Propane line for Onan 30KW


this thread has 29 replies and has been viewed 770 times

Reply
 
Thread Tools Display Modes
  #1  
Old 02-03-2017, 10:53:34 PM
nothingbutdarts nothingbutdarts is offline
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 1,727
Thanks: 3,780
Thanked 672 Times in 477 Posts
Default Propane line for Onan 30KW

I had a guy out from my propane co, I have about 125' of line to run from tank to generator, the guy said they run this kind of flex line that will only be 1/2" but they run it at 50 psi in it. Then once it get my pipe set from the generator out of the building which will be about 5' long of 3/4" black pipe they will put in a reducing regulator on my pipe. He said the 1/2" line will supply plenty of volume. I told him the generator needs up to 220 CFH at full load, he said no problem!

Does this sound like it will work? Thanks!
Reply With Quote
Sponsored Links
  #2  
Old 02-04-2017, 12:02:22 AM
lokay5's Avatar
lokay5 lokay5 is offline
Subscriber
 
Join Date: May 2007
Location: Merlin, Oregon
Posts: 1,252
Thanks: 3,228
Thanked 730 Times in 459 Posts
Default Re: Propane line for Onan 30KW

They'll install a 10PSI primary regulator at the tank and an 11"WC regulator at the 3/4" pipe. Not to worry. You'll have plenty of fuel.
Reply With Quote
The Following 2 Users Say Thank You to lokay5 For This Post:
  #3  
Old 02-04-2017, 03:19:33 AM
Ray Lynch Ray Lynch is offline
Subscriber
 
Join Date: Aug 2014
Location: New Windsor, New York, USA
Posts: 327
Thanks: 265
Thanked 185 Times in 122 Posts
Default Re: Propane line for Onan 30KW

Darts
What model set is it?
Ray
Reply With Quote
  #4  
Old 02-04-2017, 04:00:35 AM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 12,977
Thanks: 315
Thanked 4,615 Times in 3,374 Posts
Default Re: Propane line for Onan 30KW

Sounds like a 12 JC, 15JC is ~290k btu/hr

No real experience, but 10 psi is the highest I've heard of for a propane line.
Would think at 50 psi if line breaks and ignites it starts sounding like a flame thrower, all but not liquid.

Remember reading at cold temps high pressure can cause vapor to liquefy in the line. Not good, at very least causes surging in pressure in the following reg as liquid passes thru it and vaporizes. Think I read 10 psi eliminates that possibility (for most of the 48 states). Looking at a propane temp/pressure chart, propane at 10 psi can be can be ~ minus 21 deg F before it liquefies , at 50 psi it'll liquify at ~ plus 28 degs F. Maybe you can bury it deep , but think about the above ground pipe and reg. May get cold where you are and especially a mile up.
http://virtualmark.net/wx/pressure.htm

Got to run the real numbers but suspect you'll never run out of fuel at 10 psi. That's about 20 X normal 11 inches propane pressure. GUESSING at 10 psi you can lose 9 psi in the line (90% pressure loss) and reg at end of line will still be able to provide 11 inches of pressure for the demand reg. See what min input pressure for reg at end of line is (before demand reg).

Last edited by len k; 02-04-2017 at 05:07:34 AM.
Reply With Quote
  #5  
Old 02-04-2017, 05:47:22 AM
Gunny Gunny is offline
Subscriber
 
Join Date: Feb 2005
Location: North Carolina
Posts: 3,517
Thanks: 1,251
Thanked 1,430 Times in 920 Posts
Default Re: Propane line for Onan 30KW

Yes, that should work fine.

For a long run, best to go with a smaller diameter line at high pressure and reduce it at the point of usage.

Sounds like your gas supplier is on top of his game.
Reply With Quote
The Following User Says Thank You to Gunny For This Post:
  #6  
Old 02-04-2017, 10:13:48 AM
nothingbutdarts nothingbutdarts is offline
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 1,727
Thanks: 3,780
Thanked 672 Times in 477 Posts
Default Re: Propane line for Onan 30KW

It's an SK.

Thanks for the replies guys! I could have been off on the 50 psi and apologize for that. I didn't write it down and the memory kind of sucks!
Reply With Quote
  #7  
Old 02-04-2017, 10:30:29 AM
Gunny Gunny is offline
Subscriber
 
Join Date: Feb 2005
Location: North Carolina
Posts: 3,517
Thanks: 1,251
Thanked 1,430 Times in 920 Posts
Default Re: Propane line for Onan 30KW

No problem.

In this case, 10 psi can be considered high pressure and would still be good.
Reply With Quote
The Following 2 Users Say Thank You to Gunny For This Post:
  #8  
Old 02-04-2017, 10:33:58 AM
nothingbutdarts nothingbutdarts is offline
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 1,727
Thanks: 3,780
Thanked 672 Times in 477 Posts
Default Re: Propane line for Onan 30KW

Quote:
Originally Posted by len k View Post
Sounds like a 12 JC, 15JC is ~290k btu/hr
Len k, in my T-015 gaseous manual dated 2-1987 it lists a 15.0 JC @
110 CFH @ full load for both liquid and vapor LPG. Just putting that out there.

Now for natural gas it lists a 15.0 JC @ 255CFH.
Reply With Quote
  #9  
Old 02-04-2017, 11:11:49 AM
Troll Troll is offline
Registered-I
 
Join Date: Jan 2017
Location: Farmington, Illinois
Posts: 204
Thanks: 1
Thanked 89 Times in 47 Posts
Default Re: Propane line for Onan 30KW

The largest LPG sets I run are 50kw and they are plumbed with 1/2" steel pipe up to 100' distant from the actual gensets. The pipe pressure is @ 10psi leaving the pressure vessel, (tank) and reduced to 11"wc at the building entrance. We also incorporate heated atomizers in the line right before the secondary regulation, (pressure reduction) takes place to ensure smooth gaseous fuel flow in cold weather. We do not bring liquid, or high pressure gas into the facility and this allows for less expense for automated fire alarm and atmosphere monitoring for the end user.

Forgot to mention the interior piping is upsized to either 1.250" above 30kw, or upsized to .750" below 25kw as per specification(s). I always run the larger 1.250" for everything interior so well covered regardless. Remember to wrap all buried piping with environmental covering designed for this purpose and keep it deep enough it won't be crushed by weight, or dug up accidently by someone in the future. I'm not involved with residential installs so always trench 36" deep.
Reply With Quote
The Following User Says Thank You to Troll For This Post:
  #10  
Old 02-04-2017, 11:52:23 AM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,135
Thanks: 2
Thanked 313 Times in 233 Posts
Default Re: Propane line for Onan 30KW

Do you install anodes on your steel pipe? I always use poly pipe with anodeless risers for new underground. Too hard to properly protect and recoat steel fittings plus it is just harder to work with in general. I would not install without anodes any more than I would install a buried tank without anodes and that requires periodic monitoring.
Reply With Quote
  #11  
Old 02-04-2017, 11:59:56 AM
Troll Troll is offline
Registered-I
 
Join Date: Jan 2017
Location: Farmington, Illinois
Posts: 204
Thanks: 1
Thanked 89 Times in 47 Posts
Default Re: Propane line for Onan 30KW

We are precluded from using plastic pipe although I would use it or copper in my own installation. We have to bond to the perimeter counterpoise installed around structures but there is no anode, (sacrificial or permanent) installed I'm aware of.
Reply With Quote
  #12  
Old 02-04-2017, 12:32:56 PM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,135
Thanks: 2
Thanked 313 Times in 233 Posts
Default Re: Propane line for Onan 30KW

When we installed metallic pipe or tank underground it had to be insulated from building/electrical ground, etc. by a dielectric union or else the anode is kind of worthless.

If the steel pipe is bonded to building ground then it (least noble metal) becomes the sacrificial anode by default to the whole structure if there is any failure in the coating.

At least that is my understanding although using plastic almost exclusively, I have never paid much attention to it really.

Do you know of or use any better method to coat joints, elbows, and tool marks than that darn tape that never seems to stretch tight correctly? I always thought something sprayed or dipped in tar would be much better. Old pipes were coated in about 5/16" of tar it seemed. More substantial than the current plastic coatings.

I wonder why they say no plastic. Do they enforce this on natural gas utilities also? Seems like they might tell them to go pound sand.
Reply With Quote
  #13  
Old 02-04-2017, 12:57:26 PM
Troll Troll is offline
Registered-I
 
Join Date: Jan 2017
Location: Farmington, Illinois
Posts: 204
Thanks: 1
Thanked 89 Times in 47 Posts
Default Re: Propane line for Onan 30KW

I don't know why the ban on plastic either but I can't vary from the designer's drawings to go by. I can upsize pipe, and sometimes routing, but that's about it. Everything is grounded in these installs. Lots, and lots of money expended in copper and grounding type conduit connectors. The tape, or wrap as it's called comes from a couple of different vendors and it is specific to the application and does work quite well. It is a self bonding/sealing product and we set the pipe onto roller stands and spin the pipe rather than do it solely by hand. The joints are heat sealed with this same tape and heating attachment which is an open "C" shape to get around top and bottom. the wrap literally melts together and becomes an effective seal. Water or electrolysis damage has never been a problem I've seen so far. We don't use clamps but rather "CadWeld" the connections to the counterpoise and each site does have a monitor well for measuring resistance but I don't do any monitoring.
Reply With Quote
  #14  
Old 02-04-2017, 12:58:56 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 12,977
Thanks: 315
Thanked 4,615 Times in 3,374 Posts
Default Re: Propane line for Onan 30KW

Since house underground copper water pipes are bonded to utility grid and if your steel gas pipe is also bonded to that grid , there's your corrosion battery right there. Even if YOU don't have copper pipe your neighbor may. So would need some kind of anode. Here code says need to bond utility gas pipe to power ground, not sure what it has to say about propane tanks.


Seem to remember someone saying above 2 psi in HOUSE is not legal, too much fire risk if pipe breaks.
Reply With Quote
  #15  
Old 02-04-2017, 02:05:14 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 2,589
Thanks: 3,007
Thanked 1,017 Times in 713 Posts
Default Re: Propane line for Onan 30KW

Here there is a dielectric fitting between the incoming utility natural gas supply and the meter, and thus the building piping system. At first glance it looks like they didn't have the correct fitting on the truck, and so installed a 3/4" - 1" elbow, then used a bushing back down to 3/4", but that bushing is actually plastic.

I've thought about putting a dielectric union on the water line where the copper comes up out of the ground at the house, specifically to stop current flow between my interior bonded copper pipes and my line going to the meter at the street, and the rest of the water company's piping.

Code doesn't seem to require bonding the gas lines here, though they are effectively bonded as soon as even one electrically grounded appliance is connected.

Years ago, worked on a stop light job on Pacific Coast Highway, RIGHT on the beach. Specs required Rigid conduit be used exlusively (galvanized steel, like water pipe). This was being laid in trenches dug in the salt water saturated sand. I'm sure all of those cables are now just direct burial, the conduit having long since rotted away around them lol.
Reply With Quote
  #16  
Old 02-04-2017, 02:57:08 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 12,977
Thanks: 315
Thanked 4,615 Times in 3,374 Posts
Default Re: Propane line for Onan 30KW

Been told in a building code wants gas pipes bonded to utility ground. Rational is not have voltage difference between gas pipes and water pipes, in case someone is touching both at once. Voltage difference can come from bad wiring, fault or lightning. Seems dielectric at the meter could co-exist with that rule, but it would likely arc over during a lightning strike. Then seems you have to worry about melting the dielectric and having a gas leak at the point of arcing ( ignition source)
Reply With Quote
  #17  
Old 02-04-2017, 03:54:59 PM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,135
Thanks: 2
Thanked 313 Times in 233 Posts
Default Re: Propane line for Onan 30KW

Certainly interior building gas pipes are made of metal and bonded to all other metal in the building but they are not immersed in anything.

When I worked in the gas industry the single dielectric union was placed where the gas pipe came up outside and made connection to the building. So the pipe outside was (hopefully) floating to prevent electrolysis, and certainly not part of a battery. There should be no arc in a lightning strike because the interior pipe would all be at the same potential as the rest of the building and flow out on the electrical grounding system. If there was a problem the dielectric union is outside where it can be seen and dealt with, not buried interior somewhere.

The building department did not seem to care what we did with outside pipe so we were pretty much left to follow what seemed like reasonable practice.

I like the idea of a heat fused wrap. If done properly the pipe in the ground should be no wetter than the pipe inside the building. I just find it hard to imagine any coating being maintained over the years.

There is no way to bond a buried propane tank to building ground and also follow the manufacturer's instructions for cathodic protection.
Reply With Quote
  #18  
Old 02-04-2017, 04:03:04 PM
Jim Marcozzi Jim Marcozzi is offline
Registered-I
 
Join Date: Nov 2013
Location: Hempfield, PA, USA
Posts: 387
Thanks: 25
Thanked 180 Times in 103 Posts
Default Re: Propane line for Onan 30KW

Can you run the flexible metal pipe inside of a piece of PEX so that it doesn't come in contact with the soil?
Reply With Quote
  #19  
Old 02-04-2017, 04:21:57 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,002
Thanks: 541
Thanked 1,723 Times in 1,035 Posts
Default Re: Propane line for Onan 30KW

Len K not sure why you say there is a corrosion battery between the buried copper water pipe and the steel natural gas line. At this location, the incoming utility line neutral is grounded to the buried copper water pipe. The incoming steel natural gas line is NOT bonded directly to the utility neutral. However, I measured zero resistance between the kitchen gas stove frame and the 110 volt ground pin at a receptacle outlet.

Recently, the gas company came by and buried a sacrificial anode in the ground adjacent to the outdoor gas meter and connected it to the 40 psi steel gas pipe coming out of the ground to their gas meter. Around here they no longer use steel gas lines to the new homes. It is all plastic now. In fact in some areas around here, the gas mains in the street are being replaced with plastic piping.

If I thought of it, I would like to have asked them if there is a dielectric unioun somewhere in the steel gas line. I hope their anti corrosion anode will also protect my inch and one half BI gas piping to my generator shed.
Reply With Quote
  #20  
Old 02-04-2017, 04:53:59 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 12,977
Thanks: 315
Thanked 4,615 Times in 3,374 Posts
Default Re: Propane line for Onan 30KW

Just saying the iron gas pipe, copper water pipe and earth form a galvanic cell.
IF there is any electrical connection between the 2 pipes for current to flow thru then galvanic corrosion of steel pipe will occur.

I have no idea if gas company routinely uses dielectric at meter. Easy enough to test with an ohm meter. I didn't notice a dielectric at our place, but it's all painted over. Steel underground pipe to street is plastic coated. Was told gas company spent about a day cutting a ~ 14 inch dia hole thru paving near the meter and installed an anode on their line.

I know sometimes instead of an anode for corrosion protection they use a DC power supply. But maybe that is more for long pipe line installations, so you still have enough protective voltage at end of the line WRT earth.

Interesting side note, if a dielectric is used at water meter I believe code requires a jumper across it. Defeats the purpose of dielectric there.

In another application I worry about rusting of some old steel sign poles that were grounded to building power ground several years ago. Same for iron water pipe to street. Luckily nearest building that might have underground copper pipe is across street and hopefully resistance of earth is high.

Last edited by len k; 02-04-2017 at 07:48:52 PM.
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Propane or natural gas feed line for 6kw generator torque454 Carburetors, Mixers, Fuel Pumps and fuel delivery 0 01-08-2015 02:22:38 PM
Towmotor Propane Line Nat Wheatley Antique Gas Engine Discussion 7 05-03-2012 01:52:29 PM
Converting 30KW DMT from liquid propane to vapor? norcalpablo Generators & Motors General Discussion 12 11-25-2011 09:46:31 AM
Propane fuel line freezing! Need your opinion! Arkie Generators & Motors General Discussion 20 01-25-2010 11:01:46 AM
Size NG/Propane line to 7.5JB: temporary w peterson 54 Onan Generators 8 10-29-2008 01:48:59 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 02:33:25 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277