Onan JC 15kw Natural Gas Question


this thread has 27 replies and has been viewed 1128 times

Reply
 
Thread Tools Display Modes
  #1  
Old 04-16-2018, 07:41:13 PM
Mark82 Mark82 is offline
Registered
 
Join Date: Jun 2016
Location: Irwin, Pennsylvania
Posts: 42
Thanks: 0
Thanked 4 Times in 2 Posts
Default Onan JC 15kw Natural Gas Question

New to this and I have a question on natural gas supply for a onan jc 15kw. Right now it's set up to run on propane but I would like to run it on natural gas supply for my house but I'm not shore if my house supplies enough gas to run the generator and my furnace 100,000 btu/hr and hot water heater 35500 btu/hr everything else is electric. My gas meter is a Rockwell 175. Can some one point me in the right direction. And if I was to keep it propane how long will it roughly rum on a full load on 100 lb tank ?
Reply With Quote
Sponsored Links
  #2  
Old 04-16-2018, 08:32:23 PM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is offline
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 4,107
Thanks: 709
Thanked 2,270 Times in 1,313 Posts
Default Re: Onan jc 15kw Natural Gas question

Most of your answers will be here:

https://www.dropbox.com/s/jqxlcyu5rr...Fuels.pdf?dl=0

I don't know about your gas meter, but if the '175' part means 175,000 BTU/hr, then it's too small.
Reply With Quote
The Following User Says Thank You to Jim McIntyre For This Post:
  #3  
Old 04-16-2018, 08:51:18 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,950
Thanks: 712
Thanked 2,327 Times in 1,360 Posts
Default Re: Onan jc 15kw Natural Gas question

Mark.

I run my JB on natural gas. The natural gas in this area is supplied to the home at 60 PSI. Since I installed my JB in1970 I was always concerned about the capacity of the gas regulator which lowers the incoming pressure to about 4 inches. All out home appliances use natural gas except the electric clothes dryer. Many years ago I determined the current gas regulator capacity was in the area of 300 CFH. My JB alone draws about 120-140 CFH at full load. So for many years I was always cognizant of what appliances were on when the JB was running.

Well this past Summer, the local utility changed out the gas regulator indicating it was too old, since it was installed in 1969. So I merely asked the guy who was changing the pressure regulator if he cold substitute a larger capacity regulator. No problem. He replaced the 300 with a 500 CFH regulator. Now do not worry about this concern any more. Perhaps you can do the same. You need a copy of the Onan tech bulletin, T-015 referred to above which lists the fuel requirement for your JC and answers your question.

Last edited by Leon N.; 04-16-2018 at 08:56:03 PM. Reason: Typos
Reply With Quote
The Following User Says Thank You to Leon N. For This Post:
  #4  
Old 04-16-2018, 09:32:05 PM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is offline
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 4,107
Thanks: 709
Thanked 2,270 Times in 1,313 Posts
Default Re: Onan jc 15kw Natural Gas question

Quote:
Originally Posted by Leon N. View Post
...You need a copy of the Onan tech bulletin, T-015 referred to above which lists the fuel requirement for your JC and answers your question...

...which I provided in the link above...
Reply With Quote
The Following 2 Users Say Thank You to Jim McIntyre For This Post:
  #5  
Old 04-16-2018, 10:40:14 PM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,919
Thanks: 2
Thanked 635 Times in 448 Posts
Default Re: Onan jc 15kw Natural Gas question

255 CFH for genset + 100 CFH furnace + 35.5 tank = 390.5 total CFH

390.5 / 175 = 2.2 factor of over spec.

Now know that meters will typically flow a lot more than spec, just drop a bit more pressure. If your gas is set at 7" like here and 4" is the minimum, then you have a long way to go before dropping below minimum.

Also, your generator is not likely to run at full load.

Me, I would figure out a way to hook it up and test it while watching pressure to see what really happens.

Also the R175 is a cheap junky meter, maybe the utility would replace it if you asked.
Reply With Quote
The Following 2 Users Say Thank You to Birken Vogt For This Post:
  #6  
Old 04-16-2018, 10:47:23 PM
Motorhead's Avatar
Motorhead Motorhead is offline
Subscriber
 
Join Date: May 2007
Location: Central Coast, California
Posts: 3,897
Thanks: 1,830
Thanked 2,695 Times in 1,397 Posts
Default Re: Onan jc 15kw Natural Gas question

Quote:
Originally Posted by Birken Vogt View Post
255 CFH for genset + 100 CFH furnace + 35.5 tank = 390.5 total CFH

390.5 / 175 = 2.2 factor of over spec.

Now know that meters will typically flow a lot more than spec, just drop a bit more pressure. If your gas is set at 7" like here and 4" is the minimum, then you have a long way to go before dropping below minimum.

Also, your generator is not likely to run at full load.

Me, I would figure out a way to hook it up and test it while watching pressure to see what really happens.

Also the R175 is a cheap junky meter, maybe the utility would replace it if you asked.
I read the same thing about the Rockwell meter being junky . I went out and looked at my gas meter and it is good for 250 CFH. My JB at full load needs 126 CFH at full load. Unless I am running my 3 ton AC, I am only running 1/4 to 1/3 load.
I looked up and 1 cu.ft. is supposed to equal roughly 1000 BTU.
__________________
The Control panel
and gauges of my
7.5JB
Reply With Quote
  #7  
Old 04-17-2018, 09:25:07 AM
Mark82 Mark82 is offline
Registered
 
Join Date: Jun 2016
Location: Irwin, Pennsylvania
Posts: 42
Thanks: 0
Thanked 4 Times in 2 Posts
Default Re: Onan JC 15kw Natural Gas question

Ok thanks everyone for your information I called my gas company and they will up grade my meter for no charge

---------- Post added at 09:25:07 AM ---------- Previous post was at 09:17:29 AM ----------

I noticed people tap in at the meter to supply the generator but my meter is too far away to do that it is in the front of my property my question is can I tap it in at the garage where they line comes in and then to the generator the line coming in is an inch and a half pipe will that be sufficient? Probably going to be less than 15 feet from there. Technical bulletin says that I can use 1 inch pipe as long as it's 15 ft or under.
Reply With Quote
  #8  
Old 04-17-2018, 09:37:03 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is online now
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 17,158
Thanks: 8,884
Thanked 14,501 Times in 6,845 Posts
Default Re: Onan JC 15kw Natural Gas question

I would tell the gas company what you need. But as long as you have the correct pressure. At where you want to tap in you should be fine.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
  #9  
Old 04-17-2018, 10:50:18 AM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,919
Thanks: 2
Thanked 635 Times in 448 Posts
Default Re: Onan JC 15kw Natural Gas question

Quote:
Originally Posted by Mark82 View Post
I noticed people tap in at the meter to supply the generator but my meter is too far away to do that it is in the front of my property my question is can I tap it in at the garage where they line comes in and then to the generator the line coming in is an inch and a half pipe will that be sufficient? Probably going to be less than 15 feet from there. Technical bulletin says that I can use 1 inch pipe as long as it's 15 ft or under.
Add up the total flow for any given section of pipe such as your 1.5", generator, appliances, whatnot.

Figure the total run from the meter to the farthest appliance, including the branches of smaller pipe feeding that appliance.

Then use that length column from this chart: https://www.engineeringtoolbox.com/n...ing-d_826.html against the total in the 1.5" that you figured earlier.

This will tell you if the 1.5" pipe has excess capacity.

You also need to do the same calc with the generator branch line.

If you post the lengths of pipe we can do an example calc for you if you want.
Reply With Quote
  #10  
Old 04-17-2018, 11:26:29 AM
Mark82 Mark82 is offline
Registered
 
Join Date: Jun 2016
Location: Irwin, Pennsylvania
Posts: 42
Thanks: 0
Thanked 4 Times in 2 Posts
Default Re: Onan JC 15kw Natural Gas question

[QUOTE=Birken Vogt;1479159]Add up the total flow for any given section of pipe such as your 1.5", generator, appliances, whatnot.

Figure the total run from the meter to the farthest appliance, including the branches of smaller pipe feeding that appliance.

Then use that length column from this chart: https://www.engineeringtoolbox.com/n...ing-d_826.html against the total in the 1.5" that you figured earlier.

This will tell you if the 1.5" pipe has excess capacity.

You also need to do the same calc with the generator branch line.

If you post the lengths of pipe we can do an example calc for you if you want.[/QUOT

Okay I will bust out the tape after work and get some measurements thanks
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan 15KW JC high compression/ NG question Mike57 Onan Generators 45 01-02-2014 11:52:29 PM
Onan 15KW MDJF 3CR troubleshooting brief question BigBlockChev Onan Generators 9 12-15-2011 10:16:55 AM
15KW Onan Propane Question? Cruiser Onan Generators 17 11-19-2011 05:50:00 PM
Natural gas hook up question Bill Wilson Onan Generators 8 06-18-2009 03:12:22 AM
70s 15kw MDJF Diesel question bbuchorn Onan Generators 3 04-26-2009 11:57:43 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 10:49:32 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277