Onan Standby Generator 50 5KW3 phase 19820


this thread has 44 replies and has been viewed 2221 times

Reply
 
Thread Tools Display Modes
  #21  
Old 06-17-2017, 11:38:12 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 5,884
Thanks: 358
Thanked 4,954 Times in 2,380 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

+1 for the comment from pegasuspinto.

And a bit of advice from one of my favorite movies- "...Man's got to know his limitations". A laboring engine and exciter overcurrent are signs that you could easily cause damage that results in a high dollar repair.

Consider spending some money to have an experienced generator tech look it over. That will be much less expensive than a stator rewind.
Reply With Quote
The Following 2 Users Say Thank You to Wayne 440 For This Post:
Sponsored Links
  #22  
Old 06-18-2017, 12:45:42 AM
Steve Dawkins Steve Dawkins is offline
Sponsor
 
Join Date: Feb 2005
Location: Virginia Beach, Virginia, USA
Posts: 834
Thanks: 535
Thanked 321 Times in 180 Posts
Default Re: Onanstandby generator 50 5KW3 phase 19820

At this point, some good photos of the wiring might help in troubleshooting.

We know you've checked your wiring several times, but make sure that generator leads T6 and T9 haven't gotten crossed. That is an easy mistake.

It sound like something is shorting out, since the voltmeter pegs and the exciter (field) circuit breaker trips. The following procedure will be time consuming, but might help in isolating the problem.

1. Make sure the generator cannot start. Disconnect the battery.
2. Disconnect all generator leads T1 thru T12, and isolate each wire from the others.
3. Take an ohm meter, and connect one lead to a good ground on the generator. Using the other lead, touch leads T1 thru T12 one at a time. You should not have any continuity at all. If you have continuity on any of the tests, you have a winding that is shorted to ground. (Wiring may have to be disconnected from the voltage regulator for this test to be accurate.)


Next, you will check the six windings to make sure that the wires are labeled correctly. Each winding will have two ends. They are as follows:

T1 & T4
T2 & T5
T3 & T6
T7 & T10
T8 & T11
T9 & T12

1. Take your ohm meter and check to make sure you have continuity for each winding.
2. As you check each winding, leave one meter lead attached to a T lead, and touch all the other T leads to make sure there is no continuity between windings.


If the above procedure checks out, perform the following:

1. Tape off T1 thru T12 separately with electrical tape. This will be temporary. Do yourself a favor, and leave a little tail of tape folded back on itself as you wrap each lead. This tail will make it easier to remove the tape after the test.
2. Start the generator and turn on the exciter (field) circuit breaker. See if it trips. Report back to us afterwards, so we will know which way to direct you.
3. USE EXTREME CAUTION WHEN PERFORMING #2 ABOVE, and make sure those leads are insulated well.

EDIT: If you aren't comfortable with performing the above tests, follow the advice suggested by Wayne 400.

Last edited by Steve Dawkins; 06-18-2017 at 01:09:57 AM. Reason: Agreeing with Wayne 440
Reply With Quote
The Following 4 Users Say Thank You to Steve Dawkins For This Post:
  #23  
Old 06-18-2017, 12:45:05 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Onan Standby Generator 50 5KW3 phase 19820

I'll put the wire configuration back the way it was and grounded the unit it's putting out power with no problems was the reason that one putting out power the way I had it because it wasn't grounded
Reply With Quote
  #24  
Old 06-18-2017, 12:59:44 PM
pegasuspinto pegasuspinto is offline
Registered-III
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 2,642
Thanks: 327
Thanked 1,230 Times in 807 Posts
Default Re: Onan Standby Generator 50 5KW3 phase 19820

Quote:
Originally Posted by Friends with benefits View Post
I'll put the wire configuration back the way it was and grounded the unit it's putting out power with no problems was the reason that one putting out power the way I had it because it wasn't grounded
I'll be the one to say it. Grounding the unit won't make any difference to if it makes power. (Tho the frame should be grounded). IMHO you're very likely to damage something or get you or someone else hurt. I'm not trying to be mean, I just don't feel like you have a great grasp of electricity and/or generators. Please be careful and consider what you are doing...
Reply With Quote
The Following User Says Thank You to pegasuspinto For This Post:
  #25  
Old 06-18-2017, 01:38:46 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,908
Thanks: 8,728
Thanked 14,272 Times in 6,736 Posts
Default Re: Onan Standby Generator 50 5KW3 phase 19820

I have been at this for over forty years. Grounding will not effect power out put. If you rewired it and it didn't work. Then returned it to the way it was and now works. You have a wiring problem.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
  #26  
Old 06-18-2017, 02:32:27 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Onan Standby Generator 50 5KW3 phase 19820

If six and nine are crossed how is it making power on three phase
Reply With Quote
  #27  
Old 06-18-2017, 03:04:56 PM
Steve Dawkins Steve Dawkins is offline
Sponsor
 
Join Date: Feb 2005
Location: Virginia Beach, Virginia, USA
Posts: 834
Thanks: 535
Thanked 321 Times in 180 Posts
Default Re: Onan Standby Generator 50 5KW3 phase 19820

Just making suggestions for things to check, since you had modified the wiring connections.
Reply With Quote
  #28  
Old 06-18-2017, 03:48:00 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,908
Thanks: 8,728
Thanked 14,272 Times in 6,736 Posts
Default Re: Onan Standby Generator 50 5KW3 phase 19820

The six and nine connection was very easy to mix up. I liked Cat's way of marking when I worked for them. T6 and T9. Some companies just put 6/9 on the wire. So it depended on how you looked at it
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following User Says Thank You to Billy J Shafer For This Post:
  #29  
Old 06-18-2017, 04:36:40 PM
Friends with benefits Friends with benefits is offline
Registered
 
Join Date: Jun 2017
Location: Memphis, Tennessee
Posts: 18
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Onan Standby Generator 50 5KW3 phase 19820

Thanks for the help but my T6 and T9 are labeled I took all the wires apart and checked all of them for their ground I have no ground that I can find so far

I'm fixing to type all of them off and crank it up and see what happens when I excite it

Tape all of them up individually and crank it up and excite itto see what happens

When I get to the bottom of the problem what should my voltage knob be set on l1 l2or which setting
Reply With Quote
The Following User Says Thank You to Friends with benefits For This Post:
  #30  
Old 06-18-2017, 07:29:34 PM
pegasuspinto pegasuspinto is offline
Registered-III
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 2,642
Thanks: 327
Thanked 1,230 Times in 807 Posts
Default Re: Onan Standby Generator 50 5KW3 phase 19820

I don't think it will make ANY voltage with all the windings disconnected but if it does it could go wide open which can be dangerous as hell.

The voltage select knob is just for the meters and they won't work either if the windings are disconnected

There is no reason to run it with the windings disconnected anyways
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
120v single phase motor turning 3 phase generator gibbykart Generators & Electric Motors General Discussion 15 10-04-2014 12:00:37 PM
Is My Onan Standby Generator at Risk? Leon N. Onan Generators 12 02-09-2012 08:41:09 AM
US Motor Div Generator Conversion To Single Phase 220V From Three Phase jimybud Generators & Electric Motors General Discussion 4 06-27-2010 08:19:50 PM
Onan standby generator info. needed powerwagon Onan Generators 9 11-26-2009 05:57:51 PM
Converting a Kohler Generator from 3 phase to single phase KendalPernod Kohler Generators 3 09-13-2005 10:08:28 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 07:42:43 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277