Default GE 45KW Generator

I have a Mil GenSet from 1969 with a GE 45KW generator run by a GM 3-71 diesel engine. I have been all over the web trying to find service info on the generator and can not find anything. Does anyone know where I might locate a schematic or any service info on this or a similar generator?

This one is a GE 5SJ4326P23Y41 but anything similar should give me the info I need. There was a guy named Tunnelport who has the same unit and was looking for info on it back in 2009 but apparently he eventually gave up trying to get it running.

It has a couple 500V SCRs (in parallel) and a large diode in series with the SCRs that supply the field current so it SHOULD be getting a nice smooth DC current but the generator seems to put out about half the voltage it is supposed to so SOMETHING is wrong.

Any help would be very much appreciated!
Reply With Quote
Sponsored Links
  #2  
Old 04-30-2016, 09:51:13 AM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,485
Thanks: 2
Thanked 465 Times in 331 Posts
Default Re: GE 45KW generator

Can the whole enchilada be ripped out and replaced with a modern regulator setup? What is this SCR thing sending power to? I assume stationary field windings, or possibly some brushes?
Reply With Quote
  #3  
Old 05-01-2016, 01:10:01 AM
dwight44 dwight44 is offline
Registered
 
Join Date: Feb 2016
Location: Thaxton, Virginia
Posts: 10
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: GE 45KW generator

The unit has two regulated functions, the frequency which is controlled by the RPM of the engine (1800 RPM) and the voltage which is controlled by the voltage provided to the rotor in the generator. The more voltage, the stronger the rotor magnetism thus the more voltage the generator supplies. Both are controlled within + or - 1% f it is working OK which is quite good. Both of these are also manually adjustable from the control console and you can adjust the voltage to the rotor from about 6 volts to about 75 volts. The trouble seems to be that it doesn't provide any power until the control votag3e reaches about 30 volts and then it shoots up to full voltage and stays there until you reduce the control voltage to about 20 volts where it just turns off and doesn't supply any power to the rotor.

The thing is that I already have a perfectly good 25KW generator that runs my house and this is just a project to see if I can get the nearly 50 year old generator working again. Rumor has it that it last ran about 15 to twenty years ago but there is no one alive that knows if it EVER actually produced usable power. The Unit was built by Sun Electric Company of Crystal Lake IL and apparently they built very few of them and service information seems to be non-existent. I have pulled all the circuit boards and found numerous bad solder joints and bad transistors which makes me suspicious that it never actually worked as designed. The trick is that it has a lot of circuitry that allows it to be connected in sync with other generators and even the utility grid and some of the bad devices MIGHT belong to these functions which I would never have any need for.

There have been others looking for information for these units over the years, most recently gtochuck back in 2013 but no one seems to have had any success.
Reply With Quote
  #4  
Old 05-01-2016, 10:11:13 AM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,485
Thanks: 2
Thanked 465 Times in 331 Posts
Default Re: GE 45KW generator

The control voltage you mention is DC going to the field windings of the generator, correct? And output voltage is not rising and falling in lock step with field voltage?
Reply With Quote
  #5  
Old 05-01-2016, 02:46:34 PM
dwight44 dwight44 is offline
Registered
 
Join Date: Feb 2016
Location: Thaxton, Virginia
Posts: 10
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: GE 45KW generator

The control voltage TO the SCRs goes up and down OK. Trouble is that the SCRs don't seem to turn on until the voltage reaches about 30 volts and then they turn on FULL. They stay on full until the control voltage goes down to about 20 volts and then it turns completely off. They SHOULD be turning on and off gradually in concert with the control voltage.

Another problem is that when the field voltage DOES come on, the output voltage of the generator only goes up to about half of what it should. I would suspect that these problems are somehow connected but I don't see why or how. One would think that when the field voltage shoots up to 75 volts (full on) that the generator voltage would also shoot up the way OVER the normal output. There have got to be schematics of these GE generators SOMEWHERE but GE apparently does not have them posted and no one else seems to either.

The circuit boards are poorly designed which probably accounts for their unreliable behavior. They have leads on BOTH sides of the boards and some of the leads on the component sides of the boards did not get soldered. They probably worked long enough to pass a Quality Control test through a physical contact but then failed as soon as any corrosion started. They probably had many failures which might account for their scarcity and lack of service information.

They have something called a "sequencer" board that apparently shoots 24 volts the the field windings when the generator is first started and then the control circuits switch to 120 volts AC which SHOULD have been generated by the generator itself by that time. Since there is no 120 volts being generated, all the control circuits drop out a few seconds of operation and the whole thing shuts down. The way I got the control circuits operating long enough to collect some voltages was to isolate the generator from the control circuits and run them from line current. I also had to supply the actual engine governor (a Woodward 2301) with 24 volts directly from the batteries. This also s run through the "sequencer" circuit as well as other boards. They supply 24 volts to the Woodward 2301 boards long enough for the engine to start and then go into "run" mode where the boards shortly turn off the power to the Woodward governor and the engine shuts down. After I replaced some transistors and soldered some bad joints, I got this circuit to run but then the safety circuit senses a low voltage situation and puts the whole system in "emergency stop"! It has a switch that bypasses the safety sensors but when THAT is thrown, you can not START the unit! I have the start it and immediately switch the bypass switch and then it will run fine but it STILL is not producing usable current.

As you can surmise, the unit is quite complicated and especially without any former experience with these units and no service info. Just winging it and learning as I go along!
Reply With Quote
  #6  
Old 05-01-2016, 09:27:52 PM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,485
Thanks: 2
Thanked 465 Times in 331 Posts
Default Re: GE 45KW generator

Does the nameplate have field voltage/current stated?

I am speculating here but I wonder if a rotating diode out might cause the field voltage requirement to be higher than normal. Such that 75 volts does not drive it full.

On the other hand, it could be that it takes more than 75 volts normally. If the rotating diodes check OK then my next step if it were mine would be to drive it with higher DC voltage from an external source until it works.

Gauge of winding in the stationary field winding and ohms would help to know whether it expects higher voltage or is going to fry from overdriving it.

In any case, if it were mine my plan would be to replace the regulation setup with something modern, and possibly the engine controls also.
Reply With Quote
  #7  
Old 05-01-2016, 10:41:07 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 5,187
Thanks: 310
Thanked 4,247 Times in 2,034 Posts
Default Re: GE 45KW generator

Quote:
Originally Posted by Birken Vogt View Post
...if it were mine my plan would be to replace the regulation setup with something modern, and possibly the engine controls also.
+1 for the above advice. Some relative of Rube Goldberg must have worked for Sun back then.
Reply With Quote
  #8  
Old 05-01-2016, 11:03:07 PM
moteurdelco moteurdelco is offline
Registered-II
 
Join Date: May 2012
Location: St-Barnabé, Québec, Canada
Posts: 567
Thanks: 234
Thanked 194 Times in 161 Posts
Default Re: GE 45KW generator

Is it brushless? or is exciting to main rotor slip rings?
old generator were often designed to operate with 125vdc ;supplied with belt driven exciter,upgraded(modernize) with ''static exciter'' (controlled scr bridge),like Onan's and Caterpillar. did you mesure 60 hz?? what kind of governor on the 3-71? GM generator engines were habitually equiped with hydraulic governor.
Reply With Quote
  #9  
Old 05-02-2016, 11:46:02 PM
dwight44 dwight44 is offline
Registered
 
Join Date: Feb 2016
Location: Thaxton, Virginia
Posts: 10
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: GE 45KW generator

The trick is that this is an exercise to see if I can get the generator running AS IS! I have a (25KW) generator to run my house so I don't want or need to put thousands of dollars into this machine just to produce power. The challenge is to get THIS machine running as it did when new. I have numerous "hit & miss" engines and steam engines that I have restored, not to actually drive something, but to just see them run!!!

This machine is a lot more complicated than anything I have tackled so far but in that it uses discrete components without a bunch of IC chips I think I have a chance. It is just a great challenge trying to get it running without ANY servicing information as to what and how all the circuit boards do. I am trying to figure out the whole system without having prior knowledge of any similar machine so...

This thing weighs 3600 lbs so removing the engine/generator package and then separating the engine and generator is not something I want to tackle without some reason to think that something is wrong with the generator. If I had a schematic for the generator, I could do some tests and see if there was an internal problem and I don't see why there would be any diodes or ANY solid state devices internal to the generator as it is SUPPOSED to provide AC current.

The rotor should only need DC current to make AC in the stator so...

Another thought, I have never fooled with a 2 cycle diesel engine and it is possible that I am trying to run it much slower than what is called for. I realize that it has two power cycles in place of what I am used to with the numerous "four cycle" diesels I am used to but I don't have any way to tell how fast the engine is running except by the sound. Does anyone have access to a "U-Tube of a 3-71 running at something near 1800 RPM that I could listen to? I am afraid of running this engine too fast and harming it but there is no way to tell how fast it is going except the voltage and frequency gauges. Do these things really sound like they are blowing up when they run? I just have no experience with two cycle diesel engines.

You guys are asking question that I can not answer without a schematic OR just physically tearing the whole machine apart which would be a major effort and might not be necessary.

The unit only has a little over 100 hours running in its lifetime so I doubt there is anything physically wrong with the generator itself and I feel the problem probably is with the control circuits and they are a whole lot smaller and easier to deal with than tearing apart the engine/generator package.

It just seems like SOMEWHERE on the WWW there has to be a schematic for this generator, the trick is how to find it.

Any suggestions?

Thanks,
Reply With Quote
  #10  
Old 05-03-2016, 12:07:28 AM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,485
Thanks: 2
Thanked 465 Times in 331 Posts
Default Re: GE 45KW generator

To set engine speed, get a good Fluke voltmeter with a Hz function and measure the output leads and set to 60 Hz. Even with no real output the meter will still pick it up OK.

I used to take care of a similar vintage but a lot smaller and it had next to nothing for manuals. I had a schematic but I don't know where it has got to now.

Those military machines were hyper complicated and used a lot of crazy specialized components like multi tapped transformers and saturable core magnetics to do simple things so they are very hard to figure let alone actually repair.

I would guess yours is one of less than 10 in existence if I had to guess on these. Most have been to the scrap yard by now.
Reply With Quote
  #11  
Old 05-03-2016, 01:03:53 AM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 3,274
Thanks: 4,031
Thanked 1,358 Times in 908 Posts
Default Re: GE 45KW generator

Definitely plus one on using a frequency meter to set the speed.

Funny about the speed by ear. If you're not used to listening to a Detroit and you're setting the speed by ear it's pretty well guaranteed that you've got it running too slow.

Have a friend that bought a truck with a 671 in it, and started driving it home while I followed. He shifted through all the gears and topped out at 25 mph lol. As a veteran Detroit operator I got in said, no no, like THIS! He was used to his Army truck with a White diesel, four stroke of course.
Reply With Quote
  #12  
Old 05-03-2016, 11:11:32 PM
dwight44 dwight44 is offline
Registered
 
Join Date: Feb 2016
Location: Thaxton, Virginia
Posts: 10
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: GE 45KW generator

Guys, see: http://auction.hendersonauctions.com...0504531&lp=MAT

Actually, the Henderson guys seem to have acquired a number of these gen sets from a company who chopped off the outer housing, added a new housing, and are selling/sold them to the public for big money. This is exactly my gen set with most of the electronics removed, cleaned up and painted real pretty, and with the old housing cut off and a fancy new white housing built around it.

This outfit is/was just selling the units but I googled the name on the generators and wrote to the people who actually did the work but they never answered. I also wrote to the people who were selling the units and they also did not respond.

I don't know what actually happened to these generators or, how much of the old electronics were still used as the pictures are careful to not show what is in the control box. I DO notice that the original Woodward governor was a electronic/hydraulic unit that required a very complicated electronic control board and on these units this was substituted with a purely hydraulic unit.

I have a mechanical tach so I can remove the cover over the end of the generator shaft and see what RPM it is actually running. I hear these units referred to as "screamers" and such but I would feel really awful if I somehow damaged this nice engine.

The GTOCHUCK guy was looking for a couple of the boards for his unit and I would bet that the guys who converted the units would still have the stuff they cut off laying around. Trouble is that I have no way to contact him except through the Smokstak web site and apparently he is long gone from here.

I feel I would have no problem figuring what is wrong with the generator if I could get a schematic for this or a similar generator. Can anyone come up with some suggestions about how to proceed further?

Also, there is the distinct possibility that I am just running it way too slow. I will check this out and get back.
Reply With Quote
  #13  
Old 05-03-2016, 11:41:49 PM
t6299fm t6299fm is offline
Registered-III
 
Join Date: Sep 2012
Location: Woodbury, Georgia
Posts: 26
Thanks: 0
Thanked 17 Times in 9 Posts
Photo Re: GE 45KW generator

Check out Basler Regulator co. I had/have an ol 60 KW Consolidated Cummings unit with way to much old stuff in the controls. After the smoke drained out>>>I tossed it all and got one of Basler's little solid state regulators (cheap) and the thing works GREAT. It is a 12 lead alternator with a 125 volt DC exciter on the other end. The Old Cummings just chugs along at 1200 rpm. (6 pole machine) I ran it for the first time in 6 years last week all is good it started my 30 HP air compressor with no problems. I use it with others as emergency power. I am totally off grid and have been since 1994 wasting energy like mad !!!! 125 KW hydro unit runs 24/7 (most of the time)....GRRRRRR!!!! I would like to share stuff >>>BUT>>>>How do you attach pictures to this sight ????
Reply With Quote
  #14  
Old 05-03-2016, 11:45:55 PM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,485
Thanks: 2
Thanked 465 Times in 331 Posts
Default Re: GE 45KW generator

Yes, do not proceed until you have it running at rated RPM. (Make sure it is not 1200 before you crank up to 1800 but I think a 3-71 has to run 1800 to make 45 kw)

If the RPM is low the voltage will be low and nothing will work right.
Reply With Quote
  #15  
Old 05-04-2016, 11:41:27 AM
25Eagle34 25Eagle34 is offline
Registered-II
 
Join Date: May 2009
Location: Auburn, CA. in the Sierra-Nevada Foothills on the way to Reno
Posts: 279
Thanks: 1
Thanked 7 Times in 7 Posts
Default Re: GE 45KW generator

Quote:
Originally Posted by dwight44 View Post
I have a Mil GenSet from 1969 with a GE 45KW generator run by a GM 3-71 diesel engine. I have been all over the web trying to find service info on the generator and can not find anything. Does anyone know where I might locate a schematic or any service info on this or a similar generator?

This one is a GE 5SJ4326P23Y41 but anything similar should give me the info I need. There was a guy named Tunnelport who has the same unit and was looking for info on it back in 2009 but apparently he eventually gave up trying to get it running.

It has a couple 500V SCRs (in parallel) and a large diode in series with the SCRs that supply the field current so it SHOULD be getting a nice smooth DC current but the generator seems to put out about half the voltage it is supposed to so SOMETHING is wrong.

Any help would be very much appreciated!
What is the NSN from the name plate of the set, should start with 6115-?
I am have manuals, but can not chech without the NSN.
Don in Auburn, CA.
25eagle@wavecable.com
Reply With Quote
  #16  
Old 05-08-2016, 01:01:09 AM
coyote62ny coyote62ny is offline
Registered-II
 
Join Date: Jan 2011
Location: sherburne ny usa
Posts: 696
Thanks: 0
Thanked 165 Times in 144 Posts
Default Re: GE 45KW generator

check with the guys over on steel soldiers site they may be able to help you with the tm manuals and other info
Reply With Quote
  #17  
Old 05-09-2016, 02:39:39 AM
dwight44 dwight44 is offline
Registered
 
Join Date: Feb 2016
Location: Thaxton, Virginia
Posts: 10
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: GE 45KW generator

It is a Navy/Marine unit:
FSN 6115-472-5522
PU703/G
Serial 69-119
Weight 3500 lbs dry
Sun Electric Co, Crystal Lake IL

I have spent many hours trying to get ANY service information on this or any similar unit to no avail.

I would greatly appreciate any help on this!

Dwight
Reply With Quote
  #18  
Old 05-09-2016, 10:00:50 AM
25Eagle34 25Eagle34 is offline
Registered-II
 
Join Date: May 2009
Location: Auburn, CA. in the Sierra-Nevada Foothills on the way to Reno
Posts: 279
Thanks: 1
Thanked 7 Times in 7 Posts
Default Re: GE 45KW generator

Quote:
Originally Posted by dwight44 View Post
It is a Navy/Marine unit:
FSN 6115-472-5522
PU703/G
Serial 69-119
Weight 3500 lbs dry
Sun Electric Co, Crystal Lake IL

I have spent many hours trying to get ANY service information on this or any similar unit to no avail.

I would greatly appreciate any help on this!

Dwight
Dwight,
Thanks for the numbers and will check my stock of manuals.
Don
Reply With Quote
  #19  
Old 06-12-2016, 03:58:40 PM
GreasyIron GreasyIron is offline
Subscriber
 
Join Date: May 2011
Location: South Dakota, USA
Posts: 1,370
Thanks: 1,347
Thanked 1,344 Times in 662 Posts
Default Re: GE 45KW generator

That sounds much like the little brother to the 6910a we just bought! The manuals I found online so far have a bunch of maintenance information on the Screaming Jimmy, but really sparse on the generator.

I'm hoping everything works "as is" on ours, it was at a fire department and supposedly ran 5 years ago. However, once we get it fired up, I'm thinking about going to a 120/240 Delta configuration if it doesn't mess up anything else. That thing does have some interesting features - I rather hope the gasoline powered coolant heater works; that would make it a perfect [OK still at least 5times bigger than we really need] back-up set for us.
Reply With Quote
  #20  
Old 04-08-2017, 11:02:26 PM
Shade Shade is offline
Registered
 
Join Date: Apr 2017
Location: Kankakee, Illinois
Posts: 4
Thanks: 3
Thanked 1 Time in 1 Post
Default Re: GE 45KW generator

FSN 6115-472-5522
PU-703/G
Serial 69-151
Weight 3600 lbs dry
Sun Electric Co, Crystal Lake IL

Seems these generators are easier to find than the manuals for them.
I just picked one up for $600. I don't have a lot of time to work on it
right now. I did pick up new batteries for it today and will have to give
it a good cleaning. I want to pull the fuel tank and give it a good cleaning.

Anybody ever find a set of manuals for this beast.

Thanks,
Ron
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
45kW Pincor Generator - Ford 300 propane / natural gas kww1184 Multi-Cylinder Stationary Engines and Power Units 56 05-12-2014 10:02:16 PM
pu703/g 45kw generator gtochuck Military MEP and Aircraft Gen-Sets 12 01-06-2014 07:45:48 PM
Need manual 45kw poinciana Onan Generators 10 11-18-2010 11:16:06 AM
Need help with PU-710G/711-g, 45kw gen set Lvillemedic Military MEP and Aircraft Gen-Sets 6 11-05-2010 06:49:30 PM
Need help with old(er) 45KW Delco gen set Bob Greene Generators & Electric Motors General Discussion 3 03-27-2006 01:23:41 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 09:45:48 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277