Onan 30KW Diesel L634 governor setup


this thread has 30 replies and has been viewed 1684 times

Reply
 
Thread Tools Display Modes
  #1  
Old 08-19-2015, 12:55:04 PM
7mksuper 7mksuper is offline
Registered
 
Join Date: Jul 2015
Location: Alpharetta, Georgia, USA
Posts: 10
Thanks: 8
Thanked 0 Times in 0 Posts
Default Onan 30KW Diesel L634 governor setup

Hello,
I have an Onan 30KW GenSet,
Motor:
MODEL # L634D-1 / 10386C

GENERATOR:
MODEL# 30.0 DL6-15R / 14297D

I Replaced the injector pump, to get it running again, as the original sat for ten years and was gummed up to the point that it would not pass any fuel. The new pump is performing very well, and it is now running great. My question is, what is the proper procedure to set the governor and or throttle position on the new pump? it seems unlikely that simply adjusting the throttle to the 1800 RPM point is appropriate, and is likely that I should be adjusting the governor screw/spring as I advance the throttle a bit to keep it at the 1800 mark.

Any Thoughts?
Thanks all,
MK

P.S. I am looking for a copy of the operation manual 934-0125 also
Reply With Quote
Sponsored Links
  #2  
Old 08-19-2015, 06:26:44 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,370
Thanks: 8,340
Thanked 13,689 Times in 6,442 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Post an email address to get a manual.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
  #3  
Old 08-19-2015, 07:30:34 PM
7mksuper 7mksuper is offline
Registered
 
Join Date: Jul 2015
Location: Alpharetta, Georgia, USA
Posts: 10
Thanks: 8
Thanked 0 Times in 0 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Sorry for the oversight, and thanks for the response.

email is mk.colorado@outlook.com
Reply With Quote
  #4  
Old 08-19-2015, 09:16:07 PM
Motorhead's Avatar
Motorhead Motorhead is offline
Subscriber
 
Join Date: May 2007
Location: Central Coast, California
Posts: 3,408
Thanks: 1,516
Thanked 2,240 Times in 1,208 Posts
Default Re: Onan 30KW Diesel L634 governor setup

I have a smaller diesel set and the injection pump is set to just above 1800 rpm to get the 62 (+-) cycles unloaded. There is a set screw on one side of the control lever of the inj pump to speed it up and a set screw on the other side to lock it. Instead of looking for the 1800 rpm, set it to your HZ on the output.
Reply With Quote
  #5  
Old 08-19-2015, 09:33:38 PM
7mksuper 7mksuper is offline
Registered
 
Join Date: Jul 2015
Location: Alpharetta, Georgia, USA
Posts: 10
Thanks: 8
Thanked 0 Times in 0 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Yep, I have the same type of set up on the control lever, but to get 1800 rpm (About 61HZ), it is not "Centered" in the throw. It is in fact just off of what would be idle. I will get a load put on it this weekend, but it just seemed to me that if I put the lever more centered then adjusted to the correct HZ with the governor it would be a better way. I could be way wrong, and am hoping to be educated by someone here, as to the correct procedure.

Thanks,
MK
Reply With Quote
  #6  
Old 08-20-2015, 07:10:24 AM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,763
Thanks: 5,000
Thanked 5,343 Times in 2,903 Posts
Default Re: Onan 30KW Diesel L634 governor setup

If the address works, 900-0336 DL6 service manual should be in your box in a minute.
Reply With Quote
The Following 3 Users Say Thank You to Max Thompson For This Post:
  #7  
Old 08-20-2015, 07:52:53 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,370
Thanks: 8,340
Thanked 13,689 Times in 6,442 Posts
Default Re: Onan 30KW Diesel L634 governor setup

The position doesn't matter. Once it is set at the proper hertz 61 to 62 no load. That is all you need to worry about. It will take care of itself. If you want 60-60 that will take an electronic governor. Which will cost some money.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following User Says Thank You to Billy J Shafer For This Post:
  #8  
Old 08-20-2015, 08:00:53 AM
alco539 alco539 is offline
Registered
 
Join Date: Apr 2012
Location: Huntsville, Alabama
Posts: 47
Thanks: 13
Thanked 17 Times in 14 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Assuming you replaced it with the correct pump, then pretty much all you do is make sure the timing is set correctly and set the throttle to 1800 rpms. The reason I say assuming you replaced it with the correct pump is there are 2 different pumps for this engine. They will interchange just fine but will not perform the same. One of the pumps is set up with the min/max governor and the other is set up with the constant speed governor. You want the one with the constant speed governor. If you still have the old pump, compare it carefully to the new pump. Look specifically just above the high pressure output lines. On the old pump you will see a shaft sticking out maybe a couple of inches with what looks like a screw slot in the end of it. If the new one does not have that, then it is not the correct pump. If need be I can take some pictures of both to show the difference.

The bottom line is if you have the pump with the min/max governor, it will never work correctly in a generator setup. You can set it up for 1800 rpm's with no load but as soon as you drop a load on it, it will not react properly and the rpm's/frequency will drop accordingly. The more load the worse it will get. The correct pump will keep the speed relatively constant across the entire load spectrum. Don't ask me how I know this
Reply With Quote
The Following User Says Thank You to alco539 For This Post:
  #9  
Old 08-20-2015, 11:41:16 AM
MBB MBB is offline
Registered-III
 
Join Date: Apr 2009
Location: Elk Grove Village IL USA
Posts: 3,096
Thanks: 1,331
Thanked 2,426 Times in 1,292 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Sent multiple manuals this morning.
Reply With Quote
The Following 2 Users Say Thank You to MBB For This Post:
  #10  
Old 08-20-2015, 12:00:38 PM
7mksuper 7mksuper is offline
Registered
 
Join Date: Jul 2015
Location: Alpharetta, Georgia, USA
Posts: 10
Thanks: 8
Thanked 0 Times in 0 Posts
Default Re: Onan 30KW Diesel L634 governor setup

So it is not the exact part number, as the new one has an external timing adjustment, all the rest of it seems the same. it definitely has the governor adjustment screw ("shaft sticking out maybe a couple of inches with what looks like a screw slot in the end of it"). The engine runs fantastic now, and the generator is working as expected, but the throttle position was my concern, as the previous pump was dead in the middle of the throw, and this one is just off of idle, to get the 61 HZ. If this is normal, then all is good. I will put it under load, and go from there. I just want it to be correct.

I now have the the manuals, and I will read those and see if there is anything there, thank you to Max and Mike for the PDFs.

I will report after the load test.

Thanks all,
MK
Reply With Quote
  #11  
Old 08-20-2015, 01:32:41 PM
alco539 alco539 is offline
Registered
 
Join Date: Apr 2012
Location: Huntsville, Alabama
Posts: 47
Thanks: 13
Thanked 17 Times in 14 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Put it under a good load and you should hear it working harder but the speed will stay very close to the same. Drop it off and the only thing that should change is it sounds like it is no longer working hard. The frequency of the engine should not really change at all. It just grunts a little harder. It sounds like you have the right pump.

Jimmy
Reply With Quote
  #12  
Old 08-20-2015, 07:44:13 PM
Motorhead's Avatar
Motorhead Motorhead is offline
Subscriber
 
Join Date: May 2007
Location: Central Coast, California
Posts: 3,408
Thanks: 1,516
Thanked 2,240 Times in 1,208 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Quote:
Originally Posted by 7mksuper View Post
So it is not the exact part number, as the new one has an external timing adjustment, all the rest of it seems the same. it definitely has the governor adjustment screw ("shaft sticking out maybe a couple of inches with what looks like a screw slot in the end of it"). The engine runs fantastic now, and the generator is working as expected, but the throttle position was my concern, as the previous pump was dead in the middle of the throw, and this one is just off of idle, to get the 61 HZ. If this is normal, then all is good. I will put it under load, and go from there. I just want it to be correct.

I now have the the manuals, and I will read those and see if there is anything there, thank you to Max and Mike for the PDFs.

I will report after the load test.

Thanks all,

MK
Be real careful that you set the timing at STOCK specs. Those engines love to blow head gaskets.

Last edited by Motorhead; 08-20-2015 at 07:56:10 PM.
Reply With Quote
  #13  
Old 08-20-2015, 08:49:58 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,370
Thanks: 8,340
Thanked 13,689 Times in 6,442 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Except the Tech Star models. They like to blow everything.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
  #14  
Old 08-20-2015, 10:16:49 PM
Motorhead's Avatar
Motorhead Motorhead is offline
Subscriber
 
Join Date: May 2007
Location: Central Coast, California
Posts: 3,408
Thanks: 1,516
Thanked 2,240 Times in 1,208 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Quote:
Originally Posted by Billy J Shafer View Post
Except the Tech Star models. They like to blow everything.
I STILL can't figure out how "The TIGHTEST ship in the shipping business", UPS was sold that ONAN L634T/GMC chassis package car deal. They bought a BUNCH of them in 2.5 ton chassied package cars. They would send me to an airport 40 miles away when ours was fogged in in one of those. The pedal never came off of the floor board in 80 miles. On the straight-a-ways, it sat against the "High Idle" governor at 72mph for about 25 of the 40 one way miles. Sounded like they were running over 4,000 rpm. We were held to such a tight time constraint that the equipment had to take the beating. It did bother me because hammering equipment ain't my style.

Last edited by Motorhead; 08-21-2015 at 01:25:53 PM.
Reply With Quote
  #15  
Old 08-21-2015, 11:07:59 AM
Isaac-1 Isaac-1 is offline
Subscriber
 
Join Date: Aug 2008
Location: Leesville, Louisiana
Posts: 3,277
Thanks: 120
Thanked 1,153 Times in 914 Posts
Default Re: Onan 30KW Diesel L634 governor setup

My guess and it is just a guess is your new injection pump is off a 3600 rpm Techstar 50.0DL6B 2 pole version and you are running it on 30.0DL6 4 pole 1800 rpm unit. This would explain the relatively throttle position, as it would be calibrated around an expected 3600 run speed, but I don't know if timing was different on the 3600 rpm model.
Reply With Quote
  #16  
Old 08-21-2015, 03:53:43 PM
7mksuper 7mksuper is offline
Registered
 
Join Date: Jul 2015
Location: Alpharetta, Georgia, USA
Posts: 10
Thanks: 8
Thanked 0 Times in 0 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Isaac-1,
You may be correct, as there was no markings on the plate for RPM. I do not know why that was, but it is what it is. The new pump is a Onan part number, (147-0465-12) with a Mechanical advance, though I have that immobilized. I have it set at 15deg, just as the one that came off was, and it really does run great. If it comes through the load test, I have a real keeper, and only cost was a $155 pump, even if it has a low throttle position. If it fails, we may know why, but the cost to get the pump rebuilt was going to be $800+, and I did not know if that would get it running or not. if I need to, I now know it would be worth the rebuild, as everything else is good to go.

Thanks for all of the replies,
MK
Reply With Quote
  #17  
Old 08-21-2015, 05:02:07 PM
Motorhead's Avatar
Motorhead Motorhead is offline
Subscriber
 
Join Date: May 2007
Location: Central Coast, California
Posts: 3,408
Thanks: 1,516
Thanked 2,240 Times in 1,208 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Governor springs can be changed. Differences on pumps may be only where they de-fuel at high rpm.
Reply With Quote
The Following User Says Thank You to Motorhead For This Post:
  #18  
Old 08-21-2015, 05:27:15 PM
7mksuper 7mksuper is offline
Registered
 
Join Date: Jul 2015
Location: Alpharetta, Georgia, USA
Posts: 10
Thanks: 8
Thanked 0 Times in 0 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Does the pump need to be removed from the engine to replace the spring? I may try that if the load test fails.

Thanks,
MK
Reply With Quote
  #19  
Old 08-21-2015, 06:36:03 PM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,569
Thanks: 2
Thanked 498 Times in 356 Posts
Default Re: Onan 30KW Diesel L634 governor setup

http://www.biotrieb.org/fileadmin/us...nual_99009.pdf
Reply With Quote
The Following User Says Thank You to Birken Vogt For This Post:
  #20  
Old 08-21-2015, 07:45:23 PM
Motorhead's Avatar
Motorhead Motorhead is offline
Subscriber
 
Join Date: May 2007
Location: Central Coast, California
Posts: 3,408
Thanks: 1,516
Thanked 2,240 Times in 1,208 Posts
Default Re: Onan 30KW Diesel L634 governor setup

Quote:
Originally Posted by 7mksuper View Post
Does the pump need to be removed from the engine to replace the spring? I may try that if the load test fails.

Thanks,
MK
Injection pumps are very intricate and even myself, with 47 years mechanical experience, would not just jump into disassembling an injection pump unless I knew EXACTLY what I was doing. They have to worked on in a very clean enviornment and if a mistake or wrong value spring is installed, the results could be dangerously catastrophic ie, run away engine, something lets go due to too high of RPM....
Reply With Quote
The Following User Says Thank You to Motorhead For This Post:
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan 30DDA 30KW diesel generator question wireguy Onan Generators 4 10-08-2013 04:34:24 PM
onan 30kw hercules diesel 1969camaro5438 Onan Generators 6 02-10-2013 09:54:25 AM
70's kohler 30kw Diesel J.B. Castagnos Kohler Generators 12 09-27-2011 02:19:21 PM
Onan L634 - need information k-oss Onan Generators 19 08-24-2009 04:47:12 PM
Rockers for an Onan L634 R.Richard Onan Generators 0 03-31-2008 07:10:39 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 04:03:21 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277