Generac XC8000 E dead out of the box


this thread has 4 replies and has been viewed 384 times

Reply
 
Thread Tools Display Modes
  #1  
Old 08-11-2019, 01:26:59 PM
Haldew Haldew is offline
Registered
 
Join Date: Apr 2019
Location: Carlingford, New Brunswick, Canada
Posts: 7
Thanks: 1
Thanked 0 Times in 0 Posts
Default Generac XC8000 E dead out of the box

I purchased a Generac XC8000 for a replacement for an older generator supplying primary power to my camp. Model is G0068260 Serial Number 3003887515. When I hooked the unit up to my power panel cable I could not get AC at the 220V socket. I could get 120V at the appropriate socket but when the plug is put into the 220V socket the GHCI circuit breaker trips and disconnects power. Every time right out of the box. Unit now has 9 hours on it as I used it with an extension cord from the 120V plug. I purchased the unit on line from Home Depot who have a no return policy on generators. I have not yet contacted Generac customer service. Would anyone have an idea as to what would cause this to always trip the GFCI breaker. Cable and inside wiring have been checked and work fine with a borrowed generator. Thanks guys.
Reply With Quote
Sponsored Links
  #2  
Old 08-11-2019, 04:03:23 PM
Wayne 440 Wayne 440 is online now
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 7,397
Thanks: 486
Thanked 6,902 Times in 3,203 Posts
Default Re: Generac XC8000 E dead out of the box

My guesses are that (A) your borrowed generator does not have a GFCI on its "220V socket", and (B) the camp you are trying to feed has one or more neutral to ground bonds that are causing the GFCI to trip.

There is a very good chance that the generator is working as it is designed to. Generac will probably advise you to correct your camp's wiring.
Reply With Quote
The Following 3 Users Say Thank You to Wayne 440 For This Post:
  #3  
Old 08-17-2019, 07:02:05 PM
Haldew Haldew is offline
Registered
 
Join Date: Apr 2019
Location: Carlingford, New Brunswick, Canada
Posts: 7
Thanks: 1
Thanked 0 Times in 0 Posts
Default Re: Generac XC8000 E dead out of the box

I took the unit into the dealer for check out. Apparently the XC8000 comes from the factory with a bonded neutral. Here in New Brunswick the electrical code calls for a floating neutral. Hence the GFCI tripped when plugging into a floating neutral system. Easy solution seems to be remove the frame to neutral bond in the generator and adhere to local codes. Now to get back to the camp to test the theory.
Reply With Quote
  #4  
Old 08-17-2019, 07:15:03 PM
pegasuspinto pegasuspinto is online now
Registered-III
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 2,967
Thanks: 340
Thanked 1,421 Times in 925 Posts
Default Re: Generac XC8000 E dead out of the box

Anytime the generator is used as a portable, the neutral should be bonded. It's not a difference in code it's a difference in intended use. The newest codes can cause these conflicts now due to some people use this generator as a portable (like camping or construction) and some will connect it to a pre-existing electrical system.
Reply With Quote
  #5  
Old 08-18-2019, 04:29:52 PM
Peter Holmander Peter Holmander is offline
Subscriber
 
Join Date: Nov 2004
Location: West Greenwich, Rhode Island
Posts: 657
Thanks: 1,112
Thanked 607 Times in 259 Posts
Default Re: Generac XC8000 E dead out of the box

My son in law had the same issue with a brand new 10,000 watt Honda generator. I think when the dealers sell you a unit, they should be telling you this. It was just a matter of removing one wire in the unit and taping it up, but that's not the point. Some people lack the confidence to be messing around with the wiring on their brand new generator.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Generac vs Ridgid w/ Yamaha vs Generac mcmcomput Generac Generators (SEARS, etc.) 9 04-18-2017 10:58:11 PM
Generac 7550 Raised From The Dead 02/2015 Mmouse Generac Generators (SEARS, etc.) 3 02-17-2015 07:17:51 PM
Generac 10000 EXL won't spark - magnetos dead? DenkiDriver Generac Generators (SEARS, etc.) 7 10-27-2014 07:44:53 PM
IH LB With a Dead Mag Nevr-Enuf-Stuf Hit & Miss Gas Engine Discussion 8 09-24-2011 10:02:10 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 09:07:07 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277