Kohler 20resc Natural gas


this thread has 71 replies and has been viewed 1881 times

Reply
 
Thread Tools Display Modes
  #21  
Old 11-28-2018, 02:05:06 PM
Newoldstock Newoldstock is offline
Registered-III
 
Join Date: Dec 2013
Location: Toronto, Canada
Posts: 1,638
Thanks: 657
Thanked 783 Times in 423 Posts
Default Re: Kohler 20resc Natural gas

I have no idea what things cost because that's not my job ( I work in the shut the hell up and do as you are told filthy peasant dept AKA electrical ha ha... )

Sometimes I need to hook up an Ethernet thing to a node someplace and its too far for CAT cable so I use an adapter that converts CAT to Coax and then back again.

Sometimes this is easy sometimes this is hard...
Sometimes there is old jack ass cable ( RG-11 a sort of hard service coax really thick with a steel band next too it ) from days gone by no longer in service that I tap into and use to carry the RF the mile or two I need and then switch off the Taps where ever they happen to be and go back to CAT cable for the final run.

No one knows the difference....
AS long as you have good cable you can improvise a lot of stuff...

I pushed to scrap all this and move to a LoRaw gateway.
Then we could push signal miles as long as it was line of site.
But see line one about the stupid peasents?
I forgot my place...
Reply With Quote
Sponsored Links
  #22  
Old 11-28-2018, 03:12:31 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,208
Thanks: 313
Thanked 654 Times in 440 Posts
Default Re: Kohler 20resc Natural gas

Thatís like my consulting work. People pay me for what I know. I advise them what will happen if they do what they say, they donít listen. Stuff goes wrong. Good thing I told them in writing in my report too! Sometimes they pay me again to fix what they paid to ask about the first time and didnít listen. It always costs more to redo things later but whatever, itís their money.

There are way too many dumb people out there. And ďstoopidĒ is twice as stupid as regular ďstupidĒ

Bill
Reply With Quote
  #23  
Old 12-01-2018, 08:10:51 PM
Krislu Krislu is offline
Registered
 
Join Date: Nov 2018
Location: Greenlawn, New York USA
Posts: 33
Thanks: 3
Thanked 3 Times in 2 Posts
Smile Re: Kohler 20resc Natural gas

So I added the carb heater and fuel pressure regular heater today. Supposed to be 30s coming this week so will see if they help with starting. I put a filter on the regulator to stop the spyders and bugs from clogging the vent tube. An open tube like that is asking for trouble.

Kris
Attached Thumbnails
Click image for larger version

Name:	fuel pressure regular.jpg
Views:	54
Size:	163.9 KB
ID:	323791  
Reply With Quote
  #24  
Old 12-01-2018, 08:33:27 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,208
Thanks: 313
Thanked 654 Times in 440 Posts
Default Re: Kohler 20resc Natural gas

Wow, it so shiny in there! I love when stuff is new. Seems like my usual first step working on anything is scrape away cobwebs and old oily gunk from stuff.

Where does the regulator heater mount? Iíve never used one of those.

Bill
Reply With Quote
  #25  
Old 12-01-2018, 08:57:14 PM
Krislu Krislu is offline
Registered
 
Join Date: Nov 2018
Location: Greenlawn, New York USA
Posts: 33
Thanks: 3
Thanked 3 Times in 2 Posts
Smile Re: Kohler 20resc Natural gas

I took that pic before I mounted it but it is on the left side of that pic. It mounts on the back of the regulator. I will post a pic of it mounted tomorrow.

Kris
Reply With Quote
  #26  
Old 12-01-2018, 08:58:09 PM
Mark Dieckmann Mark Dieckmann is offline
Registered-I
 
Join Date: Mar 2009
Location: Osgood, IN, USA
Posts: 123
Thanks: 34
Thanked 32 Times in 24 Posts
Default Re: Kohler 20resc Natural gas

I like the idea of the filter, however I am somewhat concerned about it’s location. The purpose of the two vent tubes on the regulator is to get the vent outlet out of the engine cooling airstream. I normally just tucked them up inside the wiring cover. For awhile they didn’t come with the tubes and it was the source of severe hunting at low speed during exercise. What you have may be fine.
Reply With Quote
  #27  
Old 12-01-2018, 09:11:30 PM
Krislu Krislu is offline
Registered
 
Join Date: Nov 2018
Location: Greenlawn, New York USA
Posts: 33
Thanks: 3
Thanked 3 Times in 2 Posts
Smile Re: Kohler 20resc Natural gas

Quote:
Originally Posted by Mark Dieckmann View Post
I like the idea of the filter, however I am somewhat concerned about itís location. The purpose of the two vent tubes on the regulator is to get the vent outlet out of the engine cooling airstream. I normally just tucked them up inside the wiring cover. For awhile they didnít come with the tubes and it was the source of severe hunting at low speed during exercise. What you have may be fine.
Mark- The install guys just left the tube sticking up like the way you see in the pic. It seems short to reach the wire cover. I don't know if the guys cut it down or not.

Kris
Reply With Quote
  #28  
Old 12-02-2018, 08:21:55 AM
Mark Dieckmann Mark Dieckmann is offline
Registered-I
 
Join Date: Mar 2009
Location: Osgood, IN, USA
Posts: 123
Thanks: 34
Thanked 32 Times in 24 Posts
Default Re: Kohler 20resc Natural gas

Did you filter both tubes? I don't think both are necessary as I think they are connected internally. One should be enough if they are.
Reply With Quote
  #29  
Old 12-02-2018, 09:12:34 AM
Krislu Krislu is offline
Registered
 
Join Date: Nov 2018
Location: Greenlawn, New York USA
Posts: 33
Thanks: 3
Thanked 3 Times in 2 Posts
Smile Re: Kohler 20resc Natural gas

Mark- No, Just the one tube. I can't see where the other tube is going. There doesn't seem to be room for that filter on the other tube. Maybe look for a smaller filter. If one exists.

Kris
Reply With Quote
  #30  
Old 12-02-2018, 02:56:50 PM
Krislu Krislu is offline
Registered
 
Join Date: Nov 2018
Location: Greenlawn, New York USA
Posts: 33
Thanks: 3
Thanked 3 Times in 2 Posts
Smile Re: Kohler 20resc Natural gas

Mark- I just saw a you tube vid where both tubes had spider crap in them so I am researching a solution for the other tube. The other tube is tucked under the wiring cover. I don't think the filter will fit in there.

Kris
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Kohler 12 Res Natural Gas Gen OS fault Trekrider2001 Kohler Generators 36 12-21-2018 04:02:28 PM
new kohler 20resc generator dean l Kohler Generators 5 12-21-2016 01:04:19 AM
Kohler RZ series (Natural gas) connections Johmurray Kohler Generators 0 10-20-2015 11:17:29 PM
Kohler 7.5C62 Hook up to Natural Gas questions CRE1992 Kohler Generators 18 11-25-2013 12:56:41 AM
Kohler natural gas regulator royvoss Kohler Generators 17 09-19-2011 07:16:10 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 04:44:16 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277