Default Onan LTD100-4 Transfer Switch

Hello All,

I got a transfer switch with my 15 kw RJC. The generator is rewired to single phase, and tested. I'd like to see if I can use this for single phase and / or if it's worth the hassle. I don't see any single phase wiring diagrams so I have my doubts. Pictures attached below!
Attached Thumbnails
Click image for larger version

Name:	20171007_143037.jpg
Views:	54
Size:	136.6 KB
ID:	293049   Click image for larger version

Name:	20171007_144040.jpg
Views:	45
Size:	114.1 KB
ID:	293050   Click image for larger version

Name:	20171007_144301.jpg
Views:	42
Size:	85.2 KB
ID:	293051  
Reply With Quote
Sponsored Links
  #2  
Old 10-07-2017, 04:18:48 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,377
Thanks: 8,348
Thanked 13,695 Times in 6,444 Posts
Default Re: Onan LTD100-4 Transfer switch

I will check my files. But that one may be hard to do. Being 208.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following User Says Thank You to Billy J Shafer For This Post:
  #3  
Old 10-07-2017, 07:05:17 PM
MBB MBB is offline
Registered-III
 
Join Date: Apr 2009
Location: Elk Grove Village IL USA
Posts: 3,104
Thanks: 1,336
Thanked 2,445 Times in 1,300 Posts
Default Re: Onan LTD100-4 Transfer switch

Here is the build sheet and wiring diagram note Billy the coils re 208v as well as 240v
Attached Files
File Type: pdf 619-4449.pdf (246.1 KB, 28 views)
File Type: pdf LTD100415909E.pdf (26.8 KB, 18 views)
Reply With Quote
The Following 3 Users Say Thank You to MBB For This Post:
  #4  
Old 10-07-2017, 07:31:26 PM
whiteblaze whiteblaze is offline
Registered
 
Join Date: Apr 2017
Location: Scranton, Pennsylvania, USA
Posts: 16
Thanks: 23
Thanked 3 Times in 3 Posts
Default Re: Onan LTD100-4 Transfer switch

Would you think it would be possible just not to use the 3rd phase of the switch and still have it work properly? Still plan on going through it before use. Looks like it's in great shape, but there are a few marks on the inside top of the cabinet that seem a bit burnt.
Reply With Quote
  #5  
Old 10-07-2017, 07:55:22 PM
whiteblaze whiteblaze is offline
Registered
 
Join Date: Apr 2017
Location: Scranton, Pennsylvania, USA
Posts: 16
Thanks: 23
Thanked 3 Times in 3 Posts
Default Re: Onan LTD100-4 Transfer switch

Ok,
Just answer my question... looked at the diagram. Looks like relays k5, k6, and k7 are voltage sensitive (see attached). I just priced the 240 version and they are $700+ a pop.
Attached Thumbnails
Click image for larger version

Name:	Screenshot_2017-10-07-19-49-31.jpg
Views:	27
Size:	164.8 KB
ID:	293082  
Reply With Quote
  #6  
Old 10-07-2017, 11:58:52 PM
MBB MBB is offline
Registered-III
 
Join Date: Apr 2009
Location: Elk Grove Village IL USA
Posts: 3,104
Thanks: 1,336
Thanked 2,445 Times in 1,300 Posts
Default Re: Onan LTD100-4 Transfer switch

I believe the voltage sensing wire has to be moved from C Phase to A or B. I believe the relays as stated on the drawing are 208/240. Someone will correct me if Im wrong.
Reply With Quote
  #7  
Old 10-08-2017, 11:26:18 AM
EricWood's Avatar
EricWood EricWood is offline
Registered-III
 
Join Date: Oct 2005
Location: West Concord, Minnesota USA
Posts: 1,888
Thanks: 235
Thanked 1,348 Times in 736 Posts
Default Re: Onan LTD100-4 Transfer switch

As MBB stated, the drawing does state in the "Note" that the coils operate on 208-240VAC.

However, as you've correctly surmised, there are still some differences. If you wanted to use this switch, I would replace the three phase voltage sensors with a single phase sensor such as this: http://time-mark.com/shop/voltage_fr...tors/16-1-h-s/
I would suspect this module is probably in the $170-$200 price range.

This device would provide you with under and overvoltage protection, with a buffer time delay to prevent rapid switching.

Per the drawing the drawing, on three phase, the only thing "C" phase provides is a single wire 7, going up to power one coil leg on sensors K6 and K7.

Adding the suggested sensor above, you would remove the three existing sensors, mount it, then:
* take wire from old K5 (L2) coil leg as one power input (originates from wire #6, "B" phase)
* take wire from old K7 (L2) coil leg as other power input (originates from wire #4 "A" phase)
* Install a jumper from the wire #6 power input on landed above in first step, to one of the Normally open contacts
* take wire from old K7 sensor output contact that goes to a K4 contact, and land on the other Normally open contact
*(NOTE: This relay module would need to be calibrated--you could do that by using variable AC power supply, or bench calibrate it using a generator capable of 240 VAC, and has adjustable voltage. Suggested settings would be: 210VAC for under volts, 260 VAC for over volts)

Also, per the drawing, it appears that the K3 instant transfer relay is voltage specific-- they are listed separately in the parts table on the drawing. If the relay does not specify 208/240 volt rating on the coil (if still legible), then that would need to be replaced. Relay K3, PN 307-1083 is still listed, at around $77.

The fact that this is a mechanically-held contactor set up on utility and generator, was a desirable feature for these old switches. When (if) you power it up, make sure that when the utility contactor closes, that the utility contactor closing coil isn't still humming. There is an adjustable cut-out switch on these, that breaks the input power to the coil, as the plunger is in motion and the mechanical latch is falling into place. Have had to adjust these more than anything else on these old LT's.

Presuming at this point that K4 is dual-voltage rated (208/240), R2 could be adjusted slightly to change the pull-in voltage level, if needed. (Again, this is best done on a bench, or isolated power test set up, to get an accurate reading. Manual spec's are it should pull in at 85-90% of rated voltage.)

Do keep in mind this is an old switch, and has multiple power relays that are normally energized all the time. Those relays on that door are all fairly expensive to replace, so take in to consideration what a new switch that size will cost, versus potential upfit and maintenance repair costs over the next several years could possibly be.
Reply With Quote
The Following 2 Users Say Thank You to EricWood For This Post:
  #8  
Old 10-08-2017, 03:49:48 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,377
Thanks: 8,348
Thanked 13,695 Times in 6,444 Posts
Default Re: Onan LTD100-4 Transfer switch

Onan did use A&B phase as a single phase system. Some of the relays could be used. But as Eric said some would have to be replaced. Costly and hard to find unless you used an updated version. The main contactor set was obsolete over twenty years ago. Last one I changed out was replaced by a Cutler Hammer set.

To me the main problem with using the old switches. You must take better care of them than you might have back in the old days. Parts can be hard to find. But on the good side there is a reason you find. 50 year old switches still working.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following User Says Thank You to Billy J Shafer For This Post:
  #9  
Old 10-10-2017, 09:58:18 AM
whiteblaze whiteblaze is offline
Registered
 
Join Date: Apr 2017
Location: Scranton, Pennsylvania, USA
Posts: 16
Thanks: 23
Thanked 3 Times in 3 Posts
Default Re: Onan LTD100-4 Transfer Switch

Thanks all... I think I see the writing on the wall with this one. If anyone is near the Scranton / Poconos (Pa) region and would like this switch, let me know. It's in fantastic condition for the age, which is why I was hoping to use it. ASCO here I come.
Reply With Quote
  #10  
Old 10-10-2017, 10:18:39 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,377
Thanks: 8,348
Thanked 13,695 Times in 6,444 Posts
Default Re: Onan LTD100-4 Transfer Switch

I would love to have it. But to far for me. Great shape and I see it has been converted. To the one screw holding the control door shut.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
  #11  
Old 10-10-2017, 02:15:09 PM
whiteblaze whiteblaze is offline
Registered
 
Join Date: Apr 2017
Location: Scranton, Pennsylvania, USA
Posts: 16
Thanks: 23
Thanked 3 Times in 3 Posts
Default Re: Onan LTD100-4 Transfer Switch

I was laughing at that myself... if it weren't close to 100 lbs, I'd ship it.
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan transfer switch. farokh Onan Generators 18 08-10-2015 08:25:36 PM
Onan Transfer Switch saggys Onan Generators 5 01-24-2015 12:07:53 AM
Onan OT 800 Transfer Switch JimH Onan Generators 12 09-23-2014 12:49:44 PM
Onan transfer switch duramax58 Onan Generators 1 09-30-2013 10:42:40 AM
onan transfer switch bswalsh55 Onan Generators 5 02-07-2013 10:00:53 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 05:26:41 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277