Onan Paralleled with an Inverter Based Machine?


this thread has 72 replies and has been viewed 1551 times

Reply
 
Thread Tools Display Modes
  #41  
Old 05-15-2019, 05:07:26 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,976
Thanks: 604
Thanked 1,115 Times in 760 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Quote:
Originally Posted by AngrySailor View Post
If the inverter is outputting a frequency based on an oscillator it would be a constant frequency and should act like an isochronous non inverter set (steady frequency with no droop). It seems to me the only way to couple them would be to parallel them with the inverter set at full load, then add throttle on the non inverter set to share that load. Possibly add more load until both sets are st or near full output. Problem now is when you shed ANY load from the ďgridĒ the mechanically governed set will try to raise the grid frequency above the oscillator frequency (basically a reverse current situationĒ. I have no idea how the inverter could deal with that other than having a frequency droop option as it cannot control the mechanical governor which is now attempting to raise frequency
It's actually pretty simple on the control side. The "smart" generator's brain only really needs to know two things: how much power is going to the load from the generator it controls, and what is the phase/frequency of the inverter with respect to the line?

All the generator's brain is really doing is the following:
1 - Match the frequency of the line
2 - Measure the output kw of the smart generator
3 - Advance or retard the phase of the output sinewave until the kw measured in step (2) is whatever is desired.

Phase control of an inverter is REALLY simple. Numerically controlled oscillators have some similarities, so this link might provide more info as to how it can work: https://en.wikipedia.org/wiki/Numeri...led_oscillator

Most of those inverters are going to be PWM based, so a microprocessor is already under complete control of the waveform. Phase can be controlled by simply changing the timing of the PWM modulator a little bit (wider pulses sooner means a leading phase angle, for example). Its really easy to implement. Since the phase of the generator with respect to the line is what controls how much power the generator puts into the line, all you need to do is adjust the output phase until you see the load you want on the generator. There's not a whole lot more to it.

Bill
Reply With Quote
The Following User Says Thank You to Zephyr7 For This Post:
Sponsored Links
  #42  
Old 05-15-2019, 05:38:23 PM
Vanman Vanman is online now
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,397
Thanks: 8,163
Thanked 2,401 Times in 1,634 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Quote:
Originally Posted by armandh View Post
I would try a Schrage-Richter type motor

https://www.youtube.com/watch?v=z3fHHT4nyZg
Ok, now I'm really intrigued! How exactly does THAT motor operate? It looks REALLY neat!!
Reply With Quote
  #43  
Old 05-15-2019, 06:35:11 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,976
Thanks: 604
Thanked 1,115 Times in 760 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Quote:
Originally Posted by Vanman View Post
Ok, now I'm really intrigued! How exactly does THAT motor operate? It looks REALLY neat!!
That does look cool!

I'm going to guess that as those brushes are moved, which appears to be a form of speed adjustment, the timing (or phase) between the stator and rotor varies. I'm guessing though. I've never seen such a fancy commutator before!

Bill
Reply With Quote
  #44  
Old 05-15-2019, 08:22:46 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 7,001
Thanks: 434
Thanked 6,306 Times in 2,960 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

I wonder if a small VFT could be made based on a wound rotor motor?

https://www.ijariit.com/manuscripts/v3i3/V3I3-1297.pdf
Reply With Quote
  #45  
Old 05-15-2019, 09:13:04 PM
turtmaster turtmaster is offline
Registered-II
 
Join Date: Jun 2015
Location: Hortonville, Wisconsin
Posts: 668
Thanks: 722
Thanked 416 Times in 210 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

no a Honda inverter generator will not pair with "standard" generator, i just tested, this out quick,
https://youtu.be/a5S3RaQftbs
Reply With Quote
The Following 3 Users Say Thank You to turtmaster For This Post:
  #46  
Old 05-15-2019, 09:55:26 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,976
Thanks: 604
Thanked 1,115 Times in 760 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Quote:
Originally Posted by turtmaster View Post
no a Honda inverter generator will not pair with "standard" generator, i just tested, this out quick,
https://youtu.be/a5S3RaQftbs
Did you have them paralleled directly (really wired together), or just through the light bulbs? Iím thinking if only through the lightbulbs, the high-ish impedance might have been a problem.

Might also just be a problem for it trying to track a drifty governor like Iíd mentioned earlier too.

Bill
Reply With Quote
The Following User Says Thank You to Zephyr7 For This Post:
  #47  
Old 05-15-2019, 10:31:14 PM
turtmaster turtmaster is offline
Registered-II
 
Join Date: Jun 2015
Location: Hortonville, Wisconsin
Posts: 668
Thanks: 722
Thanked 416 Times in 210 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Just through the light bulbs, I might later try to parallel through 1500 watt 240 volt halogen light bulb, don't want to try doing it directly, the cck was at about 62 Hertz, I don't think the high impedance, is a problem, before starting the Honda when just cck was running, the light bulbs will light up.
Reply With Quote
  #48  
Old 05-15-2019, 10:48:33 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,976
Thanks: 604
Thanked 1,115 Times in 760 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Light bulbs are very nonlinear in their resistance. When they heat up, the resistance of the filament is MUCH higher. That might also be a problem.

If you want to do the paralleling experiment safely, parallel the two generators through a fuse. Use a 600V fuse, which will be one of the kinds used in electrical panels, NOT one of the small glass body fuses. Iíd try maybe a 5 or 10 amp fuse. The fuse should pop fast enough to protect things, but it wonít have any weird resistance issues the way the light bulbs do.

Bill
Reply With Quote
The Following User Says Thank You to Zephyr7 For This Post:
  #49  
Old 05-15-2019, 10:58:16 PM
Vanman Vanman is online now
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,397
Thanks: 8,163
Thanked 2,401 Times in 1,634 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Yeah, those bulbs are WAY too much resistance. Looked like the Honda kept sensing the voltage from the Onan, but as soon as it would try to take current, the voltage would fall off, being dropped across the bulbs.

The heater stands a chance of working. A larger one is more likely to work. But the fast blow fuse is the best test, as long as it is big enough to pass the current the Honda might try to take from the Onan, which will, at least in part, depend on the load on the system...
Reply With Quote
  #50  
Old 05-15-2019, 11:30:02 PM
turtmaster turtmaster is offline
Registered-II
 
Join Date: Jun 2015
Location: Hortonville, Wisconsin
Posts: 668
Thanks: 722
Thanked 416 Times in 210 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

The way the Hondas parallel with another Honda inverter series generator, is that you electrically parallel the two generators, start one generator, then start the other generator, in the second generator then "matches the phase" of the other generator. How I paralleled these 2 generators, was by wiring the neutrals together, and then wiring the two light bulbs in series between the two hot conductors, with no other load on the system. It was just basically a test to see if the Honda could "match" to a different frequency, there were no loads across the parallel, the control Transformer, to supply the voltage to the oscilloscope, was wired across the two hot conductors, just like light bulbs, basically all the wiring was basically a "poor man's synchroscope" set up, with no actual "parallel feature/switch-gear",

I would be willing to repeat the test sometime with the 1500 watt 240 volt light bulb, but I I'm not willing to repeat the test with an actual parallel with a fuse, if I needed a 600 v fuse, like that one mentioned, I do have access to them, I just a not ready willing to take a chance of possibly, of frying a $600-$800 inverter board, on a generator with only 105 hours on it.
Reply With Quote
The Following 2 Users Say Thank You to turtmaster For This Post:
  #51  
Old 05-16-2019, 06:51:05 AM
willie1959 willie1959 is offline
Registered-I
 
Join Date: Apr 2016
Location: Apsley, Ontario, Canada
Posts: 105
Thanks: 3
Thanked 23 Times in 16 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

I have done this for 10 years like this . Onan Bge 4.5kw

Start ac unit draw 13 amps loaded .

Start Onan set hertz at 60.2

Let inverter lock on .

Readjust hertz if necessary. Inverter seems to like low hertz 59-60 .

Next problem is total harmonic distortion . Most inverters require below 3%. So this is a good test to see how clean the power you are producing is.

Mechanical governor is too slow . Current project is to put fuel injection on Onan, it can be done. GM injector hall sensor on PTO shaft and control board .

or
electronic governed carburetor

Note: max amps from Onan set at 10 amp by inverter control. Suggestion you need a current limiter to do this restricting current flow though to main circuit.

yes I have too much spare time until the NFL starts

going to the lake today

Fishing opens next Saturday yabba dabba doo
Reply With Quote
  #52  
Old 05-16-2019, 07:34:50 AM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 3,054
Thanks: 271
Thanked 834 Times in 641 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Quote:
Originally Posted by Vanman View Post
Ok, now I'm really intrigued! How exactly does THAT motor operate? It looks REALLY neat!!
these are [pre VFD] Very old school, variable speed 3 phase AC motors.
VERY EFFICIENT near constant torque and the KWH went up with the speed and load
popular with one of the two machine manufacturers to the industry I was in.
I even saw a few in the 3hp range made by GE [1960s]

https://www.electrical4u.com/schrage...schrage-motor/
[not shown in their drawing is the segment connection to the tertiary rotor winding]

as I recall the rotor primary 3 phase was often 12 lead and could be re bolted on the back of the slip-rings
380/760 Y or 220/440 delta [wound for other custom voltages as needed]

Dreisilker in Chicago could rewind them, $$$ and one learned not to neglect contact maintenance

BUT ON SECOND THOUGHT...
a large inverter run from paralleled DC supplies might be easier to control.
__________________
.
by using this free advise, you, your heirs, etc
absolve, save, and hold harmless the advisor.
CAVEAT EMPTOR
YMMV

Last edited by armandh; 05-16-2019 at 03:07:46 PM.
Reply With Quote
The Following User Says Thank You to armandh For This Post:
  #53  
Old 05-16-2019, 08:58:55 AM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,976
Thanks: 604
Thanked 1,115 Times in 760 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Quote:
Originally Posted by turtmaster View Post
I would be willing to repeat the test sometime with the 1500 watt 240 volt light bulb, but I I'm not willing to repeat the test with an actual parallel with a fuse, if I needed a 600 v fuse, like that one mentioned, I do have access to them, I just a not ready willing to take a chance of possibly, of frying a $600-$800 inverter board, on a generator with only 105 hours on it.
I certainly understand your desire to ensure smoke only comes out of the exhaust and not the electronics

My guess is that with the lower resistance of the heater, the Honda will be able to track the line better by I donít know how well it will deal with a drifty mechanically governed genset. There are reports they have successfully paralleled with stable sources like utility power but Iím not aware of anyone trying with less stable sources.

Bill
Reply With Quote
  #54  
Old 05-16-2019, 10:39:39 AM
OnanParts's Avatar
OnanParts OnanParts is offline
Sponsor
 
Join Date: Nov 2008
Location: Pacific Northwest, USA
Posts: 1,014
Thanks: 98
Thanked 1,338 Times in 553 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Invert until it Hertz. Or just take the stairs.....easy now, one step at a time, don't trip.
Attached Thumbnails
Click image for larger version

Name:	812Ea copy.jpg
Views:	25
Size:	217.5 KB
ID:	334913   Click image for larger version

Name:	812Ha.jpg
Views:	27
Size:	166.4 KB
ID:	334914  
__________________
https://www.onanparts.com
Reply With Quote
  #55  
Old 05-16-2019, 10:50:24 AM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,976
Thanks: 604
Thanked 1,115 Times in 760 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Quote:
Originally Posted by OnanParts View Post
Invert until it Hertz. Or just take the stairs.....easy now, one step at a time, don't trip.
Yucky stepped sine wave

With one more step, it would be easy to low-pass filter it to get a nice sinewave output. A lot of the older big (100+ KVA) Liebert UPSes did that. The only downside is the BIG AC capacitor banks needed, and they are a scheduled maintenance item.

Bill
Reply With Quote
The Following User Says Thank You to Zephyr7 For This Post:
  #56  
Old 05-16-2019, 11:17:41 AM
Eric.S Eric.S is offline
Registered-I
 
Join Date: Jun 2018
Location: Venray Netherlands (Europe)
Posts: 283
Thanks: 24
Thanked 156 Times in 108 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Add a CVT and it looks a bit better

Eric
Attached Thumbnails
Click image for larger version

Name:	victron blokgolf uitg.jpg
Views:	31
Size:	274.5 KB
ID:	334916   Click image for larger version

Name:	sinus l cond victron.jpg
Views:	30
Size:	270.9 KB
ID:	334917  
Reply With Quote
  #57  
Old 05-16-2019, 12:30:01 PM
OnanParts's Avatar
OnanParts OnanParts is offline
Sponsor
 
Join Date: Nov 2008
Location: Pacific Northwest, USA
Posts: 1,014
Thanks: 98
Thanked 1,338 Times in 553 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Grid Vs. Battery Inverter...
Attached Thumbnails
Click image for larger version

Name:	Grid1.jpg
Views:	22
Size:	351.2 KB
ID:	334919   Click image for larger version

Name:	Inverter1.jpg
Views:	22
Size:	245.2 KB
ID:	334920  
__________________
https://www.onanparts.com
Reply With Quote
  #58  
Old 05-16-2019, 12:38:41 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,976
Thanks: 604
Thanked 1,115 Times in 760 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Looks like your grid has some lagging power factor loading going on, and maybe a bit of noise too. Nothing a few caps can't fix

Inverter output looks really clean. What kind of inverter are you using there? High frequency PWM type?

Bill
Reply With Quote
  #59  
Old 05-16-2019, 12:48:05 PM
OnanParts's Avatar
OnanParts OnanParts is offline
Sponsor
 
Join Date: Nov 2008
Location: Pacific Northwest, USA
Posts: 1,014
Thanks: 98
Thanked 1,338 Times in 553 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

Quote:
Originally Posted by Zephyr7 View Post
Looks like your grid has some lagging power factor loading going on, and maybe a bit of noise too. Nothing a few caps can't fix

Inverter output looks really clean. What kind of inverter are you using there? High frequency PWM type?

Bill
Negative on the HF. Got caps and lots of copper!
Attached Thumbnails
Click image for larger version

Name:	Rad16.jpg
Views:	34
Size:	84.8 KB
ID:	334921   Click image for larger version

Name:	Rad17.jpg
Views:	35
Size:	83.1 KB
ID:	334922   Click image for larger version

Name:	Rad11.jpg
Views:	34
Size:	95.9 KB
ID:	334923   Click image for larger version

Name:	Rad19.jpg
Views:	30
Size:	76.3 KB
ID:	334924  
__________________
https://www.onanparts.com
Reply With Quote
The Following 3 Users Say Thank You to OnanParts For This Post:
  #60  
Old 05-16-2019, 01:21:48 PM
Vanman Vanman is online now
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,397
Thanks: 8,163
Thanked 2,401 Times in 1,634 Posts
Default Re: Onan Paralleled with an Inverter Based Machine?

I know that the marketing wanks like to call them "Modified Sine Wave" inverters, but what they really mean is Modulated Square Wave. The only similarity to a sine wave is the fact that it is indeed Alternating Current.
Reply With Quote
The Following User Says Thank You to Vanman For This Post:
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan HDKAJ Controller/Inverter Trouble hoke_weise Onan Generators 2 09-24-2017 05:24:36 PM
Dimensions Pure Sine Inverter Powering an inverter directly from the panels 4Strokeguy Solar and Wind Power for Home, Farm & Industry 16 05-19-2015 05:38:25 AM
Onan Inverter converter Flash41 Onan Generators 0 08-25-2013 11:39:58 PM
Onan Quiet Diesel 7.5kw Controller/Inverter Trouble maddog468 Onan Generators 9 03-21-2012 02:02:05 PM
Onan Genset 4000 Microquiet run in with Inverter Binnie Onan Generators 35 10-23-2010 11:07:58 AM