Natural Gas Pipe Dimensions for Onan JC


this thread has 19 replies and has been viewed 398 times

Reply
 
Thread Tools Display Modes
  #1  
Old 11-10-2017, 03:28:51 PM
JT240Z JT240Z is offline
Subscriber
 
Join Date: Dec 2011
Location: Grayson, Georgia
Posts: 136
Thanks: 0
Thanked 20 Times in 16 Posts
Default Natural Gas Pipe Dimensions for Onan JC

I have a 15.0JC that I'm going to be plumbing into my NG system. The generator is going to be sitting approximately 20' from my gas meter. I currently have a 1 1/2" outlet from the gas meter. I'm trying to balance cost and needs to come up with a plan to run the gas line. I obviously don't need to run 1 1/2" all the way to the generator. The technical bulletin T-015 specifies 1" line for 15' and 1 1/4" line starting at 25'. The line going into the cutoff switch and demand regulator is only 3/4". I obviously will have to reduce the pipe dimension down to the 3/4" line sometime before that and will probably use 3/4" flex line to do the final connection although 1" line is available if needed. My current plan is to run 1 1/2" line into a tee (to provide access to supply the rest of the house in the future) and then reduce to 1 1/4" line for most of the way to the generator housing. From there I'll reduce down to either 1" or 3/4" pipe and make my entry into the generator shed with that. My question is, does this make sense? The cost and availability of 1 1/4" pipe and fittings are significantly more than either 1" or 3/4" so I really only want to run the larger diameter pipe for as long as I need to. Any suggestions on specing this out? Plan to do the work myself. I've run black iron pipe in the past so that's no issue.

The layout would be something like this:
Reply With Quote
Sponsored Links
  #2  
Old 11-10-2017, 06:36:44 PM
Jim Marcozzi Jim Marcozzi is offline
Registered-I
 
Join Date: Nov 2013
Location: Hempfield, PA, USA
Posts: 455
Thanks: 42
Thanked 244 Times in 134 Posts
Default Re: NG pipe dimensions for JC

My 12.5 JC was 90' from the meter. I teed into the meter outlet with 1" yellow plastic and went to the JC with it. In the enclosure, I had a shutoff and it went into the demand regulator with 3/4" flexible. Load tested full output.
Reply With Quote
The Following User Says Thank You to Jim Marcozzi For This Post:
  #3  
Old 11-10-2017, 06:54:01 PM
JT240Z JT240Z is offline
Subscriber
 
Join Date: Dec 2011
Location: Grayson, Georgia
Posts: 136
Thanks: 0
Thanked 20 Times in 16 Posts
Default Re: NG pipe dimensions for JC

So are you saying that I'm over thinking this? I thought about just running 1" pipe since the distance was very close, but between the Onan recommended size pipes for 15' and 25'. The problem is that the line is 20' away but will have a couple elbows along the way. I was told to add 5' of pipe length for every 90-degree bend. That would make the calculated distance more like 35'. Was thinking of running only about 10 or so feet of the 1 1/4" pipe in order to get closer to the shed and than go with the 1" pipe from there on. Right now my meter only feeds my furnace and the 1 1/2" pipe tees with a cap on one side and a 3/4" line going to the furnace. A little overkill but I asked for a larger meter so I could add the genset and future gas appliances. A gas stove and water heater would go a long way in a power outage.
Reply With Quote
  #4  
Old 11-10-2017, 07:04:01 PM
Jim Marcozzi Jim Marcozzi is offline
Registered-I
 
Join Date: Nov 2013
Location: Hempfield, PA, USA
Posts: 455
Thanks: 42
Thanked 244 Times in 134 Posts
Default Re: NG pipe dimensions for JC

I prefer a larger pipe, when possible. It acts slightly as a reservoir and dampens any pulsations.

You also need to calculate the gas usage for water heater, cooking, heating, etc then add in the generator's consumption. All added together, your meter, regulator (if used) and delivery service (street lateral pipe) needs to be able to handle the volume of all units running togther.

If not, the gas co will be glad to install a larger meter in most cases.
Reply With Quote
The Following User Says Thank You to Jim Marcozzi For This Post:
  #5  
Old 11-10-2017, 07:33:58 PM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,744
Thanks: 4,982
Thanked 5,303 Times in 2,892 Posts
Default Re: NG pipe dimensions for JC

Per. the Uniform Plumbing code 1” pipe will deliver 259 CFH up to 60’ @ 0.5” water column.

I think it is common practice to count each 90 as 10'. It looks like if you are going to do a "text book" installation, you will be real close with 1" pipe all the way.

If you have 7" WC pressure at the meter or more, I would run 1" and not worry about it. Just keep the elbows to a minimum.
Reply With Quote
  #6  
Old 11-10-2017, 07:48:49 PM
Motorhead's Avatar
Motorhead Motorhead is offline
Subscriber
 
Join Date: May 2007
Location: Central Coast, California
Posts: 3,333
Thanks: 1,470
Thanked 2,180 Times in 1,179 Posts
Default Re: NG pipe dimensions for JC

/\ +1 with Jim. I also agree with JT240Z about elbows causing some restrictions. I believe in having a little more than finding out I didn't go big enough. "Do the job right the FIRST time then you will never have to go back and fix it right the NEXT time." With extra capacity, you could add in another outdoor appliance such as a gas BBQ... And then cook ALL of US here on the site some BBQ RIBS!!!
My 7.5JB is right at my gas meter but I have a 1.25" ID rubber gas flex hose of 12 ft. I want to move my JB to the other side of my home and into my carport where I park my Pickup. For the 50 ft I need to get the Nat. gas there, the T-015 calls for 3/4 inch but jumps to 1.25" at 75 ft.
I am going 1.25" the whole length because I eventually want to tie into the line at about 1/2 way to put in a Nat Gas BBQ and maybe an outside WOK burner to be able to stir fry outside so I don't stink up the house. NO I an not going to "WOK the Dog!"
__________________
Back of 1958 5CCK
Contractors model
On trailer owned by
"Ma" Bell.
Reply With Quote
  #7  
Old 11-10-2017, 07:59:36 PM
I like oldstuff I like oldstuff is offline
Subscriber
 
Join Date: Jan 2012
Location: Milwaukee, Wisconsin, USA
Posts: 4,560
Thanks: 955
Thanked 4,154 Times in 1,785 Posts
Default Re: NG pipe dimensions for JC

JT you're golden with your approach. Run with it.
Reply With Quote
  #8  
Old 11-10-2017, 10:53:55 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 14,731
Thanks: 389
Thanked 5,329 Times in 3,881 Posts
Default Re: NG pipe dimensions for JC

I like to plan ahead, on other things been bite by designing to current needs, then later wanting to upgrade.

Like idea of larger than required line if you can afford it. Then will be set for possible larger gen in future. Most of the back breaking work is in digging the trench. I'ld even add extra empty plastic conduit for future control wires , ect.

I'ld even put the power wires in plastic conduit, so can easily replace them if they fail in 30 years or so. Read of underground 120V utility feed to house fail, was ~ 150 ft uphill.

Last edited by len k; 11-10-2017 at 11:07:02 PM.
Reply With Quote
The Following User Says Thank You to len k For This Post:
  #9  
Old 11-11-2017, 09:07:18 AM
scoops scoops is offline
Registered-III
 
Join Date: Oct 2008
Location: pittsburgh
Posts: 1,000
Thanks: 316
Thanked 424 Times in 310 Posts
Default Re: NG pipe dimensions for JC

Quote:
Originally Posted by Jim Marcozzi View Post
My 12.5 JC was 90' from the meter. I teed into the meter outlet with 1" yellow plastic and went to the JC with it. In the enclosure, I had a shutoff and it went into the demand regulator with 3/4" flexible. Load tested full output.
I never thought about this Jim.
my natural gas meter is also about 90 ft from my house.
my shed where genny will be is 1/2 way between meter and house.
are you saying i can have a plumber tee off the meter?
Reply With Quote
  #10  
Old 11-11-2017, 10:01:11 AM
Gunny Gunny is offline
Subscriber
 
Join Date: Feb 2005
Location: North Carolina
Posts: 3,624
Thanks: 1,420
Thanked 1,526 Times in 975 Posts
Default Re: Natural Gas Pipe Dimensions for Onan JC

In my opinion, for what that's worth, you'll be OK. If you can find them, use long sweep 90's, less restriction. Or even better, get some of that 1" plastic the gas company uses with no elbows.
Reply With Quote
  #11  
Old 11-11-2017, 11:04:32 AM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,482
Thanks: 2
Thanked 463 Times in 329 Posts
Default Re: Natural Gas Pipe Dimensions for Onan JC

Quote:
Originally Posted by Gunny View Post
In my opinion, for what that's worth, you'll be OK. If you can find them, use long sweep 90's, less restriction. Or even better, get some of that 1" plastic the gas company uses with no elbows.
It was my impression he is clipping this to the house. Yellow PE is for buried service only. If any part is underground, yellow PE is all I will use. I have seen too many steel pipes corrode or leak underground.
Reply With Quote
  #12  
Old 11-11-2017, 11:23:12 AM
Jim Marcozzi Jim Marcozzi is offline
Registered-I
 
Join Date: Nov 2013
Location: Hempfield, PA, USA
Posts: 455
Thanks: 42
Thanked 244 Times in 134 Posts
Default Re: Natural Gas Pipe Dimensions for Onan JC

You could have them tee off the outlet side, permitted the local gas company allows you to remove one side of the meter. Our allows it, as long as what you're doing is on the outlet side. I had a 300,000 cuft rated meter put in afterwards. Make sure to install a gas shutoff valve that meets code at the tee.
Reply With Quote
The Following 2 Users Say Thank You to Jim Marcozzi For This Post:
  #13  
Old 11-11-2017, 01:20:13 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 14,731
Thanks: 389
Thanked 5,329 Times in 3,881 Posts
Default Re: Natural Gas Pipe Dimensions for Onan JC

I'm no expert on gas , but as long as you follow any applicable piping rules I wouldn't think gas co would care what you do once the gas is metered (paid for).

Another good reason for plastic pipe underground is if nat gas leaks underground it forms some chemical that kills all the tree and vegetation roots nearby, basically killing the tree.
Reply With Quote
The Following User Says Thank You to len k For This Post:
  #14  
Old 11-11-2017, 02:57:04 PM
JT240Z JT240Z is offline
Subscriber
 
Join Date: Dec 2011
Location: Grayson, Georgia
Posts: 136
Thanks: 0
Thanked 20 Times in 16 Posts
Default Re: Natural Gas Pipe Dimensions for Onan JC

The meter has already been upgraded to a much larger volume unit as part of the pre-installation. Thus the 1 1/2" Pipe exiting the meter now. The gas company already installed a T right after the meter with a plug on one end for future expansion. That's the tee I'll tie into.

Looks like I was able to find a local pipe supplier that stocks 1 1/4" pipe and fittings. My current plan is to run 1 1/4" pipe as far as I can using standard length pipe and nipples and then transition to 1" from then on to the generator. I'll use 1" flex line to the generator and then transition to 3/4" to go into the generator fittings (drain, switch and demand regulator). I'll have a gas cutoff valve right after I enter the shed along with a drip stub just before the reduction to 3/4" pipe. At least that's the plan right now. I may put a 1 1/2" cutoff valve near the meter where I begin my work. That way I can pressurize the new line and test for leaks without interfering with the existing gas supply to the house. A little too cold to let the house go without heat for 24 hours.
Reply With Quote
  #15  
Old 11-11-2017, 03:07:07 PM
zuhnc zuhnc is offline
Registered-I
 
Join Date: Nov 2013
Location: Norfolk, Virginia
Posts: 77
Thanks: 3
Thanked 77 Times in 34 Posts
Default Re: Natural Gas Pipe Dimensions for Onan JC

I would recommend the shutoff immediately BEFORE entering the building. Better access in the event of an "event". Don't want to have to walk into a flaming inferno to shut the gas off zuhnc
Reply With Quote
  #16  
Old 11-11-2017, 03:10:29 PM
I like oldstuff I like oldstuff is offline
Subscriber
 
Join Date: Jan 2012
Location: Milwaukee, Wisconsin, USA
Posts: 4,560
Thanks: 955
Thanked 4,154 Times in 1,785 Posts
Default Re: Natural Gas Pipe Dimensions for Onan JC

Definitely put the shutoff outside the building. Or as I did, at the meter tee.
Reply With Quote
The Following 2 Users Say Thank You to I like oldstuff For This Post:
  #17  
Old 11-11-2017, 04:54:16 PM
JT240Z JT240Z is offline
Subscriber
 
Join Date: Dec 2011
Location: Grayson, Georgia
Posts: 136
Thanks: 0
Thanked 20 Times in 16 Posts
Default Re: Natural Gas Pipe Dimensions for Onan JC

Good suggestions. The current plan is to have a 1 1/4" shutoff valve at the meter tee about 20' upstream from the shed and another one inside the shed for maintenance. This gives me the ability to pressure test the line all the way back to the meter without having to disrupt my main gas line. Wife wouldn't like me cutting off the heat to the house for 24 hours. Not this time of year.

Just ordered the 1 1/2" fittings 1 1/4" reducer and various nipples along with the outside cutoff valve from SupplyHouse.com. Good prices and very reasonable shipping for domestic produced pipes. Heard bad things about imported piping from the big box stores. I'll use them more once I get it down to the 1" line.

The shutoff at the meter will also allow me to do the plumbing in stages as I complete the shed and have a better idea exactly where I want to enter it. Right now I have a completed deck with the JC still sitting covered on my trailer. All the walls and roof trusses have been framed out and are ready for assembly once I get the generator on the deck.

I'm building the shed with a 60" double door so removal of the generator is possible without too much hassle but it's just easier to drop the generator onto the shed deck before I install the wall frames since I can back the trailer right to the deck and drop the gate down. The generator is sitting on a dolly with 5" wheels so it should be able to just roll down the ramp and onto the deck with little trouble. At most, there will be a 1 1/2" drop at the end of the ramp. I'll use a cable Come-Along secured to the trailer frame to ensure I don't have a runaway situation going down the ramp.
Reply With Quote
  #18  
Old 11-11-2017, 07:55:58 PM
nothingbutdarts nothingbutdarts is offline
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 2,217
Thanks: 4,836
Thanked 1,004 Times in 674 Posts
Default Re: Natural Gas Pipe Dimensions for Onan JC

When they did my propane line install, I had them put a shut-off valve both at the beginning of the line @ the tank as well a before entering the building.
Reply With Quote
  #19  
Old 11-11-2017, 11:13:28 PM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is offline
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 3,869
Thanks: 632
Thanked 2,065 Times in 1,207 Posts
Default Re: Natural Gas Pipe Dimensions for Onan JC

Quote:
Originally Posted by Jim Marcozzi View Post
...I had a 300,000 cuft rated meter put in...
I doubt that...
Reply With Quote
  #20  
Old 11-12-2017, 10:52:29 AM
MBB MBB is offline
Registered-III
 
Join Date: Apr 2009
Location: Elk Grove Village IL USA
Posts: 3,071
Thanks: 1,320
Thanked 2,356 Times in 1,274 Posts
Default Re: Natural Gas Pipe Dimensions for Onan JC

Jim I believe he meant 300,000 btu.
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan JC mounting dimensions... farokh Onan Generators 2 09-19-2013 12:26:42 PM
Adapter to go from 1" pipe thread to regular exhaust pipe? LombardiniDiesel Small Air Cooled Gasoline Engines 2 02-07-2011 12:15:00 AM
Natural Gas Pipe size 12.5JC 3CR/8689U MBB Onan Generators 18 07-19-2010 08:13:16 PM
Pipe for Natural Gas? TxBigRed Onan Generators 22 12-08-2008 11:35:12 PM
Dimensions and weight of onan ojc? Joe Stewart Onan Generators 1 01-06-2006 02:15:20 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 06:15:14 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277