western electric generator help


this thread has 13 replies and has been viewed 1867 times

Reply
 
Thread Tools Display Modes
  #1  
Old 08-11-2013, 08:33:48 PM
Chris Wheeler Chris Wheeler is offline
Subscriber
 
Join Date: Feb 2011
Location: Pendleton, Kentucky
Posts: 492
Thanks: 0
Thanked 521 Times in 202 Posts
Default western electric generator help

Guys, I need your help. I have a Western Electric 110 volt AC generator that I don't know how to wire up. Some of the external wires were cut. It has a wire coming from each brush. These are cut. It also has 4 wires coming from the windings. How do I wire this up to an outlet. I only want to run a lightbulb for display. Also should I put a fuse in somewhere? What type would be period correct? I would also like to get a gauge and knife switch in the future. I will post pictures of my generator tomorrow. Thanks, Chris
Reply With Quote
Sponsored Links
  #2  
Old 08-11-2013, 09:17:26 PM
Chris Wheeler Chris Wheeler is offline
Subscriber
 
Join Date: Feb 2011
Location: Pendleton, Kentucky
Posts: 492
Thanks: 0
Thanked 521 Times in 202 Posts
Default Re: western electric generator help

Here you go.
Attached Thumbnails
Click image for larger version

Name:	WE generator 1.jpg
Views:	86
Size:	73.4 KB
ID:	172085   Click image for larger version

Name:	WE generator 2.jpg
Views:	102
Size:	100.1 KB
ID:	172086  
Reply With Quote
  #3  
Old 08-11-2013, 09:54:46 PM
ArodaPowerCo ArodaPowerCo is offline
Subscriber
 
Join Date: Oct 2009
Location: Whaleyville, Virginia, USA
Posts: 546
Thanks: 328
Thanked 432 Times in 216 Posts
Default Re: western electric generator help

How many brushes are there? Are they on slip rings, or a commutator? If only two on slip rings, then they most likely would be for exciting the rotor. The 4 wires coming from the field should be your AC voltage. T1, T2, T3, and T4. Sounds like a reconnectable generator, since the nameplate states 120 and 240 volt. They would connect like this...

For 120 Volts:
Connect T1 & T2 = L1
Connect T3 & T4 = L2
L1 - 120V - L2 @ full rated capacity

For 240 Volts:
T1 = L1
Connect T2 & T3 = Neutral
T4 = L2
L1 - 240V - L2
L1 - 120V - Neutral @ half capacity
L2 - 120V - Neutral @ half capacity

Hope this makes sense. I'm not a professional electrician, but my girl is. I'll double check with her to make sure terminology is right. The problem here is figuring out which of those 4 wires is which.

-Eric
Reply With Quote
  #4  
Old 08-12-2013, 07:50:31 AM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 3,088
Thanks: 292
Thanked 865 Times in 651 Posts
Default Re: western electric generator help

OK with 4 wires 120-0-120
use an ohm meter to find the pairs that go to each of the 2 coils
connect in series apply some field voltage and spin up the generator
half voltage on each side but little across the pair, one is out of phase
[subtracts rather than adds] reverse the wires of one pair.
Reply With Quote
The Following User Says Thank You to armandh For This Post:
  #5  
Old 08-12-2013, 07:06:37 PM
Chris Wheeler Chris Wheeler is offline
Subscriber
 
Join Date: Feb 2011
Location: Pendleton, Kentucky
Posts: 492
Thanks: 0
Thanked 521 Times in 202 Posts
Default Re: western electric generator help

OK. It has 2 brushes. Here they are with the ends of the wires. Where should the brush wires go?
Attached Thumbnails
Click image for larger version

Name:	We generator 3.jpg
Views:	81
Size:	101.7 KB
ID:	172158  
Reply With Quote
  #6  
Old 08-12-2013, 07:33:35 PM
John Newman, Jr.'s Avatar
John Newman, Jr. John Newman, Jr. is offline
Subscriber
 
Join Date: Apr 2005
Location: Saint Louis, Missouri, USA
Posts: 5,286
Thanks: 757
Thanked 3,237 Times in 1,653 Posts
Default Re: western electric generator help

Looks like there should be 3 brushes. I see 3 slip rings and the ID tag says it makes 110/220.
__________________
John Newman, Jr.
Saint Louis, MO

I Can Probably Fix That
Reply With Quote
  #7  
Old 08-12-2013, 09:05:27 PM
ArodaPowerCo ArodaPowerCo is offline
Subscriber
 
Join Date: Oct 2009
Location: Whaleyville, Virginia, USA
Posts: 546
Thanks: 328
Thanked 432 Times in 216 Posts
Default Re: western electric generator help

Looking at the nameplate, it says, "DC wound field". I think there is supposed to be DC voltage fed to those brushes to provide the magnetic field for the rotor. Varying the DC voltage is a means to regulate the output voltage. My guess is that the third slip ring is not used (does not appear to have ever had a brush on it), and is there because it uses a "standard" rotor. A different model of generator might have a purpose for it.

I know one of the generators in my collection has a DC field, and a regulator that senses the output voltage in order to adjust the field voltage for proper output. As for yours, I couldn't say. Just trying to offer up "trees to bark up".
Reply With Quote
  #8  
Old 08-13-2013, 12:11:07 PM
Chris Wheeler Chris Wheeler is offline
Subscriber
 
Join Date: Feb 2011
Location: Pendleton, Kentucky
Posts: 492
Thanks: 0
Thanked 521 Times in 202 Posts
Default Re: western electric generator help

That makes sense. I wonder what input voltage I need? I would assume that they originally used dry cell batteries for input voltage? I might try a 12 volt battery and see what kind of results I get.
Reply With Quote
  #9  
Old 08-13-2013, 03:21:23 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,436
Thanks: 71
Thanked 1,185 Times in 967 Posts
Default Re: western electric generator help

Probably most likely used a DC generator belted onto it to supply the field. The regulator controls the DC section (might have been as simple as a rheostat you set by hand), so that may be why it's missing along with the DC machinery.

the 12 volt plan is a good idea. See what it will do and then if it will generate, you can move on to some sort of rectifier (very cheap these days and compact, so you can hide it pretty easily so as not to detract from your display)

If all you want is to run a steady load for a display, you probably can get by just fine with a bridge rectifier and a rheostat or fixed resister and fine tune it perhaps by varying the rpm (I know it's not the "right" way to do it, varying the rpm, but if you are running lightbulbs, it won't bother them)
Reply With Quote
The Following User Says Thank You to Jim Rankin For This Post:
  #10  
Old 08-13-2013, 09:19:22 PM
ArodaPowerCo ArodaPowerCo is offline
Subscriber
 
Join Date: Oct 2009
Location: Whaleyville, Virginia, USA
Posts: 546
Thanks: 328
Thanked 432 Times in 216 Posts
Default Re: western electric generator help

I agree with Jim. A lot of older generators, especially larger ones, had a separate "exitiation" generator, and that may well have been the case with yours. It's entire purpose was to provide DC power for the field. One way you could do this in for your application would be to use an old Delco-Remy automotive generator for an exciter. That would give your setup a "period" look. They can be found in 12 volt and 6 volt models allowing you to pick the appropriate voltage level for proper output of your generator. They have two terminals. One for "Power" and one for "field". This will give you great flexibility in voltage regulation. Depending on components used for the regulator, you could end up with a set that actually produces very high quality power for not a lot of cost. The major cost will be "tinkering time".
Reply With Quote
  #11  
Old 08-14-2013, 07:25:05 AM
Chris Wheeler Chris Wheeler is offline
Subscriber
 
Join Date: Feb 2011
Location: Pendleton, Kentucky
Posts: 492
Thanks: 0
Thanked 521 Times in 202 Posts
Default Re: western electric generator help

I spun the generator last night while testing the 4 terminals. The best I got was about 12 volts AC. It did not change when I hooked a battery to the brushes. Not sure which way to go now.
Reply With Quote
  #12  
Old 08-14-2013, 09:25:50 AM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,436
Thanks: 71
Thanked 1,185 Times in 967 Posts
Default Re: western electric generator help

Sounds as if the field is not working. Did you get a spark when you touched the battery leads to the brush terminals? that would be an indication that there is a circuit through the field. Clean sliprings and recheck resistance through field (slipring to slipring) if you have not already done so.
Reply With Quote
  #13  
Old 08-14-2013, 10:34:54 AM
Chris Wheeler Chris Wheeler is offline
Subscriber
 
Join Date: Feb 2011
Location: Pendleton, Kentucky
Posts: 492
Thanks: 0
Thanked 521 Times in 202 Posts
Default Re: western electric generator help

I did get a spark when I touched the battery to the brush wire. I am going to clean the brush holders. They are somewhat rusty. These are not like modern brushes that have a wire connected directly to them. The use a piece of metal screwed into the back end of the brush. It holds it and conducts at the same time?
Reply With Quote
  #14  
Old 08-15-2013, 09:18:26 AM
Chris Wheeler Chris Wheeler is offline
Subscriber
 
Join Date: Feb 2011
Location: Pendleton, Kentucky
Posts: 492
Thanks: 0
Thanked 521 Times in 202 Posts
Default Re: western electric generator help

I took the brush holders all apart and cleaned them. I then spun the generator again and this time got up to 80.5 volts! I am on the right track for now. Thanks
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Western Electric Motor and GE DC Generator combo toddm Generators & Electric Motors General Discussion 9 02-24-2012 07:15:55 AM
Western Electric 40V generator wittenbn Unidentified Engines 5 12-28-2011 02:28:31 PM
Generator Project 1920 Dodge 4 Cyl. Side Valve and Western Electric Generator jeffery flynn Antique Gas Engine Discussion 7 05-27-2010 02:43:27 PM
Western Electric 3 phase generator David R. Fry Generators & Electric Motors General Discussion 0 01-27-2004 01:12:43 PM
Western Electric Gen Set Gary Generators & Electric Motors General Discussion 6 03-30-2002 05:36:15 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 09:31:24 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277