Kohler 20RZ82 Not starting/No Fire


this thread has 30 replies and has been viewed 593 times

Reply
 
Thread Tools Display Modes
  #11  
Old 02-10-2019, 06:46:47 PM
RobbieBott RobbieBott is offline
Registered
 
Join Date: Jan 2019
Location: Rayne, Louisiana, USA
Posts: 14
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: Kohler 20RZ82 Not starting/No Fire

Would you be able to tell me what/how this selector knob works?

What would I need it to be set to for a standard 240V Single phase home?
Attached Thumbnails
Click image for larger version

Name:	IMG_0014.jpg
Views:	13
Size:	162.8 KB
ID:	328363  
Reply With Quote
Sponsored Links
  #12  
Old 02-10-2019, 07:31:00 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,208
Thanks: 313
Thanked 654 Times in 440 Posts
Default Re: Kohler 20RZ82 Not starting/No Fire

Quote:
Originally Posted by RobbieBott View Post
Would you be able to tell me what/how this selector knob works?

What would I need it to be set to for a standard 240V Single phase home?
It just picks meter options, basically what you want the meters to see. Lower text is where itís reading voltage, upper text is which leg itís reading for current (amps). You donít use the 3 phase positions on the right when itís connected for single phase.

The two lights are just set with a manual connection inside the controller to tell the operator which of the meter scales applies (the volt meter has a low-voltage scale and a high voltage scale printed on it).

To configure the generati for 120/240 split phase (single phase) output, you need to connect the 12 generator leads as shown on the diagram that should be inside the panel on the generator end housing. You might also need to adjust the voltage adjustment screw on the front of the controller a bit. You want the ď80 ampĒ breaker installed too ó the 480v configuration I think used a 30 amp breaker.

Bill
Reply With Quote
  #13  
Old 02-10-2019, 08:36:01 PM
RobbieBott RobbieBott is offline
Registered
 
Join Date: Jan 2019
Location: Rayne, Louisiana, USA
Posts: 14
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: Kohler 20RZ82 Not starting/No Fire

I just noticed that breaker said 80 on it. I also noticed that you put "80 amp" in quotes. Why is that?

I'm a bit confused as to how I can run my whole home, which currently has a 200 Amp service, on this generator, if it only has an 80 amp breaker, which being a 20kw should be more than capable of doing. Am I missing something here?.....
Reply With Quote
  #14  
Old 02-10-2019, 09:51:56 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,208
Thanks: 313
Thanked 654 Times in 440 Posts
Default Re: Kohler 20RZ82 Not starting/No Fire

Quote:
Originally Posted by RobbieBott View Post
I just noticed that breaker said 80 on it. I also noticed that you put "80 amp" in quotes. Why is that?
Just to make it stand out, no other reason. The 20RZ shipped with two different breaker options depending on the voltage configuration. 120/208/240 was an 80A breaker, 277/480 was a 30A breaker

Quote:
Originally Posted by RobbieBott View Post
Iím a bit confused as to how I can run my whole home, which currently has a 200 Amp service, on this generator, if it only has an 80 amp breaker, which being a 20kw should be more than capable of doing. Am I missing something here?.....
Your home likely never uses anywhere near the full 200A capability of your service. Average load of houses over a large area is about 1kw per house (this is the number utility companies use). If you have a transformer dedicated to your house only, itís likely 25kva (104A at 240V) or less.

I have a 20RZ on my house here, which is rated for 18kw when configured for single phase operation. With everything in my house running, I can only get yo to around 12kw or so. Your 20RZ will probably have no trouble running your entire house.

Bill
Reply With Quote
  #15  
Old 02-11-2019, 02:41:05 AM
RobbieBott RobbieBott is offline
Registered
 
Join Date: Jan 2019
Location: Rayne, Louisiana, USA
Posts: 14
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: Kohler 20RZ82 Not starting/No Fire

How many hours are these things normally good for? The one I have has 487 hrs, I'm not sure how accurate it is but as the motor runs it counts, I have yet t run it long enough to see if it's accurate.

One thing I have noticed is an emergency stop is not present on this unit. How do you stop it in an emergency. Once it is running, if I move the switch to the off position it still runs for a bit, which I will assume is a cool down period.

Also this thing is purely manual. What kind of signal does this thing look for to make it automatic? Could I use any automatic transfer switch? Or what would I need to look for?
I have a small red and black pair that is taped off inside the transfer switch, I have yet to trace it back to see where it leads. I just assume they where the signal leads at one time when the automatic switch was functional.
Reply With Quote
  #16  
Old 02-11-2019, 02:43:35 AM
RobbieBott RobbieBott is offline
Registered
 
Join Date: Jan 2019
Location: Rayne, Louisiana, USA
Posts: 14
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: Kohler 20RZ82 Not starting/No Fire

Hour meter attached.
Attached Thumbnails
Click image for larger version

Name:	IMG_0018.jpg
Views:	10
Size:	118.7 KB
ID:	328402  
Reply With Quote
  #17  
Old 02-11-2019, 02:59:21 AM
Birken Vogt Birken Vogt is online now
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 2,265
Thanks: 2
Thanked 765 Times in 541 Posts
Default Re: Kohler 20RZ82 Not starting/No Fire

Quote:
Originally Posted by RobbieBott View Post
How many hours are these things normally good for? The one I have has 487 hrs, I'm not sure how accurate it is but as the motor runs it counts, I have yet t run it long enough to see if it's accurate.
Tens of thousands for the base engine if it is maintained properly. Those hours are in line with what a normal standby set would have if pulled from a working environment after getting "too old".

There will be a small wire 3 and 4 in the wiring area somewhere. Set the switch to auto, connect them together, it starts. Disconnect them, it stops.
Reply With Quote
  #18  
Old 02-11-2019, 12:20:31 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,208
Thanks: 313
Thanked 654 Times in 440 Posts
Default Re: Kohler 20RZ82 Not starting/No Fire

Quote:
Originally Posted by RobbieBott View Post
How many hours are these things normally good for? The one I have has 487 hrs, I'm not sure how accurate it is but as the motor runs it counts, I have yet t run it long enough to see if it's accurate.
487 hours is practically new! I have two 20RZ sets, one has around 500 hours like yours and is basically new. I put in new platinum spark plugs a few years ago (there is a thread here on the Stak about that), and replaced the thermostat (which turned out to be unecassary). I did a coolant flush too. All that was just preventative maintenance though, the unit runs fine.

The other 20RZ is at my dads place. It has around 5,000 hours on it and still runs fine. Last year I replaced the brushes in the 12v alternator (which was getting flaky but is fine now), and did a collant flush. I put platinum plugs in it too maybe 10 years ago. The only thing I notice is the oil on this one is a little dirtier at oil change time. Itís never failed to start or run though and is a reliable unit.

Iíve always been told youíll reliably get about 8,000 hours on one of these before you might have to start doing some more involved maintenance. Keep up on your oil changes, do periodic coolant flush (at least every 5 years is the usual recommendation), and these gensets will last a looong time.

Bill
Reply With Quote
  #19  
Old 02-11-2019, 06:36:33 PM
RobbieBott RobbieBott is offline
Registered
 
Join Date: Jan 2019
Location: Rayne, Louisiana, USA
Posts: 14
Thanks: 2
Thanked 0 Times in 0 Posts
Default Re: Kohler 20RZ82 Not starting/No Fire

I ran the generator today hoping to try and put a load on it, but after about a min of running, The Axillary Fault light comes on and it shuts down. If I put the switch to the off position and back to run it cranks and runs fine again for about a min. What is that fault?
Reply With Quote
  #20  
Old 02-11-2019, 07:03:47 PM
Birken Vogt Birken Vogt is online now
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 2,265
Thanks: 2
Thanked 765 Times in 541 Posts
Default Re: Kohler 20RZ82 Not starting/No Fire

That is the fault that catches everything not otherwise on the display.

Usually the low coolant level switch. Check water level and/or disconnect switch and see what happens.
Reply With Quote
The Following User Says Thank You to Birken Vogt For This Post:
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Kohler 10RY62 starting issues Kohler Model 10RY62 Serial #451811 rhondabrwn Kohler Generators 2 06-23-2013 08:04:52 AM
Kohler 161T not getting fire gumsadma Magnetos, Ignition Coils and Spark Plugs 2 09-12-2011 09:14:38 AM
Kohler 5E wont fire jayjr Kohler Generators 3 05-31-2011 09:40:06 AM
Starting my 6.5 Kohler jmoorelewy Kohler Generators 2 09-08-2010 01:30:25 PM
Kohler K301 breathing fire dhiesel Small Air Cooled Gasoline Engines 10 02-11-2010 09:33:44 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 04:57:45 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277