Kohler - unsteady voltage


this thread has 45 replies and has been viewed 1311 times

Reply
 
Thread Tools Display Modes
  #1  
Old 12-21-2018, 04:22:19 PM
Trekrider2001 Trekrider2001 is offline
Registered-I
 
Join Date: May 2015
Location: Woodinville, Washington
Posts: 60
Thanks: 4
Thanked 2 Times in 2 Posts
Default Kohler - unsteady voltage

During the power outage yesterday, we had lights dimming repeatedly. Sure I understand that if you throw a new load on the generator, you might see a drop and the lights dim, but there was nothing going on. I even turned the fridge off to see if it was kicking in but that did not change anything. The only thing on was to big screen plasma TV. When I paused the show, the dimming was reduced (not eliminated). I really can't understand that the TV might have such a variable power draw that the generator has a had time following the load. We have a pump in the septic tank, but it is only supposed to come on when the water level is high, then shut off when it gets to the low water setting. It certainly would not be going on and off multiple times per minute. Really, could this be the TV?
Reply With Quote
Sponsored Links
  #2  
Old 12-21-2018, 07:46:24 PM
K-Tron K-Tron is offline
Registered-III
 
Join Date: Sep 2010
Location: Huntington, NY
Posts: 1,766
Thanks: 840
Thanked 866 Times in 602 Posts
Default Re: Kohler - unsteady voltage

Depending on the size of your plasma display, they could take anywhere from 400-700watts each. What is the capacity of your generator? A 3000 watt generator would run the two televisions and the refrigeration without too much trouble, so if your unit is much larger in capacity, something is not quite right with your generator.

Chris
Reply With Quote
  #3  
Old 12-21-2018, 08:07:22 PM
Trekrider2001 Trekrider2001 is offline
Registered-I
 
Join Date: May 2015
Location: Woodinville, Washington
Posts: 60
Thanks: 4
Thanked 2 Times in 2 Posts
Default Re: Kohler - unsteady voltage

The generator is a 12Kw natural gas powered unit. Yes, I would think it has enough to handle the TV and then some.
Reply With Quote
  #4  
Old 12-21-2018, 09:39:57 PM
Trekrider2001 Trekrider2001 is offline
Registered-I
 
Join Date: May 2015
Location: Woodinville, Washington
Posts: 60
Thanks: 4
Thanked 2 Times in 2 Posts
Default Re: Kohler - unsteady voltage

Is this a governor gain adjustment problem? How do you know you have it correct?
Reply With Quote
  #5  
Old 12-22-2018, 12:40:50 AM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,031
Thanks: 7,061
Thanked 2,187 Times in 1,489 Posts
Default Re: Kohler - unsteady voltage

I wonder if the voltage regulator is failing, or has a dirty sensitivity adjustment pot...?

Might try adjusting that pot back and forth several times, maybe spray some contact cleaner in it, then set it back to it's original position and see if the problem changes or goes away.
Reply With Quote
  #6  
Old 12-22-2018, 01:02:36 AM
Thaumaturge Thaumaturge is offline
Subscriber
 
Join Date: Mar 2014
Location: Beryl, Utah USA
Posts: 4,198
Thanks: 3,274
Thanked 4,351 Times in 1,830 Posts
Default Re: Kohler - unsteady voltage

I'd be prompted to check for brush wear.Then look for old caps on AVR.
Doc
__________________
Beginning anew http://machinebuildersnetwork.com
Reply With Quote
  #7  
Old 12-22-2018, 11:53:15 AM
Trekrider2001 Trekrider2001 is offline
Registered-I
 
Join Date: May 2015
Location: Woodinville, Washington
Posts: 60
Thanks: 4
Thanked 2 Times in 2 Posts
Default Re: Kohler - unsteady voltage

Thanks. The generator is about 12 years old and about 280 hrs on the clock. For something that needs to be changed, there is no information on the net on how to change these brushes and where the voltage regulator is. This unit has the ADC controller and the manual has a description on how to control the voltage. I try and check the brushes.
Reply With Quote
  #8  
Old 12-22-2018, 12:40:01 PM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 2,274
Thanks: 2
Thanked 768 Times in 542 Posts
Default Re: Kohler - unsteady voltage

The brushes are in the far end of the generator and you have to take off the roof and sides and an air duct to get to them.

The VR is part of the ADC controller and there is an SCR pack that is the last stage of the VR in the controller box and replaceable although usually it works or it does not.

This is kind of a mysterious problem to diagnose over the internet, unfortunately.
Reply With Quote
  #9  
Old 12-22-2018, 12:52:42 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,227
Thanks: 319
Thanked 664 Times in 447 Posts
Default Re: Kohler - unsteady voltage

Do you have a space heater you can use for testing? If so, try running the space heater while you’re on generator. The heater will provide 1500 Watts of almost pure resistive load that will help to swamp any strange issues from your tv load. If the genset is more stable when the heater is added, then you probably have a stability issue (like gain on a speed control).

Bill
Reply With Quote
  #10  
Old 12-22-2018, 01:20:51 PM
Trekrider2001 Trekrider2001 is offline
Registered-I
 
Join Date: May 2015
Location: Woodinville, Washington
Posts: 60
Thanks: 4
Thanked 2 Times in 2 Posts
Default Re: Kohler - unsteady voltage

Like everything else on this generator, its a real pain to service, so before I take it all apart to "clean" the brushes, I might as well order new ones and just replace them. At 12 years on, do you think it is time? How long do brushes last anyway? I have 280 hrs on the machine which does not seem like a lot. The parts web site has a ton of brushes. Now to figure out which is the correct replacement. Not a good idea to have the generator out of service this time of year in the Pacific Northwest. 'Tis the season for power outages.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Kohler 2.5 CMZ RV with low, low voltage blaster88 Kohler Generators 6 11-13-2018 08:18:39 PM
Kohler 7.5 RMK Low voltage f150 limited Kohler Generators 28 11-10-2016 07:48:22 PM
Kohler 7.5-C61 Voltage Too Hi Need Help Glenn Ayers Kohler Generators 12 08-03-2013 11:06:42 AM
MEP-002 Unsteady Output DieselTech420 Military MEP and Aircraft Gen-Sets 16 12-08-2012 05:36:59 PM
Kohler 6.5kw low voltage surfventura Kohler Generators 15 09-12-2008 09:32:25 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 08:51:51 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277