"BRUTUS" my Onan 2.5LK failed.


this thread has 13 replies and has been viewed 574 times

Reply
 
Thread Tools Display Modes
  #1  
Old 09-08-2017, 06:17:43 AM
Esteban32696 Esteban32696 is offline
Registered-III
 
Join Date: Jul 2007
Location: Florida
Posts: 432
Thanks: 0
Thanked 89 Times in 67 Posts
Default "BRUTUS" my Onan 2.5LK failed.

I call my 2.5LK," Brutus " for obvious reasons . I have owned it about 15 years & it has served me well. I live in North Florida, & for a final check of everything before Irma comes for a visit, Brutus failed to start. I used it about 2 months ago, when I lost power , with no problems.
Checked it out & no fire to the plug . Checked points & they look awful. Filing didn't help these. There is no place,, or time to do anything else to it, so I will have to get by with my little Honda generator.
Reply With Quote
Sponsored Links
  #2  
Old 09-08-2017, 07:04:12 AM
lokay5's Avatar
lokay5 lokay5 is offline
Subscriber
 
Join Date: May 2007
Location: Merlin, Oregon
Posts: 1,298
Thanks: 3,362
Thanked 761 Times in 474 Posts
Default Re: " BRUTUS , " my Onan 2.5LK failed .

A bad condenser can wreak havoc with points. Try any condenser you have around that'll fit. You may be pleasantly surprised...or not.
Best wishes and good luck down there. (Glad you have the Honda.)

"Jungle Jim" Lieberman BRUTUS http://www.leblogauto.com/wp-content...s-liberman.jpg
__________________
1973 CK5 Blazer
Reply With Quote
The Following 2 Users Say Thank You to lokay5 For This Post:
  #3  
Old 09-08-2017, 08:05:52 AM
David C David C is offline
Registered-III
 
Join Date: Mar 2006
Location: Lake Jackson,Texas
Posts: 1,330
Thanks: 934
Thanked 820 Times in 538 Posts
Default Re: " BRUTUS , " my Onan 2.5LK failed .

Hook a test light to ground and while cranking, check for 12 volts at the points. If the light flashes while cranking, I would try a condenser as Lokay suggested. If you get a steady light, you have a set of points that are not completing the circuit to ground. If there is no light, check for power at the positive side of the coil while cranking. If you have power to the positive side of the coil, you have a open primary winding in the coil or a shorted out condenser or a pinched wire between the coil and the points. Coils do fail, but it is not a common failure. Hope all goes well with Irma.

David C.
Reply With Quote
  #4  
Old 09-08-2017, 01:02:32 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 14,236
Thanks: 370
Thanked 5,145 Times in 3,739 Posts
Default Re: " BRUTUS , " my Onan 2.5LK failed .

I like to sand points with good sandpaper, ~ 180 grit. Fold a strip in half and drag thru the closed points.

Condensers come in at least 2 different capacitance's, one for points (on points side of coil), other for just radio noise RF suppression ( on +12V side of coil) , don't need the RF one for engine to run. So if you can get a few of condensers just try them one at a time, they basically stop the big arcs at points ( ideally points shouldn't arc, arcing pits points)

Good to put condenser by points. But I think it just has to connect between ground and to wire from points to coil, so you can put it anywhere that's convenient. Likely good to keep it dry.

If can't buy a condenser maybe can scrounge one from a lawn mower that uses points. Got a feeling they are all about same capacitance value.


Best to use condensor for an engine. But If others can post it's rough capacitance maybe you can get capacitor from radio shack, mounting won't be same, they likely only have 2 bare wires, but in an emergency . Think voltage rating is ~ 300 or 500 volts ???, might be 3-5 mfd (3-5 uf) capacitance , non-polar (not electroytic cap = not aluminum can). Condensor is a capacitor., just the old name for it

Last edited by len k; 09-08-2017 at 09:57:26 PM.
Reply With Quote
The Following User Says Thank You to len k For This Post:
  #5  
Old 09-08-2017, 09:53:09 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 14,236
Thanks: 370
Thanked 5,145 Times in 3,739 Posts
Default Re: " BRUTUS , " my Onan 2.5LK failed .

Just got a pm from a Staker, he says

"points caps are 0.3uf to 0.5uf , notice the decimal point"

so if you go to radio shack or scroung a cap from an old TV, ect that and a voltage rating of at least ~ 300 V should work.

-------------------------

Looks like points cap is ~ .3 MFD ( MFD = uf) ~ 300 Volt rating ( more voltage is ok) see this old thread. See post 13 !!!!!! Also end of post 12.
https://www.smokstak.com/forum/showt...ghlight=points
.

Last edited by len k; 09-09-2017 at 09:59:02 AM.
Reply With Quote
The Following User Says Thank You to len k For This Post:
  #6  
Old 09-09-2017, 02:39:45 AM
lokay5's Avatar
lokay5 lokay5 is offline
Subscriber
 
Join Date: May 2007
Location: Merlin, Oregon
Posts: 1,298
Thanks: 3,362
Thanked 761 Times in 474 Posts
Default Re: " BRUTUS , " my Onan 2.5LK failed .

Re -RadioShack -

https://www.usatoday.com/story/money...eft/102372912/
__________________
1973 CK5 Blazer
Reply With Quote
  #7  
Old 09-09-2017, 06:35:34 AM
Esteban32696 Esteban32696 is offline
Registered-III
 
Join Date: Jul 2007
Location: Florida
Posts: 432
Thanks: 0
Thanked 89 Times in 67 Posts
Default Re: " BRUTUS , " my Onan 2.5LK failed .

Quote:
Originally Posted by lokay5 View Post
A bad condenser can wreak havoc with points. Try any condenser you have around that'll fit. You may be pleasantly surprised...or not.
Best wishes and good luck down there. (Glad you have the Honda.)

"Jungle Jim" Lieberman BRUTUS http://www.leblogauto.com/wp-content...s-liberman.jpg

I like your " Brutus " better than I like mine !!

Thanks for all the help !! I am sitting tight right now expecting the storm to hit late Sunday. I won't work on the generator til all this is over. It came out of a 1968 motorhome & I have gotten my money's worth out of it. I love listening to that 1800RPM machine run.
Reply With Quote
  #8  
Old 09-09-2017, 10:01:38 AM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 14,236
Thanks: 370
Thanked 5,145 Times in 3,739 Posts
Default Re: " BRUTUS , " my Onan 2.5LK failed .

TIP ..... if the cap you salvage from a TV or radio shack has a +/- or positive/negnative markings on it then it's a polarized type cap and I wouldn't use it as cap will likely die, because in use it will see both polarities ( ei will be reversed polarized 1/2 the time). But in an emergency maybe it will last long enough?? Might fail in a few minutes or days, don't know.
Reply With Quote
  #9  
Old 09-09-2017, 10:07:35 PM
dracer dracer is offline
Registered
 
Join Date: Apr 2017
Location: Klamath River, California
Posts: 35
Thanks: 0
Thanked 5 Times in 5 Posts
Default Re: " BRUTUS , " my Onan 2.5LK failed .

my 6.5 quit during a storm , the condenser went bad , in a pinch I used the one on the pos. side of the coil and worked until I could get the proper one
Reply With Quote
The Following User Says Thank You to dracer For This Post:
  #10  
Old 09-10-2017, 08:19:37 AM
Esteban32696 Esteban32696 is offline
Registered-III
 
Join Date: Jul 2007
Location: Florida
Posts: 432
Thanks: 0
Thanked 89 Times in 67 Posts
Default Re: "BRUTUS" my Onan 2.5LK failed.

Someone suggested a conversion to electronic ignition, but I don't know anything about that. Is there a " kit " for doing this ?
Reply With Quote
  #11  
Old 09-10-2017, 08:38:10 AM
AngrySailor AngrySailor is offline
Registered-I
 
Join Date: Apr 2017
Location: West Prince, Prince Edward Isand, Canada
Posts: 148
Thanks: 39
Thanked 78 Times in 47 Posts
Default Re: " BRUTUS , " my Onan 2.5LK failed .

Quote:
Originally Posted by len k View Post
TIP ..... if the cap you salvage from a TV or radio shack has a +/- or positive/negnative markings on it then it's a polarized type cap and I wouldn't use it as cap will likely die, because in use it will see both polarities ( ei will be reversed polarized 1/2 the time). But in an emergency maybe it will last long enough?? Might fail in a few minutes or days, don't know.
Or...If you have two polarized caps of double the required value, wire them in series -/- or +/+ to simulate a non polar cap
Reply With Quote
  #12  
Old 09-10-2017, 08:38:49 AM
JohnnyC JohnnyC is offline
Subscriber
 
Join Date: Jun 2014
Location: Boonton, New Jersey
Posts: 3,749
Thanks: 1,028
Thanked 1,705 Times in 1,005 Posts
Default Re: "BRUTUS" my Onan 2.5LK failed.

Quote:
Originally Posted by Esteban32696 View Post
Someone suggested a conversion to electronic ignition, but I don't know anything about that. Is there a " kit " for doing this ?
I don't know the specifics for a conversion for a 2.5LK, but if you had a 6.5NH like dracer or similar genset it can be done using an OEM Onan electronic ignition and still retain the OEM points setup as a redundant ignition backup system in case one fails. I did it to my NH with excellent results and switching between the two ignition systems is only a flip of a toggle switch.

JohnnyC
New Jersey
Reply With Quote
  #13  
Old 09-10-2017, 08:56:55 PM
dracer dracer is offline
Registered
 
Join Date: Apr 2017
Location: Klamath River, California
Posts: 35
Thanks: 0
Thanked 5 Times in 5 Posts
Default Re: "BRUTUS" my Onan 2.5LK failed.

in fact I did replace my cond with a electronic from kirk engines , two other ones that I picked up I put the gm ign module on them thy work good, the info is on the form on how to do it
Reply With Quote
The Following User Says Thank You to dracer For This Post:
  #14  
Old 09-10-2017, 09:24:11 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 14,236
Thanks: 370
Thanked 5,145 Times in 3,739 Posts
Default Re: "BRUTUS" my Onan 2.5LK failed.

Alternate electronic ignition systems, convenient list of links
https://www.smokstak.com/forum/showthread.php?t=167037
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Yall are gonna hate this, onan failed during outage quabillion Onan Generators 16 06-01-2016 01:12:08 AM
One less Brutus Brian.P Antique Gas Engine Discussion 1 01-12-2016 10:19:19 PM
Onan HDKBA failed stator or fueling Antny Onan Generators 45 07-18-2015 03:39:00 PM
Brutus Engine works Brian.P Antique Gas Engine Discussion 1 06-26-2011 10:36:56 AM
The making of the Brutus 3 hp sideshaft Brian.P Antique Gas Engine Discussion 13 03-14-2010 11:33:55 AM