general genny question


this thread has 7 replies and has been viewed 1950 times

Reply
 
Thread Tools Display Modes
  #1  
Old 06-03-2007, 02:07:27 PM
Economy Bob Economy Bob is offline
Registered-III
 
Join Date: Nov 2004
Location: Milwaukee, Wisconsin
Posts: 93
Thanks: 41
Thanked 84 Times in 27 Posts
Default general genny question

When I run my generator (30 kw single phase, propane ) and I use a load of say , 1500 watts lighting and 1500 watts electric heat, where are the rest of my watts going? Am I even making them , as I am not calling for them. And is this action causeing any damage to a pretty good size generator?
Reply With Quote
Sponsored Links
  #2  
Old 06-03-2007, 02:17:52 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is online now
Moderator
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 18,779
Thanks: 10,008
Thanked 16,613 Times in 7,716 Posts
Default Re: general genny question

Your genset is just fine. You just have more power than you need.
Reply With Quote
  #3  
Old 06-03-2007, 05:21:54 PM
Economy Bob Economy Bob is offline
Registered-III
 
Join Date: Nov 2004
Location: Milwaukee, Wisconsin
Posts: 93
Thanks: 41
Thanked 84 Times in 27 Posts
Default Re: general genny question

And another question. If I am not useing 30 kw, does my fuel milage go down since the generator isnt struggling to keep up ??
Reply With Quote
  #4  
Old 06-03-2007, 06:46:10 PM
Andrew Albrecht's Avatar
Andrew Albrecht Andrew Albrecht is offline
Moderator
 
Join Date: Nov 2004
Location: Cincinnati, Ohio, USA
Posts: 506
Thanks: 8
Thanked 125 Times in 72 Posts
Images: 69
Default Re: general genny question

Less work = less fuel used. the genny is still running at the same r.p.m. all the time. It just works harder as you put more load on it. Or draw more amps. The KW rating is generally only used to tell you what the max it can do. I use to know how to figure it but i am sure someone on here can tell you your total amps available. this is a more useable number. I get a kick out of the production truck guys that come along and ask me to give them single phase 208.
__________________
I Get My Corn From A Jar
Reply With Quote
  #5  
Old 06-03-2007, 06:54:37 PM
Bill Geyer's Avatar
Bill Geyer Bill Geyer is offline
Registered-III
 
Join Date: Jul 2005
Location: Granbury, Texas, USA
Posts: 1,275
Thanks: 257
Thanked 121 Times in 82 Posts
Images: 12
Default Re: general genny question

Yes Bob, your fuel consumption will be a lot less at 3KW than at 30KW. Your engine governor will control the fuel to make more or less watts. It will use a little more fuel at 3KW than say a 4KW generator at 3KW,however.
Reply With Quote
  #6  
Old 06-03-2007, 10:29:12 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,436
Thanks: 71
Thanked 1,185 Times in 967 Posts
Default Re: general genny question

the voltage regulator controls the magnetic field strength to keep the output voltage at set point in the face of the electrical load you place on it. More electrical load requires more excitation from the regulator and more power from the engine.

On the nameplate of the generator, there should be a spec for voltage, amperage and kW. Voltage x Amperage (VA or kVA)tells you electrical capacity of the generator and watts (W or kW) tells you the engine capacity. These are not always the same. Frequently sets are built with an engine with kW equal to 80% of kVA. This is because some electrical equipment has a low power factor (kW< kVA)and takes less engine power per amp than high power factor equipment (kW ~= kVA)which takes closer to100% engine power per amp.

A diesel engine is always more efficient at part load than a comparable size gasoline engine because it can run with a "leaner" fuel mixture and doesn't have to pull air past a partially closed throttle. Fuel injected engines can more closely approach the part load efficiency of a diesel though even at full load, a gasoline or other spark ignition engine will still almost always be less efficient than the diesel.
Reply With Quote
  #7  
Old 06-04-2007, 09:05:30 AM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 3,090
Thanks: 292
Thanked 866 Times in 652 Posts
Default Re: general genny question

power is power
if you take more power out expect to put more [fuel] in.
this is seen in the throttle position under various loads.

any system has a sweet spot, an area of the best efficiency.
if the designers had their heads screwed on....
it should be in the upper half of the output range.
Reply With Quote
  #8  
Old 06-04-2007, 07:07:31 PM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is online now
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 4,519
Thanks: 867
Thanked 2,683 Times in 1,539 Posts
Default Re: general genny question

Quote:
Originally Posted by Economy Bob View Post
...where are the rest of my watts going? Am I even making them
Nope, they never existed - the governor on the engine hasn't opened up enough to have allowed the generator to generate those 'extra' watts.

Quote:
Originally Posted by Economy Bob View Post
...And is this action causeing any damage to a pretty good size generator?
LP or Gasoline sets should be just fine. (Some Diesel engines don't fare so well under extended operation at light loading.)

Quote:
Originally Posted by Economy Bob View Post
...And another question. If I am not useing 30 kw, does my fuel milage go down since the generator isnt struggling to keep up ??
Depends by what you mean by 'milage'. Your fuel consumption per hour will be less at light load than at heavy load. But, your fuel consumption per kW-hr will be higher at light load than at heavy load, since the efficiency of the engine is lower at light load.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
General Generator Question Mike Cushway Delco and other Low Voltage DC Light Plants 5 02-15-2018 07:31:13 PM
General diesel question Handyhiker1 Onan Generators 40 06-07-2017 10:07:52 PM
general question about tubing wayne57 Welding Shop 2 04-12-2013 01:09:22 PM
general question about Generator Andrew Albrecht Generators & Electric Motors General Discussion 18 07-20-2012 05:09:35 PM
Military 3kw genny starter question. FredRoary Generators & Electric Motors General Discussion 5 05-11-2005 09:39:48 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 10:12:21 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277