Questions on Onan 30EC Generator with Ford 6 Cylinder Engine


this thread has 32 replies and has been viewed 974 times

Reply
 
Thread Tools Display Modes
  #21  
Old 09-22-2017, 02:18:31 PM
nothingbutdarts nothingbutdarts is offline
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 2,117
Thanks: 4,673
Thanked 934 Times in 632 Posts
Default Re: Questions on Onan 30EC generator with Ford 6 cylinder engine

I could not get the link to work?
Reply With Quote
Sponsored Links
  #22  
Old 09-22-2017, 02:48:22 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,226
Thanks: 8,263
Thanked 13,560 Times in 6,389 Posts
Default Re: Questions on Onan 30EC generator with Ford 6 cylinder engine

I had the same problem. But put in the ESC number and it come up.

That one would work,but first you need to find out if it is really the problem or the actuator.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
  #23  
Old 09-22-2017, 04:13:24 PM
oldjohndeere oldjohndeere is offline
Registered
 
Join Date: Sep 2017
Location: Brooklet, Georgia
Posts: 12
Thanks: 9
Thanked 2 Times in 2 Posts
Default Re: Questions on Onan 30EC generator with Ford 6 cylinder engine

When I run 12 volts to the actuator it goes full open, so I think it is good. I just bought a new multi-meter as mine did not work good. I am going to check it out as per instructions above.

]I unplugged the speed control sensor and got a reading of 1026. I then cranked the motor and got voltage readings but the numbers were bouncing all over the place. Should it be a constant number??
Reply With Quote
The Following User Says Thank You to oldjohndeere For This Post:
  #24  
Old 09-22-2017, 04:53:56 PM
pegasuspinto pegasuspinto is offline
Registered-III
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 2,517
Thanks: 319
Thanked 1,156 Times in 759 Posts
Default Re: Questions on Onan 30EC generator with Ford 6 cylinder engine

were you reading AC volts? it will vary with the speed so it might jump up and down a half volt or so while cranking. 1024 ohms sounds good tho. what was the volts?
Reply With Quote
  #25  
Old 09-22-2017, 05:26:26 PM
oldjohndeere oldjohndeere is offline
Registered
 
Join Date: Sep 2017
Location: Brooklet, Georgia
Posts: 12
Thanks: 9
Thanked 2 Times in 2 Posts
Default Re: Questions on Onan 30EC generator with Ford 6 cylinder engine

Yes it was set on AC. I need to do it again with a helper. I think I had a good connection but had to hold the prongs and reach around to push the start button. Voltage varied rapidly from 0 to 4 digits which can,t be right. But it did appear to have a decimal and seemed to be reading 3.452 at the highest reading.
Reply With Quote
  #26  
Old 09-22-2017, 05:45:25 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 5,137
Thanks: 303
Thanked 4,224 Times in 2,022 Posts
Default Re: Questions on Onan 30EC generator with Ford 6 cylinder engine

Quote:
Originally Posted by oldjohndeere View Post
the numbers were bouncing all over the place. Should it be a constant number??

There are times when an old fashioned analog meter is helpful. This might be one of those.
Reply With Quote
The Following 3 Users Say Thank You to Wayne 440 For This Post:
  #27  
Old 09-25-2017, 06:51:25 PM
Copperhead1971 Copperhead1971 is offline
Subscriber
 
Join Date: Sep 2017
Location: Courtright, Ontario, Canada
Posts: 12
Thanks: 12
Thanked 2 Times in 2 Posts
Default Re: Questions on Onan 30EC generator with Ford 6 cylinder engine

few on ebay and one said its 24 volt alittle pricey
/https://www.ebay.ca/dsc/Generator-Parts-Accessories/42907/i.html?_sac=1&_nkw=barber+colman

/http://www.ebay.ca/itm/ONAN-LISTER-MARINE-DYN1-10724-100-0-12-BARBER-COLMAN-CONTROLLER-DYN1-10724-/311663040739?hash=item48909098e3:g:mDYAAOSwj9lZqui p
Reply With Quote
The Following User Says Thank You to Copperhead1971 For This Post:
  #28  
Old 10-04-2017, 05:54:38 PM
oldjohndeere oldjohndeere is offline
Registered
 
Join Date: Sep 2017
Location: Brooklet, Georgia
Posts: 12
Thanks: 9
Thanked 2 Times in 2 Posts
Default Re: Questions on Onan 30EC generator with Ford 6 cylinder engine

OK, I got busy and just got a little time for the generator. I hooked my volt meter up to the speed sensor, started the motor and set speed with vise grips to give me 225 volts on the meter on the instrument panel. Checked hertz and read 60. With the volt meter set to AC it reads 31.00 and set on DC it reads 138.00 mV with the numbers behind the decimal fluctuating. Does this look like what it should read at normal run speed??
Reply With Quote
  #29  
Old 10-04-2017, 08:50:37 PM
pegasuspinto pegasuspinto is offline
Registered-III
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 2,517
Thanks: 319
Thanked 1,156 Times in 759 Posts
Default Re: Questions on Onan 30EC generator with Ford 6 cylinder engine

Sounds fine. The DC readings are meaningless. The MPU is actually a tiny AC generator, nothing more.
Reply With Quote
The Following User Says Thank You to pegasuspinto For This Post:
  #30  
Old 10-11-2017, 01:00:07 PM
oldjohndeere oldjohndeere is offline
Registered
 
Join Date: Sep 2017
Location: Brooklet, Georgia
Posts: 12
Thanks: 9
Thanked 2 Times in 2 Posts
Default Re: Questions on Onan 30EC generator with Ford 6 cylinder engine

I got my new controller yesterday, part number ESC2301-A. I need help understanding the wiring instructions. This is a quote of one instruction. Terminal 10 and 11is the MPU signal input terminal. The wiring used to connect it to the terminals must use 2 wire shield cable. The drain shield wire is to be connected to terminal 10and the other end of the drain shield wire must be cut off and taped. Is the wire on my old sensor shield cable and what does drain shield mean??

Another one says the harness used to connect terminal 1, 2, 4 and 5 must use 2.0 Omm twist pair harness. What does that mean.
Reply With Quote
  #31  
Old 10-11-2017, 03:20:42 PM
Birken Vogt Birken Vogt is online now
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,434
Thanks: 2
Thanked 446 Times in 318 Posts
Default Re: Questions on Onan 30EC Generator with Ford 6 Cylinder Engine

Drain = shield

Just hook it up using the wire you have and following the instructions otherwise and see if it works before you go changing wire, etc.
Reply With Quote
The Following User Says Thank You to Birken Vogt For This Post:
  #32  
Old 10-11-2017, 04:17:35 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,226
Thanks: 8,263
Thanked 13,560 Times in 6,389 Posts
Default Re: Questions on Onan 30EC Generator with Ford 6 Cylinder Engine

Twisted pair cable is also called cat 5 cable. Special cable with the wires twisted around each other. Covered in a protected foil cover call the shield. Grounded at one end to stop interference from an out side source. Such as a radio,transmitter,electronic noise. Your old system should have it. But it might be a good idea to up grade. You can run with out it. But you run the risk the chance of losing control of the engine.
Attached Thumbnails
Click image for larger version

Name:	img135.jpg
Views:	11
Size:	123.1 KB
ID:	293314  
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following User Says Thank You to Billy J Shafer For This Post:
  #33  
Old 10-12-2017, 03:10:46 PM
oldjohndeere oldjohndeere is offline
Registered
 
Join Date: Sep 2017
Location: Brooklet, Georgia
Posts: 12
Thanks: 9
Thanked 2 Times in 2 Posts
Default Re: Questions on Onan 30EC Generator with Ford 6 Cylinder Engine

It works!!! I still have to make some adjustments but it started at idle speed which it would not do before, it was idled to low to run, I then turned the run speed up to get 225 volts. I am having a fuel problem and when it started skipping the speed actuator moved the throttle faster. When it shut down the actuator went full throttle so all that is working as it should. I thought I had the running problem fixed as I put in new points last week and ran it 20 minutes with no problems.

The speed sensor is 2 wire shielded cable. I did not hook up the drain wire as I did not know which wire was which. I assumed the red wire was hot and hooked it to terminal 9 and the black wire to 10 as the instructions said 10 was ground. Is that correct?? If so then I need to hook the drain wire to 10.

Thank you guys for all your help
Reply With Quote
The Following User Says Thank You to oldjohndeere For This Post:
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan 10 kw Generator w/Ford 8nnn Engine Gramps Multi-Cylinder Stationary Engines and Power Units 1 03-08-2017 01:36:51 AM
Just bought an Onan generator with a Ford engine cmrobins Onan Generators 22 11-26-2014 11:42:24 AM
Onan generator (1964 30ec) jethro Onan Generators 2 04-10-2012 07:24:14 AM
Onan 30EC with Ford need manuals 7mpoole Onan Generators 5 01-04-2012 07:53:22 PM
Onan Generator w Ford 4 cyc engine Tim_Ball Onan Generators 10 11-16-2007 07:21:15 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 11:30:22 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277