Which control wires need to be hooked together to make a standby generator excited all the time so I can convert to portable generator

---------- Post added at 02:49:30 PM ---------- Previous post was at 02:43:34 PM ----------

Model number 55.OEN 15R/25432D
Reply With Quote
Sponsored Links
  #2  
Old 06-04-2017, 03:50:05 PM
BRae's Avatar
BRae BRae is offline
Sponsor
 
Join Date: Oct 2013
Location: Escanaba, Michigan
Posts: 656
Thanks: 277
Thanked 371 Times in 217 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

Please post the COMPLETE model and serial numbers so the smart guys can lead you in the right direction.
Reply With Quote
The Following User Says Thank You to BRae For This Post:
  #3  
Old 06-04-2017, 04:39:12 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,322
Thanks: 8,299
Thanked 13,666 Times in 6,432 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

Don't understand your question. What are you trying to do. 55KW is hardly a portable generator. If you want to be able to run it. Just flip the switch to RUN. It will do the rest.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following 5 Users Say Thank You to Billy J Shafer For This Post:
  #4  
Old 06-04-2017, 06:04:49 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 3,277
Thanks: 4,031
Thanked 1,361 Times in 910 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

To make it excited ALL of the time, put a nice photo of a classic Kohler with the cowl doors open in front of it.
Reply With Quote
The Following 12 Users Say Thank You to Vanman For This Post:
  #5  
Old 06-04-2017, 06:22:52 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,322
Thanks: 8,299
Thanked 13,666 Times in 6,432 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

Quote:
Originally Posted by Vanman View Post
To make it excited ALL of the time, put a nice photo of a classic Kohler with the cowl doors open in front of it.
You could also show it. A picture of a Generac in flames.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following 10 Users Say Thank You to Billy J Shafer For This Post:
  #6  
Old 06-04-2017, 07:45:08 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Onanstandby generator 50 5KW3 phase 19820

Model number 55.OEN-15R25432D. Serial number F820623029. The generator was placed at three please reword it for single phase it had a transfer switch on it there is no transfer switch on it now it will not produce power what am I doing wrong

---------- Post added at 06:45:08 PM ---------- Previous post was at 06:19:47 PM ----------

I have a Onan 55KW generator three-phase model number 55.OEN-15R25432D. Serial number F820623029when I purchased it it was hooked up on three phase with a transfer switch I have reconfigured the wiring for single phase 220 I do not have a transfer switch I cannot figure out how to make it produce power
Reply With Quote
  #7  
Old 06-04-2017, 08:42:47 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 5,188
Thanks: 310
Thanked 4,250 Times in 2,035 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

At this point, there is no way to tell what you may have done incorrectly.

Please answer these questions-

(1) Did you see the generator produce voltage when it was wired for 3 phase?

(2) What reference material did you use to determine your wiring for single phase?

(3) When you started the set up after rewiring, did the engine labor at any time?

(4) Did you record the original wiring scheme, so you might return it to the previous 3 phase condition?
Reply With Quote
The Following 5 Users Say Thank You to Wayne 440 For This Post:
  #8  
Old 06-04-2017, 08:50:43 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,322
Thanks: 8,299
Thanked 13,666 Times in 6,432 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

Your wiring should look like this. Be sure to move wire 63 to H5. Are you checking voltage at L1/L2 or just using the meters
Attached Thumbnails
Click image for larger version

Name:	img075.jpg
Views:	68
Size:	132.3 KB
ID:	283672  
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following 2 Users Say Thank You to Billy J Shafer For This Post:
  #9  
Old 06-04-2017, 11:21:32 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Onanstandby generator 50 5KW3 phase 19820

Are use the schematic that's inside the panel behind the breaker I did change the war in the control panel behind the gauges but there is a jumper wire going from age 3 to 63 I disconnected the 63 side of the jumper wire no I did not ever see this generator make voltage after I got it home

No the generator has never labeled like it's got a loadall the wars that went to the remote for inside the house and all the wires that went to the transfer switch the small wires have got wire twist nights on all of them

I did move the wire to h5 what is the jumper wire for that goes from h3 to63 for

When I got the generator it was wired like number three colony on the wiring diagram I rewired it to diagram one
Reply With Quote
  #10  
Old 06-05-2017, 04:57:25 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,322
Thanks: 8,299
Thanked 13,666 Times in 6,432 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

Wire 63 goes on terminal 63. With the jumper wire going to H5. Jumper to H3 is for another voltage.120/208 3 phase which you have changed. You no longer need H3. The jumper from 63 will now go to H5
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
  #11  
Old 06-05-2017, 03:25:19 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Onanstandby generator 50 5KW3 phase 19820

Going by the schematic inside my generator it matches the schematic y'all have sent me the reason I ask about controllers wires out I assumed there was a real relay in the transfer switch that told the generator to only excite if it notice no power at the transfer switch
Reply With Quote
  #12  
Old 06-05-2017, 04:58:16 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,322
Thanks: 8,299
Thanked 13,666 Times in 6,432 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

The transfer switch would only tell it to start and stop. Thru B+and RMT. The power production is all done at the generator. You need to download manual 900-0150. Should be on the twinslan list on this site.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following User Says Thank You to Billy J Shafer For This Post:
  #13  
Old 06-05-2017, 05:16:56 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Onanstandby generator 50 5KW3 phase 19820

Thanks Billy Really appreciate your help
Reply With Quote
  #14  
Old 06-05-2017, 09:38:57 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,436
Thanks: 71
Thanked 1,186 Times in 969 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

Is exciter breaker on the control panel switched on?
Reply With Quote
The Following User Says Thank You to Jim Rankin For This Post:
  #15  
Old 06-06-2017, 07:46:31 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Onanstandby generator 50 5KW3 phase 19820

Thanks for your support and help generators making power I'll change the points today because the old ones were totally burn up does anybody know what the gap sets to on The points it's natural gas how do idol this generator up The governor is working but it won't Riv up to 1800 RPM's and does anybody know what the Dwale should set it on these points
Reply With Quote
  #16  
Old 06-06-2017, 10:23:15 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Onanstandby generator 50 5KW3 phase 19820

Since I know it runs and puts out power I replaced the point gotdwell close to what I think to right does anybody know if a regular automotive cool with an external resister will work on my unit does this unit have a resistor built in for the coal somewhere on it or do I need to put a resistor on it I cannot find alternate part number for the does anybody know if a regular automotive cool with external resistor will work on my unit does this unit have a resistor built in for the Coulp somewhere only or do I need to put a resistor on it I cannot find alternate part number for the Coil that come on the ford 460 does the belt driven governor use oilif so what type of role I cannot find a manual on this generator once again thanks for all y'all's help maybe I can help y'all sometime
Reply With Quote
  #17  
Old 06-07-2017, 06:15:42 AM
Kevin K Kevin K is online now
Registered-III
 
Join Date: Jan 2005
Location: upstate New York USA
Posts: 3,524
Thanks: 3,163
Thanked 3,520 Times in 1,907 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

I'm attaching the factory production order and wiring diagrams for your generator.

You can download manuals here: http://www.twinslan.net/~n0nas/manuals/onan/

928-0121
900-0150

The wiring diagram does not show an ignition resistor, so you should be able to use a standard 12 volt coil.
Attached Files
File Type: pdf 550EN15R25432D.pdf (31.8 KB, 9 views)
File Type: pdf 612-5301.pdf (148.4 KB, 11 views)
File Type: pdf 612-5311.pdf (143.9 KB, 9 views)
Reply With Quote
The Following 3 Users Say Thank You to Kevin K For This Post:
  #18  
Old 06-07-2017, 08:02:08 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,322
Thanks: 8,299
Thanked 13,666 Times in 6,432 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

The engine is a standard Ford 460. With a few things Onan added to make it a generator engine. The gov uses the same oil as the engine.The belt should be a little lose. To tight and you will destroy a 900.00 dollar gov. The service manual will explain all. Be sure and study it before you cost yourself some money.

928-0121 will have the information you need.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
  #19  
Old 06-17-2017, 11:16:15 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Onanstandby generator 50 5KW3 phase 19820

Check my wire in three or four times wired right when I turned excited broke her own shows The voltmeter maxed out votes on the lower scale and trips the exciter breakerevery time with a severe load

---------- Post added at 10:14:22 PM ---------- Previous post was at 10:13:12 PM ----------

Breaker shows

---------- Post added at 10:16:15 PM ---------- Previous post was at 10:14:22 PM ----------

It's like the voltage regulator is not working
Reply With Quote
  #20  
Old 06-17-2017, 11:23:16 PM
pegasuspinto pegasuspinto is online now
Registered-III
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 2,533
Thanks: 320
Thanked 1,162 Times in 765 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

Generally we tell anyone who will listen, to check and fix the set before they rewire it. Now you don't know if it was broken or your wired it wrong.

You can disconnect the windings and then check them with a megger....then re-assemble.
Reply With Quote
The Following User Says Thank You to pegasuspinto For This Post:
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
120v single phase motor turning 3 phase generator gibbykart Generators & Electric Motors General Discussion 15 10-04-2014 12:00:37 PM
Is My Onan Standby Generator at Risk? Leon N. Onan Generators 12 02-09-2012 08:41:09 AM
US Motor Div Generator Conversion To Single Phase 220V From Three Phase jimybud Generators & Electric Motors General Discussion 4 06-27-2010 08:19:50 PM
Onan standby generator info. needed powerwagon Onan Generators 9 11-26-2009 05:57:51 PM
Converting a Kohler Generator from 3 phase to single phase KendalPernod Kohler Generators 3 09-13-2005 10:08:28 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 08:19:01 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277