Onan 45EM Project


this thread has 30 replies and has been viewed 1081 times

Reply
 
Thread Tools Display Modes
  #1  
Old 02-09-2017, 06:24:30 PM
Kyle K Kyle K is offline
Subscriber
 
Join Date: Jan 2007
Location: Bechtelsville, Pennsylvania
Posts: 675
Thanks: 188
Thanked 526 Times in 157 Posts
Default Onan 45EM Project

Well another Craigslist find. I am now the owner of a 45 EM. By all means its mostly a toy as I know it has a healthy fuel appetite. After cleaning the mud wasp nest out of gas valve it came back to life and made voltage. Hour meter says 1073. Looks like someone was in head recently. Any do's or don'ts? Is 6 gallons a hour consumption a accurate fuel number?

Thanks Kyle
Reply With Quote
Sponsored Links
  #2  
Old 02-09-2017, 06:53:16 PM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,719
Thanks: 4,953
Thanked 5,252 Times in 2,873 Posts
Default Re: Onan 45EM project

Quote:
Originally Posted by Kyle K View Post
Is 6 gallons a hour consumption a accurate fuel number? Thanks Kyle
I would guess that is pretty close for full load consumption.
Reply With Quote
The Following User Says Thank You to Max Thompson For This Post:
  #3  
Old 02-09-2017, 11:04:27 PM
Utah Onan Utah Onan is offline
Registered-I
 
Join Date: Nov 2013
Location: West Jordan, Utah
Posts: 92
Thanks: 127
Thanked 32 Times in 17 Posts
Default Re: Onan 45EM project

I'm not sure about gasoline consumption.
But from the T-015 Gaseous Fuels guide it says that a 45.0EM uses 690 CFH of Natural Gas & 290 CFH of LPG. Hope that helps some. You've got an awesome set there with that 45.0EM.
- Utah
Reply With Quote
The Following User Says Thank You to Utah Onan For This Post:
  #4  
Old 02-09-2017, 11:36:34 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 3,173
Thanks: 3,916
Thanked 1,296 Times in 879 Posts
Default Re: Onan 45EM project

690 CF/Hr natural gas is roughly 690,000 BTU/Hr.

Gasoline is around 115,000 BTU per Gallon, so

That math works out to 6 gallons of gasoline / hr.
Reply With Quote
The Following 2 Users Say Thank You to Vanman For This Post:
  #5  
Old 02-09-2017, 11:38:56 PM
Troll Troll is offline
Subscriber
 
Join Date: Jan 2017
Location: Farmington, Illinois
Posts: 467
Thanks: 14
Thanked 259 Times in 137 Posts
Default Re: Onan 45EM project

Quote:
Originally Posted by Vanman View Post
690 CF/Hr natural gas is roughly 690,000 BTU/Hr.

Gasoline is around 115,000 BTU per Gallon, so

That math works out to 6 gallons of gasoline / hr.
Just about what my 45kva "EF" set uses at full load.
Reply With Quote
The Following User Says Thank You to Troll For This Post:
  #6  
Old 02-10-2017, 12:49:09 AM
Troll Troll is offline
Subscriber
 
Join Date: Jan 2017
Location: Farmington, Illinois
Posts: 467
Thanks: 14
Thanked 259 Times in 137 Posts
Default Re: Onan 45EM project

As a side note: Retard engine timing about 4 degrees when using gasoline as opposed to gaseous fuels. Backfiring through carburetor is usually the result upon engine starting is usually the result if timing is not retarded.
Reply With Quote
The Following User Says Thank You to Troll For This Post:
  #7  
Old 02-12-2017, 10:23:08 AM
Kyle K Kyle K is offline
Subscriber
 
Join Date: Jan 2007
Location: Bechtelsville, Pennsylvania
Posts: 675
Thanks: 188
Thanked 526 Times in 157 Posts
Default Re: Onan 45EM project

Thanks for replies all. I would not go to gasoline but keep it on propane. To clarify my question a bit I found the 6 gallons on a google search how does that relate to propane. I have a all electric house which I have a 15 JC on right now to run partial load if need be. Its fed from a 250 gallon tank. If I really got in a long outage the 45 EM would handle the whole load. Do I have enough tank for even a short term run? In other words run the 45EM for a few hours to warm everything back up.
Reply With Quote
  #8  
Old 02-12-2017, 10:38:31 AM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,719
Thanks: 4,953
Thanked 5,252 Times in 2,873 Posts
Default Re: Onan 45EM project

45 EM will burn 290 CFH of propane at "Full Load" which equates to 8.6 Gallons per hr.

Though the 45 KW set would likely not be running at full load very often, so your consumption could be more like 1/2 - 2/3 of that amount. Still a bunch of fuel.

I would not get rid of the JC.
Reply With Quote
The Following User Says Thank You to Max Thompson For This Post:
  #9  
Old 02-12-2017, 10:47:51 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is online now
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,238
Thanks: 8,265
Thanked 13,587 Times in 6,396 Posts
Default Re: Onan 45EM project

The 45 does love fuel.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
  #10  
Old 02-12-2017, 11:08:49 AM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 5,147
Thanks: 303
Thanked 4,235 Times in 2,028 Posts
Default Re: Onan 45EM project

I keep having a mental picture of the 45EM starting and that tank freezing up like a Popsicle.
Reply With Quote
  #11  
Old 02-12-2017, 12:59:01 PM
Kyle K Kyle K is offline
Subscriber
 
Join Date: Jan 2007
Location: Bechtelsville, Pennsylvania
Posts: 675
Thanks: 188
Thanked 526 Times in 157 Posts
Default Re: Onan 45EM project

No the JC is really the primary back up even though I have a JB gaseous and CCKK 4 kw gasoline for smaller loads if need be.

---------- Post added at 11:59:01 AM ---------- Previous post was at 11:55:05 AM ----------

I drug over a 40lb tank to get it running and it wasn't doing work but I also wondered if it would freeze it up but it didn't. Guess I am looking for some real world tank thoughts. I live in a classic 1970's subdivision with primary being blind alley construction so its all hook work if there is damage so that gets put to bottom of list aka wait till the contractors are called in.
Reply With Quote
  #12  
Old 02-12-2017, 04:40:39 PM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,719
Thanks: 4,953
Thanked 5,252 Times in 2,873 Posts
Default Re: Onan 45EM project

Quote:
Originally Posted by Kyle K View Post
Guess I am looking for some real world tank thoughts.

The biggest one you can get and afford. Propane does not go bad, you do not have to fill it full all at once. I see NO down side to bigger is better when it comes to tank size.
Reply With Quote
The Following User Says Thank You to Max Thompson For This Post:
  #13  
Old 02-12-2017, 10:14:27 PM
Doug Reed Doug Reed is offline
Registered-III
 
Join Date: May 2013
Location: St Paul, Minnesota
Posts: 1,079
Thanks: 210
Thanked 486 Times in 375 Posts
Default Re: Onan 45EM project

Download the T-015 Gaseous Fuels manual. That is where Onan explains their suggestions and requirements for propane and natural gas fuels.

The requirements of your 45EM under full load would probably require a liquid withdrawl system, that is my guess. If your power requirements are lower, so is the tank size. The charts in T-015 say your 45EM needs 295 cubic feet of propane vapor per hour at maximum load. The charts also say that a 500 gallon tank will work to about +20F at full load. A 1000 gallon tank would probably be marginal at full load if the weather is below +20F, At least according to the chart.....

You can get by with a much smaller tank if using liquid withdrawl but your local supplier may not provide the service..... The liquid systems are more common on gensets with a radiator system because the hot water can be used to vaporize the liquid propane. If the fuel system on the generator includes a hose loop from the radiator, that is what you have.

Instead of another guess, I'm just going to suggest you call a local propane supplier and tell them what you want and the fuel requirements of the genset. They will tell you what they can provide. Good luck.
Reply With Quote
  #14  
Old 02-12-2017, 11:17:18 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 3,173
Thanks: 3,916
Thanked 1,296 Times in 879 Posts
Default Re: Onan 45EM project

Another approach that I always suggest to anyone with an all electric house.

Get a smallish water cooled generator set, ideally a marine unit with a heat exchanger and water cooled exhaust manifold, of say 4 or 5 kW, and don't run any of your electric heating from it. Instead plumb a loop between your electric water heater tank and the set.

Now you have "free" hot water.

Then, add a heat exchanger to your electric FAU (If that's what you have) and run a pair of pipes to it. Now you have free house heat as well.

A couple of small circulating pumps and thermostats, maybe an outdoor radiator for when the set is making more heat than the house needs, and you're golden.

The savings are not just fuel cost, but size of fuel tank needed, size of generator needed, size of wiring and transfer switch. It eliminates the need to have a transfer switch for the main panel. Instead add an emergency panel, leaving the electric heating stuff in the main panel.

For instance, let's say that 45 kW set is averaging 5 gallons per hour. If you started out with a full 250 gallon tank, it's gone in two days. But if you have a small set taking 1 gallon per hour, now you have ten day's worth of fuel, and just as much heat for your house.
Reply With Quote
  #15  
Old 09-27-2017, 03:21:55 PM
radiotech radiotech is offline
Registered
 
Join Date: Mar 2017
Location: Rockford, Illinois
Posts: 21
Thanks: 2
Thanked 1 Time in 1 Post
Default Re: Onan 45EM project

Does anyone know if you can run a 3/4" natural gas line or will it take a 1" for the 45EM generator.
Reply With Quote
  #16  
Old 09-27-2017, 04:31:57 PM
Utah Onan Utah Onan is offline
Registered-I
 
Join Date: Nov 2013
Location: West Jordan, Utah
Posts: 92
Thanks: 127
Thanked 32 Times in 17 Posts
Default Re: Onan 45EM Project

Depends on what pressure you're pushing through that pipe AND how long the pipe is from the gas meter.

We'll need some more info from you to figure it out.
Reply With Quote
  #17  
Old 09-27-2017, 04:43:37 PM
radiotech radiotech is offline
Registered
 
Join Date: Mar 2017
Location: Rockford, Illinois
Posts: 21
Thanks: 2
Thanked 1 Time in 1 Post
Default Re: Onan 45EM Project

I tried to download the T-015 tech bulletin mentioned above, but twinslan.net seems to be no more.
But I am about 12 feet from the gas meter. I have Nicor Gas and they tell me the pressure is 1/4 lbs and 7" of water column.
Reply With Quote
  #18  
Old 09-27-2017, 06:21:28 PM
Pauls12 Pauls12 is offline
Subscriber
 
Join Date: Jan 2015
Location: Milan, Michigan, USA
Posts: 133
Thanks: 779
Thanked 83 Times in 54 Posts
Default Re: Onan 45EM Project

https://drive.google.com/drive/folde...DZmX19sb1FIN28 you may find the manual here.
Reply With Quote
The Following User Says Thank You to Pauls12 For This Post:
  #19  
Old 09-28-2017, 09:04:38 AM
Utah Onan Utah Onan is offline
Registered-I
 
Join Date: Nov 2013
Location: West Jordan, Utah
Posts: 92
Thanks: 127
Thanked 32 Times in 17 Posts
Default Re: Onan 45EM Project

radiotech,
going off the T-015 you'll need at least an 1 1/4" gas line to feed that 45EM. If the distance is greater than 15' then the gas line needs to be upsized to 1 1/2".
In addition to that, I would like to see a picture(s) of your house's gas meter & gas regulator. I don't think your standard gas meter we'll be able to maintain a flow rate of 690 CFH (Cubic Feet an Hour) otherwise your meter may spin its guts out and then they don't flow ANY gas. You'll probably have to have your meter upsized.
I work for the gas company out here and the "standard" or "house" gas meter only flows 320 CFH.
Reply With Quote
  #20  
Old 09-28-2017, 11:05:34 AM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,439
Thanks: 2
Thanked 448 Times in 319 Posts
Default Re: Onan 45EM Project

Somewhere once I saw curves for gas meters at various flow rates exceeding their nominal rate.

The standard AC-250 meter for instance can flow 250 CFH (kBTUH) at 1/2" pressure drop.

If you allow the pressure drop to be 1" the acceptable flow rate is a lot higher, and even higher at 2".

If your regulator setting is 7" then 2" drop or even 2.5" *should* be acceptable to keep appliance pressure above minimum stated 4" for natural gas appliances.

I worked in a gas company also and saw many meters run well beyond nominal rating for years such as in an auto paint shop.

Also, there is the matter that the generator does not really draw the full 690 except at full load but I would wonder what would happen when it is starting.

If it were mine, I would build it as specified and measure the pressures under worst case scenario and see what happens, and only call for meter upgrade after that.
Reply With Quote
The Following User Says Thank You to Birken Vogt For This Post:
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan cooling fan 45em bikehead Onan Generators 24 09-08-2017 02:30:35 PM
ONAN 45EM-15R bad boards? mefroe1 Onan Generators 15 01-26-2016 03:18:50 PM
Onan 45em generator Gregcrankshaft Onan Generators 50 08-19-2015 06:08:05 PM
Onan 45em won't start Nail banger Onan Generators 13 02-10-2015 05:26:51 AM
Radiator for Onan 45EM Dave Hammen Onan Generators 5 01-11-2008 10:58:44 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 08:21:33 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277