  #1  
Old 06-24-2008, 01:25:29 PM
porbob porbob is offline
Registered
 
Join Date: Jun 2008
Location: Bothell,Wa. US
Posts: 3
Thanks: 1
Thanked 0 Times in 0 Posts
Question Western Electric 120kw

Help!!
I have a large diesel gen/set. It's gray and on a very solid trailer. My guess is ex-Navy. The diesel runs like a watch but the gen won't gen. Any ideas, ops manuals available, service persons?

Western Electric set#82114 ks 15622 list 1

G.E 340771 type AT1 frame 954 ?y 230v 3ph

Hercules DFXH 5.75 X 6.00 C377 938

Any ideas are welcome, thanx Bob

porbob52@yahoo.com
Reply With Quote
Sponsored Links
  #2  
Old 06-25-2008, 12:09:58 AM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,436
Thanks: 71
Thanked 1,185 Times in 967 Posts
Default Re: Western Electric 120kw

First inspect the windings and brushes and sliprings or exciter rotor and field if it's a brushless set. Look for burned coils, broken wires, stuck brushes etc. You should be able to lift the brushes and ohm through the fields for continuity and check them for grounds to the frame or shaft. Diodes on the armature of a brushless generator are a common problem. If this all checks out, then the most common problem is loss of the residual magnetic field that is required to excite it. A generator with no/weak residual will show no or very low AC output voltage. If you measure AC voltages on the output with a meter, you should see balanced voltages on the phases even if only a few 10's of volts. The only exception to this would be a delta connected 120/240 3 phase stator. That will show one line-neutral voltage that's 1.73 times the other two lines.

Depending on the configuration, you should be able to flash either the main alternator field through the sliprings/brush leads if it has them, of if it's brushless, flash the exciter field. You need to match Positive and negative so the exciter/regulator doesn't buck the restored field.

The field can be flashed with the engine stopped or with it running. Safer with it stopped! Flashing is usually done using a small battery or using the starting battery through a light bulb or resister to limit current through the field. If it is running and makes voltage when you supply the field with DC, then it may build up to full voltage (quickly disconnect the flashing leads if output voltage begins rising). If voltage builds up, but falls back off immmediately when the flashing connection is broken, there's some problem with the exciter/regulator system, but the main alternator is probably good.

Be careful! It's supposed to make enough voltage to hurt/kill you if it works properly, so don't take for granted it isn't working and touch terminals etc that may have high voltages on them.
Reply With Quote
The Following User Says Thank You to Jim Rankin For This Post:
  #3  
Old 07-04-2008, 01:10:15 PM
porbob porbob is offline
Registered
 
Join Date: Jun 2008
Location: Bothell,Wa. US
Posts: 3
Thanks: 1
Thanked 0 Times in 0 Posts
Default Re: Western Electric 120kw

Thank you for the exellent instructions. I'll be back at our mine in Baker Ore. to do the tests next week or two. It's a nice set that has enjoyed good maintenance unlike some other military surplus you see. I hope this brings the 'old brute' to life again.

Bob
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Need help, Western Electric Gen Joe Musser Generators & Electric Motors General Discussion 3 01-03-2005 06:12:42 PM
8B Western Electric Phil Robinson Generators & Electric Motors General Discussion 0 08-18-2004 09:41:49 AM
IHC M 1&1/2 Western Electric 32 VOLT gen set Greg Doby Generators & Electric Motors General Discussion 1 08-08-2003 11:45:30 PM
Western Electric Gen Set Gary Generators & Electric Motors General Discussion 6 03-30-2002 05:36:15 PM
Western Electric Model G1 Warren Galliano Generators & Electric Motors General Discussion 0 03-22-2002 07:54:20 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 04:47:18 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277