Onan LT II Transfer Switch JB 7.5


this thread has 105 replies and has been viewed 4414 times

Reply
 
Thread Tools Display Modes
  #61  
Old 10-10-2017, 08:56:50 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,954
Thanks: 712
Thanked 2,327 Times in 1,360 Posts
Default Re: Onan LT II Transfer Switch / JB 7.5

I guess I still do not understand what you are doing? So, do you wait until the power goes out and then pull the fridge and plug it into the ATS circuit or do you set this up prior to the outage? if the later, then "you" are paying for the juice they draw from your 240 volt tap?

As for your last question, keep in mind, the neutral and the earth ground are bonded together at the utility incoming service panel. So I would assume your ATS would respect that fact and carry the neutral and the ground wire along from the service entrance panel via that 240 volt receptacle. Yes, some single phase 240 volt receptacles are just three-wire plugs, but note in those cases, I believe the neutral is connected to the 240 volt appliance frame or chassis.
Reply With Quote
Sponsored Links
  #62  
Old 10-10-2017, 09:17:18 PM
JohnnyC JohnnyC is offline
Subscriber
 
Join Date: Jun 2014
Location: Boonton, New Jersey
Posts: 4,947
Thanks: 1,739
Thanked 2,484 Times in 1,431 Posts
Default Re: Onan LT II Transfer Switch / JB 7.5

Quote:
Originally Posted by Leon N. View Post
I guess I still do not understand what you are doing? So, do you wait until the power goes out and then pull the fridge and plug it into the ATS circuit or do you set this up prior to the outage? if the later, then "you" are paying for the juice they draw from your 240 volt tap?
Prior to a storm. Yes, I will pay for the utility power for a short duration which is no big deal since I am only supplying minimal power, but it sure beats having to go out into a heavy snow storm foot of snow or during a hurricane with pounding rain and wind, dragging the JB through the weather into position and laying out the lines. I rather setup before hand and let nature take its course. If or when the utility goes out I will be inside a nice warm house while the ATS transfers the load from the non-working utility to the JB and the reverse once the utility power is restored. I am getting too old to be running around outside during storms.

As for your last question, keep in mind, the neutral and the earth ground are bonded together at the utility incoming service panel. So I would assume your ATS would respect that fact and carry the neutral and the ground wire along from the service entrance panel via that 240 volt receptacle. I agree.

JohnnyC
New Jersey

Last edited by JohnnyC; 10-10-2017 at 10:56:38 PM.
Reply With Quote
  #63  
Old 10-10-2017, 09:25:13 PM
Steve Dawkins Steve Dawkins is offline
Sponsor
 
Join Date: Feb 2005
Location: Virginia Beach, Virginia, USA
Posts: 900
Thanks: 621
Thanked 406 Times in 216 Posts
Default Re: Onan LT II Transfer Switch / JB 7.5

As long as the input plug for the ATS stays connected to the MIG welder receptacle, do not bond the neutral and ground in the ATS.

If you want to run the gen & ATS together without the "Utility Input" plug connected to the MIG receptacle (don't know why you would do this, other than metering and power distribution), get another receptacle like the MIG outlet, and jumper the neutral and ground terminals together. Then you can plug the ATS plug into this receptacle for your neutral/ground bond. Mount the "bonding" receptacle on the ATS, and you won't have to worry about losing it. It will also make a conversation piece when people ask why the ATS is plugged into itself.
Reply With Quote
  #64  
Old 10-10-2017, 10:59:28 PM
JohnnyC JohnnyC is offline
Subscriber
 
Join Date: Jun 2014
Location: Boonton, New Jersey
Posts: 4,947
Thanks: 1,739
Thanked 2,484 Times in 1,431 Posts
Default Re: Onan LT II Transfer Switch / JB 7.5

Quote:
Originally Posted by Steve Dawkins View Post
As long as the input plug for the ATS stays connected to the MIG welder receptacle, do not bond the neutral and ground in the ATS.

If you want to run the gen & ATS together without the "Utility Input" plug connected to the MIG receptacle (don't know why you would do this, other than metering and power distribution), get another receptacle like the MIG outlet, and jumper the neutral and ground terminals together. Then you can plug the ATS plug into this receptacle for your neutral/ground bond. Mount the "bonding" receptacle on the ATS, and you won't have to worry about losing it. It will also make a conversation piece when people ask why the ATS is plugged into itself.
Excellent suggestion / solution!!

Thanks!
JohnnyC
New Jersey
Reply With Quote
  #65  
Old 10-22-2017, 10:40:48 PM
JohnnyC JohnnyC is offline
Subscriber
 
Join Date: Jun 2014
Location: Boonton, New Jersey
Posts: 4,947
Thanks: 1,739
Thanked 2,484 Times in 1,431 Posts
Default Re: Onan LT II Transfer Switch JB 7.5

Late last week I ran a bi-monthly exercise of my JB and the LTII automatic transfer switch. All went well until the utility power was restored. The ATS did not transfer the load from the generator back to the utility and the JB did not shut down. Basically, the JB would have ran forever until it either ran out of fuel . This did not happen last time I exercised the complete setup. I posted about this in the following post from "what Have You Done to Your Onan Today": https://www.smokstak.com/forum/showp...postcount=3397

Today I had several minutes to trouble shoot the problem and as I guessed, it was a relay. Specifically the problem relay is the K4 Time Delay Retransfer relay. The relay's delay is adjustable from 2 to 30 minutes and begins the moment when utility power is restored. After the delay time is achieved, the transfer switch will retransfer the load from the generator to the utility power and activate the K5 Stop Time Delay relay which will shut down the generator.

The way I trouble shot the problem was very simple. It is clear that when the K4 relay is activated when utility power is present, 120vac should be present at the K4 relay socket. This was verified as seen in the second picture below. This tells me that the ATS box's wiring and circuitry for this function is working and something may be wrong with the Time Delay Retransfer switch.

My next step was to remove the Time Delay Retransfer switch from the ATS and test. These relays are simple and activated by a 120 vac coil with a timer circuit that is user adjustable. The third picture is not too clear, but I have a line cord plugged into a 120 vac source and attached to the pins of the relay. The picture did not capture the cord as I was trying to focus on the relay and the meter. The timer is adjusted to trip the relay at 3 minutes. It did not trip. I have my volt meter on PC board where the 2 blue wires are soldered to and lead to the relay coil. If the timer circuit was working correctly I would be seeing 120 vac on my meter after 3 minutes. I see nothing.

In conclusion, something in the Time Delay Retransfer relay's electronic circuitry failed and may cost me several hundred dollars to replace. There is no evidence of burnt components and I hit all solder points on the PC board with my solder iron to eliminate the possibility of a cold solder joint. Looks like I will have to find another relay on ebay.

JohnnyC
New Jersey
Attached Thumbnails
Click image for larger version

Name:	20171021_212749.jpg
Views:	48
Size:	166.6 KB
ID:	294175   Click image for larger version

Name:	20171022_202014.jpg
Views:	45
Size:	96.2 KB
ID:	294176   Click image for larger version

Name:	20171022_203135.jpg
Views:	46
Size:	112.3 KB
ID:	294177  

Last edited by JohnnyC; 10-23-2017 at 06:23:48 AM.
Reply With Quote
The Following User Says Thank You to JohnnyC For This Post:
  #66  
Old 10-22-2017, 11:55:47 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 4,278
Thanks: 5,524
Thanked 1,821 Times in 1,230 Posts
Default Re: Onan LT II Transfer Switch JB 7.5

Ugh, electronics. Seems to be the Achilles Heel of everything these days.

One of my "old" (1943) Kohlers has an automatic transfer switch built in. It has a time delay retransfer relay as well, but no electronics there! It's all motors and coils and springs and such.
Reply With Quote
The Following User Says Thank You to Vanman For This Post:
  #67  
Old 10-23-2017, 08:32:00 AM
JT240Z JT240Z is offline
Subscriber
 
Join Date: Dec 2011
Location: Grayson, Georgia
Posts: 259
Thanks: 0
Thanked 81 Times in 50 Posts
Default Re: Onan LT II Transfer Switch JB 7.5

My LTII is a little simpler it seems. No red relays for delays. I'll post pics of the internal some time today.
Reply With Quote
  #68  
Old 10-23-2017, 08:41:44 AM
JohnnyC JohnnyC is offline
Subscriber
 
Join Date: Jun 2014
Location: Boonton, New Jersey
Posts: 4,947
Thanks: 1,739
Thanked 2,484 Times in 1,431 Posts
Default Re: Onan LT II Transfer Switch JB 7.5

Quote:
Originally Posted by JT240Z View Post
My LTII is a little simpler it seems. No red relays for delays. I'll post pics of the internal some time today.
Well, my LTII will now have one less red relay

JohnnyC
New Jersey
Reply With Quote
  #69  
Old 10-23-2017, 10:04:53 AM
squidtrap squidtrap is offline
Subscriber
 
Join Date: Nov 2012
Location: Forked River, New Jersey
Posts: 1,241
Thanks: 1,826
Thanked 589 Times in 395 Posts
Default Re: Onan LT II Transfer Switch JB 7.5

"one less relay" the price of those things is crazy.
Reply With Quote
  #70  
Old 10-23-2017, 10:47:05 AM
AngrySailor AngrySailor is offline
Subscriber
 
Join Date: Apr 2017
Location: West Prince, Prince Edward Isand, Canada
Posts: 1,018
Thanks: 387
Thanked 667 Times in 368 Posts
Default Re: Onan LT II Transfer Switch JB 7.5

Can you substitute another timer (read more cheaper) to trigger the relay? Or if current is the issue, use it to trigger a small relay to trigger the big relay?
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan Transfer Switch saggys Onan Generators 5 01-24-2015 12:07:53 AM
Onan OT 150 transfer switch jurick Onan Generators 9 08-26-2013 11:51:48 AM
onan transfer switch bswalsh55 Onan Generators 5 02-07-2013 10:00:53 AM
Transfer Switch for my Onan BigBlockChev Onan Generators 6 03-08-2012 04:19:38 PM
Help on Onan OT Transfer Switch hoghunter69 Onan Generators 11 12-07-2011 08:25:19 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 06:43:05 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277