Quick help with Onan 12.5


this thread has 113 replies and has been viewed 4056 times

Reply
 
Thread Tools Display Modes
  #61  
Old 03-19-2017, 02:15:54 PM
Ben Cowan Ben Cowan is offline
Registered-II
 
Join Date: Jun 2009
Location: RioHondo, Tx, USA
Posts: 497
Thanks: 25
Thanked 172 Times in 136 Posts
Default Re: Quick help with Onan 12.5

might as well get it. If you dont use it. youll probably help someone else by having it in hand! thats still a cheap price!
Reply With Quote
Sponsored Links
  #62  
Old 03-19-2017, 04:10:39 PM
Handyhiker1 Handyhiker1 is offline
Registered-II
 
Join Date: Jul 2014
Location: Akron, Ohio
Posts: 736
Thanks: 426
Thanked 337 Times in 176 Posts
Default Re: Quick help with Onan 12.5

I had the generator inning today for 45 minutes give or take. Got it good and warm and did some checks. The pictures are all from today.
I also turned the blower housing to the exhaust side so all the hot air goes one direction.
The one thing I noticed after it ran a while, ice formed on the intake manifold right where the carb bolts up and it tees off left and right. This one does not have the air preheater since it is dual fuel or vacuflo cooling, not sure which.
With what I saw today, I now have no problem doing whatever work is needed to this unit.
Something else I checked today, with it running and warmed up, I pulled off the crank case vent line from the intake. It still has a little vacuum on the crank case side.
So I will get the new stuff ordered for the run / stop solinoid and start doing a good cleaning inside and out. After I get it all figured out and cleaned up, I want to get the gaseous stuff to hook it up that way too.
Attached Thumbnails
Click image for larger version

Name:	0319171505.jpg
Views:	39
Size:	54.7 KB
ID:	277924   Click image for larger version

Name:	0319171454.jpg
Views:	39
Size:	57.4 KB
ID:	277925   Click image for larger version

Name:	0319171451.jpg
Views:	35
Size:	57.4 KB
ID:	277926   Click image for larger version

Name:	0319171453.jpg
Views:	43
Size:	56.2 KB
ID:	277927  

Reply With Quote
  #63  
Old 03-19-2017, 07:04:16 PM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,915
Thanks: 5,194
Thanked 5,593 Times in 2,999 Posts
Default Re: Quick help with Onan 12.5

Give him the $25. The relay and socket will cost close to $20 by the time you pay postage.

It is not worth $5 to do the work to change it over.
Reply With Quote
The Following User Says Thank You to Max Thompson For This Post:
  #64  
Old 04-01-2017, 03:36:30 PM
Handyhiker1 Handyhiker1 is offline
Registered-II
 
Join Date: Jul 2014
Location: Akron, Ohio
Posts: 736
Thanks: 426
Thanked 337 Times in 176 Posts
Default Re: Quick help with Onan 12.5

I installed the new style relay today and now rhe generator won't start. I believe it is a fuel problem but not sure. Question, for testing, would it hurt to run a jumper 12 volt hot wire to the coil? I would only do this for a short time just to get it running then start my trouble shooting once it runs.
Reply With Quote
  #65  
Old 04-01-2017, 04:14:56 PM
nothingbutdarts nothingbutdarts is offline
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 2,573
Thanks: 5,679
Thanked 1,239 Times in 820 Posts
Default Re: Quick help with Onan 12.5

Before I would do that, I would check that you are getting voltage to the + side of the coil while cranking and that the propane electric solenoid valve is getting voltage and is actually opening up.
Just my thoughts.
Reply With Quote
The Following User Says Thank You to nothingbutdarts For This Post:
  #66  
Old 04-02-2017, 04:03:35 PM
Handyhiker1 Handyhiker1 is offline
Registered-II
 
Join Date: Jul 2014
Location: Akron, Ohio
Posts: 736
Thanks: 426
Thanked 337 Times in 176 Posts
Default Re: Quick help with Onan 12.5

Okay, I have it down to a wiring issue. Actually a low voltage issue. The big problem I have is that my set has an over temp sensor that is wired in to the centrifugal points somehow. I have looked at the diagram for JC units and mine is not wired like that. I looked at 967-0500 books and mine is different. I am only getting 2.5 volts at the centrifugal points at the bell housing. I have it traced back to the control box and have the same voltage there. I need to do more tracing but the wire diagram is about useless as it is different then mine. Does anyone have a different wire diagram for the latter JC units? Mine is spec AB.

Forgot to add, If I apply 12 volts to the centrifugal switch the unit runs and stops as it should. So my problem is just getting 12 volts to feed the switch.
Reply With Quote
  #67  
Old 04-02-2017, 09:34:22 PM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,915
Thanks: 5,194
Thanked 5,593 Times in 2,999 Posts
Default Re: Quick help with Onan 12.5

According to the build sheet, the correct diagram should be attached.
Attached Files
File Type: pdf 12.5JC-3R 10259AB.pdf (19.6 KB, 19 views)
File Type: pdf 612-5564 C.pdf (159.6 KB, 29 views)
Reply With Quote
The Following 2 Users Say Thank You to Max Thompson For This Post:
  #68  
Old 04-03-2017, 06:12:55 AM
Handyhiker1 Handyhiker1 is offline
Registered-II
 
Join Date: Jul 2014
Location: Akron, Ohio
Posts: 736
Thanks: 426
Thanked 337 Times in 176 Posts
Thumbs up Re: Quick help with Onan 12.5

Max,
I am not out by the generator right now but that sure looks like the right diagram. Thank you very much. Maybe now I can figure this thing out.
Reply With Quote
  #69  
Old 04-03-2017, 05:00:53 PM
Handyhiker1 Handyhiker1 is offline
Registered-II
 
Join Date: Jul 2014
Location: Akron, Ohio
Posts: 736
Thanks: 426
Thanked 337 Times in 176 Posts
Default Re: Quick help with Onan 12.5

Life is GOOD!! With the new diagram I was able to trace the wires and find the bad connection. Fixed it and now all is good. It starts as it should and stops with the switch. The starter cut off works when it starts and all seems good. Now I have 2 more things to get and then tune up and clean up. I still need to find a new main jet for the bottom of the float bowl and I discovered that the exhaust flange that connects the header pipe to the manifold is broken in 2 places 180 degrees from each other. I did pull the AMP meter pick up that was in the connection box and will list it in the used parts thread.
I am sure I will have more questions as I continue to go through the unit but I do want to say a HUGE thanks to all who have helped me get this unit up and working.
Reply With Quote
  #70  
Old 04-03-2017, 06:38:03 PM
nothingbutdarts nothingbutdarts is offline
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 2,573
Thanks: 5,679
Thanked 1,239 Times in 820 Posts
Default Re: Quick help with Onan 12.5

Just curious, where did you find the bad wire/connection to be at?

Very nice that you got it fixed!!!
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan Quick CCK remote prime question. Flintstone Onan Generators 41 02-19-2015 05:21:28 AM
Onan JC quick connect natural gas hose vlocci Onan Generators 9 09-15-2014 03:27:03 PM
Quick question on Onan DJB rcowboy Onan Generators 7 02-10-2013 04:38:03 PM
Found a good quick way to strip paint from an Onan CCK carburetor Motorhead Onan Generators 14 02-06-2013 03:21:37 AM
Need quick help!! Kman Oil Field Engines 4 02-03-2008 07:21:14 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 06:23:49 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277