Wisconsin TH with US Light Power 5.5kw genset


this thread has 9 replies and has been viewed 2669 times

Reply
 
Thread Tools Display Modes
  #1  
Old 12-22-2005, 10:57:07 AM
Shootist357 Shootist357 is offline
Registered-II
 
Join Date: Dec 2005
Location: Crestview, Florida USA
Posts: 23
Thanks: 0
Thanked 0 Times in 0 Posts
Default Wisconsin TH with US Light Power 5.5kw genset

I recently purchased a very old Wisconsin TH Genset marked US Light Power 5.5kw. Runs on Propane, and has electric start via the generator end. Info is as follows;
>
>
> WISCONSIN TH>
> Ser: 3086075> (Any help on the year of production?)
> spec: 165745>
> 3 1/4 X 3 1/4
>
> 5500 WATT
>
> Ensign 1" carburetor and regulator model B, 4-6 oz
>>
>
> US light power>
> Model:PE505G18>
> Ser: 325649>
> 5.5kw>
> 115 volt>
> 47.8 A>
> phase 1>
> 60 Hz>
> 1800 rpm>
>
> I'd appreciate any (and all) info you may have on this item. I'll post some pics later. Shootist
Reply With Quote
Sponsored Links
  #2  
Old 12-22-2005, 06:01:50 PM
K D Redd K D Redd is offline
In Memory Of
 
Join Date: Nov 2004
Location: Southwest Missouri
Posts: 5,348
Thanks: 166
Thanked 1,197 Times in 1,058 Posts
Default Re: Wisconsin TH with US Light Power 5.5kw genset

See my reply to you under "This old generator"

Kent
Reply With Quote
  #3  
Old 12-22-2005, 06:05:39 PM
K D Redd K D Redd is offline
In Memory Of
 
Join Date: Nov 2004
Location: Southwest Missouri
Posts: 5,348
Thanks: 166
Thanked 1,197 Times in 1,058 Posts
Default Re: Wisconsin TH with US Light Power 5.5kw genset

I forgot something. If your TF is a magneto type ignition, you can use one of the single cylinder solidstate points replacments chips in you mag. I am using this in the mag on a THD.

Kent
Reply With Quote
  #4  
Old 12-22-2005, 07:10:58 PM
Shootist357 Shootist357 is offline
Registered-II
 
Join Date: Dec 2005
Location: Crestview, Florida USA
Posts: 23
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Wisconsin TH with US Light Power 5.5kw genset

Well, here is a pic of the generator as I found it. I'm in the process of cleaning it up a bit. I'll post more pics later. Mike
Attached Thumbnails
Click image for larger version

Name:	wisconsin gen.jpg
Views:	254
Size:	91.5 KB
ID:	5688  
Reply With Quote
  #5  
Old 12-23-2005, 09:27:15 PM
Shootist357 Shootist357 is offline
Registered-II
 
Join Date: Dec 2005
Location: Crestview, Florida USA
Posts: 23
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Wisconsin TH with US Light Power 5.5kw genset

If you want to appreciate old quality, check out these pics... Seeing as the electronics were all rusted away, what do you guys think I should fuse this thing with? I was thinking at least a 30A on the main leads. The nameplate states 47.8 A @ 115. Did I mention I LOVE this website...
Attached Thumbnails
Click image for larger version

Name:	brushes.JPG
Views:	147
Size:	76.1 KB
ID:	5702   Click image for larger version

Name:	heavy metal.JPG
Views:	171
Size:	89.5 KB
ID:	5703  
Reply With Quote
  #6  
Old 12-23-2005, 11:12:41 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 6,746
Thanks: 423
Thanked 5,995 Times in 2,833 Posts
Default Re: Wisconsin TH with US Light Power 5.5kw genset

Quote:
Originally Posted by Shootist357
... what do you guys think I should fuse this thing with? I was thinking at least a 30A on the main leads. The nameplate states 47.8 A @ 115...
Why fuse it at 30a fuse (30 X 115= 3450w) if the rating is much higher? I would use a 40 or 50 amp fuse, depending on how "idiot proof" you want it to be.

W
Reply With Quote
  #7  
Old 12-24-2005, 10:48:46 AM
Shootist357 Shootist357 is offline
Registered-II
 
Join Date: Dec 2005
Location: Crestview, Florida USA
Posts: 23
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Wisconsin TH with US Light Power 5.5kw genset

I just wanted a sanity check...The only protection on the generator when I opened it up was a 25A thermal overload hooked to a couple of relays. I believe this was to protect the generator during cranking. It was rusted solid, and also melted. The gen head still works fine and puts out plenty of AC. This is a 4 pole unit with two main leads coming from the head. Since I need lugs to hook everything up anyway, I'll look for something I can bolt right in. I'm thinking 45A fuses/breakers (provided my main leads are heavy enough). Thanks for the reply. Mike
Reply With Quote
  #8  
Old 12-25-2005, 01:20:02 PM
B.Sparks B.Sparks is offline
Registered-III
 
Join Date: May 2005
Location: Central, Wisconsin USA
Posts: 252
Thanks: 1
Thanked 19 Times in 16 Posts
Default Re: Wisconsin TH with US Light Power 5.5kw genset

"I'm thinking 45A fuses/breakers (provided my main leads are heavy enough)"

Be careful selecting overcurrent protection for your genset. The safest approach would be to use a 50 amp fuse. If you want to use a breaker, find one intended for use with a genset. DO NOT use a general-purpose circuit breaker of the type you'll find in your home's electrical service panel.

The circuit breakers in your electrical service panel were designed to protect WIRING, not EQUIPMENT. Being made to sell for a low price, the calibration (trip current and time delay curves) are quite 'loose.' When selected properly, electrical service panel circuit breakers will (at least should) keep the house from burning down but countless motors, appliances and the like have burned out despite the 'protection.'

The main technical issue is "fault current." The electrical power grid has nearly unlimited current available in the event of a short circuit ("fault") or overload. In the event of a short circuit tens of thousands of amps can (very briefly) be drawn from a residential electrical service. Household circuit breakers were designed with this fact in mind. They need this big-time 'kick in the pants' to trip. It all happens so quickly that the wiring doesn't have time to heat up despite the massive current.

On the other hand, a genset has a relatively small amount of fault current available. A generator that can provide 50 amps under normal load conditions might only be able to pump out a fault current of 75-100 amps into a short circuit or overload. A 50 amp breaker electrical service panel breaker cannot be counted on to trip and clear the fault. The genset just doesn't have the same sort of "kick in the pants" current available.
Reply With Quote
  #9  
Old 12-31-2005, 09:39:56 AM
Shootist357 Shootist357 is offline
Registered-II
 
Join Date: Dec 2005
Location: Crestview, Florida USA
Posts: 23
Thanks: 0
Thanked 0 Times in 0 Posts
Photo Re: Wisconsin TH with US Light Power 5.5kw genset

After thinking it over, I've decided to go the old safe route and use a couple of big Buss fuses for the internal main leads. I have another generator I restored and used a screw in house fuse for the mains. (see before and after Pics). It is an old winco and runs like a champ. I'll add a nice power distribution panel to the Wisconsin. Thanks for all the info. Shootist
Attached Thumbnails
Click image for larger version

Name:	winco final.JPG
Views:	149
Size:	82.9 KB
ID:	5874   Click image for larger version

Name:	winco original.JPG
Views:	133
Size:	62.6 KB
ID:	5875  
Reply With Quote
  #10  
Old 01-01-2006, 04:48:28 AM
ListerDiesel's Avatar
ListerDiesel ListerDiesel is offline
In Memory Of
 
Join Date: Oct 2004
Location: Rushden, Northamptonshire, United Kingdom
Posts: 3,616
Thanks: 44
Thanked 2,166 Times in 757 Posts
Default Re: Wisconsin TH with US Light Power 5.5kw genset

Quote:
Originally Posted by Shootist357
After thinking it over, I've decided to go the old safe route and use a couple of big Buss fuses for the internal main leads. I have another generator I restored and used a screw in house fuse for the mains. (see before and after Pics). It is an old winco and runs like a champ. I'll add a nice power distribution panel to the Wisconsin. Thanks for all the info. Shootist
Very nice job!

Peter
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
OK, The Power Is Out And Your Genset Is Up And Running, Robert in W. Mi. Generators & Electric Motors General Discussion 19 10-31-2006 07:50:05 AM
Small Buda diesel with Kato-Light genset? Robt. Generators & Electric Motors General Discussion 1 04-09-2006 12:05:38 PM
Wisconsin Genset Brian Tindall Generators & Electric Motors General Discussion 18 12-22-2005 07:35:33 PM
please identify genset wisconsin?? steve tyson Generators & Electric Motors General Discussion 2 12-27-2002 03:18:32 AM
Wards power light Tracy Schroeder Generators & Electric Motors General Discussion 5 12-19-2002 10:46:24 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 12:13:11 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277