2011
Location: tenneessee
Posts: 86
Thanks: 18
Thanked 56 Times in 36 Posts
Default Re: onan gen set model #5.0cck stops running ater 10 or 20 min

question I forgot and it is one of the important ones

Does it surge up and down like it's running out of gas or does it shut down like you hit the stop switch?
Reply With Quote
The Following User Says Thank You to kg5388 For This Post:
  #8  
Old 04-22-2011, 08:20:54 PM
M.Linskens M.Linskens is offline
Registered-I
 
Join Date: Apr 2011
Location: Daytona Beach, Florida
Posts: 7
Thanks: 9
Thanked 0 Times in 0 Posts
Default Re: onan gen set model #5.0cck stops running ater 10 or 20 min

well it spudders an pops then stops . i have it hook up to a 5 gal tank an its out of the rv thanks
Reply With Quote
  #9  
Old 04-22-2011, 08:32:38 PM
John Newman, Jr.'s Avatar
John Newman, Jr. John Newman, Jr. is offline
Subscriber
 
Join Date: Apr 2005
Location: Saint Louis, Missouri, USA
Posts: 5,286
Thanks: 757
Thanked 3,238 Times in 1,654 Posts
Default Re: onan gen set model #5.0cck stops running ater 10 or 20 min

Could be a simple as a bad condenser...
I would do the cheap / easy stuff first: Points, plugs, condenser. See if that makes any diference and then consider the more expensive items.
__________________
John Newman, Jr.
Saint Louis, MO

I Can Probably Fix That
Reply With Quote
The Following User Says Thank You to John Newman, Jr. For This Post:
  #10  
Old 04-22-2011, 08:38:20 PM
M.Linskens M.Linskens is offline
Registered-I
 
Join Date: Apr 2011
Location: Daytona Beach, Florida
Posts: 7
Thanks: 9
Thanked 0 Times in 0 Posts
Default Re: onan gen set model #5.0cck stops running ater 10 or 20 min

thanks i'll try that an let you know if its the fix .
Reply With Quote
  #11  
Old 04-22-2011, 09:34:33 PM
MBB MBB is offline
Registered-III
 
Join Date: Apr 2009
Location: Elk Grove Village IL USA
Posts: 3,417
Thanks: 1,514
Thanked 3,083 Times in 1,519 Posts
Default Re: Onan genset model #5.0 CCK stops running ater 10 or 20 min

If this problems after the engine is warm but not when first started. A couple of things come to mind. Choke or valve adjustment. If its hard to start after its warm check valve clearance.
Reply With Quote
The Following User Says Thank You to MBB For This Post:
  #12  
Old 04-22-2011, 10:01:19 PM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 6,292
Thanks: 5,739
Thanked 6,225 Times in 3,236 Posts
Default Re: Onan genset model #5.0 CCK stops running ater 10 or 20 min

I am real good at asking the stupid questions. What type of tank are you using & is it vented?
Reply With Quote
The Following User Says Thank You to Max Thompson For This Post:
  #13  
Old 04-23-2011, 12:30:41 PM
M.Linskens M.Linskens is offline
Registered-I
 
Join Date: Apr 2011
Location: Daytona Beach, Florida
Posts: 7
Thanks: 9
Thanked 0 Times in 0 Posts
Default Re: Onan genset model #5.0 CCK stops running ater 10 or 20 min

it starts up after it shuts off , i'll take a look at the choke thanks

5 gal. gas tank vented , the only stupid question is one thats never ask thanks
Reply With Quote
  #14  
Old 04-25-2011, 11:43:32 AM
Dave Edmonds's Avatar
Dave Edmonds Dave Edmonds is offline
Registered-III
 
Join Date: Nov 2006
Location: Jackson, Mississippi, USA
Posts: 1,780
Thanks: 422
Thanked 679 Times in 495 Posts
Smile Re: Onan genset model #5.0 CCK stops running ater 10 or 20 min

Improperly set points gap will cause similar problems. Points gap is "acceptable" when unit is cold, but closes (or opens)when unit heats up until the points don't function. A tune-up (new points and condenser) never hurts anything.
Dave Edmonds
Reply With Quote
The Following User Says Thank You to Dave Edmonds For This Post:
  #15  
Old 04-26-2011, 03:04:08 PM
M.Linskens M.Linskens is offline
Registered-I
 
Join Date: Apr 2011
Location: Daytona Beach, Florida
Posts: 7
Thanks: 9
Thanked 0 Times in 0 Posts
Default Re: Onan genset model #5.0 CCK stops running ater 10 or 20 min

thanks thats what i'm going to try , do you know the gap thanks again
Reply With Quote
  #16  
Old 04-26-2011, 07:52:35 PM
Ben Cowan Ben Cowan is offline
Registered-II
 
Join Date: Jun 2009
Location: RioHondo, Tx, USA
Posts: 634
Thanks: 55
Thanked 255 Times in 185 Posts
Default Re: Onan genset model #5.0 CCK stops running ater 10 or 20 min

I believe most cck units use a point gap of 0.020 inches, 20 thousands of an inch. Luck, Ben
Reply With Quote
The Following 2 Users Say Thank You to Ben Cowan For This Post:
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Engine stops running when switched to run. the1moe Generac Generators (SEARS, etc.) 7 03-31-2011 06:43:22 PM
'97 Onan Marquis 7000 Stops Producing Voltage and Still Running MariettaEddie Onan Generators 13 08-26-2010 10:11:52 AM
Maytag 92 STOPS running Todd Hodges Maytag Engines and Collectibles 8 07-13-2009 04:19:06 PM
Onan 4.5 genset starts but stops after start pb is released deproch Onan Generators 1 05-28-2008 05:51:34 PM
Onan BGE consistently stops running after a few minutes scubar Onan Generators 19 02-07-2008 03:54:32 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 03:04:22 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277