Kohler w/ VG4D1 will start but not run


this thread has 8 replies and has been viewed 287 times

Reply
 
Thread Tools Display Modes
  #1  
Old 01-27-2019, 06:25:26 PM
Grizzly Hill Grizzly Hill is offline
Registered-I
 
Join Date: Nov 2010
Location: Nevada City, CA, USA
Posts: 11
Thanks: 19
Thanked 0 Times in 0 Posts
Default Kohler w/ VG4D1 will start but not run

I have a low hour Kohler Jenny (Propane- but was NG) - 15RMY62 w/ Wisc, VG4D1 Zenith 87 carb - starts fine- but will not keep running- Unless I toggle the start switch- Fuel is good- but It seems to me that it is not getting electrical power to magneto unless the start switch is activated- there is no "run" switch or ignition switch and I cannot find where the Magneto gets its power from- so I can make sure it it getting power- HELP IF YOU CAN- Thanks! Ray

Last edited by Grizzly Hill; 01-27-2019 at 09:43:08 PM.
Reply With Quote
Sponsored Links
  #2  
Old 01-27-2019, 08:29:32 PM
I like oldstuff I like oldstuff is offline
Subscriber
 
Join Date: Jan 2012
Location: Milwaukee, Wisconsin, USA
Posts: 5,673
Thanks: 1,376
Thanked 6,065 Times in 2,359 Posts
Default Re: Kohler w/ VG4D1 will start but not run

If it's a magneto they are self powered by internal magnets. The wire connected to the side of the magneto is the stop wire. To stop the spark and shut the unit off this wire is grounded through a switch. That's all there is.

Your unit may have a low oil pressure cut out switch that also can shut off the engine. (This also grounds out the magneto.) Note that these engines put out very low oil pressure. Maybe 10-12 psi cold and 5-7 psi when warmed up.

See if there's a pressure switch on the oil line plumbing that runs up to the governor. It'll be down by the oil filter/dipstick. To verify pressure, you can take the switch off and put a pressure gauge in place. Take the grounding wire off the magneto and fire it up. If you have oil pressure and it continues to run you have a bad low oil pressure cut off switch.

If it still quits with the magneto stop wire disconnected you have a fuel delivery problem. *Perhaps the switch that you wiggle may be turning off the propane solenoid valve which will kill the engine.

Pic is of mine with the magneto. You can see the low oil pressure switch I installed.
Attached Thumbnails
Click image for larger version

Name:	IMG_7687.jpg
Views:	54
Size:	153.9 KB
ID:	327302  
Reply With Quote
  #3  
Old 01-27-2019, 09:42:14 PM
Jack Hottel Jack Hottel is offline
Subscriber
 
Join Date: Oct 2005
Location: Haymarket, Virginia, USA
Posts: 942
Thanks: 292
Thanked 468 Times in 307 Posts
Default Re: Kohler w/ VG4D1 will start but not run

I don't know about your unit, but the 15RMY series won't stay running if AC is not produced.
Relay 1CR controls that. Unplug it and if engine continues to run check for AC output. Wiring Diagram attached.
Jack Hottel
Attached Files
File Type: pdf Kohler Wiring Diagram 256277.pdf (256.2 KB, 13 views)

Last edited by Jack Hottel; 01-27-2019 at 09:46:53 PM. Reason: Forgot attachment
Reply With Quote
  #4  
Old 01-27-2019, 10:20:56 PM
I like oldstuff I like oldstuff is offline
Subscriber
 
Join Date: Jan 2012
Location: Milwaukee, Wisconsin, USA
Posts: 5,673
Thanks: 1,376
Thanked 6,065 Times in 2,359 Posts
Default Re: Kohler w/ VG4D1 will start but not run

Yeah without AC or low AC the overcrank switch will actuate and stop cranking. Seems to take about 15 seconds on mine.
Reply With Quote
  #5  
Old 01-28-2019, 01:46:44 PM
Andrew Mackey Andrew Mackey is offline
Sponsor
 
Join Date: Nov 2004
Location: Rockaway, New Jersey USA
Posts: 13,573
Thanks: 1,926
Thanked 6,288 Times in 4,063 Posts
Default Re: Kohler w/ VG4D1 will start but not run

The others have pretty well covered it. Low voltage or a sensor. If the engine is distributer operated you might also have a fault in the ignition resister. When the engine quits, see if the coil is getting voltage. The resister is bypassed when the starter is engaged, but once the starter kicks out, the resister takes over . If the resister goes bad, the engine will quit as soon as the starter stops cranking the engine.
Reply With Quote
  #6  
Old 01-28-2019, 04:17:21 PM
Grizzly Hill Grizzly Hill is offline
Registered-I
 
Join Date: Nov 2010
Location: Nevada City, CA, USA
Posts: 11
Thanks: 19
Thanked 0 Times in 0 Posts
Default Re: Kohler w/ VG4D1 will start but not run

Seems like the OVERCRANK WATER TEMP OIL PRESS RESET-
Switch is broken but I cannot find the switch listed anywhere in the Kohler parts listing- it is a strange switch with the numbers "APGN1 / 8347-1 /1REC2
no other identifiers on the switch-
Reply With Quote
  #7  
Old 01-28-2019, 06:57:26 PM
I like oldstuff I like oldstuff is offline
Subscriber
 
Join Date: Jan 2012
Location: Milwaukee, Wisconsin, USA
Posts: 5,673
Thanks: 1,376
Thanked 6,065 Times in 2,359 Posts
Default Re: Kohler w/ VG4D1 will start but not run

Toss a pic up of the switch. That may help.
Reply With Quote
  #8  
Old 02-08-2019, 09:25:15 PM
q930 q930 is offline
Registered
 
Join Date: Apr 2016
Location: Clear Lake, Wisconsin
Posts: 6
Thanks: 1
Thanked 2 Times in 1 Post
Default Re: Kohler w/ VG4D1 will start but not run

[Your unit may have a low oil pressure cut out switch that also can shut off the engine. (This also grounds out the magneto.) Note that these engines put out very low oil pressure. Maybe 10-12 psi cold and 5-7 psi when warmed up.]

I like oldstuff: If the low pressure cut-out switch grounds out the magneto, how do you get it started? Obviously there's no pressure when the engine is not running, so you'd should never be able to get a spark until you get pressure. Or am I missing something?
Thanks. I enjoy your comments.
Terry Q.
NW Wis.
Reply With Quote
  #9  
Old 02-08-2019, 10:58:11 PM
I like oldstuff I like oldstuff is offline
Subscriber
 
Join Date: Jan 2012
Location: Milwaukee, Wisconsin, USA
Posts: 5,673
Thanks: 1,376
Thanked 6,065 Times in 2,359 Posts
Default Re: Kohler w/ VG4D1 will start but not run

930:
When you crank the engine yes, the low pressure switch is killing the spark. It takes about 8-10?? seconds of cranking then it lights off when the spark is enabled. When it's cold like 20 degrees or less it takes longer before it fires up.
Bear in mind as it's a splashy squirty oiling system, the switch enables spark at I think 2-3 psi.

On mine I added a bypass switch that disables the LOP switch. Then it fires quickly. Once it's running that switch is flipped which enables the low pressure switch to kill it.

Mine is nat gas and I plug in the fuel hose when I run it. It takes 8-10 seconds of cranking to get the hose purged and the gas to the carb.
Once it's been running and on a restart it's like 2-3 seconds of cranking before it kicks off.
Attached Thumbnails
Click image for larger version

Name:	IMG_7754.jpg
Views:	14
Size:	94.9 KB
ID:	328204  

Last edited by I like oldstuff; 02-09-2019 at 08:03:17 AM.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Lindsay 80-WC with Wisconsin VG4D1 Slim tech Wisconsin Engines 3 11-03-2018 01:42:46 PM
Kohler NO START princecharles904 Kohler Generators 8 01-29-2014 06:38:35 AM
7.5KW Kohler - Won't Start Jerry Healy Kohler Generators 0 02-27-2010 04:21:29 PM
Wisconson VG4D1 oil change Kahuni Small Air Cooled Gasoline Engines 1 05-21-2005 11:44:11 AM
How do I Start Kohler Keith Childers Kohler Generators 1 11-25-2004 02:25:01 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 07:15:42 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277