Propane line for Onan 30KW


this thread has 29 replies and has been viewed 1034 times

Reply
 
Thread Tools Display Modes
  #1  
Old 02-03-2017, 10:53:34 PM
nothingbutdarts nothingbutdarts is online now
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 2,600
Thanks: 5,783
Thanked 1,250 Times in 824 Posts
Default Propane line for Onan 30KW

I had a guy out from my propane co, I have about 125' of line to run from tank to generator, the guy said they run this kind of flex line that will only be 1/2" but they run it at 50 psi in it. Then once it get my pipe set from the generator out of the building which will be about 5' long of 3/4" black pipe they will put in a reducing regulator on my pipe. He said the 1/2" line will supply plenty of volume. I told him the generator needs up to 220 CFH at full load, he said no problem!

Does this sound like it will work? Thanks!
Reply With Quote
Sponsored Links
  #2  
Old 02-04-2017, 12:02:22 AM
lokay5's Avatar
lokay5 lokay5 is offline
Subscriber
 
Join Date: May 2007
Location: Merlin, Oregon
Posts: 1,361
Thanks: 3,533
Thanked 794 Times in 498 Posts
Default Re: Propane line for Onan 30KW

They'll install a 10PSI primary regulator at the tank and an 11"WC regulator at the 3/4" pipe. Not to worry. You'll have plenty of fuel.
Reply With Quote
The Following 2 Users Say Thank You to lokay5 For This Post:
  #3  
Old 02-04-2017, 03:19:33 AM
Ray Lynch Ray Lynch is offline
Subscriber
 
Join Date: Aug 2014
Location: New Windsor, New York, USA
Posts: 494
Thanks: 333
Thanked 325 Times in 206 Posts
Default Re: Propane line for Onan 30KW

Darts
What model set is it?
Ray
Reply With Quote
  #4  
Old 02-04-2017, 04:00:35 AM
len k len k is online now
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 15,875
Thanks: 427
Thanked 5,748 Times in 4,175 Posts
Default Re: Propane line for Onan 30KW

Sounds like a 12 JC, 15JC is ~290k btu/hr

No real experience, but 10 psi is the highest I've heard of for a propane line.
Would think at 50 psi if line breaks and ignites it starts sounding like a flame thrower, all but not liquid.

Remember reading at cold temps high pressure can cause vapor to liquefy in the line. Not good, at very least causes surging in pressure in the following reg as liquid passes thru it and vaporizes. Think I read 10 psi eliminates that possibility (for most of the 48 states). Looking at a propane temp/pressure chart, propane at 10 psi can be can be ~ minus 21 deg F before it liquefies , at 50 psi it'll liquify at ~ plus 28 degs F. Maybe you can bury it deep , but think about the above ground pipe and reg. May get cold where you are and especially a mile up.
http://virtualmark.net/wx/pressure.htm

Got to run the real numbers but suspect you'll never run out of fuel at 10 psi. That's about 20 X normal 11 inches propane pressure. GUESSING at 10 psi you can lose 9 psi in the line (90% pressure loss) and reg at end of line will still be able to provide 11 inches of pressure for the demand reg. See what min input pressure for reg at end of line is (before demand reg).

Last edited by len k; 02-04-2017 at 05:07:34 AM.
Reply With Quote
  #5  
Old 02-04-2017, 05:47:22 AM
Gunny Gunny is offline
Subscriber
 
Join Date: Feb 2005
Location: North Carolina
Posts: 3,695
Thanks: 1,567
Thanked 1,585 Times in 1,008 Posts
Default Re: Propane line for Onan 30KW

Yes, that should work fine.

For a long run, best to go with a smaller diameter line at high pressure and reduce it at the point of usage.

Sounds like your gas supplier is on top of his game.
Reply With Quote
The Following User Says Thank You to Gunny For This Post:
  #6  
Old 02-04-2017, 10:13:48 AM
nothingbutdarts nothingbutdarts is online now
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 2,600
Thanks: 5,783
Thanked 1,250 Times in 824 Posts
Default Re: Propane line for Onan 30KW

It's an SK.

Thanks for the replies guys! I could have been off on the 50 psi and apologize for that. I didn't write it down and the memory kind of sucks!
Reply With Quote
  #7  
Old 02-04-2017, 10:30:29 AM
Gunny Gunny is offline
Subscriber
 
Join Date: Feb 2005
Location: North Carolina
Posts: 3,695
Thanks: 1,567
Thanked 1,585 Times in 1,008 Posts
Default Re: Propane line for Onan 30KW

No problem.

In this case, 10 psi can be considered high pressure and would still be good.
Reply With Quote
The Following 2 Users Say Thank You to Gunny For This Post:
  #8  
Old 02-04-2017, 10:33:58 AM
nothingbutdarts nothingbutdarts is online now
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 2,600
Thanks: 5,783
Thanked 1,250 Times in 824 Posts
Default Re: Propane line for Onan 30KW

Quote:
Originally Posted by len k View Post
Sounds like a 12 JC, 15JC is ~290k btu/hr
Len k, in my T-015 gaseous manual dated 2-1987 it lists a 15.0 JC @
110 CFH @ full load for both liquid and vapor LPG. Just putting that out there.

Now for natural gas it lists a 15.0 JC @ 255CFH.
Reply With Quote
  #9  
Old 02-04-2017, 11:11:49 AM
Troll's Avatar
Troll Troll is offline
Subscriber
 
Join Date: Jan 2017
Location: Farmington, Illinois
Posts: 869
Thanks: 22
Thanked 513 Times in 267 Posts
Default Re: Propane line for Onan 30KW

The largest LPG sets I run are 50kw and they are plumbed with 1/2" steel pipe up to 100' distant from the actual gensets. The pipe pressure is @ 10psi leaving the pressure vessel, (tank) and reduced to 11"wc at the building entrance. We also incorporate heated atomizers in the line right before the secondary regulation, (pressure reduction) takes place to ensure smooth gaseous fuel flow in cold weather. We do not bring liquid, or high pressure gas into the facility and this allows for less expense for automated fire alarm and atmosphere monitoring for the end user.

Forgot to mention the interior piping is upsized to either 1.250" above 30kw, or upsized to .750" below 25kw as per specification(s). I always run the larger 1.250" for everything interior so well covered regardless. Remember to wrap all buried piping with environmental covering designed for this purpose and keep it deep enough it won't be crushed by weight, or dug up accidently by someone in the future. I'm not involved with residential installs so always trench 36" deep.
Reply With Quote
The Following User Says Thank You to Troll For This Post:
  #10  
Old 02-04-2017, 11:52:23 AM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 1,808
Thanks: 2
Thanked 585 Times in 417 Posts
Default Re: Propane line for Onan 30KW

Do you install anodes on your steel pipe? I always use poly pipe with anodeless risers for new underground. Too hard to properly protect and recoat steel fittings plus it is just harder to work with in general. I would not install without anodes any more than I would install a buried tank without anodes and that requires periodic monitoring.
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Propane or natural gas feed line for 6kw generator torque454 Carburetors, Mixers, Fuel Pumps and fuel delivery 0 01-08-2015 02:22:38 PM
Towmotor Propane Line Nat Wheatley Antique Gas Engine Discussion 7 05-03-2012 01:52:29 PM
Converting 30KW DMT from liquid propane to vapor? norcalpablo Generators & Electric Motors General Discussion 12 11-25-2011 09:46:31 AM
Propane fuel line freezing! Need your opinion! Arkie Generators & Electric Motors General Discussion 20 01-25-2010 11:01:46 AM
Size NG/Propane line to 7.5JB: temporary w peterson 54 Onan Generators 8 10-29-2008 01:48:59 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 07:14:47 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277