Neutral bond wire


this thread has 7 replies and has been viewed 382 times

Reply
 
Thread Tools Display Modes
  #1  
Old 04-05-2019, 11:52:56 AM
opus opus is offline
Registered-II
 
Join Date: Mar 2005
Location: Trout Creek, Montana USA
Posts: 459
Thanks: 17
Thanked 44 Times in 28 Posts
Default Neutral bond wire

I have a Honda EB6500 that I need to use on a transfer switch. It trips the generator breaker due to GFCI. I've read many places as well as here and the fix is removing the neutral bond wire:




Would I be wise to do some other sort of grounding when using this only on the transfer switch? Do I need an additional generator to frame ground, etc?

I didnt get this age by being stupid, so I was wanting to double check what I was doing.
Reply With Quote
Sponsored Links
  #2  
Old 04-05-2019, 06:04:45 PM
Vanman Vanman is online now
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,247
Thanks: 7,714
Thanked 2,297 Times in 1,566 Posts
Default Re: Neutral bond wire

Yes, that appears to be bonding jumper in the diagram.

Yes, you do need a grounding conductor in the cable between the generator set frame and the inlet to your transfer switch, also of course with it's ground all the way back to the ground bus in the panel / transfer switch.

If the set is also to be used as stand - alone, the jumper should be reconnected. Some people devise a means of switching it.

Last edited by Vanman; 04-05-2019 at 06:48:52 PM.
Reply With Quote
  #3  
Old 04-05-2019, 07:26:07 PM
opus opus is offline
Registered-II
 
Join Date: Mar 2005
Location: Trout Creek, Montana USA
Posts: 459
Thanks: 17
Thanked 44 Times in 28 Posts
Default Re: Neutral bond wire

I removed the wire and left it hanging on the cover screws as a reminder. Also wrote on the breaker on the generator.
I also checked, there is a wire going from the generator head to the frame.
Reply With Quote
  #4  
Old 04-05-2019, 07:35:34 PM
I like oldstuff I like oldstuff is offline
Subscriber
 
Join Date: Jan 2012
Location: Milwaukee, Wisconsin, USA
Posts: 5,810
Thanks: 1,430
Thanked 6,357 Times in 2,437 Posts
Default Re: Neutral bond wire

I have no recent experience with Honda generators as I left that biz like thirty years ago. But here's a thought.

Check around to be sure that by isolating the neutral it won't affect the regulator. I'd hate to see you smoke the regulator and with Honda prices I'm sure it's priced in the stratosphere.
Reply With Quote
  #5  
Old 04-05-2019, 07:39:23 PM
opus opus is offline
Registered-II
 
Join Date: Mar 2005
Location: Trout Creek, Montana USA
Posts: 459
Thanks: 17
Thanked 44 Times in 28 Posts
Default Re: Neutral bond wire

I've not read anything about that, but......
Reply With Quote
  #6  
Old 04-05-2019, 08:20:23 PM
Vanman Vanman is online now
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,247
Thanks: 7,714
Thanked 2,297 Times in 1,566 Posts
Default Re: Neutral bond wire

That would be cheesy if that could damage the regulator, but... As long as the set is plugged into the transfer switch inlet, it will be bonded. It won't be able to tell that the bond is remote.
Reply With Quote
The Following User Says Thank You to Vanman For This Post:
  #7  
Old 04-06-2019, 04:54:27 AM
Steve Dawkins Steve Dawkins is offline
Sponsor
 
Join Date: Feb 2005
Location: Virginia Beach, Virginia, USA
Posts: 1,068
Thanks: 770
Thanked 577 Times in 293 Posts
Default Re: Neutral bond wire

At one point, Honda had a "kit" for dealing with the removal of the neutral/ground bonding jumper on their generators with GFCI breakers. The kit consisted of instructions on how to remove the jumper, and a warning label to install on the control panel that stated the bonding jumper had been removed.

When home standby power first got popular in the 80s and 90s, we installed several Gen-Tran manual transfer switches. Most of the customers used them with Honda generators. When the NEC started requiring portable generators of 5 kW and up to have GFCI protection, people started having problems with the generator GFCI tripping as soon as they connected their generator to the Gen-Tran switches. The generator's GFCI "saw" the neutral/ground bond at the main panel as a ground fault condition, and would trip immediately. Once the bonding jumper was removed, that problem went away.

If the generator was going to be used without the Gen-Tran (or other application where the neutral and ground were bonded together downstream of the generator) the jumper should be reinstalled so as to enable GFCI protection. IIRC, we would remove the jumper and attach it externally with one of the end bell screws so that it was a visible reminder to the customer.

As a side note, removing the jumper had no effect on the AVR.
Reply With Quote
The Following User Says Thank You to Steve Dawkins For This Post:
  #8  
Old 04-06-2019, 08:26:52 AM
Peter Holmander Peter Holmander is offline
Subscriber
 
Join Date: Nov 2004
Location: West Greenwich, Rhode Island
Posts: 556
Thanks: 987
Thanked 489 Times in 211 Posts
Default Re: Neutral bond wire

My son in law just went through this with his new Honda EB10000 . He has a new home and it is wired with a generator lockout breaker. He had an older 6000 watt unit that worked fine but he wanted more power. We lost power this past winter so he hooks up his $5000 generator and it keeps tripping on him. Of course, everyone is out so he can't call the place where he bought the unit. The next day when power was restored, I google the issue and I get a ton of hits on the bonded neutral issue. He calls the dealership and they say, "Oh yeah, we forgot to disconnect that for you" The service tech sent him pics on his cell showing what wire to remove. We taped it up really good and reinstalled the access cover. Works fine now. I honestly think the dealer just did not want to disconnect that wire due to liability issues. Now he has to change the breaker from 30 amp to 50 amp. At least he can use the generator now. I was told that Honda does that because so many of their units are used on construction sites.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Remoting the Neutral/Ground bond on a 5CCK PnishrPW Onan Generators 1 03-15-2016 11:11:04 AM
Let' find some double neutral gr bond point accident reports Kpack Onan Generators 97 01-15-2014 03:36:04 PM
Generac GTS neutral wire bubbagump225 Generac Generators (SEARS, etc.) 7 10-19-2013 01:30:10 PM
Not finding the neutral bond. AndersonMillTexas Onan Generators 14 11-10-2012 09:12:29 PM
My Word is My Bond. Dick Welty Antique Gas Engine Discussion 29 06-21-2005 11:29:18 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 12:24:18 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277