Stuart and Stevenson Generator Help?


this thread has 15 replies and has been viewed 1380 times

Reply
 
Thread Tools Display Modes
  #1  
Old 07-11-2018, 04:04:39 PM
Arkie Arkie is offline
Registered-III
 
Join Date: Sep 2009
Location: Oklahoma USA
Posts: 1,164
Thanks: 12
Thanked 288 Times in 262 Posts
Default Stuart and Stevenson Generator Help?

Guy called and has a Stuart and Stevenson Gen, model 6GD-100, 3 phase 100 kw 320 amp, 1800 rpm.
I have not seen the unit and I suspect these are the gen head model numbers and maybe not the complete rig model number.

Says bought the rig and it will only generate 180v and can run rpm and fre up and down from 58-63hz and the voltage adjustments don't change the voltage and voltage remains at 180 volts constant.

Anyone got any idea where I can find some service or owners manuals for the unit?

Or anyone care to take a guess at the electrical issue or know anything about these rigs?

I see they are still in business out of Houston, Tx, tried a phone call and had to leave a voice mail with the power generator guy and he has not returned my call.
Reply With Quote
Sponsored Links
  #2  
Old 07-11-2018, 07:05:06 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,148
Thanks: 7,407
Thanked 2,247 Times in 1,528 Posts
Default Re: Stuart and Stevenson Generator help?

What voltage is it supposed to be? 320 amps and 100 kw works out to ~180 volts at unity power factor, or ~225 volts at the typical rating of 80% pf.

75% pf works out to ~240 volts. That would be odd! But I have seen 90% and 70%, so...
Reply With Quote
  #3  
Old 07-11-2018, 07:48:03 PM
Arkie Arkie is offline
Registered-III
 
Join Date: Sep 2009
Location: Oklahoma USA
Posts: 1,164
Thanks: 12
Thanked 288 Times in 262 Posts
Default Re: Stuart and Stevenson Generator help?

Quote:
Originally Posted by Vanman View Post
What voltage is it supposed to be? 320 amps and 100 kw works out to ~180 volts at unity power factor, or ~225 volts at the typical rating of 80% pf.

75% pf works out to ~240 volts. That would be odd! But I have seen 90% and 70%, so...
You know that is strange that they gave me a amperage and no voltage from a name tag.

Their main point being it's hung at 180 volts and the voltage controls will not change the voltage at all.
Reply With Quote
  #4  
Old 07-12-2018, 06:38:38 PM
Arkie Arkie is offline
Registered-III
 
Join Date: Sep 2009
Location: Oklahoma USA
Posts: 1,164
Thanks: 12
Thanked 288 Times in 262 Posts
Default Re: Stuart and Stevenson Generator help?

Quote:
Originally Posted by Vanman View Post
What voltage is it supposed to be? 320 amps and 100 kw works out to ~180 volts at unity power factor, or ~225 volts at the typical rating of 80% pf.

75% pf works out to ~240 volts. That would be odd! But I have seen 90% and 70%, so...
They emailed me a pic of the tag

220volts at 80% pf.

It stays at 180 with no load and won't move up or down with regulator adjustments.

Trying to communicate with (the horses mouth) Stuart and Stevenson in Houston, Tx. Not going great.
Reply With Quote
  #5  
Old 07-12-2018, 10:07:45 PM
Wayne 440 Wayne 440 is online now
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 6,860
Thanks: 426
Thanked 6,115 Times in 2,888 Posts
Default Re: Stuart and Stevenson Generator help?

Quote:
Originally Posted by Arkie View Post
...Trying to communicate with (the horses mouth) Stuart and Stevenson in Houston, Tx. Not going great.
I'm not surprised. About 20 years ago I called them and they tried to help me, but the eventual conclusion was (this may not be a 100% accurate quote, memory fades) "I have no idea, back then we made many different models, for many different buyers, and once they were out of warranty we didn't worry too much about keeping that stuff...".
Reply With Quote
  #6  
Old 07-12-2018, 11:10:08 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,148
Thanks: 7,407
Thanked 2,247 Times in 1,528 Posts
Default Re: Stuart and Stevenson Generator help?

I wonder if the generator has a manual voltage control rheostat for use when the AVR fails, and he is manipulating that control instead of the voltage adjustment on the AVR itself?
Reply With Quote
  #7  
Old 07-13-2018, 12:19:46 AM
Steve Dawkins Steve Dawkins is online now
Sponsor
 
Join Date: Feb 2005
Location: Virginia Beach, Virginia, USA
Posts: 1,048
Thanks: 743
Thanked 564 Times in 286 Posts
Default Re: Stuart and Stevenson Generator help?

Maybe the AVR board has a coarse adjustment potentiometer, and he is adjusting the fine adjustment trimmer pot on the face of the control panel. I used to set the trimmer pot to mid-position, and then adjust the coarse pot for the desired voltage. Then the trimmer could be used to fine tune the output voltage one way or the other, if necessary.
Reply With Quote
The Following User Says Thank You to Steve Dawkins For This Post:
  #8  
Old 07-13-2018, 06:34:23 AM
Arkie Arkie is offline
Registered-III
 
Join Date: Sep 2009
Location: Oklahoma USA
Posts: 1,164
Thanks: 12
Thanked 288 Times in 262 Posts
Default Re: Stuart and Stevenson Generator help?

Quote:
Originally Posted by Wayne 440 View Post
I'm not surprised. About 20 years ago I called them and they tried to help me, but the eventual conclusion was (this may not be a 100% accurate quote, memory fades) "I have no idea, back then we made many different models, for many different buyers, and once they were out of warranty we didn't worry too much about keeping that stuff...".
This is what I'm beginning to suspect also.

Seems to be the norm last few years, they want to sell new or get a service contract.

The ease of availability of real good Onan generator electrical Service manuals can sure spoil a guy.

The S&S vintage gen is about 60 miles away from me, 100 F heat, it's a new old purchase, 3 electrical guys have already told them they don't know why. I'm wondering why they did not test the unit BEFORE buying?
I'm not interested in going and wasting time with no service data or even knowing if parts can be obtained.

I have enough contact info that I can hiss the owner of the gen onto them.
Reply With Quote
  #9  
Old 07-13-2018, 07:40:04 AM
pegasuspinto pegasuspinto is offline
Registered-III
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 2,830
Thanks: 336
Thanked 1,342 Times in 871 Posts
Default Re: Stuart and Stevenson Generator help?

I wouldn't waste my time with S&S on this old set. I also wouldn't waste time looking up any service manual. This thing is probably a straight connected simple AVR likely with 6 wires. 2 to the panel knob, two for the field, 2 for sensing. Step 1, does the generator have equal voltage on all 3 phases? Yes-go on, no, generator end may be bad. Step 2, check the rotating rectifier and ohm out the exciter stator and rotor and the main field. Step 3, replace the VR. You can go with the new version of whatever is on there, or I would just probably put in a power tronics.
Reply With Quote
The Following User Says Thank You to pegasuspinto For This Post:
  #10  
Old 07-13-2018, 01:59:16 PM
Arkie Arkie is offline
Registered-III
 
Join Date: Sep 2009
Location: Oklahoma USA
Posts: 1,164
Thanks: 12
Thanked 288 Times in 262 Posts
Default Re: Stuart and Stevenson Generator help?

Quote:
Originally Posted by pegasuspinto View Post
I wouldn't waste my time with S&S on this old set. I also wouldn't waste time looking up any service manual. This thing is probably a straight connected simple AVR likely with 6 wires. 2 to the panel knob, two for the field, 2 for sensing. Step 1, does the generator have equal voltage on all 3 phases? Yes-go on, no, generator end may be bad. Step 2, check the rotating rectifier and ohm out the exciter stator and rotor and the main field. Step 3, replace the VR. You can go with the new version of whatever is on there, or I would just probably put in a power tronics.
Would you want to take a shot at working on it?
(or know anyone that would)

It's in NE Oklahoma, around Grove area I think.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
One of a Kind Stuart Compound Made From Larger Cylinders of a Stuart Triple Expansion Gil Garceau Scale Model Engineering 0 08-07-2018 10:07:00 PM
Stewart and Stevenson - Help Identifying Generator cnr0616 Vintage Diesel and Oil Engines 27 05-09-2017 05:13:55 PM
Stuart Turner P4 generator skankingiant Antique Engine Photos 5 01-19-2013 11:31:28 AM
Stuart Turner P55 35v generator Neville Bond Antique Gas Engine Discussion 0 03-25-2012 03:44:52 PM
Stuart Generator Set Paul Spence Antique Engine Archives 0 04-03-2002 10:43:08 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 08:21:18 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277