Default Lubricity Issues? MEP vs Commercial Diesel Unit

Good morning, all....first post to the forum, although I've been gathering info for awhile.

My question, for the clearly knowledgeable folks here, is that of lubricity. I'm decided to upgrade my Briggs 8KW gas generator, to be replaced with a diesel unit of some description. One of the reasons for doing so is access to a cheap, dependable source of Jet-A.

I know that the MEP802/3 are certified for JP8, the military equivalent of Jet-A, so shouldn't be a problem. I"m looking for information about 'do it, don't do it, do it this way' running Jet-A in, for example, an Onan-type genset. I would also welcome feedback of the dependability of each type (MEP vs. commercial) of genset.

I did a site search here on lubricity, and found nothing helpful. What say ye?

Thanks in advance!

Jim
Reply With Quote
Sponsored Links
  #2  
Old 10-08-2018, 08:42:35 PM
dependable dependable is offline
Registered-II
 
Join Date: Jan 2013
Location: Massachusetts, USA
Posts: 678
Thanks: 114
Thanked 218 Times in 155 Posts
Default Re: Lubricity Issues?....MEP vs Commercial Diesel Unit

Am not an expert, but have both MEP-802 and MEP-002s. On a military generator forum I read US forces used russian diesel/jet fuel in afganistan sometimes when it was what they had. Other times they used Jet-whatever. (I think spec plate on 002 mentions Jet-4 or something) Some of the units I've seen on auction had over 5,000 hours before depot service, still running, and am pretty sure they got no lubricity additives. Not that it would hurt to add a little to your tank.

A 002 has the same motor as the DJ series Onans, and the 802 runs a ListerPetter LPW2, which I think is speced for diesel. The MEPs do have redundant fuel pumps and much more fuel filter capacity than most civilian rigs, perhaps for a good reason. Don't know if that helps.
Reply With Quote
  #3  
Old 10-08-2018, 09:55:18 PM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 2,278
Thanks: 2
Thanked 769 Times in 542 Posts
Default Re: Lubricity Issues?....MEP vs Commercial Diesel Unit

The military can afford to replace pumps and injectors whenever they break due to jet fuel. They are not concerned about long life of anything. It is doubtful there are any parts different because of jet fuel.
Reply With Quote
  #4  
Old 10-09-2018, 11:50:14 AM
BTPost's Avatar
BTPost BTPost is offline
Moderator
 
Join Date: Jan 2005
Location: Excursion Inlet, Alaska USA 99850-0090
Posts: 4,823
Thanks: 552
Thanked 1,833 Times in 1,197 Posts
Images: 1
Talking Re: Lubricity Issues?....MEP vs Commercial Diesel Unit

I run JetA-50 (#1 Diesel low Sulfur) in my pair of 20Kw Northern Lights Gensets, and have for the last 30 years, with NO ISSUES... The previous pair that these two replaced were retired when the both had 66K operational hours on them, and the two I currently run are at 20k operational hours, all on the same fuel type.
__________________
Bruce in alaska
Reply With Quote
The Following User Says Thank You to BTPost For This Post:
  #5  
Old 10-09-2018, 07:00:24 PM
shazam shazam is offline
Registered
 
Join Date: Oct 2018
Location: Smithville, Ohio
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Lubricity Issues?....MEP vs Commercial Diesel Unit

Thank you all for the replies!

The logic seems sound that the military may not do anything different to run jet fuel in their MEPs...I understand that their overhaul cycle is 4000 hours on the units. Is that high, low, or indifferent?

Ideally, I'd like something in the 5kW range to keep fuel consumption down. BTPost....I had someone else tell me the Northern Lights units are awsome also...would love to find one of them.

Don't know if this should be a different topic or not, but here goes. I see that Generac makes a construction-grade diesel....6864 XD5000E. Yanmar diesel (3600), pressure lube, little oil filter, 16 gallon tank. I'm looking at a $4k MEP803 (10kW, .9 gph), the little Generac is 5kW, .5 gph). Anyone care to opine on those options, or hopefully offer another? Total newbie....all thoughts are welcome.

Thanks!

Jim

Oops...don't know how to edit a post. The Generac is $3500 on Amazon.

Jim
Reply With Quote
  #6  
Old 10-09-2018, 09:40:47 PM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 2,278
Thanks: 2
Thanked 769 Times in 542 Posts
Default Re: Lubricity Issues?....MEP vs Commercial Diesel Unit

Quote:
Originally Posted by shazam View Post
The logic seems sound that the military may not do anything different to run jet fuel in their MEPs...I understand that their overhaul cycle is 4000 hours on the units. Is that high, low, or indifferent?

Ideally, I'd like something in the 5kW range to keep fuel consumption down. BTPost....I had someone else tell me the Northern Lights units are awsome also...would love to find one of them.

Don't know if this should be a different topic or not, but here goes. I see that Generac makes a construction-grade diesel....6864 XD5000E. Yanmar diesel (3600), pressure lube, little oil filter, 16 gallon tank. I'm looking at a $4k MEP803 (10kW, .9 gph), the little Generac is 5kW, .5 gph). Anyone care to opine on those options, or hopefully offer another? Total newbie....all thoughts are welcome.
4000 hours is nothing for an 1800 RPM diesel. We commonly see them go 20,000 and they are not even getting worn out then.

I no longer care for those Onan/Listers. Too many issues and support is drying up fast.

5kw, you will not find anything using a reliable engine. They are all 3600 RPM toys at that level. The smallest 1800 RPM you can find is about 1.3 liter 3 cylinder in diesel these days. Kubota, Isuzu/Yanmar, Perkins, pick which one has the best dealer network to you. Something like this would do nicely.

http://www.multiquip.com/multiquip/DCA10SPXU4C.htm
Reply With Quote
  #7  
Old 10-09-2018, 10:24:19 PM
shazam shazam is offline
Registered
 
Join Date: Oct 2018
Location: Smithville, Ohio
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Lubricity Issues?....MEP vs Commercial Diesel Unit

Nice unit!....but $14k and change is a bit out of my price range :-)

Someone posted this to the site recently....it's just a couple Counties away from me. Comments??

https://www.smokstak.com/forum/showthread.php?t=181514

..and please be gentle if that's a stupid question. When I started this journey, my biggest qualification was that I could SPELL generator :-)

Jim
Reply With Quote
  #8  
Old 10-09-2018, 11:17:46 PM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is offline
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 4,368
Thanks: 792
Thanked 2,529 Times in 1,455 Posts
Default Re: Lubricity Issues? MEP vs Commercial Diesel Unit

You should describe how you will be using the generator. How many hours per year? Will it be mobile or stationary? What is the load?
Reply With Quote
  #9  
Old 10-10-2018, 06:28:50 PM
shazam shazam is offline
Registered
 
Join Date: Oct 2018
Location: Smithville, Ohio
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Lubricity Issues? MEP vs Commercial Diesel Unit

That makes perfect sense, Jim M!

Essentially, this will be just a back-up generator for our house. Ironically, in the 7 years we've had the current generator, the power has not been off long enough to use it.

I like to plan ahead, and see the aging of our national electrical infrastructure as an issue, and potential for weather-related and intentional interruptions as increasing. So, the short answer to how many hours a year is hopefully just for maintenance.

The longer, more involved story, involves a possible movement to solar and wind power for the house, and the use of the generator as a back-up for that process. We use between 900-1000 kwh a month at the house, which is totally reliant on electric....no LP or natural gas in place.

No need for the unit to be particularly mobile, once sited.

Thanks!

Jim
Reply With Quote
  #10  
Old 10-11-2018, 07:33:36 AM
dependable dependable is offline
Registered-II
 
Join Date: Jan 2013
Location: Massachusetts, USA
Posts: 678
Thanks: 114
Thanked 218 Times in 155 Posts
Default Re: Lubricity Issues? MEP vs Commercial Diesel Unit

I like my MEPs for similar use. Yes they are "overly complicated" due to ability to go from 1-3 phase, and parts are not around the corner, but can be found.

I don't know if I would recommend to someone if they were not interested in learning how to service them themselves, but you'll have a hard time finding quality, lower hours, 5 or 10 KW 1,800 RPM machines that kind of money.

All the manuals, plus some pretty good advice available the ss auxiliary equipment forum.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Murphy Diesel power unit worth anything? finkey5 Multi-Cylinder Stationary Engines and Power Units 11 01-02-2012 10:57:39 PM
Commercial Series Quiet Diesel 10000 Overheating after Coolant Flush BCS Onan Generators 5 11-08-2010 11:36:06 AM
Voltage Issues with Onan Diesel JBFL Generator DustyWake Onan Generators 3 04-13-2009 07:46:48 PM
Good Diesel house backup unit? Isaac-1 Generators & Electric Motors General Discussion 10 09-28-2008 07:55:51 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 11:22:59 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277