Onan Standby Generator 50 5KW3 phase 19820


this thread has 44 replies and has been viewed 2261 times

Reply
 
Thread Tools Display Modes
  #1  
Old 06-04-2017, 03:49:30 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Onan Standby Generator 50 5KW3 phase 19820

Which control wires need to be hooked together to make a standby generator excited all the time so I can convert to portable generator

---------- Post added at 02:49:30 PM ---------- Previous post was at 02:43:34 PM ----------

Model number 55.OEN 15R/25432D
Reply With Quote
Sponsored Links
  #2  
Old 06-04-2017, 03:50:05 PM
BRae's Avatar
BRae BRae is offline
Sponsor
 
Join Date: Oct 2013
Location: Escanaba, Michigan
Posts: 679
Thanks: 291
Thanked 394 Times in 225 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

Please post the COMPLETE model and serial numbers so the smart guys can lead you in the right direction.
Reply With Quote
The Following User Says Thank You to BRae For This Post:
  #3  
Old 06-04-2017, 04:39:12 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 17,029
Thanks: 8,826
Thanked 14,394 Times in 6,793 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

Don't understand your question. What are you trying to do. 55KW is hardly a portable generator. If you want to be able to run it. Just flip the switch to RUN. It will do the rest.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following 5 Users Say Thank You to Billy J Shafer For This Post:
  #4  
Old 06-04-2017, 06:04:49 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 4,138
Thanks: 5,330
Thanked 1,768 Times in 1,191 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

To make it excited ALL of the time, put a nice photo of a classic Kohler with the cowl doors open in front of it.
Reply With Quote
The Following 12 Users Say Thank You to Vanman For This Post:
  #5  
Old 06-04-2017, 06:22:52 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 17,029
Thanks: 8,826
Thanked 14,394 Times in 6,793 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

Quote:
Originally Posted by Vanman View Post
To make it excited ALL of the time, put a nice photo of a classic Kohler with the cowl doors open in front of it.
You could also show it. A picture of a Generac in flames.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following 10 Users Say Thank You to Billy J Shafer For This Post:
  #6  
Old 06-04-2017, 07:45:08 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Onanstandby generator 50 5KW3 phase 19820

Model number 55.OEN-15R25432D. Serial number F820623029. The generator was placed at three please reword it for single phase it had a transfer switch on it there is no transfer switch on it now it will not produce power what am I doing wrong

---------- Post added at 06:45:08 PM ---------- Previous post was at 06:19:47 PM ----------

I have a Onan 55KW generator three-phase model number 55.OEN-15R25432D. Serial number F820623029when I purchased it it was hooked up on three phase with a transfer switch I have reconfigured the wiring for single phase 220 I do not have a transfer switch I cannot figure out how to make it produce power
Reply With Quote
  #7  
Old 06-04-2017, 08:42:47 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 5,970
Thanks: 363
Thanked 5,050 Times in 2,428 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

At this point, there is no way to tell what you may have done incorrectly.

Please answer these questions-

(1) Did you see the generator produce voltage when it was wired for 3 phase?

(2) What reference material did you use to determine your wiring for single phase?

(3) When you started the set up after rewiring, did the engine labor at any time?

(4) Did you record the original wiring scheme, so you might return it to the previous 3 phase condition?
Reply With Quote
The Following 5 Users Say Thank You to Wayne 440 For This Post:
  #8  
Old 06-04-2017, 08:50:43 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 17,029
Thanks: 8,826
Thanked 14,394 Times in 6,793 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

Your wiring should look like this. Be sure to move wire 63 to H5. Are you checking voltage at L1/L2 or just using the meters
Attached Thumbnails
Click image for larger version

Name:	img075.jpg
Views:	68
Size:	132.3 KB
ID:	283672  
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following 2 Users Say Thank You to Billy J Shafer For This Post:
  #9  
Old 06-04-2017, 11:21:32 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Onanstandby generator 50 5KW3 phase 19820

Are use the schematic that's inside the panel behind the breaker I did change the war in the control panel behind the gauges but there is a jumper wire going from age 3 to 63 I disconnected the 63 side of the jumper wire no I did not ever see this generator make voltage after I got it home

No the generator has never labeled like it's got a loadall the wars that went to the remote for inside the house and all the wires that went to the transfer switch the small wires have got wire twist nights on all of them

I did move the wire to h5 what is the jumper wire for that goes from h3 to63 for

When I got the generator it was wired like number three colony on the wiring diagram I rewired it to diagram one
Reply With Quote
  #10  
Old 06-05-2017, 04:57:25 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 17,029
Thanks: 8,826
Thanked 14,394 Times in 6,793 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

Wire 63 goes on terminal 63. With the jumper wire going to H5. Jumper to H3 is for another voltage.120/208 3 phase which you have changed. You no longer need H3. The jumper from 63 will now go to H5
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
120v single phase motor turning 3 phase generator gibbykart Generators & Electric Motors General Discussion 15 10-04-2014 12:00:37 PM
Is My Onan Standby Generator at Risk? Leon N. Onan Generators 12 02-09-2012 08:41:09 AM
US Motor Div Generator Conversion To Single Phase 220V From Three Phase jimybud Generators & Electric Motors General Discussion 4 06-27-2010 08:19:50 PM
Onan standby generator info. needed powerwagon Onan Generators 9 11-26-2009 05:57:51 PM
Converting a Kohler Generator from 3 phase to single phase KendalPernod Kohler Generators 3 09-13-2005 10:08:28 PM