  #11  
Old 12-08-2018, 05:21:53 PM
Wayne 440 Wayne 440 is online now
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 6,743
Thanks: 423
Thanked 5,994 Times in 2,833 Posts
Default Re: Governor Adjustment

Quote:
Originally Posted by Tbirddillon View Post
...the legs aren't marked. How do I know what leg does what?
Yes they are, look on the side of the case.
Reply With Quote
Sponsored Links
  #12  
Old 12-08-2018, 05:25:03 PM
Wayne 440 Wayne 440 is online now
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 6,743
Thanks: 423
Thanked 5,994 Times in 2,833 Posts
Default Re: Governor Adjustment

Note the "AC" near the corner.
Attached Thumbnails
Click image for larger version

Name:	here.jpg
Views:	23
Size:	227.4 KB
ID:	324157  
Reply With Quote
  #13  
Old 12-08-2018, 05:40:16 PM
Tbirddillon Tbirddillon is offline
Registered
 
Join Date: Oct 2018
Location: Wilmington, Delaware
Posts: 40
Thanks: 7
Thanked 6 Times in 5 Posts
Default Re: Governor Adjustment

Ahh ok I thought it was just stating information not designating that side of it as AC. Thank you.
Reply With Quote
  #14  
Old 12-08-2018, 05:48:48 PM
Wayne 440 Wayne 440 is online now
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 6,743
Thanks: 423
Thanked 5,994 Times in 2,833 Posts
Default Re: Governor Adjustment

Each corner will probably be marked "AC", "+" or "-" respectively. Most of the time, the "AC" terminals are diagonally opposite.
Reply With Quote
The Following User Says Thank You to Wayne 440 For This Post:
  #15  
Old 12-08-2018, 08:11:35 PM
Zephyr7 Zephyr7 is online now
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,233
Thanks: 322
Thanked 671 Times in 452 Posts
Default Re: Governor Adjustment

AC May also be marked as “~”. DC out will be the usual + and -

Sometimes one corner is beveled, in which case that corner is +. The opposite corner diagonally will be - and the remaining two corners are the AC terminals. On your specific rectifier, the + terminal will be the one that is rotated 90* with respect to the other three. The other three terminals are as a described for the beveled corner example.

Bill

Last edited by Zephyr7; 12-08-2018 at 11:13:48 PM.
Reply With Quote
The Following User Says Thank You to Zephyr7 For This Post:
  #16  
Old 12-09-2018, 10:05:25 AM
dkamp dkamp is offline
eMail NOT Working
 
Join Date: Oct 2007
Location: LeClaire, Iowa, USA
Posts: 1,490
Thanks: 32
Thanked 758 Times in 498 Posts
Default Re: Governor Adjustment

Tbird -

If you happen to confuse the field + and field - wires, when you start the gen, she'll generate output, but when your load increases, the voltage will drop.

Don't ask how I know...
Reply With Quote
  #17  
Old 12-11-2018, 07:57:40 PM
Newoldstock Newoldstock is offline
Registered-III
 
Join Date: Dec 2013
Location: Toronto, Canada
Posts: 1,638
Thanks: 657
Thanked 783 Times in 423 Posts
Default Re: Governor adjustment

Quote:
Originally Posted by Vanman View Post
Lastly, (should have been first) are you still running the square finned Selenium rectifier in the control box? If so I would advise against running the set with load until it is replaced with a Silicon recrifier. If the rectifier fails, the compounding transformer will be ruined. It would have to be rewound as they are not an off the shelf component.
Vanman is right about the adjustments thats how you do it.

Replace the rectifier
Don't get clever and fuse it.
CTs much never be left open in a circuit under a load or major over voltages can happen that ruin them
If you must disconnect it because of rectifier failure short it.
YES short the CT out.
Never leave it open
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
LB Governor Adjustment jboyer1028 Antique Gas Engine Discussion 4 07-01-2014 09:04:24 AM
12 hp Reid governor adjustment Ron Haskell Oil Field Engines & Related Equipment 2 10-23-2013 10:32:11 PM
2 1/2hp Economy XK governor adjustment? bustedmp Antique Gas Engine Discussion 6 05-26-2011 06:44:41 PM
Need help on governor adjustment Donald A Smith Antique Gas Engine Discussion 2 06-18-2007 09:16:46 AM
Governor adjustment Christopher Brewer Kohler Generators 2 10-16-2004 08:21:48 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 07:09:53 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277