Default Re: Onan 7.5 JB Information Monitoring Panel

Maybe a better way to go is a 3 position switch like the one attached. Normally open contact blocks that are activated when the switch is moved to the right or left. Rest position in the center. This way "other people" don't push both at the same time.
https://cdn.automationdirect.com/sta...22mmselect.pdf

Anyone ever try the ultrasonic mice things?

Leon, I travel to Chelmsford for work now and then... I'll let you know next time.
Attached Thumbnails
Click image for larger version

Name:	111017-1.png
Views:	21
Size:	174.4 KB
ID:	295772   Click image for larger version

Name:	111017-2.png
Views:	12
Size:	45.9 KB
ID:	295773  
Reply With Quote
Sponsored Links
  #22  
Old 11-10-2017, 05:03:12 PM
mjd325is mjd325is is offline
Registered
 
Join Date: Nov 2014
Location: Sandown, New Hampshire
Posts: 31
Thanks: 16
Thanked 3 Times in 2 Posts
Default Re: Onan 7.5 JB Information Monitoring Panel

Quote:
Originally Posted by Steve Dawkins View Post
^ I think he would hold the START or STOP pushbutton for the same duration as a toggle switch. The N/O contact will remain closed as long as the button is pressed.
Yes, that was my thought on those.
Reply With Quote
  #23  
Old 11-10-2017, 11:03:32 PM
dmeed dmeed is offline
Registered-I
 
Join Date: Nov 2014
Location: Victoria Corner, New Brunswick, Canada
Posts: 232
Thanks: 149
Thanked 118 Times in 70 Posts
Default Re: Onan 7.5 JB Information Monitoring Panel

Looking at the JB schematic I have - if both start and stop were pressed simultaneously by using pushbuttons - that shorts both terminal 3(start) and terminal 2(stop) to terminal 1 (ground). Since terminal 3 engages the start relay, the starter would engage - but since terminal 2 cuts off the K12 run relay it would not latch in to keep the set running - so the starter would not be disconnected by the K12 nc contacts when the set comes up to speed - Theoretically it could burn out the starter by holding too long (where normally the start relay (and starter) is released as soon as the centrifugal switch indicates the set is up to 900 rpm.)

Other than that I don't think I see a major issue other than the set wouldn't stay running because of pushing the stop button. Especially if those pushbuttons have nc contacts that can be wired in series with the other pushbutton to disable pressing both at once.

Someone else want to chase out the jb schematic and see if both connected at the same time would cause catastrophic issues?

David Meed
Reply With Quote
The Following User Says Thank You to dmeed For This Post:
  #24  
Old 11-11-2017, 07:39:10 AM
Mike57 Mike57 is offline
Subscriber
 
Join Date: Sep 2013
Location: Sunnyvale, Texas, USA
Posts: 161
Thanks: 107
Thanked 88 Times in 58 Posts
Default Re: Onan 7.5 JB Information Monitoring Panel

The NO momentary switches will work just fine, it's the same setup I have on my JB and JC. You don't need any additional relays. The switches remain NC as long as you have the button/switch engaged, when you release the button/switch, the contacts open. You can buy these in pairs with a mechanical interlock if you want to go full on stupid-proof.

As for the 12VDC control wires running with the power wires, single phase isn't going to induce any voltages high enough to activate 12VDC controls. If you're concerned about it, pull the control wires using shielded cable, Belden is a good brand.
Reply With Quote
The Following User Says Thank You to Mike57 For This Post:
  #25  
Old 11-11-2017, 10:32:47 AM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,512
Thanks: 645
Thanked 2,004 Times in 1,204 Posts
Default Re: Onan 7.5 JB Information Monitoring Panel

I run my generator 3 power cables in the same trench as the start/stop cables and 120 VAC for the battery charger some 125 feet. No pick up problems because these are low impedance circuits.
Reply With Quote
The Following User Says Thank You to Leon N. For This Post:
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan ATS monitoring via serial connection ttyR2 Onan Generators 10 12-02-2015 11:45:12 AM
Power monitoring, load monitoring. imjustdave Generators & Electric Motors General Discussion 21 12-04-2014 01:55:18 PM
Onan....Remote monitoring.....found on Ebay AndersonMillTexas Onan Generators 3 01-20-2014 03:03:06 PM
Monitoring Onan Generator Amperes Leon N. Onan Generators 41 03-28-2013 11:01:08 PM
Onan Monitoring box Nubian Onan Generators 2 11-24-2012 01:03:20 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 08:54:13 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277