Wiring Question


this thread has 10 replies and has been viewed 782 times

Reply
 
Thread Tools Display Modes
  #1  
Old 10-13-2018, 11:24:49 PM
Reed Engine's Avatar
Reed Engine Reed Engine is online now
Subscriber
 
Join Date: Apr 2009
Location: Hominy, Oklahoma
Posts: 4,110
Thanks: 1,764
Thanked 4,560 Times in 1,770 Posts
Default Wiring Question

Asking for advice. My wife bought a “she shed” and wants some outlets and lights put in. Should I go with 12/2 with ground or is 14/2 big enough. We do plan on using a 110 window unit air conditioner.
__________________
Wake up and smell the Fool-Aid.
Reply With Quote
Sponsored Links
  #2  
Old 10-14-2018, 12:36:32 AM
Dwayne Fuller's Avatar
Dwayne Fuller Dwayne Fuller is offline
Subscriber
 
Join Date: Apr 2008
Location: Longview, Texas, USA
Posts: 2,235
Thanks: 3,450
Thanked 3,644 Times in 1,080 Posts
Default Re: Wiring question.

No 14/2. Use the 12/2 on all the circuits. Use 15amp breakers on the lights. 20 amp on the a/c. Anything needing a 30 amp breaker will need bigger wire.
Reply With Quote
The Following User Says Thank You to Dwayne Fuller For This Post:
  #3  
Old 10-14-2018, 07:55:52 AM
Peter Holmander Peter Holmander is offline
Subscriber
 
Join Date: Nov 2004
Location: West Greenwich, Rhode Island
Posts: 626
Thanks: 1,066
Thanked 579 Times in 247 Posts
Default Re: Wiring Question

Rule of thumb: 14ga. wire/15 amps, 12ga. wire/20 amps, 10ga. wire/30 amps
Reply With Quote
The Following User Says Thank You to Peter Holmander For This Post:
  #4  
Old 10-14-2018, 09:11:16 AM
posborne80 posborne80 is offline
Registered
 
Join Date: Jul 2015
Location: Hendersonville, North Carolina
Posts: 18
Thanks: 0
Thanked 16 Times in 10 Posts
Default Re: Wiring Question

Both answers are correct, as far as they go, for the inside wiring. Depending on the distance from the circuit panel, voltage drop could be an issue requiring larger sized conductors for the supply. Local codes may require a disconnect and ground rod at the wiring entry to the structure. Get an electrician friend to look at this to be safe. Just a few thoughts as I read your question.......

Paul
Reply With Quote
The Following User Says Thank You to posborne80 For This Post:
  #5  
Old 10-14-2018, 09:31:45 AM
Reed Engine's Avatar
Reed Engine Reed Engine is online now
Subscriber
 
Join Date: Apr 2009
Location: Hominy, Oklahoma
Posts: 4,110
Thanks: 1,764
Thanked 4,560 Times in 1,770 Posts
Default Re: Wiring Question

Thank you.
__________________
Wake up and smell the Fool-Aid.
Reply With Quote
  #6  
Old 10-14-2018, 02:03:05 PM
Power Power is offline
Registered-III
 
Join Date: Aug 2011
Location: New Jersey
Posts: 5,288
Thanks: 1,220
Thanked 3,163 Times in 1,860 Posts
Default Re: Wiring Question

You have not said how long the run is, which, along with load determines wire size.
I would run 3 conductor of whatever size you need- ie 12/3 with ground. Does not cost much more, and you get 2 circuits. Perhaps put AC on one circuit, lights, coffee pot, etc on other. I would use GFI/AFCI breaker in house panel, and spend a bit extra for GFI outlets- just in case.. Helps keep wife around.
Reply With Quote
The Following 2 Users Say Thank You to Power For This Post:
  #7  
Old 10-15-2018, 07:51:50 PM
Reed Engine's Avatar
Reed Engine Reed Engine is online now
Subscriber
 
Join Date: Apr 2009
Location: Hominy, Oklahoma
Posts: 4,110
Thanks: 1,764
Thanked 4,560 Times in 1,770 Posts
Default Re: Wiring Question

Power, I'm going this way. Thanks for a great suggestion.
__________________
Wake up and smell the Fool-Aid.
Reply With Quote
  #8  
Old 10-16-2018, 08:02:57 AM
posborne80 posborne80 is offline
Registered
 
Join Date: Jul 2015
Location: Hendersonville, North Carolina
Posts: 18
Thanks: 0
Thanked 16 Times in 10 Posts
Default Re: Wiring Question

Using a supply with three phase conductors and a ground kinda gives you two circuits. What you really have is two hot lines and one neutral. This configuration means that the neutral will carry the combined load of both circuits. Maybe not a problem here, just sayin'. The wisdom of placing GFCI receptacles downstream of GFCI/AFCI breakers is much discussed. Do a search on Mike Holme's forums for some interesting reading on this. Practically speaking, you probably could throw a hunk of Romex out the window and hook it up, no problem. Maybe the place where the shed came from has some plans or drawings for reference.
Reply With Quote
  #9  
Old 10-16-2018, 03:35:42 PM
Power Power is offline
Registered-III
 
Join Date: Aug 2011
Location: New Jersey
Posts: 5,288
Thanks: 1,220
Thanked 3,163 Times in 1,860 Posts
Default Re: Wiring Question

Quote:
Originally Posted by posborne80 View Post
Using a supply with three phase conductors and a ground kinda gives you two circuits. What you really have is two hot lines and one neutral. This configuration means that the neutral will carry the combined load of both circuits. Maybe not a problem here, just sayin'. The wisdom of placing GFCI receptacles downstream of GFCI/AFCI breakers is much discussed. Do a search on Mike Holme's forums for some interesting reading on this. Practically speaking, you probably could throw a hunk of Romex out the window and hook it up, no problem. Maybe the place where the shed came from has some plans or drawings for reference.
WOW- you are WAY off.

1. Normal residential circuits are single phase.
2. This is a well accepted wiring method referenced in NEC.
3. Wired this way, neutral only carries unbalance current. Greatest load on neutral is when 1 conductor is loaded to rated capacity and other conductor has no load. As load on other conductor increases, neutral current decreases.
Reply With Quote
The Following 2 Users Say Thank You to Power For This Post:
  #10  
Old 10-16-2018, 09:21:23 PM
Frank DeWitt Frank DeWitt is offline
Subscriber
 
Join Date: Feb 2005
Location: Bloomfield, New York, USA
Posts: 729
Thanks: 138
Thanked 643 Times in 288 Posts
Default Re: Wiring Question

Quote:
Originally Posted by Power View Post
WOW- you are WAY off.

1. Normal residential circuits are single phase.
2. This is a well accepted wiring method referenced in NEC.
3. Wired this way, neutral only carries unbalance current. Greatest load on neutral is when 1 conductor is loaded to rated capacity and other conductor has no load. As load on other conductor increases, neutral current decreases.
This is all true. Go with the two hots and a neutral.
Reply With Quote
The Following User Says Thank You to Frank DeWitt For This Post:
  #11  
Old 10-17-2018, 10:46:14 AM
posborne80 posborne80 is offline
Registered
 
Join Date: Jul 2015
Location: Hendersonville, North Carolina
Posts: 18
Thanks: 0
Thanked 16 Times in 10 Posts
Default Re: Wiring Question

Power and Frank, you are both correct. I am completely wrong about figuring the load on those single phase circuits. There should be little chance of a problem if the lines are taken from both sides of the panel. My apologies to you two, Reed and all the readers here for my mistake.

Paul
Reply With Quote
The Following 2 Users Say Thank You to posborne80 For This Post:
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
VH4D Wiring Question WallyB Wisconsin Engines 17 07-26-2014 07:44:33 PM
aj wiring question tope1505 Onan Generators 4 05-19-2012 08:19:45 PM
4KW BF 220 Wiring Question enzo86 Onan Generators 0 09-05-2011 08:25:01 PM
Question about wiring CurtisFoley Generators & Electric Motors General Discussion 12 08-20-2009 12:59:32 AM
Wiring Question Jim Davis Generators & Electric Motors General Discussion 15 11-25-2008 09:13:00 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 06:59:19 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277