Unable to Field Flash


this thread has 12 replies and has been viewed 1165 times

Reply
 
Thread Tools Display Modes
  #1  
Old 12-15-2018, 03:17:48 PM
Cavalry Cavalry is offline
Registered
 
Join Date: Jan 2018
Location: Albany, New York
Posts: 17
Thanks: 2
Thanked 3 Times in 3 Posts
Default Unable to Field Flash

I have a 6KW brushless gen head on a light tower that I cannot get to field flash. I successfully retrofitted from a transformer AVR to a SX460 knockoff last year but due to my negligence burned up the AVR after a couple hours use. I tested the windings and found they were not damaged so I picked up another SX460 but no matter what I tried could not get it to flash. I tried the AC drill method, static 12vdc flash to field, etc all with no success. I maintained correct polarity when applicable.
If I apply 12VDC across the field with the AVR disconnected and engine running I get generator output, so I believe the gen head to be mechanically sound. THe AVR appeared to be working during the same disconnected field test the field outputs had current. As soon as I reconnect the field to the AVR I am back to 5VAC output at the generator.
The stamford manual suggests field flashing while running and the AVR connected via 12VDC to field with a blocking diode. I tried this and instantly smoked the AVR.
I have yet another AVR on the way. The only thing I can think of now is to get generating again with 12vdc directly to the field and let it run awhile, maybe with some resistive load on it to help "set" the magnetism of the field?
Any other suggestions?
Reply With Quote
Sponsored Links
  #2  
Old 12-15-2018, 05:15:15 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,134
Thanks: 7,367
Thanked 2,235 Times in 1,521 Posts
Default Re: Unable to Field Flash

What was wrong with the transformer compounding system? That is a vastly superior system from the standpoint of being rugged and reliable while being perfectly adequate. Do you still have those parts? We can help get that working, and ditch the Chinese electronics.
Reply With Quote
  #3  
Old 12-15-2018, 05:28:33 PM
turtmaster turtmaster is offline
Registered-II
 
Join Date: Jun 2015
Location: Hortonville, Wisconsin
Posts: 625
Thanks: 637
Thanked 380 Times in 191 Posts
Default Re: Unable to Field Flash

One suggestion, if the is a diode bridge, before the voltage regulator, is it partially shorted, or open?
Reply With Quote
  #4  
Old 12-15-2018, 06:35:39 PM
Cavalry Cavalry is offline
Registered
 
Join Date: Jan 2018
Location: Albany, New York
Posts: 17
Thanks: 2
Thanked 3 Times in 3 Posts
Default Re: Unable to Field Flash

Quote:
Originally Posted by Vanman View Post
What was wrong with the transformer compounding system? That is a vastly superior system from the standpoint of being rugged and reliable while being perfectly adequate. Do you still have those parts? We can help get that working, and ditch the Chinese electronics.
Story short, mice set up residence on top of the terminal strip and made a direct short blowing the rectifier and transformer. There is no support or parts from the manufacturer and the labels on the components were not legible.
The Chinese parts while not as robust are pretty cheap. At $25 each and only a minute to swap its not the end of the world if they only last a year or two. Having a spare on hand would be likely. I wouldn't be against buying a real stamford if it was known that they are superior.
I priced out transformer parts from a similar sized set and got a little sticker shock. Even if I was sure it would work it was 1/3 the price of another used light tower.
Here is my original post about the mouse incident
https://www.smokstak.com/forum/showthread.php?t=174847

Quote:
Originally Posted by turtmaster View Post
One suggestion, if the is a diode bridge, before the voltage regulator, is it partially shorted, or open?
I guess I am not following you on this? The original rectifying circuit was deleted. I am using the AVR in its place.
Reply With Quote
The Following User Says Thank You to Cavalry For This Post:
  #5  
Old 12-16-2018, 03:42:16 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,134
Thanks: 7,367
Thanked 2,235 Times in 1,521 Posts
Default Re: Unable to Field Flash

I see, bummer about the mice.

If the generator is brushless that means that it has a separate exciter generator, and there is a shaft mounted rectifier between it and the main generator field. If that fails, the generator will be unable to build up.
Reply With Quote
  #6  
Old 12-17-2018, 08:01:49 PM
Cavalry Cavalry is offline
Registered
 
Join Date: Jan 2018
Location: Albany, New York
Posts: 17
Thanks: 2
Thanked 3 Times in 3 Posts
Default Re: Unable to Field Flash

Quote:
Originally Posted by Vanman View Post

If the generator is brushless that means that it has a separate exciter generator, and there is a shaft mounted rectifier between it and the main generator field. If that fails, the generator will be unable to build up.
I desoldered and checked both rotor rectifiers, both test good
Reply With Quote
  #7  
Old 12-17-2018, 10:14:45 PM
nblack nblack is offline
Registered-I
 
Join Date: Dec 2012
Location: Rutledge, Tennessee
Posts: 186
Thanks: 119
Thanked 82 Times in 64 Posts
Default Re: Unable to Field Flash

the exciter winding checked OK? Only other thought is how were the diodes tested, with a multimeter, or something that could test their reverse bias voltage capability. I have seen diodes pass on a multimeter, but fail in circuit because the reverse voltage in-situ made them conduct in reverse when they should'a been open.
Reply With Quote
  #8  
Old 12-18-2018, 06:26:13 AM
Cavalry Cavalry is offline
Registered
 
Join Date: Jan 2018
Location: Albany, New York
Posts: 17
Thanks: 2
Thanked 3 Times in 3 Posts
Default Re: Unable to Field Flash

Quote:
Originally Posted by nblack View Post
the exciter winding checked OK? Only other thought is how were the diodes tested, with a multimeter, or something that could test their reverse bias voltage capability. I have seen diodes pass on a multimeter, but fail in circuit because the reverse voltage in-situ made them conduct in reverse when they should'a been open.
Yes, I checked each exciter winding individually and the math in total works out.
I too have had issues testing diodes even with a high quality meter in "diode mode" I checked not only with a meter but with a 12v test light.
Reply With Quote
  #9  
Old 12-18-2018, 06:35:42 PM
Rich Mc Rich Mc is offline
Registered-II
 
Join Date: Nov 2004
Location: Near Boston
Posts: 368
Thanks: 39
Thanked 55 Times in 51 Posts
Default Re: Unable to Field Flash

One or several turns shorted together among many can still indicate the correct resistance of the total winding.
Reply With Quote
  #10  
Old 12-18-2018, 08:06:14 PM
Cavalry Cavalry is offline
Registered
 
Join Date: Jan 2018
Location: Albany, New York
Posts: 17
Thanks: 2
Thanked 3 Times in 3 Posts
Default Re: Unable to Field Flash

Quote:
Originally Posted by Rich Mc View Post
One or several turns shorted together among many can still indicate the correct resistance of the total winding.
I checked each field stator coil individually, each was the same at 5Ω

I found a manual that is about the same vintage as my gen head and from Baldor who bought out Powr Gard, for the most part its more alike than anything else I have found (4 lead generator, rotor rectifiers in the right configuration with 7 leads). I'm using it as a reference and not gospel.

https://www.allmand.com/content/dam/...ting_Guide.pdf

I checked the rotor windings
+ to - 1.4Ω
+ to + 0Ω
- to - 0Ω
∿to ∿ .4Ω even across 3 legs
no chassis to ground issues

The only thing that kind of red flagged for me was the +to+ and -to-. The "spec" was .1Ω, I was getting 0Ω on two different meters. Its a pretty small amount, possibly just the resolution/accuracy of the meters? The +to- at 1.4Ω was less than the "spec" of 3-5Ω I'm assuming 2 field windings on the rotor and both being equal its ok?

At this point unless anyone has any other troubleshooting, i'm going to throw it back together, pop in the new AVR and see if it takes a flash. I guess its possible I just had a bad AVR out of the box and have been digging into this just for fun.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
How to Field Flash? m151 Kohler Generators 16 05-13-2009 08:36:18 PM
Field Flash Diode GlobalEnergies Onan Generators 1 03-15-2007 09:00:49 PM
DJC low voltage, flash the field? rich9499 Onan Generators 1 08-21-2006 06:26:39 PM
Exciting the field/ Flash the field?? Gary Bright Generators & Electric Motors General Discussion 1 03-18-2004 10:46:06 PM
What does 'Manual Field Flash' mean ? Jorrit Generators & Electric Motors General Discussion 4 06-16-2001 06:06:15 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 02:18:35 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277