  #11  
Old 12-23-2018, 11:23:06 AM
Cavalry Cavalry is offline
Registered
 
Join Date: Jan 2018
Location: Albany, New York
Posts: 17
Thanks: 2
Thanked 3 Times in 3 Posts
Default Re: Unable to Field Flash

I was able to once again resuscitate the pile. It would not take a flash with the standard 12v method, the hand turning AC drill method was equally ineffective, but 10 seconds spinning the drill with another drill did the trick. Thanks to all that helped get it going again.
Reply With Quote
Sponsored Links
  #12  
Old 12-23-2018, 01:10:48 PM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is offline
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 4,385
Thanks: 799
Thanked 2,543 Times in 1,465 Posts
Default Re: Unable to Field Flash

Quote:
Originally Posted by Cavalry View Post
...THe AVR appeared to be working during the same disconnected field test the field outputs had current.
It's not at all clear what you meant to say here - at least to me...


Quote:
As soon as I reconnect the field to the AVR I am back to 5VAC output at the generator.
That should be enough for a SX460 to self-flash. (at least according to the SX460 specs.)

Quote:
The stamford manual suggests field flashing while running and the AVR connected via 12VDC to field with a blocking diode. I tried this and instantly smoked the AVR.
Well, that's weird. I'd double check and be sure you have things connected as the SX460 manual describes. I can't imagine why this test, properly conducted, would smoke an SX460. Unless, of course your field is under 15 ohms, you had the diode installed wrong, connected the 12V to the wrong place, or your field needs more than the SX460's 4 amp rating.

What is your field resistance? And how much current does the field need?

For what it's worth, I've used SX460's on several brushless sets, and never needed to flash them, not even once. I have a hunch that the field polarity matters, and it's not obvious that reversing it will do any damage on the brushless sets I'm familiar with. So, if you understand the risks, it might be worth swapping the F+ and F- drive to your static field coil.
Reply With Quote
  #13  
Old 12-25-2018, 01:18:42 AM
Cavalry Cavalry is offline
Registered
 
Join Date: Jan 2018
Location: Albany, New York
Posts: 17
Thanks: 2
Thanked 3 Times in 3 Posts
Default Re: Unable to Field Flash

Quote:
Originally Posted by Jim McIntyre View Post
It's not at all clear what you meant to say here - at least to me...

What I was attempting to say was during the test where I applied unregulated 12vdc to the field for testing, I also checked the output of the AVR to make sure it was working.


Quote:
Originally Posted by Jim McIntyre View Post
Well, that's weird. I'd double check and be sure you have things connected as the SX460 manual describes. I can't imagine why this test, properly conducted, would smoke an SX460. Unless, of course your field is under 15 ohms, you had the diode installed wrong, connected the 12V to the wrong place, or your field needs more than the SX460's 4 amp rating.

What is your field resistance? And how much current does the field need?
Everything was connected correctly, field was 30ohms. I have no clue what the field other requires other than I=V/R




Quote:
Originally Posted by Jim McIntyre View Post
For what it's worth, I've used SX460's on several brushless sets, and never needed to flash them, not even once. I have a hunch that the field polarity matters, and it's not obvious that reversing it will do any damage on the brushless sets I'm familiar with. So, if you understand the risks, it might be worth swapping the F+ and F- drive to your static field coil.
I tried swapping the field polarity, same lack of magnetism.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
How to Field Flash? m151 Kohler Generators 16 05-13-2009 08:36:18 PM
Field Flash Diode GlobalEnergies Onan Generators 1 03-15-2007 09:00:49 PM
DJC low voltage, flash the field? rich9499 Onan Generators 1 08-21-2006 06:26:39 PM
Exciting the field/ Flash the field?? Gary Bright Generators & Electric Motors General Discussion 1 03-18-2004 10:46:06 PM
What does 'Manual Field Flash' mean ? Jorrit Generators & Electric Motors General Discussion 4 06-16-2001 06:06:15 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 12:27:54 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277