Continuity may not work unless t2 is bolted to frame. In the picture looks like t3 is bolted too t2. Hope the experts get in.
The picture is out of 900-0184 pg 40.
Attached Thumbnails
Click image for larger version

Name:	image.png
Views:	15
Size:	170.5 KB
ID:	236252  
Reply With Quote
Sponsored Links
  #42  
Old 10-07-2015, 05:51:19 PM
Mike57 Mike57 is offline
Subscriber
 
Join Date: Sep 2013
Location: Sunnyvale, Texas, USA
Posts: 159
Thanks: 103
Thanked 87 Times in 57 Posts
Default Re: Onan Generator (15KW) 15.OJC-C3R 112471AA

Sorry to come in on this thread late.

In this particular case, because your generator is the sole source of power for the structure, your bonding of the neutral to the grounding system takes place at the gen-set, just as Kpack stated in post #26. T1 and T4 are your hots. T2 and T3 tie together at the gen-set and are bonded to the generator frame. Your ground rod (or rods, or optional grounding electrodes used) are tied in at the bonding point in the generator.

Do run 4 wires (2 hots, a neutral and a ground) from the generator to the cabin.

There will be no bonding at your service panel, the grounds and neutrals will be isolated from one another.

You can run 50' to a ground rod but it's not an ideal situation. It's not a code violation to do so. The goal is to to have the grounding system at or below 25 ohms to ground. Often this takes more than one ground rod, particularly in bad soil or rocky soil. Each rod must be at least 6' apart. FYI as an example: Two ground rods are minimum in the State of Oregon because of poor soil conductivity.

You have grounding alternatives to a driven ground rod(s):

Plate electrode(s):>= 2sq.ft surface area and >= 1/4" thick buried at least 30 inches. typically this is a steel plate with a 3/4" stud welded to it in order to attach the grounding electrode conductor using a standard ground rod clamp.

Ground ring circling the building:>= 20 ft. of >= #2awg bare copper buried at least 30 inches.

You can use any combination of the above to achieve the necessary ohms to ground.

There are other grounding electrode options but these should cover you.

If you have copper pipe in the building, bond the hot to the cold at the hot water tank and carry that wire, unbroken, to the ground bar in the panel. The size of this wire is dependent on the size of your main service disconnect breaker.

Hope this helps you out.
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
MEP 15kw Generator Cruiser Military MEP and Aircraft Gen-Sets 20 02-15-2016 03:08:18 PM
Help with Delco 15kw generator. Sergey Generators & Motors General Discussion 0 08-11-2015 02:59:56 PM
Onan 15kw JC3R Generator RichM1983 Onan Generators 74 10-22-2012 11:36:43 PM
Need info on 15KW Onan Generator Danile Onan Generators 6 02-28-2011 01:45:33 PM
IDE military generator 15kw D Wilson Generators & Motors General Discussion 2 06-30-2006 01:31:43 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 05:11:20 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277