Natural gas supply to 20 Es generator


this thread has 13 replies and has been viewed 1387 times

Reply
 
Thread Tools Display Modes
  #1  
Old 09-28-2014, 10:07:39 PM
GADavis GADavis is offline
Registered
 
Join Date: Nov 2005
Location: Tennille, Georgia USA
Posts: 494
Thanks: 45
Thanked 160 Times in 122 Posts
Default Natural gas supply to 20 Es generator

Starting a new thread because the other one has gotten so long.

The local gas company now reccomends that instead of running a 125 ft. long 1&1/4" line with 5-7 " w.c. gas pressure that I should run a 1' line and they would use 2# pressure and I should install a regulator on the gen end of the line. how good would this be? Suggestions and thoughts/prices on where to buy a regulator of this size? Thanks again, I have the generator on the slab and ready to start hooking it up.
Later, Gene Davis
Reply With Quote
Sponsored Links
  #2  
Old 09-28-2014, 10:39:41 PM
MBB MBB is offline
Registered
 
Join Date: Apr 2009
Location: Elk Grove Village IL USA
Posts: 3,417
Thanks: 1,514
Thanked 3,083 Times in 1,519 Posts
Default Re: Natural gas supply to 20 Es generator

How will that effect everything else in the house. Try uscarb.com for regulator.
Reply With Quote
  #3  
Old 09-29-2014, 02:27:46 AM
Power Power is offline
Registered
 
Join Date: Aug 2011
Location: New Jersey
Posts: 5,453
Thanks: 1,260
Thanked 3,327 Times in 1,944 Posts
Default Re: Natural gas supply to 20 Es generator

I believe you will need 2! 1 at gen, 1 at entrance to house. House appliances cannot take 2#. They like around 6# WC.
As they are critical safety items, I have a STRONG preference for MADE IN USA.
There are many inexpensive regulators coming in from certain countries not known for top quality products.
Approved regulators (FM)are designed to be fail safe, so devices downstream can never be subject to overpressure.
I like a well established company with a good reputation. 3 come to mind Garretson, Fisher and Maxitrol. Plumbing supply house should be able to get them for you, otherwise Grainger, McMaster.

Last edited by Power; 09-29-2014 at 02:39:10 AM. Reason: spelling error
Reply With Quote
  #4  
Old 09-29-2014, 06:09:04 AM
Mike57 Mike57 is offline
Subscriber
 
Join Date: Sep 2013
Location: Sunnyvale, Texas, USA
Posts: 174
Thanks: 136
Thanked 101 Times in 64 Posts
Default Re: Natural gas supply to 20 Es generator

I went to a 2 psi setup for my generator, a 15JC. You'll need a regulator to reduce pressure at each appliance. They are sized according to incoming pressure(2 or 5 psi), pipe size, number of appliances, largest single appliance and total BTU requirements. Depending on your piping layout you may be able to use one for the entire house and one for the generator. My generator is at the end of my gas piping system with appliances between the meter and the genset so I had to reduce pressure at three locations, one furnace, another furnace and two hot water tanks and then the genset. They are relatively inexpensive.
I got mine at Supplyhouse.com. Maxitrol is quality equipment. Here's a link:http://www.supplyhouse.com/Maxitrol-...BTU-10701000-p
Remember to get the proper vent. Also, you can install them prior to having the meter changed over so when the gas company shows up you're all ready to go.. They will put low pressure in and out with no issues.
Reply With Quote
  #5  
Old 09-29-2014, 06:53:04 AM
GADavis GADavis is offline
Registered
 
Join Date: Nov 2005
Location: Tennille, Georgia USA
Posts: 494
Thanks: 45
Thanked 160 Times in 122 Posts
Default Re: Natural gas supply to 20 Es generator

Hopefully this will make the plan a little clearer. The gas company I guess will keep the present regulator for furnace and the clothes dryer and the line for the generator will be connected just ahead of them if I am understanding him correctly and I will install a # to W.C. " regulator with a cutoff and then a union before going into the generator enclosure. At least that is how I am understanding it. Will advise after the gas man comes and fully relates this to me. If this is the plan he recommends 1" black iron pipe above and below grade. Stay tuned.

Thanks Gene Davis
Reply With Quote
  #6  
Old 09-29-2014, 06:56:50 AM
JHFoster JHFoster is offline
Registered
 
Join Date: Mar 2005
Location: Starkville, Mississippi USA
Posts: 1,784
Thanks: 1,184
Thanked 3,016 Times in 634 Posts
Default Re: Natural gas supply to 20 Es generator

Around here a 2# system has a different meter. I have never seen both pressures ran at the same time. Therefore I have always need to put a reg. at each appliance.

Also uncoated black iron can not be used below grade (very long).
Reply With Quote
  #7  
Old 09-29-2014, 07:11:54 AM
MBB MBB is offline
Registered
 
Join Date: Apr 2009
Location: Elk Grove Village IL USA
Posts: 3,417
Thanks: 1,514
Thanked 3,083 Times in 1,519 Posts
Default Re: Natural gas supply to 20 Es generator

So the Generator is the only thing with the 2# line going to it? That sounds much better. No extra regulators inside the house needed. Do a search for Pex pipe here on the Stak there was some discussion. Most utilities in my area use plastic for gas. Pex or the like.
Reply With Quote
  #8  
Old 09-29-2014, 07:14:27 AM
Mike57 Mike57 is offline
Subscriber
 
Join Date: Sep 2013
Location: Sunnyvale, Texas, USA
Posts: 174
Thanks: 136
Thanked 101 Times in 64 Posts
Default Re: Natural gas supply to 20 Es generator

I've never seen two meters with different pressures set on a property. They'll set one 2 psi meter and then you'll set a regulator for the house ( make sure it's rated for exterior) and one at the generator to knock the pressure down. Ditto on the black pipe underground, you can't do it.
Reply With Quote
  #9  
Old 09-29-2014, 07:16:04 AM
MBB MBB is offline
Registered
 
Join Date: Apr 2009
Location: Elk Grove Village IL USA
Posts: 3,417
Thanks: 1,514
Thanked 3,083 Times in 1,519 Posts
Default Re: Natural gas supply to 20 Es generator

JHFoster There probably just installing a T before the house regulator and off the T using a different regulator for the generator. The pressure to the house is above 2 pounds before it comes in and gets regulated. Should work fine. Mike57 does the meter do the regulation or the regulator? I would guess the meters the same and the regulator is different?? I dont know.
Reply With Quote
  #10  
Old 09-29-2014, 07:46:45 AM
I like oldstuff I like oldstuff is offline
Subscriber
 
Join Date: Jan 2012
Location: Milwaukee, Wisconsin, USA
Posts: 6,260
Thanks: 1,599
Thanked 7,422 Times in 2,723 Posts
Default Re: Natural gas supply to 20 Es generator

I'm waiting for a quote from a plumber to run about 75 feet of 3/4" heavy wall copper with crimp fittings. Per the guy it will be significantly cheaper to run high pressure 2 psi with regulators on my furnace and water heater than running 1.25 inch black pipe.
Reply With Quote
  #11  
Old 09-29-2014, 07:52:35 AM
Mike57 Mike57 is offline
Subscriber
 
Join Date: Sep 2013
Location: Sunnyvale, Texas, USA
Posts: 174
Thanks: 136
Thanked 101 Times in 64 Posts
Default Re: Natural gas supply to 20 Es generator

On my setup there is a gas company regulator ahead of the meter. It takes the incoming line pressure(unknown psi) down to 2 psi and feeds the 2 psi meter. I then have 2 psi everywhere in the house. At each appliance I had to set a regulator to reduce to 7-11". Previously the gas company regulator took incoming gas pressure down to 7-11" and then fed the low pressure gas meter. The gas company simply changed a spring out in their regulator when they changed meters. I understand this setup has the generator piping originating at the meter location. The gas company can't put two pressures onto a property unless they set two separate meters, which I have never seen done.
Reply With Quote
  #12  
Old 09-29-2014, 10:20:51 AM
Andrew Mackey Andrew Mackey is offline
Moderator
 
Join Date: Nov 2004
Location: Rockaway, New Jersey USA
Posts: 14,149
Thanks: 1,992
Thanked 6,767 Times in 4,301 Posts
Default Re: Natural gas supply to 20 Es generator

Distance/friction loss at low pressure will starve your generator for fuel at WC pressures. With 2 PSI, the smaller pipe will be able to supply the volume you need, and the regulator at the end will knock down to the pressure the generator needs.

I like oldstuff - I would not use Pro-Press (TM) copper for underground supply for gas. Pro-Press fittings have been known to separate under pressure (any ground movement), wether it be frost, earth shift or construction. At 2 PSI, it creates a gas leak hazard as well. NOTE - Pro-Press seals also degrade after about 25 years of service! There is another hazard as well - different manufacturers have different fittings that are NOT compatible! I ran into this on a construction site. My boss bought fittings from a reputable supplier. After assembly, when testing we found several leaks in fitting to fitting make ups. Turns out the supplier changed his source, and the crimp bores was slightly different, allowing some fittings to blow apart or seep under pressure. re-crimping did not stop the leaks!. Here in NJ, the only copper gas supply allowed is either continuous (one piece), or silver soldered connections. All underground must be K type copper. ALL gas lines are to be identified with a yellow cover/wrapping, and must have a minimum of 1 foot of sand above and below the piping. On top of the sand cover, a yellow plastic marking tape with the words NATURAL GAS has to be laid down before covering with earth. If you use propane, the appropriate labeling is to be used.
Reply With Quote
  #13  
Old 09-29-2014, 11:58:47 AM
I like oldstuff I like oldstuff is offline
Subscriber
 
Join Date: Jan 2012
Location: Milwaukee, Wisconsin, USA
Posts: 6,260
Thanks: 1,599
Thanked 7,422 Times in 2,723 Posts
Default Re: Natural gas supply to 20 Es generator

Thanks Andrew.
The copper will be from the meter output through the house and to the garage. It won't be buried. Yes, I would prefer 1.25 iron pipe and not needing regs on the existing devices, but until plumber guy calls me back I won't know the cost differential.
Reply With Quote
  #14  
Old 09-29-2014, 01:54:49 PM
Bob Willman Bob Willman is offline
Registered
 
Join Date: Sep 2009
Location: Bowling Green, Ohio
Posts: 433
Thanks: 1
Thanked 271 Times in 173 Posts
Default Re: Natural gas supply to 20 Es generator

The gas company has a 6" high pressure line across my front lawn. All they will tell me is that it is over 100# pressure. I suspect it is several hundred pounds. There are 2 regulators between the underground line and the meter. I have 15# after the second regulator to the meter - special meter I paid for. I wanted 15# to the blacksmith shop for my 25hp oilfield engine, maybe a natural gas/oxygen torch and some day a gas forge. I had to buy the regulator for the house systems and any other downstream regulators. I believe the underground pipe is plastic with metal risers. So far all is going well.

Bob
WB8NQW
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Generator Not starting on Natural Gas sharp Generators & Electric Motors General Discussion 21 06-01-2018 05:21:02 PM
Natural gas supply line and regulator for 20 ES Gen Set GADavis Onan Generators 7 07-31-2014 10:57:27 PM
Onan Generator Fuel Supply Leon N. Onan Generators 12 11-12-2013 10:18:18 PM
New player in town supply side - Amazon Supply! PTSideshow Machine Shop and Tool Talk 1 04-25-2012 02:59:59 PM
natural gas generator bentley Generators & Electric Motors General Discussion 4 06-22-2004 04:31:41 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 04:11:22 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277